Modbus openHAB2 binding available for alpha testing

That is part of modbus protocol, not specific to this binding. Error 6 comes from the slave device. You can find explanations here

http://simplymodbus.ca/exceptions.htm

Specialized use in conjunction with programming commands.
The slave is engaged in processing a long-duration program command. The master should retransmit the message later when the slave is free…

Best
Sami

Thanks Sami!
Need to debug for what my unit is doing at that moment.

Regards

I have modbus-binding up and running. But I have no glue how I can transform a integer to boolean using transform.js. I read the value 32769 witch means door closed or 32768 witch means door open. Is there a way to transform this using transform.js? thanks for any hint what I had to search for …

1 Like

I assume you mean contact or switch item with boolean. There is no general boolean type as far as I know.

Since there are just two values (32768 and 32769), the map transformation might be the most straight forward: https://docs.openhab.org/addons/transformations/map/readme.html

You can examples from modbus binding documentation that use transformation. Instead of JS(…) you would have MAP(…) as the transformation.

@ssalonen, could you please advice what might impact ‘strange’ behavior of the binding?
When I try to change item status (i.e. lower vent unit power) I’m switching the status, meaning writing to a registry different value.
The strange thing is that I see my item is switching back and forth few times:
2018-01-11 14:35:53.475 [ome.event.ItemCommandEvent] - Item ‘komfoCurrentModeWrite’ received command 1
2018-01-11 14:35:53.481 [vent.ItemStateChangedEvent] - komfoCurrentModeWrite changed from 2 to 1
2018-01-11 14:35:56.096 [vent.ItemStateChangedEvent] - komfoCurrentModeWrite changed from 1 to 2
2018-01-11 14:35:56.859 [vent.ItemStateChangedEvent] - komfoCurrentModeWrite changed from 2 to 1
2018-01-11 14:36:00.771 [vent.ItemStateChangedEvent] - komfoCurrentModeWrite changed from 1 to 2
2018-01-11 14:36:01.184 [vent.ItemStateChangedEvent] - komfoCurrentModeWrite changed from 2 to 1

meantime openhab.log shows:
2018-01-11 14:35:46.558 [TRACE] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:HVAC:CurrentMode:komfoCurrentMode ‘Modbus data’, channel modbus:data:HVAC:CurrentMode:komfoCurrentMode:number will be updated to ‘2’ (type DecimalType). Numeric state ‘2’ and bool value 'true’
2018-01-11 14:35:46.560 [DEBUG] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:HVAC:CurrentMode:komfoCurrentMode ‘Modbus data’, channel modbus:data:HVAC:CurrentMode:komfoCurrentMode:datetime will not be updated since transformation was unsuccesful
2018-01-11 14:35:46.572 [TRACE] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:HVAC:CurrentMode:komfoCurrentMode ‘Modbus data’, channel modbus:data:HVAC:CurrentMode:komfoCurrentMode:string will be updated to ‘2’ (type StringType). Numeric state ‘2’ and bool value 'true’
2018-01-11 14:35:46.574 [TRACE] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:HVAC:CurrentMode:komfoCurrentMode ‘Modbus data’, channel modbus:data:HVAC:CurrentMode:komfoCurrentMode:contact will be updated to ‘OPEN’ (type OpenClosedType). Numeric state ‘2’ and bool value 'true’
2018-01-11 14:35:46.580 [TRACE] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:HVAC:CurrentMode:komfoCurrentMode ‘Modbus data’, channel modbus:data:HVAC:CurrentMode:komfoCurrentMode:rollershutter will be updated to ‘2’ (type PercentType). Numeric state ‘2’ and bool value ‘true’

thing:
/* MODES */
Bridge poller CurrentMode [ start=4, length=1, refresh=2000, type=“holding” ] {
Thing data komfoCurrentMode [ readStart=“4”, readValueType=“uint16” ] //5 Current mode R/W unsigned char 0 - 10
}
Bridge poller CurrentModeWrite [ start=4, length=1, refresh=2000, type=“holding” ] {
Thing data komfoCurrentModeWrite [ readStart=“4”, readValueType=“uint16”, writeStart=“4”, writeValueType=“uint16”, writeType=“holding” ] //reg5: WRITE ONLY:Away=1,Normal=2,Intensive=3,Boost=4
}

items:
/* Control */
Number komfoCurrentMode “[MAP(komfoOperationModes.map):%s]” { channel=“modbus:data:HVAC:CurrentMode:komfoCurrentMode:number” }
Number komfoCurrentModeWrite “[%s]” { channel=“modbus:data:HVAC:CurrentModeWrite:komfoCurrentModeWrite:number” }

sitemap:
Frame label=“Control” item=komfoCurrentMode
Selection item=komfoCurrentModeWrite label=“Operation Mode Select” icon=“rgb” mappings=[0=Null, 1=Away, 2=Normal, 3=Intensive, 4=Boost]

What I’m missing here or why this might be happening?

thx

Hi @ArC!

It’s a bit hard to read the logs, could you please format all configuration and logs using code formatting: Auto highlighting/formatting on code blocks in posts

Also, it looks like the openhab.log is not from the correct time (ends at 14:35:46, while the events are from 14:35:53) so there’s not much to go on…

This is just a wild guess (correct logs would help!) Please understand that openHAB automatically changes the state of the item when command is received by an item. You can disable this behaviour using autoupdate parameter, refer to openHAB docs: https://docs.openhab.org/configuration/items.html#exception-autoupdate

This could partly explain what’s going on:

Item ‘komfoCurrentModeWrite’ received command 1
komfoCurrentModeWrite changed from 2 to 1  // changed by openhab, since command was received
komfoCurrentModeWrite changed from 1 to 2  // polled value from modbus? (command did not yet have an impact)
komfoCurrentModeWrite changed from 2 to 1  // polled value from modbus updated to new  value?
komfoCurrentModeWrite changed from 1 to 2 // ??
komfoCurrentModeWrite changed from 2 to 1 // ??

Looking at the correct logs tells exactly what is polled from the slave.

Best,
Sami

EDIT: also interested to hear more about the CPU usage. How much does it increase with the modbus binding? Do you have stats with 1.x binding?

@narf27 hmm I think you are right :frowning: modpoll does not work with raspi and mbpoll only supports TCP slaves…

Not sure what to advice. We have seen slaves that do not answer to some specific requests, perhaps this is similar case. Can you read in two parts (two registers + two registers)?

Is there anything in device documentation regarding some limitations with respect to requests?

Edit : realized you previously used the old binding (successfully?) to read values. Please ensure that the serial port parameters are correct. I am curious if you find a case which worked before but anymore.

EDIT2: @narf27 here are two examples using python libraries pymodbus and minimalmodbus

These should work with python 2.7 or higher. The only trick is to install dependencies for these scripts (pymodbus or minimalmodbus). Hope you get the idea and adjust the scripts accordingly.

test_pymodbus.py:

# Installation
# - install dependencies:
#       pip install pymodbus six
#     or 
#       easy_install pymodbus six
# Running script:
#      python test_pymodbus.py

from pymodbus.client.sync import ModbusSerialClient

# https://github.com/riptideio/pymodbus/blob/master/pymodbus/constants.py
port = '/dev/pts/3'
baudrate = 38400
stopbits = 1
bytesize = 8
parity = 'N'  # 'E', 'O' or 'N'


address = 0
count = 5
unit = 1



slave = ModbusSerialClient(method='rtu', 
                           port=port, 
                           baudrate=baudrate, 
                           stopbits=stopbits, 
                           bytesize=bytesize, 
                           parity=parity)
out = slave.read_holding_registers(address, count, unit=unit)
 
print('%s: %s' % (out, out.registers))

test_minimalmodbus.py:


# Installation
# - install dependencies:
#       pip install minimalmodbus
#     or 
#       easy_install minimalmodbus
# Running script:
#      python test_minimalmodbus.py

import minimalmodbus
import serial

unit = 1
address = 24
count = 1

port = '/dev/pts/3'
baudrate = 38400
stopbits = 1
bytesize = 8
parity = serial.PARITY_NONE


slave = minimalmodbus.Instrument(port, unit)

slave.serial.port          # this is the serial port name
slave.serial.baudrate = baudrate   # Baud
slave.serial.bytesize = bytesize
slave.serial.parity   = parity
slave.serial.stopbits = stopbits

print(slave.read_register(address, count))

There are others as well, e.g. https://github.com/favalex/modbus-cli (assumes parity=none)

meaning? =)
this:

    Bridge1 poller inputRegisters [ start=200, length=2, refresh=1000, type="input" ] {
        Thing data input1 [ readStart="200", readValueType="int32" ]

    Bridge2 poller inputRegisters [ start=202, length=2, refresh=1000, type="input" ] {
        Thing data input2 [ readStart="202", readValueType="int32" ]

instead of this:

    Bridge poller inputRegisters [ start=200, length=4, refresh=1000, type="input" ] {
        Thing data input1 [ readStart="200", readValueType="int32" ]
        Thing data input2 [ readStart="202", readValueType="int32" ]

?

cheers
Peter

1 Like

Hi,
thanks for the hint as to how format the log correctly, apologies, I’ve not used much forum before.
Yesterday played a little bit with various options and must say cannot re-produce the same behavior again :frowning:

What I did is: restarted openhab itself in the first place, then added autoupdate value next to the item, enabled TRACE option in karaf:

openhab> log:set TRACE org.openhab.binding.modbus
openhab> log:set TRACE org.openhab.io.transport.modbus
openhab> log:set TRACE net.wimpi.modbus

So I paste here the log output (matching the time-stamp, thanks @ssalonen! ) as what I can see (sorry if that’s a longer trail than expected):

events.log
2018-01-12 10:39:09.680 [ome.event.ItemCommandEvent] - Item 'komfoCurrentModeWrite' received command 2
2018-01-12 10:39:09.684 [vent.ItemStateChangedEvent] - komfoCurrentModeWrite changed from 1 to 2
2018-01-12 10:39:10.073 [vent.ItemStateChangedEvent] - komfoCurrentMode changed from 1 to 2

