- Platform information:
- Hardware: Raspberry PI
- OS: openhabian
- Java Runtime Environment: openjdk version “11.0.11” 2021-04-20 LTS
- openHAB version: openHAB 3.1.0
- Issue of the topic: I want to access my SMA Inverter Tripower 8000 using the modbus binding. The log of ModbusSlaveConnectionFactoryImpl tells, that initially a connection was established but on subsequent connects it always reports “connect timed out”. My inverter does not use the default password “0000” for user “User”. Can anybody tell me if an authentication is required that the binding can communicate with the inverter and if so, how can I configure it?
- Please post configurations (if applicable):
- Things configuration related to the issue
Bridge modbus:tcp:sma "SMA" @ "Modbus" [ host="192.168.178.29", port=502, id=3, connectMaxTries=3] {
// SMA Inverter Device Type
Bridge poller DevType [ start=30053, length=4, refresh=5000, type="input" ] {
Thing data type [ readStart="30053", readValueType="uint32" ]
// SMA Inverter Status
Bridge poller SMA_Status [ start=30201, length=36, refresh=6000, type="input" ] {
Thing data status [ readStart="30201", readValueType="int32" ]
Thing data Grid_Contactor [ readStart="30217", readValueType="int32" ]
Thing data Max_Power [ readStart="30231", readValueType="int32" ]
Thing data Set_Max_Power [ readStart="30233", readValueType="int32" ]
// SMA Inverter Operation
Bridge poller SMA_Operation [ start=33001, length=36, refresh=6000, type="input" ] {
Thing data Standby [ readStart="33001", readValueType="uint32" ]
Thing data Betrieb [ readStart="33003", readValueType="uint32" ]
// SMA Inverter Temperatur
Bridge poller SMA_Temp_Innen [ start=30953, length=2, refresh=6000, type="input" ] {
Thing data Temp1 [ readStart="30954", readValueType="int16", readTransform="JS(divide10.js)" ]
Bridge poller SMA_Temp_Kuehl [ start=34113, length=2, refresh=6000, type="input" ] {
Thing data Temp2 [ readStart="34114", readValueType="int16", readTransform="JS(divide10.js)" ]
// SMA Inverter Yield
Bridge poller Yield [ start=30517, length=16, refresh=5000, type="input" ] {
Thing data Day_Yield [ readStart="30517", readValueType="int64", readTransform="JS(divide1000.js)" ]
Thing data Total_Yield [ readStart="30529", readValueType="int32", readTransform="JS(divide1000.js)" ]
// SMA Inverter Power Section A
Bridge poller power_a [ start=30769, length=20, refresh=5000, type="input" ] {
Thing data current_input [ readStart="30769", readValueType="int32", readTransform="JS(smalimit1000.js)" ]
Thing data voltage_input [ readStart="30771", readValueType="uint32", readTransform="JS(smalimit100A.js)" ]
Thing data power_west [ readStart="30773", readValueType="int32", readTransform="JS(smalimit1000.js)"]
Thing data active_power [ readStart="30775", readValueType="int32", readTransform="JS(smalimit1000.js)" ]
Thing data active_powerWatt [ readStart="30775", readValueType="int32", readTransform="JS(smalimit.js)" ]
Thing data power_L1 [ readStart="30777", readValueType="int32", readTransform="JS(smalimit1000.js)" ]
Thing data power_L2 [ readStart="30779", readValueType="int32", readTransform="JS(smalimit1000.js)" ]
Thing data power_L3 [ readStart="30781", readValueType="int32", readTransform="JS(smalimit1000.js)" ]
Thing data volt_G1 [ readStart="30783", readValueType="uint32", readTransform="JS(smalimit100A.js)" ]
Thing data volt_G2 [ readStart="30785", readValueType="uint32", readTransform="JS(smalimit100A.js)" ]
Thing data volt_G3 [ readStart="30787", readValueType="uint32", readTransform="JS(smalimit100A.js)"]
// SMA Inverter Power B
Bridge poller power_b [ start=30957, length=8, refresh=5000, type="input" ] {
Thing data currentB_input [ readStart="30957", readValueType="int32", readTransform="JS(smalimit1000.js)" ]
Thing data voltageB_input [ readStart="30959", readValueType="int32", readTransform="JS(smalimit100.js)" ]
Thing data power_east [ readStart="30961", readValueType="int32", readTransform="JS(smalimit1000.js)" ]
Bridge poller SMA_Status_Operate [ start=40029, length=4, refresh=5000, type="holding" ] {
Thing data operatestatus [ readStart="40029", readValueType="uint32" ]
Bridge poller SunSpecTest [ start=40200, length=4, refresh=5000, type="holding" ] {
Thing data Amp [ readStart="40200", readValueType="int16" ]
