Hi,

I’m starting a project for my smart home with openhab2. I want to avoid wireless systems and use a wired network. I choose the RS485 Modbus. I will connect some arduinos on the modbus with sensors and switches.

I’m trying now to start with a simple example just for testing purposes of swithing a LED on the arduino throught a modbus connection between the arduino and the Raspberry Pi with Openhab2.

I have this material:

  • Raspberry Pi with Openhab2 (raspbian);
  • USB-to-RS485 FT232 FTDI Adapter (to connect the Raspberry pi to Modbus); IMG
  • MAX485 RS-485-TTL Module (to connect arduino to Modbus); IMG

Connection:
[Raspberry Pi] ----- [USB-to-RS485 FTDI Adapter] =========== [MAX485 RS-485-TTL Module] ------- Arduino

I connected everything in accordance with this image:
https://techsparx.com/energy-system/modbus/img/HTB1vCDNGFXXXXbCXVXXq6xXFXXXI.jpg

Can anyone explain how to make the example of making a LED blink on the arduino side using a switch on the Openhab?

I tried some examples from the internet but without success. I also tried with several USB adapters (I have 3 different).

I think It will be very useful for others to have this example as a wired way of connect things on openhab2.

Hello everyone…

i´m trying to get some data from a EPEVER/Tracer, but i only get errors :disappointed_relieved:

To see if “something” is working i first tried with QModBus over a virtual Com-Port:



what is working fine so far.

After this i tried to do the same thing with openhab:

Bridge modbus:tcp:endpointTCP [ host="192.168.125.128", port=502, id=1, reconnectAfterMillis=10 ] {
    Bridge poller input [ start=12544, length=20, refresh=30000, type="input" ] {
        Thing data do2 [ readStart="12544" , readValueType="uint16"]
        Thing data do3 [ readStart="12545", readValueType="int16"]
        Thing data do4 [ readStart="12546", readValueType="uint16"]
        Thing data do5 [ readStart="12547", readValueType="int16"]
    }
}

And it looks like the Binding does not connect to my USR:

2018-04-08 17:30:53.930 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute try 1/1 error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@1db070f (unit id 1 & transaction 111). Address: /192.168.125.128:502

2018-04-08 17:30:53.932 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute reached max tries 1, throwing last error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@1db070f (unit id 1 & transaction 111). Address: /192.168.125.128:502

2018-04-08 17:30:53.936 [ERROR] [rt.modbus.internal.ModbusManagerImpl] - Last try 3 failed when executing request (ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@1a48b4[slaveId=1,functionCode=READ_INPUT_REGISTERS,start=12544,length=20,maxTries=3]). Aborting. Error was I/O error, so reseting the connection. Error details: net.wimpi.modbus.ModbusIOException I/O exception: SocketTimeoutException Read timed out [operation ID 3eaf4848-d90d-470a-987e-8d4a985e01ff]

2018-04-08 17:30:53.957 [ERROR] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:endpointTCP:input:do2 'Modbus data' had ModbusSlaveIOExceptionImpl error on read: ModbusSlaveIOException(cause=ModbusIOException, EOF=false, message='I/O exception: SocketTimeoutException Read timed out', cause=null)

2018-04-08 17:30:53.964 [ERROR] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:endpointTCP:input:do3 'Modbus data' had ModbusSlaveIOExceptionImpl error on read: ModbusSlaveIOException(cause=ModbusIOException, EOF=false, message='I/O exception: SocketTimeoutException Read timed out', cause=null)

2018-04-08 17:30:53.978 [ERROR] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:endpointTCP:input:do4 'Modbus data' had ModbusSlaveIOExceptionImpl error on read: ModbusSlaveIOException(cause=ModbusIOException, EOF=false, message='I/O exception: SocketTimeoutException Read timed out', cause=null)

2018-04-08 17:30:53.986 [ERROR] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:endpointTCP:input:do5 'Modbus data' had ModbusSlaveIOExceptionImpl error on read: ModbusSlaveIOException(cause=ModbusIOException, EOF=false, message='I/O exception: SocketTimeoutException Read timed out', cause=null)

2018-04-08 17:31:26.958 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute try 1/1 error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@159089a (unit id 1 & transaction 112). Address: /192.168.125.128:502

2018-04-08 17:31:26.965 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute reached max tries 1, throwing last error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@159089a (unit id 1 & transaction 112). Address: /192.168.125.128:502