openhab.log

2018-01-12 10:39:09.680 [TRACE] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:HVAC:CurrentModeWrite:komfoCurrentModeWrite 'Modbus data' received command '2' to channel 'modbus:data:HVA
C:CurrentModeWrite:komfoCurrentModeWrite:number'
2018-01-12 10:39:09.681 [TRACE] [odbus.handler.ModbusDataThingHandler] - Submitting write task: WriteTaskImpl@3f424d26[request=ModbusWriteRegisterRequestBlueprintImpl@5e8b40c5[slaveId=254,reference
=4,functionCode=WRITE_SINGLE_REGISTER,registers=ModbusRegisterArrayImpl(ModbusRegisterImpl(bytes=[0, 2],ushort=2)),maxTries=3],endpoint=ModbusTCPSlaveEndpoint@6ef8c4f2[address=192.168.8.199,port=50
2],callback=org.openhab.binding.modbus.handler.ModbusDataThingHandler@5c8857d6]
2018-01-12 10:39:09.684 [DEBUG] [rt.modbus.internal.ModbusManagerImpl] - Scheduling one-off write task WriteTaskImpl@3f424d26[request=ModbusWriteRegisterRequestBlueprintImpl@5e8b40c5[slaveId=254,re
ference=4,functionCode=WRITE_SINGLE_REGISTER,registers=ModbusRegisterArrayImpl(ModbusRegisterImpl(bytes=[0, 2],ushort=2)),maxTries=3],endpoint=ModbusTCPSlaveEndpoint@6ef8c4f2[address=192.168.8.199,
port=502],callback=org.openhab.binding.modbus.handler.ModbusDataThingHandler@5c8857d6]
2018-01-12 10:39:09.685 [DEBUG] [rt.modbus.internal.ModbusManagerImpl] - Will now execute one-off write task WriteTaskImpl@3f424d26[request=ModbusWriteRegisterRequestBlueprintImpl@5e8b40c5[slaveId=
254,reference=4,functionCode=WRITE_SINGLE_REGISTER,registers=ModbusRegisterArrayImpl(ModbusRegisterImpl(bytes=[0, 2],ushort=2)),maxTries=3],endpoint=ModbusTCPSlaveEndpoint@6ef8c4f2[address=192.168.
8.199,port=502],callback=org.openhab.binding.modbus.handler.ModbusDataThingHandler@5c8857d6], waited in thread pool for 2
2018-01-12 10:39:09.686 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Starting new operation with task WriteTaskImpl@3f424d26[request=ModbusWriteRegisterRequestBlueprintImpl@5e8b40c5[slaveId=254
,reference=4,functionCode=WRITE_SINGLE_REGISTER,registers=ModbusRegisterArrayImpl(ModbusRegisterImpl(bytes=[0, 2],ushort=2)),maxTries=3],endpoint=ModbusTCPSlaveEndpoint@6ef8c4f2[address=192.168.8.1
99,port=502],callback=org.openhab.binding.modbus.handler.ModbusDataThingHandler@5c8857d6]. Trying to get connection [operation ID a6c4cae0-c17a-48ef-8a32-76eea586cd30]
2018-01-12 10:39:09.686 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Executing task WriteTaskImpl@3f424d26[request=ModbusWriteRegisterRequestBlueprintImpl@5e8b40c5[slaveId=254,reference=4,funct
ionCode=WRITE_SINGLE_REGISTER,registers=ModbusRegisterArrayImpl(ModbusRegisterImpl(bytes=[0, 2],ushort=2)),maxTries=3],endpoint=ModbusTCPSlaveEndpoint@6ef8c4f2[address=192.168.8.199,port=502],callb
ack=org.openhab.binding.modbus.handler.ModbusDataThingHandler@5c8857d6] (oneOff=true)! Waiting for connection. Idle connections for this endpoint: 1, and active 0 [operation ID a6c4cae0-c17a-48ef-8
a32-76eea586cd30]
2018-01-12 10:39:09.689 [DEBUG] [wimpi.modbus.net.TCPMasterConnection] - connect()
2018-01-12 10:39:09.690 [DEBUG] [nding.modbus.internal.Transformation] - transformed response is '1.5'
2018-01-12 10:39:09.690 [TRACE] [ing.ModbusSlaveConnectionFactoryImpl] - Waited 0ms (interTransactionDelayMillis 100ms) before giving returning connection TCPMasterConnection@438ee00b[socket=Socket
[addr=/192.168.8.199,port=502,localport=32794]] for endpoint ModbusTCPSlaveEndpoint@6ef8c4f2[address=192.168.8.199,port=502], to ensure delay between transactions.
2018-01-12 10:39:09.691 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - borrowing connection (got Optional[TCPMasterConnection@438ee00b[socket=Socket[addr=/192.168.8.199,port=502,localport=32794]]
]) for endpoint ModbusTCPSlaveEndpoint@6ef8c4f2[address=192.168.8.199,port=502] took 4 ms
2018-01-12 10:39:09.691 [DEBUG] [nding.modbus.internal.Transformation] - Could not transform item state '15' (of type DecimalType) to a State (tried the following types: [class org.eclipse.smarthom
e.core.library.types.DateTimeType, class org.eclipse.smarthome.core.types.UnDefType])! Input state as string '15', transformed string '1.5', transformation 'JS(divide10.js)'
2018-01-12 10:39:09.692 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Executing task WriteTaskImpl@3f424d26[request=ModbusWriteRegisterRequestBlueprintImpl@5e8b40c5[slaveId=254,reference=4,funct
ionCode=WRITE_SINGLE_REGISTER,registers=ModbusRegisterArrayImpl(ModbusRegisterImpl(bytes=[0, 2],ushort=2)),maxTries=3],endpoint=ModbusTCPSlaveEndpoint@6ef8c4f2[address=192.168.8.199,port=502],callb
ack=org.openhab.binding.modbus.handler.ModbusDataThingHandler@5c8857d6] (oneOff=true)! Connection received in 4 ms [operation ID a6c4cae0-c17a-48ef-8a32-76eea586cd30]
2018-01-12 10:39:09.692 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Operation with task WriteTaskImpl@3f424d26[request=ModbusWriteRegisterRequestBlueprintImpl@5e8b40c5[slaveId=254,reference=4,
functionCode=WRITE_SINGLE_REGISTER,registers=ModbusRegisterArrayImpl(ModbusRegisterImpl(bytes=[0, 2],ushort=2)),maxTries=3],endpoint=ModbusTCPSlaveEndpoint@6ef8c4f2[address=192.168.8.199,port=502],
callback=org.openhab.binding.modbus.handler.ModbusDataThingHandler@5c8857d6]. Got a connection successfully [operation ID a6c4cae0-c17a-48ef-8a32-76eea586cd30]
2018-01-12 10:39:09.693 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Try 1 out of 3 [operation ID a6c4cae0-c17a-48ef-8a32-76eea586cd30]
2018-01-12 10:39:09.693 [DEBUG] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:HVAC:DetailedInformation:holding3 'Modbus data', channel modbus:data:HVAC:DetailedInformation:holding3:dat
etime will not be updated since transformation was unsuccesful
2018-01-12 10:39:09.695 [DEBUG] [rt.modbus.internal.ModbusManagerImpl] - Executing scheduled (1000ms) poll task PollTaskImpl@786ba83e[request=ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@74
8793f[slaveId=254,functionCode=READ_MULTIPLE_REGISTERS,start=4,length=1,maxTries=3],endpoint=ModbusTCPSlaveEndpoint@6ef8c4f2[address=192.168.8.199,port=502],callback=org.openhab.binding.modbus.hand
ler.ModbusPollerThingHandlerImpl$ReadCallbackDelegator@2fc27b3a]. Current millis: 1515746349695
2018-01-12 10:39:09.693 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Ensuring that enough time passes before retrying again. Sleeping if necessary [operation ID a6c4cae0-c17a-48ef-8a32-76eea586
cd30]
2018-01-12 10:39:09.696 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Starting new operation with task PollTaskImpl@786ba83e[request=ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@748793f[
slaveId=254,functionCode=READ_MULTIPLE_REGISTERS,start=4,length=1,maxTries=3],endpoint=ModbusTCPSlaveEndpoint@6ef8c4f2[address=192.168.8.199,port=502],callback=org.openhab.binding.modbus.handler.Mo
dbusPollerThingHandlerImpl$ReadCallbackDelegator@2fc27b3a]. Trying to get connection [operation ID abc175ae-335f-48b1-a1ff-6f401cb4ec80]
2018-01-12 10:39:09.696 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Sleep ended, slept a6c4cae0-c17a-48ef-8a32-76eea586cd30 [operation ID 0]
2018-01-12 10:39:09.696 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Executing task PollTaskImpl@786ba83e[request=ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@748793f[slaveId=254,functionCode=READ_MULTIPLE_REGISTERS,start=4,length=1,maxTries=3],endpoint=ModbusTCPSlaveEndpoint@6ef8c4f2[address=192.168.8.199,port=502],callback=org.openhab.binding.modbus.handler.ModbusPollerThingHan
dlerImpl$ReadCallbackDelegator@2fc27b3a] (oneOff=false)! Waiting for connection. Idle connections for this endpoint: 0, and active 1 [operation ID abc175ae-335f-48b1-a1ff-6f401cb4ec80]
2018-01-12 10:39:09.698 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Going execute transaction with read request (FC=WRITE_SINGLE_REGISTER): 00 00 00 00 00 06 fe 06 00 04 00 02  [operation ID a
6c4cae0-c17a-48ef-8a32-76eea586cd30]
2018-01-12 10:39:09.701 [TRACE] [wimpi.modbus.io.ModbusTCPTransaction] - Sending request with transaction ID 4767: net.wimpi.modbus.msg.WriteSingleRegisterRequest@440f5e09
2018-01-12 10:39:09.707 [DEBUG] [nding.modbus.internal.Transformation] - transformed response is '1.5'
2018-01-12 10:39:09.709 [DEBUG] [nding.modbus.internal.Transformation] - Transformed item state '15' (of type DecimalType) to a state 1.5 (of type StringType). Input state as string '15', transform
ed string '1.5', transformation 'JS(divide10.js)'
2018-01-12 10:39:09.711 [TRACE] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:HVAC:DetailedInformation:holding3 'Modbus data', channel modbus:data:HVAC:DetailedInformation:holding3:str
ing will be updated to '1.5' (type StringType). Numeric state '15' and bool value 'true'
2018-01-12 10:39:09.722 [DEBUG] [nding.modbus.internal.Transformation] - transformed response is '22.0'
2018-01-12 10:39:09.732 [DEBUG] [nding.modbus.internal.Transformation] - Could not transform item state '220' (of type DecimalType) to a State (tried the following types: [class org.eclipse.smartho
me.core.library.types.OpenClosedType, class org.eclipse.smarthome.core.types.UnDefType])! Input state as string '220', transformed string '22.0', transformation 'JS(divide10.js)'
2018-01-12 10:39:09.733 [DEBUG] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:HVAC:modeSettings:komfoModeIntensiveTempSetpoint 'Modbus data', channel modbus:data:HVAC:modeSettings:komf
oModeIntensiveTempSetpoint:contact will not be updated since transformation was unsuccesful
2018-01-12 10:39:09.745 [DEBUG] [nding.modbus.internal.Transformation] - transformed response is '22.0'
2018-01-12 10:39:09.746 [DEBUG] [nding.modbus.internal.Transformation] - Transformed item state '220' (of type DecimalType) to a state 22.0 (of type PercentType). Input state as string '220', trans