Bridge poller SMA_Betriebszeit [ start=30521, length=8, refresh=5000, type="input" ] {
Thing data Betriebszeit [ readStart="30521", readValueType="uint64", readTransform="JS(divide3600.js)" ]
Thing data Einspeisezeit [ readStart="30525", readValueType="uint64", readTransform="JS(divide3600.js)" ]
- Sitemap configuration related to the issue
- Rules code related to the issue
- Services configuration related to the issue
- If logs where generated please post these here using code fences:
2021-07-22 14:35:10.836 [DEBUG] [rt.modbus.internal.ModbusManagerImpl] - bundle org.openhab.core.io.transport.modbus:3.1.0 (302)[org.openhab.core.io.transport.modbus.internal.ModbusManagerImpl] : BundleComponentActivator : ComponentHolder created.
2021-07-22 14:35:10.852 [DEBUG] [rt.modbus.internal.ModbusManagerImpl] - bundle org.openhab.core.io.transport.modbus:3.1.0 (302)[org.openhab.core.io.transport.modbus.internal.ModbusManagerImpl] : Component created: DS=DS13, implementation=org.openhab.core.io.transport.modbus.internal.ModbusManagerImpl, immediate=false, default-enabled=true, factory=null, configuration-policy=optional, activate=activate, deactivate=deactivate, modified=null configuration-pid=[transport.modbus]
2021-07-22 14:35:11.201 [DEBUG] [rt.modbus.internal.ModbusManagerImpl] - bundle org.openhab.core.io.transport.modbus:3.1.0 (302)[org.openhab.core.io.transport.modbus.internal.ModbusManagerImpl(351)] : Changed state from satisfied to active
2021-07-22 14:35:11.214 [TRACE] [ternal.ModbusManagerImpl.PollMonitor] - POLL MONITOR: scheduledThreadPoolExecutor queue size: 0, remaining space 2147483647. Active threads 1
2021-07-22 14:35:11.217 [TRACE] [ternal.ModbusManagerImpl.PollMonitor] - </POLL MONITOR>
2021-07-22 14:35:12.032 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Registering poll task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_INPUT_REGISTERS, start=30053, length=4, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@acdde7, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@acdde7] with period 5000 using initial delay 0
2021-07-22 14:35:12.046 [DEBUG] [rt.modbus.internal.ModbusManagerImpl] - Executing scheduled (5000ms) poll task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_INPUT_REGISTERS, start=30053, length=4, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@acdde7, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@acdde7]. Current millis: 1626957312046
2021-07-22 14:35:12.056 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Starting new operation with task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_INPUT_REGISTERS, start=30053, length=4, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@acdde7, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@acdde7]. Trying to get connection [operation ID c545bda6-b5e4-4b12-b76f-169f91c87cb4]
2021-07-22 14:35:12.060 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Executing task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_INPUT_REGISTERS, start=30053, length=4, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@acdde7, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@acdde7] (oneOff=false)! Waiting for connection. Idle connections for this endpoint: 0, and active 0 [operation ID c545bda6-b5e4-4b12-b76f-169f91c87cb4]
2021-07-22 14:35:12.063 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Registered poll task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_INPUT_REGISTERS, start=30053, length=4, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@acdde7, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@acdde7] with period 5000 using initial delay 0
2021-07-22 14:35:12.100 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Registering poll task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_INPUT_REGISTERS, start=30201, length=36, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@16e3a07, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@16e3a07] with period 6000 using initial delay 0
2021-07-22 14:35:12.103 [DEBUG] [rt.modbus.internal.ModbusManagerImpl] - Executing scheduled (6000ms) poll task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_INPUT_REGISTERS, start=30201, length=36, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@16e3a07, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@16e3a07]. Current millis: 1626957312103