2018-04-08 17:31:26.968 [WARN ] [rt.modbus.internal.ModbusManagerImpl] - Try 1 out of 3 failed when executing request (ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@1a48b4[slaveId=1,functionCode=READ_INPUT_REGISTERS,start=12544,length=20,maxTries=3]). Will try again soon. Error was I/O error, so reseting the connection. Error details: net.wimpi.modbus.ModbusIOException I/O exception: SocketTimeoutException Read timed out [operation ID 6e6d441b-a093-4c52-b404-bbea609dfbab]

2018-04-08 17:31:30.039 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute try 1/1 error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@12f9359 (unit id 1 & transaction 113). Address: /192.168.125.128:502

2018-04-08 17:31:30.042 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute reached max tries 1, throwing last error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@12f9359 (unit id 1 & transaction 113). Address: /192.168.125.128:502

2018-04-08 17:31:30.045 [WARN ] [rt.modbus.internal.ModbusManagerImpl] - Try 2 out of 3 failed when executing request (ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@1a48b4[slaveId=1,functionCode=READ_INPUT_REGISTERS,start=12544,length=20,maxTries=3]). Will try again soon. Error was I/O error, so reseting the connection. Error details: net.wimpi.modbus.ModbusIOException I/O exception: SocketTimeoutException Read timed out [operation ID 6e6d441b-a093-4c52-b404-bbea609dfbab]

Can somebody see my error?!

Thank you very much - Greetings Tom

Ok, I found my error - i only had to switch the USR to “ModbusTCP” - that was all.

But this brings me to my next problem:
If i only use one poller i am able to get data every second.
If i use more than one poller i get my Timeout-Problems again - as far as i understand the EPEVER/Tracer i am not allowed to have more than one request at the same time.

After many tries i´m nearly giving up - how can i execute a pollar if the previous pollar is finished?

Hope anybody can help… Tom

Hi,

The binding makes sure only one connection is established at a time. So even if you have many pollers defined, they will wait each other.

That said, perhaps the interval between requests is too short for your serial device? In Modbus RTU, there should be enough silent period between the messages. To control this, check out the advanced parameters of your tcp thing.

Or perhaps there is some parameter in the “USR IOT” device that could help?

I think I have seen the USR IOT dashboard also before. By opening a new thread, you might be able to get help more easily – perhaps someone has had similar issues.

Best,
Sami

Hello @ssalonen, thank you for your answer.

I just found out, that changing/saving the configuration is messing the Tracer up.
If i restart the Tracer each time i made a change it is running quite well.
Can the binding head off that somehow?

Looking for the perfect timing now…

This is working quite well:

Bridge modbus:tcp:EPEVER [ host="192.168.125.128", port=502, id=1, timeBetweenTransactionsMillis=500, timeBetweenReconnectMillis=500, reconnectAfterMillis=0 ] {
	Bridge poller realtime_data1 [start=12548, length=14, refresh=1000, type="input"] {
		Thing data 3104 "Battery voltage"		@ "EPEVER"	[readStart="12548", readValueType="int16", readTransform="JS(divide100.js)"]
		Thing data 310C "Load Voltage"		@ "EPEVER"	[readStart="12556", readValueType="int16", readTransform="JS(divide100.js)"]
		Thing data 3110 "Battery Temperature"			@ "EPEVER"	[readStart="12560", readValueType="int16", readTransform="JS(divide100.js)"]
		Thing data 3111 "Temperature inside equipment"	@ "EPEVER"	[readStart="12561", readValueType="int16", readTransform="JS(divide100.js)"]
	}
	
	Bridge poller realtime_data3 [start=12570, length=1, refresh=1000, type="input"] {
		Thing data 311A "Battery SOC"			@ "EPEVER" [readStart="12570", readValueType="int16" ]
	}
	
	Bridge poller switch_value	[start=2, length=1, maxTries=5, refresh=1000, type="coil"] {
        Thing data 0002 [ readStart="2", readValueType="bit" , writeStart="2", writeValueType="bit", writeType="coil"]
	}
}

What is not working:
Bridge poller switch_value -> if i switch this via openhab everything is messed up again.
Switching this one works fine, as long as refresh=0 on all three pollers.