formed string '22.0', transformation 'JS(divide10.js)'
2018-01-12 10:39:09.747 [TRACE] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:HVAC:modeSettings:komfoModeIntensiveTempSetpoint 'Modbus data', channel modbus:data:HVAC:modeSettings:komf
oModeIntensiveTempSetpoint:rollershutter will be updated to '22.0' (type PercentType). Numeric state '220' and bool value 'true'
2018-01-12 10:39:09.759 [DEBUG] [nding.modbus.internal.Transformation] - transformed response is '22.0'
2018-01-12 10:39:09.759 [DEBUG] [nding.modbus.internal.Transformation] - Transformed item state '220' (of type DecimalType) to a state 22.0 (of type PercentType). Input state as string '220', trans
formed string '22.0', transformation 'JS(divide10.js)'
2018-01-12 10:39:09.905 [TRACE] [wimpi.modbus.io.ModbusTCPTransaction] - Received response with transaction ID 4767
2018-01-12 10:39:09.908 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Response for write request (FC=6, transaction ID=4767): 12 9f 00 00 00 06 fe 06 00 04 00 02  [operation ID a6c4cae0-c17a-48e
f-8a32-76eea586cd30]
2018-01-12 10:39:09.909 [TRACE] [ing.ModbusSlaveConnectionFactoryImpl] - Validating endpoint ModbusTCPSlaveEndpoint@6ef8c4f2[address=192.168.8.199,port=502] connection TCPMasterConnection@438ee00b[
socket=Socket[addr=/192.168.8.199,port=502,localport=32794]] -> true
2018-01-12 10:39:09.912 [TRACE] [ing.ModbusSlaveConnectionFactoryImpl] - Passivating connection TCPMasterConnection@438ee00b[socket=Socket[addr=/192.168.8.199,port=502,localport=32794]] for endpoin
t ModbusTCPSlaveEndpoint@6ef8c4f2[address=192.168.8.199,port=502]...
2018-01-12 10:39:09.760 [TRACE] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:HVAC:modeSettings:komfoModeIntensiveTempSetpoint 'Modbus data', channel modbus:data:HVAC:modeSettings:komf
oModeIntensiveTempSetpoint:dimmer will be updated to '22.0' (type PercentType). Numeric state '220' and bool value 'true'
2018-01-12 10:39:09.910 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Calling write response callback org.openhab.binding.modbus.handler.ModbusDataThingHandler@5c8857d6 for request ModbusWriteRe
gisterRequestBlueprintImpl@5e8b40c5[slaveId=254,reference=4,functionCode=WRITE_SINGLE_REGISTER,registers=ModbusRegisterArrayImpl(ModbusRegisterImpl(bytes=[0, 2],ushort=2)),maxTries=3]. Response was
 ModbusResponseImpl(responseFC=6)
2018-01-12 10:39:09.916 [DEBUG] [odbus.handler.ModbusDataThingHandler] - Successful write, matching request ModbusWriteRegisterRequestBlueprintImpl@5e8b40c5[slaveId=254,reference=4,functionCode=WRI
TE_SINGLE_REGISTER,registers=ModbusRegisterArrayImpl(ModbusRegisterImpl(bytes=[0, 2],ushort=2)),maxTries=3]
2018-01-12 10:39:09.917 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Called write response callback org.openhab.binding.modbus.handler.ModbusDataThingHandler@5c8857d6 for request ModbusWriteReg
isterRequestBlueprintImpl@5e8b40c5[slaveId=254,reference=4,functionCode=WRITE_SINGLE_REGISTER,registers=ModbusRegisterArrayImpl(ModbusRegisterImpl(bytes=[0, 2],ushort=2)),maxTries=3]. Response was
ModbusResponseImpl(responseFC=6)
2018-01-12 10:39:09.918 [TRACE] [ing.ModbusSlaveConnectionFactoryImpl] - (passivate) Connection TCPMasterConnection@438ee00b[socket=Socket[addr=/192.168.8.199,port=502,localport=32794]] (endpoint M
odbusTCPSlaveEndpoint@6ef8c4f2[address=192.168.8.199,port=502]) age 227ms is over the reconnectAfterMillis=0ms limit or has been connection time (1515746349690) is after the "disconnectBeforeConnec
tedMillis"=1515746092229 -> disconnecting.
2018-01-12 10:39:09.909 [DEBUG] [nding.modbus.internal.Transformation] - transformed response is '1.5'
2018-01-12 10:39:09.922 [DEBUG] [nding.modbus.internal.Transformation] - Could not transform item state '15' (of type DecimalType) to a State (tried the following types: [class org.eclipse.smarthom
e.core.library.types.OpenClosedType, class org.eclipse.smarthome.core.types.UnDefType])! Input state as string '15', transformed string '1.5', transformation 'JS(divide10.js)'
2018-01-12 10:39:09.922 [DEBUG] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:HVAC:DetailedInformation:holding3 'Modbus data', channel modbus:data:HVAC:DetailedInformation:holding3:con
tact will not be updated since transformation was unsuccesful
2018-01-12 10:39:09.922 [TRACE] [ing.ModbusSlaveConnectionFactoryImpl] - ...Passivated connection TCPMasterConnection@438ee00b[socket=Socket[addr=/192.168.8.199,port=502,localport=32794]] for endpo
int ModbusTCPSlaveEndpoint@6ef8c4f2[address=192.168.8.199,port=502]
2018-01-12 10:39:09.925 [DEBUG] [wimpi.modbus.net.TCPMasterConnection] - connect()
2018-01-12 10:39:09.926 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - returned connection to pool for endpoint ModbusTCPSlaveEndpoint@6ef8c4f2[address=192.168.8.199,port=502]
2018-01-12 10:39:09.930 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Connection was returned to the pool, ending operation [operation ID a6c4cae0-c17a-48ef-8a32-76eea586cd30]
2018-01-12 10:39:09.937 [DEBUG] [nding.modbus.internal.Transformation] - transformed response is '1.5'
2018-01-12 10:39:09.938 [DEBUG] [nding.modbus.internal.Transformation] - Transformed item state '15' (of type DecimalType) to a state 1.5 (of type PercentType). Input state as string '15', transfor
med string '1.5', transformation 'JS(divide10.js)'
2018-01-12 10:39:09.938 [TRACE] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:HVAC:DetailedInformation:holding3 'Modbus data', channel modbus:data:HVAC:DetailedInformation:holding3:rol
lershutter will be updated to '1.5' (type PercentType). Numeric state '15' and bool value 'true'
2018-01-12 10:39:09.964 [DEBUG] [nding.modbus.internal.Transformation] - transformed response is '1.5'
2018-01-12 10:39:09.964 [DEBUG] [nding.modbus.internal.Transformation] - Transformed item state '15' (of type DecimalType) to a state 1.5 (of type PercentType). Input state as string '15', transfor
med string '1.5', transformation 'JS(divide10.js)'
2018-01-12 10:39:09.965 [TRACE] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:HVAC:DetailedInformation:holding3 'Modbus data', channel modbus:data:HVAC:DetailedInformation:holding3:dim
mer will be updated to '1.5' (type PercentType). Numeric state '15' and bool value 'true'
2018-01-12 10:39:09.970 [DEBUG] [nding.modbus.internal.Transformation] - transformed response is '22.0'
2018-01-12 10:39:09.985 [DEBUG] [nding.modbus.internal.Transformation] - Could not transform item state '220' (of type DecimalType) to a State (tried the following types: [class org.eclipse.smartho
me.core.library.types.OnOffType, class org.eclipse.smarthome.core.types.UnDefType])! Input state as string '220', transformed string '22.0', transformation 'JS(divide10.js)'
2018-01-12 10:39:09.986 [DEBUG] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:HVAC:modeSettings:komfoModeIntensiveTempSetpoint 'Modbus data', channel modbus:data:HVAC:modeSettings:komf
oModeIntensiveTempSetpoint:switch will not be updated since transformation was unsuccesful
2018-01-12 10:39:09.988 [DEBUG] [nding.modbus.internal.Transformation] - transformed response is '1.5'
2018-01-12 10:39:09.992 [DEBUG] [nding.modbus.internal.Transformation] - transformed response is '0'
2018-01-12 10:39:09.998 [DEBUG] [nding.modbus.internal.Transformation] - Transformed item state '0' (of type DecimalType) to a state 0 (of type DecimalType). Input state as string '0', transformed
string '0', transformation 'default'
2018-01-12 10:39:10.000 [TRACE] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:HVAC:modeSettings:komfoModeIntensiveHeating 'Modbus data', channel modbus:data:HVAC:modeSettings:komfoMode
IntensiveHeating:number will be updated to '0' (type DecimalType). Numeric state '0' and bool value 'false'
2018-01-12 10:39:10.001 [DEBUG] [nding.modbus.internal.Transformation] - transformed response is '0'
2018-01-12 10:39:10.002 [DEBUG] [nding.modbus.internal.Transformation] - Could not transform item state '15' (of type DecimalType) to a State (tried the following types: [class org.eclipse.smarthom
e.core.library.types.OnOffType, class org.eclipse.smarthome.core.types.UnDefType])! Input state as string '15', transformed string '1.5', transformation 'JS(divide10.js)'
2018-01-12 10:39:10.005 [DEBUG] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:HVAC:DetailedInformation:holding3 'Modbus data', channel modbus:data:HVAC:DetailedInformation:holding3:swi
tch will not be updated since transformation was unsuccesful
2018-01-12 10:39:10.006 [DEBUG] [nding.modbus.internal.Transformation] - transformed response is '20'
2018-01-12 10:39:10.007 [DEBUG] [nding.modbus.internal.Transformation] - Transformed item state '20' (of type DecimalType) to a state 20 (of type DecimalType). Input state as string '20', transform
ed string '20', transformation 'default'
2018-01-12 10:39:10.007 [TRACE] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:HVAC:DetailedInformation:holding4 'Modbus data', channel modbus:data:HVAC:DetailedInformation:holding4:num
ber will be updated to '20' (type DecimalType). Numeric state '20' and bool value 'true'
2018-01-12 10:39:10.011 [TRACE] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:HVAC:DetailedInformation:holding4 'Modbus data', channel modbus:data:HVAC:DetailedInformation:holding4:str
ing will be updated to '20' (type StringType). Numeric state '20' and bool value 'true'
2018-01-12 10:39:10.017 [TRACE] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:HVAC:DetailedInformation:holding4 'Modbus data', channel modbus:data:HVAC:DetailedInformation:holding4:contact will be updated to 'OPEN' (type OpenClosedType). Numeric state '20' and bool value 'true'
