rule "Boiler Start/Stop"
when
Member of HeaterValve changed
then
if(BoilerAndCirculation.state > 0) {
BoilerAndCirculation.persist
YourSwitch.sendCommand(ON)
}
else {
YourSwitch.sendCommand(OFF)
}
end
I think you will need to use if(triggeringItem.state > 0) and not BoilerAndCirculation.state as this is a switch item not a number.
Maybe like this:
rule "persistOnEveryChange"
when
Member of persistOnEveryChange changed
then
if(triggeringItem.state > 0) {
triggeringItem.persist
BoilerAndCirculation.sendCommand(ON)
}
else {
BoilerAndCirculation.sendCommand(OFF)
}
end
Im pretty sure im close, but the switch doesnt trip, only manually in OH Controlpanel, and when I mouseover the group in the rule in visual I get all the states for the group etc…
rule "Boiler Start/Stop"
when
Member of HeaterValveGroup changed
then
if(HeaterValveGroup.state > 0) {
HeaterValveGroup.persist
BoilerAndCirculation.sendCommand(ON)
}
else {
BoilerAndCirculation.sendCommand(OFF)
}
end
2020-05-10 18:35:34.000 [ome.event.ItemCommandEvent] - Item 'Dagligstue_ActualTemp_Lox_V' received command 25.2 °C
2020-05-10 18:35:34.019 [nt.ItemStatePredictedEvent] - Dagligstue_ActualTemp_Lox_V predicted to become 25.2 °C
2020-05-10 18:36:04.210 [ome.event.ItemCommandEvent] - Item 'Dagligstue_ActualTemp_Lox_V' received command 25.2 °C
2020-05-10 18:36:04.233 [nt.ItemStatePredictedEvent] - Dagligstue_ActualTemp_Lox_V predicted to become 25.2 °C
2020-05-10 18:36:34.384 [vent.ItemStateChangedEvent] - Stue_2_Valve changed from 80 to 0
2020-05-10 18:36:34.395 [ome.event.ItemCommandEvent] - Item 'BoilerAndCirculation' received command OFF
2020-05-10 18:36:34.440 [nt.ItemStatePredictedEvent] - BoilerAndCirculation predicted to become OFF
2020-05-10 18:36:34.466 [ome.event.ItemCommandEvent] - Item 'Dagligstue_ActualTemp_Lox_V' received command 25.2 °C
2020-05-10 18:36:34.477 [nt.ItemStatePredictedEvent] - Dagligstue_ActualTemp_Lox_V predicted to become 25.2 °C
2020-05-10 18:37:04.525 [vent.ItemStateChangedEvent] - Trappe_ActualTemp changed from 19.3 °C to 19.1 °C
2020-05-10 18:37:04.603 [vent.ItemStateChangedEvent] - Dagligstue_Mode changed from BOOST to AUTOMATIC
2020-05-10 18:37:04.615 [ome.event.ItemCommandEvent] - Item 'Dagligstue_ActualTemp_Lox_V' received command 25.2 °C
2020-05-10 18:37:04.639 [nt.ItemStatePredictedEvent] - Dagligstue_ActualTemp_Lox_V predicted to become 25.2 °C
2020-05-10 18:37:34.798 [vent.ItemStateChangedEvent] - Sovevaerelse_ActualTemp changed from 21.9 °C to 21.8 °C
2020-05-10 18:37:34.840 [ome.event.ItemCommandEvent] - Item 'Dagligstue_ActualTemp_Lox_V' received command 25.2 °C
2020-05-10 18:37:34.851 [nt.ItemStatePredictedEvent] - Dagligstue_ActualTemp_Lox_V predicted to become 25.2 °C
2020-05-10 18:38:05.002 [ome.event.ItemCommandEvent] - Item 'Dagligstue_ActualTemp_Lox_V' received command 25.2 °C
2020-05-10 18:38:05.021 [nt.ItemStatePredictedEvent] - Dagligstue_ActualTemp_Lox_V predicted to become 25.2 °C
2020-05-10 18:38:16.655 [hingStatusInfoChangedEvent] - 'hue:0220:ecb5fa1ed4d2:16' changed from OFFLINE: Hue bridge reports light as not reachable. to ONLINE
2020-05-10 18:38:35.166 [vent.ItemStateChangedEvent] - Spisestue_ActualTemp changed from 24.6 °C to 24.5 °C
2020-05-10 18:38:35.262 [ome.event.ItemCommandEvent] - Item 'Dagligstue_ActualTemp_Lox_V' received command 25.2 °C
2020-05-10 18:38:35.281 [nt.ItemStatePredictedEvent] - Dagligstue_ActualTemp_Lox_V predicted to become 25.2 °C
2020-05-10 18:38:56.826 [hingStatusInfoChangedEvent] - 'hue:0220:ecb5fa1ed4d2:27' changed from ONLINE to OFFLINE: Hue bridge reports light as not reachable.