2021-07-22 14:35:12.104 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Registered poll task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_INPUT_REGISTERS, start=30201, length=36, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@16e3a07, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@16e3a07] with period 6000 using initial delay 0
2021-07-22 14:35:12.109 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Starting new operation with task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_INPUT_REGISTERS, start=30201, length=36, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@16e3a07, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@16e3a07]. Trying to get connection [operation ID 6622532d-67ed-4cbe-8351-88497256bec6]
2021-07-22 14:35:12.113 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Executing task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_INPUT_REGISTERS, start=30201, length=36, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@16e3a07, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@16e3a07] (oneOff=false)! Waiting for connection. Idle connections for this endpoint: 0, and active 0 [operation ID 6622532d-67ed-4cbe-8351-88497256bec6]
2021-07-22 14:35:12.127 [TRACE] [ing.ModbusSlaveConnectionFactoryImpl] - Created connection TCPMasterConnection [m_Socket=null, m_Timeout=3000, m_Connected=false, m_Address=/192.168.178.29, m_Port=502, m_ModbusTransport=null, m_ConnectTimeoutMillis=10000, rtuEncoded=false] for endpoint ModbusIPSlaveEndpoint [address=192.168.178.29, port=502]
2021-07-22 14:35:12.145 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Registering poll task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_INPUT_REGISTERS, start=33001, length=36, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@1cf1481, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@1cf1481] with period 6000 using initial delay 0
2021-07-22 14:35:12.148 [DEBUG] [rt.modbus.internal.ModbusManagerImpl] - Executing scheduled (6000ms) poll task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_INPUT_REGISTERS, start=33001, length=36, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@1cf1481, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@1cf1481]. Current millis: 1626957312148
2021-07-22 14:35:12.152 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Starting new operation with task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_INPUT_REGISTERS, start=33001, length=36, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@1cf1481, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@1cf1481]. Trying to get connection [operation ID c66f0e6b-93a8-41df-8b08-a7579648e315]
2021-07-22 14:35:12.156 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Executing task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_INPUT_REGISTERS, start=33001, length=36, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@1cf1481, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@1cf1481] (oneOff=false)! Waiting for connection. Idle connections for this endpoint: 0, and active 1 [operation ID c66f0e6b-93a8-41df-8b08-a7579648e315]
2021-07-22 14:35:12.161 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Registered poll task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_INPUT_REGISTERS, start=33001, length=36, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@1cf1481, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@1cf1481] with period 6000 using initial delay 0
2021-07-22 14:35:12.193 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Registering poll task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_INPUT_REGISTERS, start=30953, length=2, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@70cefd, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@70cefd] with period 6000 using initial delay 0
2021-07-22 14:35:12.195 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Registered poll task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_INPUT_REGISTERS, start=30953, length=2, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@70cefd, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@70cefd] with period 6000 using initial delay 0