2018-01-12 10:39:10.018 [TRACE] [ing.ModbusSlaveConnectionFactoryImpl] - Waited 91ms (interTransactionDelayMillis 100ms) before giving returning connection TCPMasterConnection@438ee00b[socket=Socke
t[addr=/192.168.8.199,port=502,localport=32800]] for endpoint ModbusTCPSlaveEndpoint@6ef8c4f2[address=192.168.8.199,port=502], to ensure delay between transactions.
2018-01-12 10:39:10.018 [DEBUG] [nding.modbus.internal.Transformation] - transformed response is '20'
2018-01-12 10:39:10.018 [DEBUG] [nding.modbus.internal.Transformation] - Transformed item state '20' (of type DecimalType) to a state 20 (of type PercentType). Input state as string '20', transform
ed string '20', transformation 'default'
2018-01-12 10:39:10.018 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - borrowing connection (got Optional[TCPMasterConnection@438ee00b[socket=Socket[addr=/192.168.8.199,port=502,localport=32800]]
]) for endpoint ModbusTCPSlaveEndpoint@6ef8c4f2[address=192.168.8.199,port=502] took 321 ms
2018-01-12 10:39:10.019 [TRACE] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:HVAC:DetailedInformation:holding4 'Modbus data', channel modbus:data:HVAC:DetailedInformation:holding4:rol
lershutter will be updated to '20' (type PercentType). Numeric state '20' and bool value 'true'
2018-01-12 10:39:10.019 [TRACE] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:HVAC:DetailedInformation:holding4 'Modbus data', channel modbus:data:HVAC:DetailedInformation:holding4:dim
mer will be updated to 'ON' (type OnOffType). Numeric state '20' and bool value 'true'
2018-01-12 10:39:10.020 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Operation with task PollTaskImpl@786ba83e[request=ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@748793f[slaveId=254,f
unctionCode=READ_MULTIPLE_REGISTERS,start=4,length=1,maxTries=3],endpoint=ModbusTCPSlaveEndpoint@6ef8c4f2[address=192.168.8.199,port=502],callback=org.openhab.binding.modbus.handler.ModbusPollerThi
ngHandlerImpl$ReadCallbackDelegator@2fc27b3a]. Got a connection successfully [operation ID abc175ae-335f-48b1-a1ff-6f401cb4ec80]
2018-01-12 10:39:10.020 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Try 1 out of 3 [operation ID abc175ae-335f-48b1-a1ff-6f401cb4ec80]
2018-01-12 10:39:10.022 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Ensuring that enough time passes before retrying again. Sleeping if necessary [operation ID abc175ae-335f-48b1-a1ff-6f401cb4
ec80]
2018-01-12 10:39:10.023 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Sleep ended, slept abc175ae-335f-48b1-a1ff-6f401cb4ec80 [operation ID 0]
2018-01-12 10:39:10.024 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Going execute transaction with request request (FC=READ_MULTIPLE_REGISTERS): 00 00 00 00 00 06 fe 03 00 04 00 01  [operation
 ID abc175ae-335f-48b1-a1ff-6f401cb4ec80]
2018-01-12 10:39:10.024 [DEBUG] [nding.modbus.internal.Transformation] - transformed response is '20'
2018-01-12 10:39:10.025 [TRACE] [wimpi.modbus.io.ModbusTCPTransaction] - Sending request with transaction ID 4768: net.wimpi.modbus.msg.ReadMultipleRegistersRequest@25a225a4
2018-01-12 10:39:10.025 [DEBUG] [nding.modbus.internal.Transformation] - Transformed item state '20' (of type DecimalType) to a state 20 (of type DecimalType). Input state as string '20', transform
ed string '20', transformation 'default'
2018-01-12 10:39:10.026 [TRACE] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:HVAC:DetailedInformation:holding5 'Modbus data', channel modbus:data:HVAC:DetailedInformation:holding5:num
ber will be updated to '20' (type DecimalType). Numeric state '20' and bool value 'true'
2018-01-12 10:39:10.026 [DEBUG] [nding.modbus.internal.Transformation] - transformed response is '20'
2018-01-12 10:39:10.017 [TRACE] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:HVAC:modeSettings:komfoModeIntensiveHeating 'Modbus data', channel modbus:data:HVAC:modeSettings:komfoMode
IntensiveHeating:string will be updated to '0' (type StringType). Numeric state '0' and bool value 'false'
2018-01-12 10:39:10.027 [DEBUG] [nding.modbus.internal.Transformation] - Could not transform item state '20' (of type DecimalType) to a State (tried the following types: [class org.eclipse.smarthom
e.core.library.types.DateTimeType, class org.eclipse.smarthome.core.types.UnDefType])! Input state as string '20', transformed string '20', transformation 'default'
2018-01-12 10:39:10.027 [DEBUG] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:HVAC:DetailedInformation:holding5 'Modbus data', channel modbus:data:HVAC:DetailedInformation:holding5:dat
etime will not be updated since transformation was unsuccesful
2018-01-12 10:39:10.027 [DEBUG] [nding.modbus.internal.Transformation] - transformed response is '20'
2018-01-12 10:39:10.028 [DEBUG] [nding.modbus.internal.Transformation] - Transformed item state '20' (of type DecimalType) to a state 20 (of type StringType). Input state as string '20', transforme
d string '20', transformation 'default'
2018-01-12 10:39:10.028 [TRACE] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:HVAC:DetailedInformation:holding5 'Modbus data', channel modbus:data:HVAC:DetailedInformation:holding5:str
ing will be updated to '20' (type StringType). Numeric state '20' and bool value 'true'
2018-01-12 10:39:10.028 [TRACE] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:HVAC:modeSettings:komfoModeIntensiveHeating 'Modbus data', channel modbus:data:HVAC:modeSettings:komfoMode
IntensiveHeating:contact will be updated to 'CLOSED' (type OpenClosedType). Numeric state '0' and bool value 'false'
2018-01-12 10:39:10.029 [TRACE] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:HVAC:DetailedInformation:holding5 'Modbus data', channel modbus:data:HVAC:DetailedInformation:holding5:con
tact will be updated to 'OPEN' (type OpenClosedType). Numeric state '20' and bool value 'true'
2018-01-12 10:39:10.037 [DEBUG] [nding.modbus.internal.Transformation] - transformed response is '0'
2018-01-12 10:39:10.037 [DEBUG] [nding.modbus.internal.Transformation] - transformed response is '20'
2018-01-12 10:39:10.038 [DEBUG] [nding.modbus.internal.Transformation] - Transformed item state '20' (of type DecimalType) to a state 20 (of type PercentType). Input state as string '20', transformed string '20', transformation 'default'
2018-01-12 10:39:10.038 [TRACE] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:HVAC:DetailedInformation:holding5 'Modbus data', channel modbus:data:HVAC:DetailedInformation:holding5:rol
lershutter will be updated to '20' (type PercentType). Numeric state '20' and bool value 'true'
2018-01-12 10:39:10.038 [TRACE] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:HVAC:DetailedInformation:holding5 'Modbus data', channel modbus:data:HVAC:DetailedInformation:holding5:dim
mer will be updated to 'ON' (type OnOffType). Numeric state '20' and bool value 'true'
2018-01-12 10:39:10.038 [DEBUG] [nding.modbus.internal.Transformation] - Transformed item state '0' (of type DecimalType) to a state 0 (of type PercentType). Input state as string '0', transformed
string '0', transformation 'default'
2018-01-12 10:39:10.039 [TRACE] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:HVAC:DetailedInformation:holding5 'Modbus data', channel modbus:data:HVAC:DetailedInformation:holding5:swi
tch will be updated to 'ON' (type OnOffType). Numeric state '20' and bool value 'true'
2018-01-12 10:39:10.040 [TRACE] [wimpi.modbus.io.ModbusTCPTransaction] - Received response with transaction ID 4768
2018-01-12 10:39:10.042 [TRACE] [rt.modbus.internal.ModbusManagerImpl] - Response for read request (FC=3, transaction ID=4768): 12 a0 00 00 00 05 fe 03 02 00 02  [operation ID abc175ae-335f-48b1-a1
ff-6f401cb4ec80]
2018-01-12 10:39:10.043 [TRACE] [modbus.internal.ModbusLibraryWrapper] - Calling read response callback org.openhab.binding.modbus.handler.ModbusPollerThingHandlerImpl$ReadCallbackDelegator@2fc27b3
a for request ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@748793f[slaveId=254,functionCode=READ_MULTIPLE_REGISTERS,start=4,length=1,maxTries=3]. Response was net.wimpi.modbus.msg.ReadMulti
pleRegistersResponse@41689b8f
2018-01-12 10:39:10.046 [DEBUG] [nding.modbus.internal.Transformation] - transformed response is '2'
2018-01-12 10:39:10.047 [DEBUG] [nding.modbus.internal.Transformation] - Could not transform item state '2' (of type DecimalType) to a State (tried the following types: [class org.eclipse.smarthome
.core.library.types.DateTimeType, class org.eclipse.smarthome.core.types.UnDefType])! Input state as string '2', transformed string '2', transformation 'default'
2018-01-12 10:39:10.067 [TRACE] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:HVAC:CurrentMode:komfoCurrentMode 'Modbus data', channel modbus:data:HVAC:CurrentMode:komfoCurrentMode:swi
tch will be updated to 'ON' (type OnOffType). Numeric state '2' and bool value 'true'
2018-01-12 10:39:10.067 [DEBUG] [nding.modbus.internal.Transformation] - transformed response is '20.3'
2018-01-12 10:39:10.068 [DEBUG] [nding.modbus.internal.Transformation] - Transformed item state '203' (of type DecimalType) to a state 20.3 (of type DecimalType). Input state as string '203', trans
formed string '20.3', transformation 'JS(divide10.js)'
2018-01-12 10:39:10.068 [TRACE] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:HVAC:DetailedInformation:komfoSupplyFanIntensivity 'Modbus data', channel modbus:data:HVAC:DetailedInforma
tion:komfoSupplyFanIntensivity:number will be updated to '20.3' (type DecimalType). Numeric state '203' and bool value 'true'
2018-01-12 10:39:10.073 [DEBUG] [nding.modbus.internal.Transformation] - Transformed item state '100' (of type DecimalType) to a state 100 (of type DecimalType). Input state as string '100', transf
ormed string '100', transformation 'default'