Here the errors:

2018-04-12 13:31:52.021 [ome.event.ItemCommandEvent] - Item 'EPEVER_0002_switch' received command ON

2018-04-12 13:31:52.029 [vent.ItemStateChangedEvent] - EPEVER_0002_switch changed from OFF to ON

2018-04-12 13:31:52.620 [vent.ItemStateChangedEvent] - EPEVER_3104_number changed from 25.41 to 25.4

2018-04-12 13:31:52.628 [vent.ItemStateChangedEvent] - EPEVER_3104_lastReadSuccess changed from 2018-04-12T13:31:50.699+0200 to 2018-04-12T13:31:52.607+0200

==> /var/log/openhab2/openhab.log <==

2018-04-12 13:31:55.975 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute try 1/1 error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.WriteCoilRequest@14d83b2 (unit id 1 & transaction 1368). Address: /192.168.125.128:502

2018-04-12 13:31:55.981 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute reached max tries 1, throwing last error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.WriteCoilRequest@14d83b2 (unit id 1 & transaction 1368). Address: /192.168.125.128:502

2018-04-12 13:31:55.987 [WARN ] [rt.modbus.internal.ModbusManagerImpl] - Try 1 out of 3 failed when executing request (ModbusWriteCoilRequestBlueprintImpl@16cfbe8[slaveId=1,reference=2,functionCode=WRITE_COIL,bits=SingleBitArray(true),maxTries=3]). Will try again soon. Error was I/O error, so reseting the connection. Error details: net.wimpi.modbus.ModbusIOException I/O exception: SocketTimeoutException Read timed out [operation ID a3b517fc-a961-4b70-9e03-da7db4788fa2]

2018-04-12 13:31:59.508 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute try 1/1 error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@19a58b4 (unit id 1 & transaction 1369). Address: /192.168.125.128:502

2018-04-12 13:31:59.512 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute reached max tries 1, throwing last error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@19a58b4 (unit id 1 & transaction 1369). Address: /192.168.125.128:502

2018-04-12 13:31:59.516 [WARN ] [rt.modbus.internal.ModbusManagerImpl] - Try 1 out of 3 failed when executing request (ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@1a7eaf3[slaveId=1,functionCode=READ_INPUT_REGISTERS,start=12570,length=1,maxTries=3]). Will try again soon. Error was I/O error, so reseting the connection. Error details: net.wimpi.modbus.ModbusIOException I/O exception: SocketTimeoutException Read timed out [operation ID 78742dd4-f1ab-44b6-b123-1ee072ab1ef0]

2018-04-12 13:32:03.057 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute try 1/1 error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.ReadCoilsRequest@1c8087b (unit id 1 & transaction 1370). Address: /192.168.125.128:502

2018-04-12 13:32:03.060 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute reached max tries 1, throwing last error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.ReadCoilsRequest@1c8087b (unit id 1 & transaction 1370). Address: /192.168.125.128:502

2018-04-12 13:32:03.064 [WARN ] [rt.modbus.internal.ModbusManagerImpl] - Try 1 out of 5 failed when executing request (ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@120789[slaveId=1,functionCode=READ_COILS,start=2,length=1,maxTries=5]). Will try again soon. Error was I/O error, so reseting the connection. Error details: net.wimpi.modbus.ModbusIOException I/O exception: SocketTimeoutException Read timed out [operation ID 514012bb-82d2-4df6-a91c-d89314f1864a]

2018-04-12 13:32:06.579 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute try 1/1 error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@a34c50 (unit id 1 & transaction 1371). Address: /192.168.125.128:502

2018-04-12 13:32:06.583 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute reached max tries 1, throwing last error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@a34c50 (unit id 1 & transaction 1371). Address: /192.168.125.128:502

2018-04-12 13:32:06.588 [WARN ] [rt.modbus.internal.ModbusManagerImpl] - Try 1 out of 3 failed when executing request (ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@43e080[slaveId=1,functionCode=READ_INPUT_REGISTERS,start=12548,length=14,maxTries=3]). Will try again soon. Error was I/O error, so reseting the connection. Error details: net.wimpi.modbus.ModbusIOException I/O exception: SocketTimeoutException Read timed out [operation ID 80ae9bed-4f8c-4556-af00-806f7aa4f8b5]

2018-04-12 13:32:10.103 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute try 1/1 error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.WriteCoilRequest@11d027b (unit id 1 & transaction 1372). Address: /192.168.125.128:502

2018-04-12 13:32:10.108 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute reached max tries 1, throwing last error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.WriteCoilRequest@11d027b (unit id 1 & transaction 1372). Address: /192.168.125.128:502