2020-05-10 18:39:05.382 [vent.ItemStateChangedEvent] - Stue_2_Valve changed from 0 to 80
2020-05-10 18:39:05.390 [ome.event.ItemCommandEvent] - Item 'BoilerAndCirculation' received command OFF
2020-05-10 18:39:05.420 [nt.ItemStatePredictedEvent] - BoilerAndCirculation predicted to become OFF
2020-05-10 18:39:05.452 [vent.ItemStateChangedEvent] - Stue_3_Valve changed from 0 to 80
2020-05-10 18:39:05.453 [vent.ItemStateChangedEvent] - Dagligstue_Mode changed from AUTOMATIC to BOOST
2020-05-10 18:39:05.456 [ome.event.ItemCommandEvent] - Item 'BoilerAndCirculation' received command OFF
2020-05-10 18:39:05.469 [ome.event.ItemCommandEvent] - Item 'Dagligstue_ActualTemp_Lox_V' received command 25.2 °C
2020-05-10 18:39:05.482 [nt.ItemStatePredictedEvent] - BoilerAndCirculation predicted to become OFF
2020-05-10 18:39:05.492 [nt.ItemStatePredictedEvent] - Dagligstue_ActualTemp_Lox_V predicted to become 25.2 °C
2020-05-10 18:39:35.597 [ome.event.ItemCommandEvent] - Item 'Dagligstue_ActualTemp_Lox_V' received command 25.2 °C
2020-05-10 18:39:35.624 [nt.ItemStatePredictedEvent] - Dagligstue_ActualTemp_Lox_V predicted to become 25.2 °C
rule "Boiler Start/Stop"
when
Member of HeaterValveGroup changed
then
if(HeaterValveGroup.state > 0) {
HeaterValveGroup.persist
BoilerAndCirculation.sendCommand(ON)
}
else if (HeaterValveGroup.state <= 0){
BoilerAndCirculation.sendCommand(OFF)
}
end
Nope, Im thinking, could it be a problem for the Rule, if some valves are 0 and some lets say 80? all valves are independent, and when the shines, all valves upstairs are 0 but basement still 18 or so…
Make sence?
Yes, as the rule is checking for all to be at or equal to 0. You may need to split the rule and groups, one for upstairs and one for downstairs if that will work for what you need.
You will need circulation if the valves are open correct?
That would work, but it all depends on if you need circulation when a valve is open, assuming the switch controls the pump. You would also need to know the correct value of each valve that is not 0 for when you want the switch off.