About CPU:
When I set all poller to refresh=1000 I usually see the load of

top - 14:55:54 up 2 day, 11:39,  3 users,  load average: 6.79, 5.88, 3.93

Memory: ~1.7Gb...

Today I’ve changed poller to be various numbers, a mix, and can see less cpu/mem usage overall:

top - 11:15:54 up 1 day, 17:33,  3 users,  load average: 1.79, 1.88, 1.93
Tasks: 193 total,   1 running, 192 sleeping,   0 stopped,   0 zombie
%Cpu(s): 46.8 us,  6.6 sy,  0.0 ni, 45.9 id,  0.5 wa,  0.0 hi,  0.2 si,  0.0 st
KiB Mem :  7767316 total,  3406784 free,  1120244 used,  3240288 buff/cache
KiB Swap:  7973884 total,  7973884 free,        0 used.  6217528 avail Mem

Seems like if I try to poll my slave very frequently - it becomes a “hard” task :slight_smile:

The only remaining thing to work out left is - how to ensure stable connectivity, as I see time to time unsuccessful connections:

2018-01-12 11:39:25.794 [WARN ] [rt.modbus.internal.ModbusManagerImpl] - Try 1 out of 3 failed when executing request (ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@748793f[slaveId=254,functionCode=READ_MULTIPLE_REGISTERS,start=4,length=1,maxTries=3]). Will try again soon. Error was: net.wimpi.modbus.ModbusSlaveException Error Code = 6 [operation ID b79dba2d-c16d-407d-81d3-8cbaea985657]

thing:

Bridge modbus:tcp:HVAC [ host="192.168.8.199", port=502, id=254, timeBetweenTransactionsMillis=100, timeBetweenReconnectMillis=50, connectMaxTries=3, connectTimeoutMillis=100 ]

Regards

1 Like

I have an eastron sdm630 powermeter with modbus.

Is there a way to get the modbus data out of the meter using for example an esp8266 ?

Then send the modbus data with wifi.

And openhab will get the modbus data over network-connection.

So can i use your binding to read out the data?

Anybody knows how to do this?

Hi @halloween,

yes, you can achieve that. As long there is a nice write up for your powermeter [http://www.eastrongroup.com/data/uploads/Eastron_SDM630-Modbus_protocol_V1_5.pdf] and you can check i.e. [http://fab.cba.mit.edu/classes/863.14/tutorials/Programming/serialwifi.html] for Serial-to-Wifi communication example.

Once you get there - Modbus binding will be pretty straight forward to read/write data by Openhab.

regards

Yes @narf27, that is correct.

@ArC Thanks for the reply. Let me know if the issue happens again.

If I understand correctly, the cpu load is quite moderate (below 5%)?

The error 6 is interesting. Does it work when the binding retries (in your log try 1/3 fails but does the second try work?)?

Best
Sami

@ssalonen, yes, CPU looks ok now.
Since I put connectMaxTries=3 I only see the message once:

2018-01-12 14:35:13.710 [WARN ] [rt.modbus.internal.ModbusManagerImpl] - Try 1 out of 3 failed when executing request (ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@313519cd[slaveId=254,functionCode=READ_MULTIPLE_REGISTERS,start=99,length=24,maxTries=3]). Will try again soon. Error was: net.wimpi.modbus.ModbusSlaveException Error Code = 6 [operation ID ab422011-157f-4673-b9a4-e980c703068a]

do not see 2/3 or 3/3 as an error/warn and the values seems being updated afterwards. So my only guess is that I’m lucky that trying to poll data at the same time when the unit is doing something etc, who knows.

and the error of 6 (advised by you earlier) shows that the slave is busy at that moment.

Regards

1 Like

I have to read holding registers from a wide range of addresses. For that reason I had defined a couple of holding pollers. But only the first holding-poller is working. Dos I have to create for every holding-poller a new *.things-file?