2018-04-12 13:32:10.114 [WARN ] [rt.modbus.internal.ModbusManagerImpl] - Try 2 out of 3 failed when executing request (ModbusWriteCoilRequestBlueprintImpl@16cfbe8[slaveId=1,reference=2,functionCode=WRITE_COIL,bits=SingleBitArray(true),maxTries=3]). Will try again soon. Error was I/O error, so reseting the connection. Error details: net.wimpi.modbus.ModbusIOException I/O exception: SocketTimeoutException Read timed out [operation ID a3b517fc-a961-4b70-9e03-da7db4788fa2]

2018-04-12 13:32:13.629 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute try 1/1 error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@e331fd (unit id 1 & transaction 1373). Address: /192.168.125.128:502

2018-04-12 13:32:13.631 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute reached max tries 1, throwing last error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@e331fd (unit id 1 & transaction 1373). Address: /192.168.125.128:502

2018-04-12 13:32:13.635 [WARN ] [rt.modbus.internal.ModbusManagerImpl] - Try 2 out of 3 failed when executing request (ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@1a7eaf3[slaveId=1,functionCode=READ_INPUT_REGISTERS,start=12570,length=1,maxTries=3]). Will try again soon. Error was I/O error, so reseting the connection. Error details: net.wimpi.modbus.ModbusIOException I/O exception: SocketTimeoutException Read timed out [operation ID 78742dd4-f1ab-44b6-b123-1ee072ab1ef0]

2018-04-12 13:32:17.152 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute try 1/1 error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.ReadCoilsRequest@3eb32e (unit id 1 & transaction 1374). Address: /192.168.125.128:502

2018-04-12 13:32:17.155 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute reached max tries 1, throwing last error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.ReadCoilsRequest@3eb32e (unit id 1 & transaction 1374). Address: /192.168.125.128:502

2018-04-12 13:32:17.158 [WARN ] [rt.modbus.internal.ModbusManagerImpl] - Try 2 out of 5 failed when executing request (ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@120789[slaveId=1,functionCode=READ_COILS,start=2,length=1,maxTries=5]). Will try again soon. Error was I/O error, so reseting the connection. Error details: net.wimpi.modbus.ModbusIOException I/O exception: SocketTimeoutException Read timed out [operation ID 514012bb-82d2-4df6-a91c-d89314f1864a]

2018-04-12 13:32:20.672 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute try 1/1 error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@1102a80 (unit id 1 & transaction 1375). Address: /192.168.125.128:502

2018-04-12 13:32:20.676 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute reached max tries 1, throwing last error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@1102a80 (unit id 1 & transaction 1375). Address: /192.168.125.128:502

2018-04-12 13:32:20.683 [WARN ] [rt.modbus.internal.ModbusManagerImpl] - Try 2 out of 3 failed when executing request (ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@43e080[slaveId=1,functionCode=READ_INPUT_REGISTERS,start=12548,length=14,maxTries=3]). Will try again soon. Error was I/O error, so reseting the connection. Error details: net.wimpi.modbus.ModbusIOException I/O exception: SocketTimeoutException Read timed out [operation ID 80ae9bed-4f8c-4556-af00-806f7aa4f8b5]

2018-04-12 13:32:24.198 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute try 1/1 error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.WriteCoilRequest@1ce13b7 (unit id 1 & transaction 1376). Address: /192.168.125.128:502

2018-04-12 13:32:24.203 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute reached max tries 1, throwing last error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.WriteCoilRequest@1ce13b7 (unit id 1 & transaction 1376). Address: /192.168.125.128:502

2018-04-12 13:32:24.209 [ERROR] [rt.modbus.internal.ModbusManagerImpl] - Last try 3 failed when executing request (ModbusWriteCoilRequestBlueprintImpl@16cfbe8[slaveId=1,reference=2,functionCode=WRITE_COIL,bits=SingleBitArray(true),maxTries=3]). Aborting. Error was I/O error, so reseting the connection. Error details: net.wimpi.modbus.ModbusIOException I/O exception: SocketTimeoutException Read timed out [operation ID a3b517fc-a961-4b70-9e03-da7db4788fa2]

2018-04-12 13:32:24.224 [ERROR] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:EPEVER:switch_value:0002 'Modbus data' had ModbusSlaveIOExceptionImpl error on write: ModbusSlaveIOException(cause=ModbusIOException, EOF=false, message='I/O exception: SocketTimeoutException Read timed out', cause=null)