2021-07-22 14:35:12.196 [DEBUG] [rt.modbus.internal.ModbusManagerImpl] - Executing scheduled (6000ms) poll task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_INPUT_REGISTERS, start=30953, length=2, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@70cefd, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@70cefd]. Current millis: 1626957312195
2021-07-22 14:35:12.200 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Starting new operation with task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_INPUT_REGISTERS, start=30953, length=2, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@70cefd, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@70cefd]. Trying to get connection [operation ID 8d653481-795b-4877-9cc6-320a95386542]
2021-07-22 14:35:12.205 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Executing task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_INPUT_REGISTERS, start=30953, length=2, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@70cefd, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@70cefd] (oneOff=false)! Waiting for connection. Idle connections for this endpoint: 0, and active 1 [operation ID 8d653481-795b-4877-9cc6-320a95386542]
2021-07-22 14:35:12.239 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Registering poll task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_INPUT_REGISTERS, start=34113, length=2, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@670c3c, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@670c3c] with period 6000 using initial delay 0
2021-07-22 14:35:12.241 [DEBUG] [rt.modbus.internal.ModbusManagerImpl] - Executing scheduled (6000ms) poll task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_INPUT_REGISTERS, start=34113, length=2, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@670c3c, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@670c3c]. Current millis: 1626957312241
2021-07-22 14:35:12.244 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Starting new operation with task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_INPUT_REGISTERS, start=34113, length=2, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@670c3c, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@670c3c]. Trying to get connection [operation ID 00bb2c28-908b-4c9a-a1ee-aa53cd1f6359]
2021-07-22 14:35:12.246 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Registered poll task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_INPUT_REGISTERS, start=34113, length=2, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@670c3c, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@670c3c] with period 6000 using initial delay 0
2021-07-22 14:35:12.248 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Executing task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_INPUT_REGISTERS, start=34113, length=2, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@670c3c, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@670c3c] (oneOff=false)! Waiting for connection. Idle connections for this endpoint: 0, and active 1 [operation ID 00bb2c28-908b-4c9a-a1ee-aa53cd1f6359]
2021-07-22 14:35:11.930 [INFO ] [ab.event.ThingStatusInfoChangedEvent] - Thing 'modbus:tcp:sma' changed from UNINITIALIZED to INITIALIZING
2021-07-22 14:35:11.975 [INFO ] [ab.event.ThingStatusInfoChangedEvent] - Thing 'modbus:tcp:sma' changed from INITIALIZING to ONLINE
2021-07-22 14:35:11.996 [INFO ] [ab.event.ThingStatusInfoChangedEvent] - Thing 'modbus:poller:sma:DevType' changed from UNINITIALIZED to INITIALIZING
2021-07-22 14:35:12.070 [INFO ] [ab.event.ThingStatusInfoChangedEvent] - Thing 'modbus:poller:sma:DevType' changed from INITIALIZING to ONLINE
2021-07-22 14:35:12.078 [INFO ] [ab.event.ThingStatusInfoChangedEvent] - Thing 'modbus:poller:sma:SMA_Status' changed from UNINITIALIZED to INITIALIZING
2021-07-22 14:35:12.113 [INFO ] [ab.event.ThingStatusInfoChangedEvent] - Thing 'modbus:poller:sma:SMA_Status' changed from INITIALIZING to ONLINE
2021-07-22 14:35:12.121 [INFO ] [ab.event.ThingStatusInfoChangedEvent] - Thing 'modbus:poller:sma:SMA_Operation' changed from UNINITIALIZED to INITIALIZING
2021-07-22 14:35:12.166 [INFO ] [ab.event.ThingStatusInfoChangedEvent] - Thing 'modbus:poller:sma:SMA_Operation' changed from INITIALIZING to ONLINE
2021-07-22 14:35:12.171 [INFO ] [ab.event.ThingStatusInfoChangedEvent] - Thing 'modbus:poller:sma:SMA_Temp_Innen' changed from UNINITIALIZED to INITIALIZING