// EMA.things
Bridge modbus:tcp:ema [ host="192.168.10.210", port=502, id=1 ] {
    
	Bridge poller holding [ start=10011, length=4, refresh=5000, type="holding" ] {
        Thing data AL_RK_EINGANG [ readStart="10011", readValueType="uint16", readTransform="MAP(EMA.map)" ]
        Thing data AL_MK_EINGANG [ readStart="10012", readValueType="uint16", readTransform="MAP(EMA.map)" ]
        Thing data AL_MK_KUCHE_L [ readStart="10013", readValueType="uint16", readTransform="MAP(EMA.map)" ]
        //Thing data BUS1001_4 [ readStart="10014", readValueType="uint16", readTransform="MAP(EMA.map)" ]
	}

    Bridge poller holding [ start=10021, length=4, refresh=5000, type="holding" ] {
        Thing data AL_MK_WOHNEN_L [ readStart="10021", readValueType="uint16", readTransform="MAP(EMA.map)" ]
        Thing data AL_MK_WOHNEN_R [ readStart="10022", readValueType="uint16", readTransform="MAP(EMA.map)" ]
        Thing data AL_MK_WOHNEN_K [ readStart="10023", readValueType="uint16", readTransform="MAP(EMA.map)" ]
        Thing data AL_PIR_WOHNEN [ readStart="10024", readValueType="uint16", readTransform="MAP(EMA.map)" ]
    }
 
    Bridge poller holding [ start=10031, length=4, refresh=5000, type="holding" ] {
        Thing data AL_MK_KUCHE_R [ readStart="10031", readValueType="uint16", readTransform="MAP(EMA.map)" ]
        //Thing data BUS1003_2 [ readStart="10032", readValueType="uint16", readTransform="MAP(EMA.map)" ]
        //Thing data BUS1003_3 [ readStart="10033", readValueType="uint16", readTransform="MAP(EMA.map)" ]
        //Thing data BUS1003_4 [ readStart="10034", readValueType="uint16", readTransform="MAP(EMA.map)" ]
    }
    
	Bridge poller holding [ start=10041, length=4, refresh=5000, type="holding" ] {
        //Thing data BUS1004_1 [ readStart="10041", readValueType="uint16", readTransform="MAP(EMA.map)" ]
        Thing data AL_MK_LUFTSCHUTZ [ readStart="10042", readValueType="uint16", readTransform="MAP(EMA.map)" ]
        //Thing data BUS1004_3 [ readStart="10043", readValueType="uint16", readTransform="MAP(EMA.map)" ]
        //Thing data BUS1004_4 [ readStart="10044", readValueType="uint16", readTransform="MAP(EMA.map)" ]
    }
    
	Bridge poller holding [ start=10051, length=4, refresh=5000, type="holding" ] {
        //Thing data BUS1005_1 [ readStart="10051", readValueType="uint16", readTransform="MAP(EMA.map)" ]
        Thing data AL_MK_BAD_K [ readStart="10052", readValueType="uint16", readTransform="MAP(EMA.map)" ]
        Thing data AL_MK_BAD_G [ readStart="10053", readValueType="uint16", readTransform="MAP(EMA.map)" ]
        //Thing data BUS1005_4 [ readStart="10054", readValueType="uint16", readTransform="MAP(EMA.map)" ]
    }
    
	Bridge poller holding [ start=30011, length=4, refresh=5000, type="holding" ] {
        Thing data AL_MK_KELLER [ readStart="30011", readValueType="uint16", readTransform="MAP(EMA.map)" ]
        Thing data AL_RK_KELLER [ readStart="30012", readValueType="uint16", readTransform="MAP(EMA.map)" ]
        //Thing data BUS3001_4 [ readStart="30013", readValueType="uint16", readTransform="MAP(EMA.map)" ]
        //Thing data BUS3001_4 [ readStart="30014", readValueType="uint16", readTransform="MAP(EMA.map)" ]
    }
    
	Bridge poller holding [ start=30051, length=4, refresh=5000, type="holding" ] {
        //Thing data BUS3005_1 [ readStart="30051", readValueType="uint16", readTransform="MAP(EMA.map)" ]
        Thing data AL_MK_SCHLAFEN_L [ readStart="30052", readValueType="uint16", readTransform="MAP(EMA.map)" ]
        Thing data AL_MK_SCHLAFEN_R [ readStart="30053", readValueType="uint16", readTransform="MAP(EMA.map)" ]
        //Thing data BUS3005_4 [ readStart="30054", readValueType="uint16", readTransform="MAP(EMA.map)" ]
    }
    
	Bridge poller holding [ start=60011, length=4, refresh=5000, type="holding" ] {
        Thing data AL_MK_WC [ readStart="60011", readValueType="uint16", readTransform="MAP(EMA.map)" ]
    }
    
	Bridge poller holding [ start=60031, length=4, refresh=5000, type="holding" ] {
        Thing data AL_MK_BURO_VORNE [ readStart="60031", readValueType="uint16", readTransform="MAP(EMA.map)" ]
    }
    
	Bridge poller holding [ start=60041, length=4, refresh=5000, type="holding" ] {
        Thing data AL_MK_BURO_SEITE [ readStart="60041", readValueType="uint16", readTransform="MAP(EMA.map)" ]
    }
    
	Bridge poller holding [ start=60051, length=4, refresh=5000, type="holding" ] {
        Thing data AL_MK_DUSCHE [ readStart="60051", readValueType="uint16", readTransform="MAP(EMA.map)" ]
    }
    
	Bridge poller holding [ start=60061, length=4, refresh=5000, type="holding" ] {
        Thing data AL_MK_GAESTEZIMMER [ readStart="60061", readValueType="uint16", readTransform="MAP(EMA.map)" ]
    }
    
	Bridge poller holding [ start=60071, length=4, refresh=5000, type="holding" ] {
        Thing data AL_MK_KINDERZIMMER [ readStart="60071", readValueType="uint16", readTransform="MAP(EMA.map)" ]
    }
}
1 Like

Ready made converters are available for RS485 or RS232 Modbus-RTU to Modbus-TCP over WiFi

There is no need to split to many things files, as far as I know. What do you mean by “not working”?

Best
Sami

Hi
First great job and many thanks to all here.
I want to give some feedback and several questions in the end.

My hardware

  • Raspi 3
  • non FTDI Modbus USB Converter
  • SDM630 Powermeter

My software on raspi

  • openhab (latest stable)
  • influxdb + grafana

Working PC with Win10:

  • I am not using eclipse, but I read something about switching to visual sorce code as next step…?

things:

Bridge modbus:serial:modbus1 [ port="/dev/ttyUSB0", id=1, baud=9600, stopBits="1", parity="none", dataBits=8, encoding="rtu" ] 
{
    	Bridge poller inputRegisters [ start=0, length=18, refresh=60000, type="input" ] {
        	Thing data phase1Volt [ readStart="0",  readValueType="float32" ]
        	Thing data phase2Volt [ readStart="2",  readValueType="float32" ]
		Thing data phase3Volt [ readStart="4",  readValueType="float32" ]
		Thing data phase1Amps [ readStart="6",  readValueType="float32" ]
        	Thing data phase2Amps [ readStart="8",  readValueType="float32" ]
		Thing data phase3Amps [ readStart="10", readValueType="float32" ]
		Thing data phase1Power [ readStart="12", readValueType="float32" ]
        	Thing data phase2Power [ readStart="14", readValueType="float32" ]
		Thing data phase3Power [ readStart="16", readValueType="float32" ]
	}
	Bridge poller inputRegisters2 [ start=48, length=12, refresh=60000, type="input" ] {
        	Thing data sumAmps [ readStart="48", readValueType="float32" ]
		//Thing data xxx [ readStart="50", readValueType="float32" ]
		Thing data totalPower [ readStart="52", readValueType="float32" ]
		//Thing data xxx [ readStart="54", readValueType="float32" ]
		Thing data totalVA [ readStart="56", readValueType="float32" ]
		//Thing data xxx [ readStart="58", readValueType="float32" ]
	}
	Bridge poller inputRegisters3 [ start=342, length=2, refresh=60000, type="input" ] {
		Thing data totalKWh [ readStart="342", readValueType="float32" ]
    	}
}

I didn’t understand first the adress rules, so I run into troubles with

  • modbus-adresses, like 30049 (sumAmps) and the corresponding input read with start=48 instead of 49
  • readStart must also be start (or higher) from start-adress, I thought start means start-adress and readStart is an offset, so using first:
Bridge poller inputRegisters3 [ start=342, length=2, refresh=60000, type="input" ] {
wrong:		Thing data totalKWh [ readStart="0", readValueType="float32" ]
correct:	Thing data totalKWh [ readStart="342", readValueType="float32" ]
}

but “wrong” ends in some errors (reading negative bits…), I didn’t read carefully enough :roll_eyes:.
Now all works fine, saving several datas to influx and generating graphs with grafana.