==> /var/log/openhab2/events.log <==

2018-04-12 13:32:24.243 [hingStatusInfoChangedEvent] - 'modbus:data:EPEVER:switch_value:0002' changed from ONLINE to OFFLINE (COMMUNICATION_ERROR): Error (ModbusSlaveIOExceptionImpl) with write. Request: ModbusWriteCoilRequestBlueprintImpl@16cfbe8[slaveId=1,reference=2,functionCode=WRITE_COIL,bits=SingleBitArray(true),maxTries=3]. Description: ModbusSlaveIOException(cause=ModbusIOException, EOF=false, message='I/O exception: SocketTimeoutException Read timed out', cause=null). Message: null

==> /var/log/openhab2/openhab.log <==

2018-04-12 13:32:27.725 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute try 1/1 error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@bea531 (unit id 1 & transaction 1377). Address: /192.168.125.128:502

2018-04-12 13:32:27.728 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute reached max tries 1, throwing last error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@bea531 (unit id 1 & transaction 1377). Address: /192.168.125.128:502

2018-04-12 13:32:27.733 [ERROR] [rt.modbus.internal.ModbusManagerImpl] - Last try 3 failed when executing request (ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@1a7eaf3[slaveId=1,functionCode=READ_INPUT_REGISTERS,start=12570,length=1,maxTries=3]). Aborting. Error was I/O error, so reseting the connection. Error details: net.wimpi.modbus.ModbusIOException I/O exception: SocketTimeoutException Read timed out [operation ID 78742dd4-f1ab-44b6-b123-1ee072ab1ef0]

2018-04-12 13:32:27.744 [ERROR] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:EPEVER:realtime_data3:311A 'Battery SOC' had ModbusSlaveIOExceptionImpl error on read: ModbusSlaveIOException(cause=ModbusIOException, EOF=false, message='I/O exception: SocketTimeoutException Read timed out', cause=null)

==> /var/log/openhab2/events.log <==

2018-04-12 13:32:27.763 [hingStatusInfoChangedEvent] - 'modbus:data:EPEVER:realtime_data3:311A' changed from ONLINE to OFFLINE (COMMUNICATION_ERROR): Error (ModbusSlaveIOExceptionImpl) with read. Request: ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@1a7eaf3[slaveId=1,functionCode=READ_INPUT_REGISTERS,start=12570,length=1,maxTries=3]. Description: ModbusSlaveIOException(cause=ModbusIOException, EOF=false, message='I/O exception: SocketTimeoutException Read timed out', cause=null). Message: null

2018-04-12 13:32:27.770 [hingStatusInfoChangedEvent] - 'modbus:poller:EPEVER:realtime_data3' changed from ONLINE to OFFLINE (COMMUNICATION_ERROR): Error with read: org.openhab.io.transport.modbus.internal.ModbusSlaveIOExceptionImpl: null

2018-04-12 13:32:27.777 [vent.ItemStateChangedEvent] - EPEVER_311A_lastReadError changed from 2018-04-12T13:21:34.559+0200 to 2018-04-12T13:32:27.749+0200

2018-04-12 13:32:27.785 [hingStatusInfoChangedEvent] - 'modbus:data:EPEVER:realtime_data3:311A' changed from OFFLINE (COMMUNICATION_ERROR): Error (ModbusSlaveIOExceptionImpl) with read. Request: ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@1a7eaf3[slaveId=1,functionCode=READ_INPUT_REGISTERS,start=12570,length=1,maxTries=3]. Description: ModbusSlaveIOException(cause=ModbusIOException, EOF=false, message='I/O exception: SocketTimeoutException Read timed out', cause=null). Message: null to OFFLINE: Thing disposed -- bridge initializing?

2018-04-12 13:32:27.794 [hingStatusInfoChangedEvent] - 'modbus:data:EPEVER:realtime_data3:311A' changed from OFFLINE: Thing disposed -- bridge initializing? to ONLINE

==> /var/log/openhab2/openhab.log <==

2018-04-12 13:32:31.256 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute try 1/1 error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.ReadCoilsRequest@598f3c (unit id 1 & transaction 1378). Address: /192.168.125.128:502

2018-04-12 13:32:31.261 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute reached max tries 1, throwing last error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.ReadCoilsRequest@598f3c (unit id 1 & transaction 1378). Address: /192.168.125.128:502