2020-05-10 19:54:48.230 [INFO ] [el.core.internal.ModelRepositoryImpl] - Refreshing model 'Varme.rules'
==> /var/log/openhab2/events.log <==
2020-05-10 19:54:54.590 [hingStatusInfoChangedEvent] - 'hue:0220:ecb5fa1ed4d2:15' changed from OFFLINE: Hue bridge reports light as not reachable. to ONLINE
2020-05-10 19:55:04.637 [hingStatusInfoChangedEvent] - 'hue:0220:ecb5fa1ed4d2:14' changed from OFFLINE: Hue bridge reports light as not reachable. to ONLINE
2020-05-10 19:55:06.787 [vent.ItemStateChangedEvent] - Gaestevaerelse_ActualTemp changed from 21.1 °C to 21.0 °C
2020-05-10 19:55:06.835 [vent.ItemStateChangedEvent] - Sovevaerelse_ActualTemp changed from 21.5 °C to 21.6 °C
2020-05-10 19:55:07.092 [ome.event.ItemCommandEvent] - Item 'BoilerAndCirculation' received command OFF
2020-05-10 19:55:07.106 [ome.event.ItemCommandEvent] - Item 'BoilerAndCirculation' received command OFF
2020-05-10 19:55:07.158 [ome.event.ItemCommandEvent] - Item 'BoilerAndCirculation' received command OFF
2020-05-10 19:55:07.168 [ome.event.ItemCommandEvent] - Item 'Dagligstue_ActualTemp_Lox_V' received command 25.1 °C
2020-05-10 19:55:07.177 [ome.event.ItemCommandEvent] - Item 'BoilerAndCirculation' received command OFF
2020-05-10 19:55:07.188 [ome.event.ItemCommandEvent] - Item 'BoilerAndCirculation' received command OFF
2020-05-10 19:55:07.197 [ome.event.ItemCommandEvent] - Item 'BoilerAndCirculation' received command OFF
2020-05-10 19:55:07.209 [nt.ItemStatePredictedEvent] - BoilerAndCirculation predicted to become OFF
2020-05-10 19:55:07.217 [nt.ItemStatePredictedEvent] - BoilerAndCirculation predicted to become OFF
2020-05-10 19:55:07.227 [nt.ItemStatePredictedEvent] - BoilerAndCirculation predicted to become OFF
2020-05-10 19:55:07.235 [nt.ItemStatePredictedEvent] - Dagligstue_ActualTemp_Lox_V predicted to become 25.1 °C
2020-05-10 19:55:07.245 [nt.ItemStatePredictedEvent] - BoilerAndCirculation predicted to become OFF
2020-05-10 19:55:07.254 [nt.ItemStatePredictedEvent] - BoilerAndCirculation predicted to become OFF
2020-05-10 19:55:07.264 [nt.ItemStatePredictedEvent] - BoilerAndCirculation predicted to become OFF
2020-05-10 19:55:34.755 [hingStatusInfoChangedEvent] - 'hue:0220:ecb5fa1ed4d2:27' changed from ONLINE to OFFLINE: Hue bridge reports light as not reachable.
2020-05-10 19:55:37.006 [ome.event.ItemCommandEvent] - Item 'BoilerAndCirculation' received command OFF
2020-05-10 19:55:37.041 [nt.ItemStatePredictedEvent] - BoilerAndCirculation predicted to become OFF
2020-05-10 19:55:37.094 [vent.ItemStateChangedEvent] - Stue_1_Valve changed from 0 to 100
2020-05-10 19:55:37.095 [vent.ItemStateChangedEvent] - Stue_2_Valve changed from 0 to 80
2020-05-10 19:55:37.096 [ome.event.ItemCommandEvent] - Item 'BoilerAndCirculation' received command OFF
2020-05-10 19:55:37.110 [vent.ItemStateChangedEvent] - Stue_3_Valve changed from 0 to 80
2020-05-10 19:55:37.123 [ome.event.ItemCommandEvent] - Item 'BoilerAndCirculation' received command OFF
2020-05-10 19:55:37.134 [ome.event.ItemCommandEvent] - Item 'BoilerAndCirculation' received command OFF
2020-05-10 19:55:37.144 [vent.ItemStateChangedEvent] - Dagligstue_Mode changed from AUTOMATIC to BOOST
2020-05-10 19:55:37.146 [ome.event.ItemCommandEvent] - Item 'Dagligstue_ActualTemp_Lox_V' received command 25.1 °C
2020-05-10 19:55:37.157 [ome.event.ItemCommandEvent] - Item 'BoilerAndCirculation' received command OFF