If someone wants item or other settings, simple tell, i don’t want to spam too much with my first entry :sweat_smile:

Questions:
A) What is the difference beetween same or unique Bridge poller “names”? (look at @aco example)
B) I am using marketplace binding inside openhab (level beta) to install the two modbus bindings. How to keep them updated? How can I see which “version” I use?
C) Here are some log-Errors, I am not sure, what I can do to avoid this:


This I see a often in an hour, with polling every Minute:

2018-01-13 16:13:23.566 [ERROR] [t.wimpi.modbus.io.ModbusRTUTransport] - Last request: 01 04 01 56 00 02 90 27

2018-01-13 16:13:23.569 [ERROR] [t.wimpi.modbus.io.ModbusRTUTransport] - failed to read: Error reading response (EOF)

2018-01-13 16:13:23.574 [ERROR] [pi.modbus.io.ModbusSerialTransaction] - execute try 1/1 error: I/O exception: IOException Error reading response (EOF). Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@1a814e6 (unit id 1 & transaction 351). Serial parameters: SerialParameters@10214c8[portName=/dev/ttyUSB0,baudRate=9600,flowControlIn=none,flowControlOut=none,databits=8,stopbits=1,parity=none,encoding=rtu,echo=false,receiveTimeoutMillis=1500]

2018-01-13 16:13:23.577 [ERROR] [pi.modbus.io.ModbusSerialTransaction] - execute reached max tries 1, throwing last error: I/O exception: IOException Error reading response (EOF). Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@1a814e6 (unit id 1 & transaction 351). Serial parameters: SerialParameters@10214c8[portName=/dev/ttyUSB0,baudRate=9600,flowControlIn=none,flowControlOut=none,databits=8,stopbits=1,parity=none,encoding=rtu,echo=false,receiveTimeoutMillis=1500]

2018-01-13 16:13:23.581 [WARN ] [rt.modbus.internal.ModbusManagerImpl] - Try 1 out of 3 failed when executing request (ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@11a50e0[slaveId=1,functionCode=READ_INPUT_REGISTERS,start=342,length=2,maxTries=3]). Will try again soon. Error was I/O error, so reseting the connection. Error details: net.wimpi.modbus.ModbusIOException I/O exception: IOException Error reading response (EOF) [operation ID d7066bd7-2894-4b58-9ac3-f4235a76cad0]

This I saw only once last hours:

2018-01-13 15:54:10.815 [ERROR] [t.wimpi.modbus.io.ModbusRTUTransport] - awaited 38 bytes, but received 16

2018-01-13 15:54:10.818 [ERROR] [t.wimpi.modbus.io.ModbusRTUTransport] - Last request: 01 04 00 00 00 12 70 07

2018-01-13 15:54:10.820 [ERROR] [t.wimpi.modbus.io.ModbusRTUTransport] - failed to read: CRC Error in received frame: 17 bytes: 01 04 24 43 6a bf 88 43 6b 76 13 43 6a 1c 64 3f 24 

2018-01-13 15:54:10.823 [ERROR] [pi.modbus.io.ModbusSerialTransaction] - execute try 1/1 error: I/O exception: IOException CRC Error in received frame: 17 bytes: 01 04 24 43 6a bf 88 43 6b 76 13 43 6a 1c 64 3f 24 . Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@71949c (unit id 1 & transaction 288). Serial parameters: SerialParameters@10214c8[portName=/dev/ttyUSB0,baudRate=9600,flowControlIn=none,flowControlOut=none,databits=8,stopbits=1,parity=none,encoding=rtu,echo=false,receiveTimeoutMillis=1500]

2018-01-13 15:54:10.826 [ERROR] [pi.modbus.io.ModbusSerialTransaction] - execute reached max tries 1, throwing last error: I/O exception: IOException CRC Error in received frame: 17 bytes: 01 04 24 43 6a bf 88 43 6b 76 13 43 6a 1c 64 3f 24 . Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@71949c (unit id 1 & transaction 288). Serial parameters: SerialParameters@10214c8[portName=/dev/ttyUSB0,baudRate=9600,flowControlIn=none,flowControlOut=none,databits=8,stopbits=1,parity=none,encoding=rtu,echo=false,receiveTimeoutMillis=1500]

2018-01-13 15:54:10.828 [WARN ] [rt.modbus.internal.ModbusManagerImpl] - Try 1 out of 3 failed when executing request (ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@1f2c74c[slaveId=1,functionCode=READ_INPUT_REGISTERS,start=0,length=18,maxTries=3]). Will try again soon. Error was I/O error, so reseting the connection. Error details: net.wimpi.modbus.ModbusIOException I/O exception: IOException CRC Error in received frame: 17 bytes: 01 04 24 43 6a bf 88 43 6b 76 13 43 6a 1c 64 3f 24  [operation ID 9cdcd858-e467-4cf4-b0f6-02a0e9139345]

2018-01-13 15:54:12.692 [ERROR] [t.wimpi.modbus.io.ModbusRTUTransport] - Last request: 01 04 00 00 00 12 70 07

2018-01-13 15:54:12.694 [ERROR] [t.wimpi.modbus.io.ModbusRTUTransport] - failed to read: Error reading response (EOF)

2018-01-13 15:54:12.696 [ERROR] [pi.modbus.io.ModbusSerialTransaction] - execute try 1/1 error: I/O exception: IOException Error reading response (EOF). Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@6a4820 (unit id 1 & transaction 289). Serial parameters: SerialParameters@10214c8[portName=/dev/ttyUSB0,baudRate=9600,flowControlIn=none,flowControlOut=none,databits=8,stopbits=1,parity=none,encoding=rtu,echo=false,receiveTimeoutMillis=1500]

2018-01-13 15:54:12.699 [ERROR] [pi.modbus.io.ModbusSerialTransaction] - execute reached max tries 1, throwing last error: I/O exception: IOException Error reading response (EOF). Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@6a4820 (unit id 1 & transaction 289). Serial parameters: SerialParameters@10214c8[portName=/dev/ttyUSB0,baudRate=9600,flowControlIn=none,flowControlOut=none,databits=8,stopbits=1,parity=none,encoding=rtu,echo=false,receiveTimeoutMillis=1500]

2018-01-13 15:54:12.701 [WARN ] [rt.modbus.internal.ModbusManagerImpl] - Try 2 out of 3 failed when executing request (ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@1f2c74c[slaveId=1,functionCode=READ_INPUT_REGISTERS,start=0,length=18,maxTries=3]). Will try again soon. Error was I/O error, so reseting the connection. Error details: 
net.wimpi.modbus.ModbusIOException I/O exception: IOException Error reading response (EOF) [operation ID 9cdcd858-e467-4cf4-b0f6-02a0e9139345]

I only can see the first tree things: I can’t find any error in the log (only Error logging):

Problem Solved. I had not realized that I had to set for every poller a different name (holding1, holding2, …)