To expand, this Group has no type or function to give it a state
So, in the rule,
if(HeaterValveGroup.state > 0)
no meaning.
As @H102 says, give type and function. MIN would do as well, here.
To expand, this Group has no type or function to give it a state
So, in the rule,
if(HeaterValveGroup.state > 0)
no meaning.
As @H102 says, give type and function. MIN would do as well, here.
Weeeee it works, im so thankfull, hope I can contribute some day
Ill save a lot of KW and m3 gas, because of theese lines
rule "Boiler Start/Stop"
when
Member of HeaterValveGroup changed
then
if(HeaterValveGroup.state > 0) {
BoilerAndCirculation.sendCommand(ON)
}
else {
BoilerAndCirculation.sendCommand(OFF)
}
end
Group:Number:AVG HeaterValveGroup "Radiator Ventil Position" (HeaterValveGroup)
Weeeee it works, im so thankfull, hope I can contribute some day
Ill save a lot of KW and m3 gas, because of theese lines
rule "Boiler Start/Stop"
when
Member of HeaterValveGroup changed
then
if(HeaterValveGroup.state > 0) {
BoilerAndCirculation.sendCommand(ON)
}
else {
BoilerAndCirculation.sendCommand(OFF)
}
end
Group:Number:AVG HeaterValveGroup "Radiator Ventil Position" (HeaterValveGroup)
Glad you have it working and look forward to some future community contributions.
Please click the square box on post that provided the solution to mark the topic as solved.