2021-07-22 14:35:12.201 [INFO ] [ab.event.ThingStatusInfoChangedEvent] - Thing 'modbus:poller:sma:SMA_Temp_Innen' changed from INITIALIZING to ONLINE
2021-07-22 14:35:12.216 [INFO ] [ab.event.ThingStatusInfoChangedEvent] - Thing 'modbus:poller:sma:SMA_Temp_Kuehl' changed from UNINITIALIZED to INITIALIZING
2021-07-22 14:35:12.418 [INFO ] [ab.event.ThingStatusInfoChangedEvent] - Thing 'modbus:poller:sma:SMA_Temp_Kuehl' changed from INITIALIZING to ONLINE
2021-07-22 14:35:12.497 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Registering poll task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_INPUT_REGISTERS, start=30517, length=16, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@15761ed, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@15761ed] with period 5000 using initial delay 0
2021-07-22 14:35:12.500 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Registered poll task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_INPUT_REGISTERS, start=30517, length=16, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@15761ed, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@15761ed] with period 5000 using initial delay 0
2021-07-22 14:35:12.571 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Registering poll task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_INPUT_REGISTERS, start=30769, length=20, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@8dd130, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@8dd130] with period 5000 using initial delay 0
2021-07-22 14:35:12.582 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Registered poll task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_INPUT_REGISTERS, start=30769, length=20, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@8dd130, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@8dd130] with period 5000 using initial delay 0
2021-07-22 14:35:12.627 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Registering poll task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_INPUT_REGISTERS, start=30957, length=8, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@ecedba, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@ecedba] with period 5000 using initial delay 0
2021-07-22 14:35:12.630 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Registered poll task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_INPUT_REGISTERS, start=30957, length=8, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@ecedba, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@ecedba] with period 5000 using initial delay 0
2021-07-22 14:35:12.668 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Registering poll task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_MULTIPLE_REGISTERS, start=40029, length=4, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@16f7, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@16f7] with period 5000 using initial delay 0
2021-07-22 14:35:12.672 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Registered poll task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_MULTIPLE_REGISTERS, start=40029, length=4, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@16f7, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@16f7] with period 5000 using initial delay 0
2021-07-22 14:35:12.715 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Registering poll task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_MULTIPLE_REGISTERS, start=40200, length=4, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@ea143f, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@ea143f] with period 5000 using initial delay 0
2021-07-22 14:35:12.719 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Registered poll task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_MULTIPLE_REGISTERS, start=40200, length=4, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@ea143f, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@ea143f] with period 5000 using initial delay 0
2021-07-22 14:35:12.759 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Registering poll task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_INPUT_REGISTERS, start=30521, length=8, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@180b2a5, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@180b2a5] with period 5000 using initial delay 0