2020-05-10 19:55:37.168 [ome.event.ItemCommandEvent] - Item 'BoilerAndCirculation' received command OFF
2020-05-10 19:55:37.177 [nt.ItemStatePredictedEvent] - BoilerAndCirculation predicted to become OFF
2020-05-10 19:55:37.185 [nt.ItemStatePredictedEvent] - BoilerAndCirculation predicted to become OFF
2020-05-10 19:55:37.193 [nt.ItemStatePredictedEvent] - BoilerAndCirculation predicted to become OFF
2020-05-10 19:55:37.200 [nt.ItemStatePredictedEvent] - Dagligstue_ActualTemp_Lox_V predicted to become 25.1 °C
2020-05-10 19:55:37.209 [nt.ItemStatePredictedEvent] - BoilerAndCirculation predicted to become OFF
2020-05-10 19:55:37.217 [nt.ItemStatePredictedEvent] - BoilerAndCirculation predicted to become OFF
2020-05-10 19:56:07.173 [ome.event.ItemCommandEvent] - Item 'BoilerAndCirculation' received command OFF
2020-05-10 19:56:07.214 [nt.ItemStatePredictedEvent] - BoilerAndCirculation predicted to become OFF
2020-05-10 19:56:07.244 [ome.event.ItemCommandEvent] - Item 'BoilerAndCirculation' received command OFF
2020-05-10 19:56:07.260 [ome.event.ItemCommandEvent] - Item 'BoilerAndCirculation' received command OFF
2020-05-10 19:56:07.272 [ome.event.ItemCommandEvent] - Item 'BoilerAndCirculation' received command OFF
2020-05-10 19:56:07.289 [ome.event.ItemCommandEvent] - Item 'BoilerAndCirculation' received command OFF
2020-05-10 19:56:07.298 [ome.event.ItemCommandEvent] - Item 'Dagligstue_ActualTemp_Lox_V' received command 25.1 °C
2020-05-10 19:56:07.309 [vent.ItemStateChangedEvent] - Boernevaerelse_ActualTemp changed from 24.7 °C to 24.8 °C
2020-05-10 19:56:07.310 [ome.event.ItemCommandEvent] - Item 'BoilerAndCirculation' received command OFF
2020-05-10 19:56:07.319 [nt.ItemStatePredictedEvent] - BoilerAndCirculation predicted to become OFF
2020-05-10 19:56:07.330 [nt.ItemStatePredictedEvent] - BoilerAndCirculation predicted to become OFF
2020-05-10 19:56:07.344 [nt.ItemStatePredictedEvent] - BoilerAndCirculation predicted to become OFF
2020-05-10 19:56:07.357 [nt.ItemStatePredictedEvent] - BoilerAndCirculation predicted to become OFF
2020-05-10 19:56:07.367 [nt.ItemStatePredictedEvent] - Dagligstue_ActualTemp_Lox_V predicted to become 25.1 °C
2020-05-10 19:56:07.374 [nt.ItemStatePredictedEvent] - BoilerAndCirculation predicted to become OFF
Groups:
Group HeaterValveGroup "Radiator Ventil Position" (HeaterValveGroup)
Items:
Number Laboratoriet_Valve "Laboratoriet Ventilposition" <settings> (HeaterValveGroup) {channel="max:thermostat:LEQ1324948:JTS0011714:valve"}
Number Fyrrum_Valve "Fyrrum Ventilposition" <settings> (HeaterValveGroup) {channel="max:thermostat:LEQ1324948:KTS0000426:valve"}
Number Spisestue_Valve "Spisestue Ventilposition" <settings> (HeaterValveGroup) {channel="max:thermostat:LEQ1324948:JTS0010022:valve"}
Number Stue_2_Valve "Stue 2 Ventilposition" <settings> (HeaterValveGroup) {channel="max:thermostat:LEQ1324948:JTS0002525:valve"}
Number Stue_3_Valve "Stue 3 Ventilposition" <settings> (HeaterValveGroup) {channel="max:thermostat:LEQ1324948:JTS0006269:valve"}
Number Boernevaerelse_Valve "Børneværelse Ventilposition" <settings> (HeaterValveGroup) {channel="max:thermostat:LEQ1324948:JTS0011821:valve"}
Switch BoilerAndCirculation "Vaskerum / *centralvarme" {channel="loxone:miniserver:504F94100E77:12EE1147-0355-4A01-FFFFEEE000000000"}