2021-07-22 14:35:12.762 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Registered poll task BasicPollTask [getEndpoint=ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], request=ModbusReadRequestBlueprint [slaveId=3, functionCode=READ_INPUT_REGISTERS, start=30521, length=8, maxTries=3], getResultCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@180b2a5, getFailureCallback()=org.openhab.binding.modbus.handler.ModbusPollerThingHandler$ReadCallbackDelegator@180b2a5] with period 5000 using initial delay 0
2021-07-22 14:35:12.437 [INFO ] [ab.event.ThingStatusInfoChangedEvent] - Thing 'modbus:poller:sma:Yield' changed from UNINITIALIZED to INITIALIZING
2021-07-22 14:35:12.517 [INFO ] [ab.event.ThingStatusInfoChangedEvent] - Thing 'modbus:poller:sma:Yield' changed from INITIALIZING to ONLINE
2021-07-22 14:35:12.532 [INFO ] [ab.event.ThingStatusInfoChangedEvent] - Thing 'modbus:poller:sma:power_a' changed from UNINITIALIZED to INITIALIZING
2021-07-22 14:35:12.588 [INFO ] [ab.event.ThingStatusInfoChangedEvent] - Thing 'modbus:poller:sma:power_a' changed from INITIALIZING to ONLINE
2021-07-22 14:35:13.826 [INFO ] [ab.event.ThingStatusInfoChangedEvent] - Thing 'modbus:data:sma:SMA_Betriebszeit:Betriebszeit' changed from INITIALIZING to ONLINE
2021-07-22 14:35:13.831 [INFO ] [ab.event.ThingStatusInfoChangedEvent] - Thing 'modbus:data:sma:SMA_Betriebszeit:Einspeisezeit' changed from UNINITIALIZED to INITIALIZING
2021-07-22 14:35:13.849 [INFO ] [ab.event.ThingStatusInfoChangedEvent] - Thing 'modbus:data:sma:SMA_Betriebszeit:Einspeisezeit' changed from INITIALIZING to ONLINE
2021-07-22 14:35:22.152 [WARN ] [ing.ModbusSlaveConnectionFactoryImpl] - connect try 1/3 error: connect timed out. Connection TCPMasterConnection [m_Socket=Socket[unconnected], m_Timeout=3000, m_Connected=false, m_Address=/192.168.178.29, m_Port=502, m_ModbusTransport=null, m_ConnectTimeoutMillis=10000, rtuEncoded=false]. Endpoint ModbusIPSlaveEndpoint [address=192.168.178.29, port=502]
2021-07-22 14:35:22.215 [TRACE] [ing.ModbusSlaveConnectionFactoryImpl] - Waited 60ms (interConnectDelayMillis 0ms, interTransactionDelayMillis 60ms) before connecting disconnected connection TCPMasterConnection [m_Socket=Socket[unconnected], m_Timeout=3000, m_Connected=false, m_Address=/192.168.178.29, m_Port=502, m_ModbusTransport=null, m_ConnectTimeoutMillis=10000, rtuEncoded=false] for endpoint ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], to allow delay between connections re-connects
2021-07-22 14:35:32.222 [WARN ] [ing.ModbusSlaveConnectionFactoryImpl] - connect try 2/3 error: connect timed out. Connection TCPMasterConnection [m_Socket=Socket[unconnected], m_Timeout=3000, m_Connected=false, m_Address=/192.168.178.29, m_Port=502, m_ModbusTransport=null, m_ConnectTimeoutMillis=10000, rtuEncoded=false]. Endpoint ModbusIPSlaveEndpoint [address=192.168.178.29, port=502]
2021-07-22 14:35:32.286 [TRACE] [ing.ModbusSlaveConnectionFactoryImpl] - Waited 60ms (interConnectDelayMillis 0ms, interTransactionDelayMillis 60ms) before connecting disconnected connection TCPMasterConnection [m_Socket=Socket[unconnected], m_Timeout=3000, m_Connected=false, m_Address=/192.168.178.29, m_Port=502, m_ModbusTransport=null, m_ConnectTimeoutMillis=10000, rtuEncoded=false] for endpoint ModbusIPSlaveEndpoint [address=192.168.178.29, port=502], to allow delay between connections re-connects
2021-07-22 14:35:42.303 [WARN ] [ing.ModbusSlaveConnectionFactoryImpl] - connect try 3/3 error: connect timed out. Connection TCPMasterConnection [m_Socket=Socket[unconnected], m_Timeout=3000, m_Connected=false, m_Address=/192.168.178.29, m_Port=502, m_ModbusTransport=null, m_ConnectTimeoutMillis=10000, rtuEncoded=false]. Endpoint ModbusIPSlaveEndpoint [address=192.168.178.29, port=502]
2021-07-22 14:35:42.312 [ERROR] [ing.ModbusSlaveConnectionFactoryImpl] - re-connect reached max tries 3, throwing last error: connect timed out. Connection TCPMasterConnection [m_Socket=Socket[unconnected], m_Timeout=3000, m_Connected=false, m_Address=/192.168.178.29, m_Port=502, m_ModbusTransport=null, m_ConnectTimeoutMillis=10000, rtuEncoded=false]. Endpoint ModbusIPSlaveEndpoint [address=192.168.178.29, port=502]