2018-04-12 13:32:31.265 [WARN ] [rt.modbus.internal.ModbusManagerImpl] - Try 3 out of 5 failed when executing request (ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@120789[slaveId=1,functionCode=READ_COILS,start=2,length=1,maxTries=5]). Will try again soon. Error was I/O error, so reseting the connection. Error details: net.wimpi.modbus.ModbusIOException I/O exception: SocketTimeoutException Read timed out [operation ID 514012bb-82d2-4df6-a91c-d89314f1864a]

2018-04-12 13:32:34.779 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute try 1/1 error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@15f4246 (unit id 1 & transaction 1379). Address: /192.168.125.128:502

2018-04-12 13:32:34.782 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute reached max tries 1, throwing last error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@15f4246 (unit id 1 & transaction 1379). Address: /192.168.125.128:502

2018-04-12 13:32:34.787 [ERROR] [rt.modbus.internal.ModbusManagerImpl] - Last try 3 failed when executing request (ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@43e080[slaveId=1,functionCode=READ_INPUT_REGISTERS,start=12548,length=14,maxTries=3]). Aborting. Error was I/O error, so reseting the connection. Error details: net.wimpi.modbus.ModbusIOException I/O exception: SocketTimeoutException Read timed out [operation ID 80ae9bed-4f8c-4556-af00-806f7aa4f8b5]

2018-04-12 13:32:34.799 [ERROR] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:EPEVER:realtime_data1:3104 'Battery voltage' had ModbusSlaveIOExceptionImpl error on read: ModbusSlaveIOException(cause=ModbusIOException, EOF=false, message='I/O exception: SocketTimeoutException Read timed out', cause=null)

2018-04-12 13:32:34.813 [ERROR] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:EPEVER:realtime_data1:310C 'Load Voltage' had ModbusSlaveIOExceptionImpl error on read: ModbusSlaveIOException(cause=ModbusIOException, EOF=false, message='I/O exception: SocketTimeoutException Read timed out', cause=null)

2018-04-12 13:32:34.824 [ERROR] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:EPEVER:realtime_data1:3110 'Battery Temperature' had ModbusSlaveIOExceptionImpl error on read: ModbusSlaveIOException(cause=ModbusIOException, EOF=false, message='I/O exception: SocketTimeoutException Read timed out', cause=null)

==> /var/log/openhab2/events.log <==

2018-04-12 13:32:34.827 [vent.ItemStateChangedEvent] - EPEVER_3104_lastReadError changed from 2018-04-12T13:21:34.670+0200 to 2018-04-12T13:32:34.805+0200

==> /var/log/openhab2/openhab.log <==

2018-04-12 13:32:34.837 [ERROR] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:EPEVER:realtime_data1:3111 'Temperature inside equipment' had ModbusSlaveIOExceptionImpl error on read: ModbusSlaveIOException(cause=ModbusIOException, EOF=false, message='I/O exception: SocketTimeoutException Read timed out', cause=null)

==> /var/log/openhab2/events.log <==

2018-04-12 13:32:34.858 [hingStatusInfoChangedEvent] - 'modbus:data:EPEVER:realtime_data1:3104' changed from ONLINE to OFFLINE (COMMUNICATION_ERROR): Error (ModbusSlaveIOExceptionImpl) with read. Request: ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@43e080[slaveId=1,functionCode=READ_INPUT_REGISTERS,start=12548,length=14,maxTries=3]. Description: ModbusSlaveIOException(cause=ModbusIOException, EOF=false, message='I/O exception: SocketTimeoutException Read timed out', cause=null). Message: null

2018-04-12 13:32:34.871 [hingStatusInfoChangedEvent] - 'modbus:data:EPEVER:realtime_data1:3104' changed from OFFLINE (COMMUNICATION_ERROR): Error (ModbusSlaveIOExceptionImpl) with read. Request: ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@43e080[slaveId=1,functionCode=READ_INPUT_REGISTERS,start=12548,length=14,maxTries=3]. Description: ModbusSlaveIOException(cause=ModbusIOException, EOF=false, message='I/O exception: SocketTimeoutException Read timed out', cause=null). Message: null to OFFLINE: Thing disposed -- bridge initializing?

2018-04-12 13:32:34.885 [hingStatusInfoChangedEvent] - 'modbus:data:EPEVER:realtime_data1:310C' changed from ONLINE to OFFLINE (COMMUNICATION_ERROR): Error (ModbusSlaveIOExceptionImpl) with read. Request: ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@43e080[slaveId=1,functionCode=READ_INPUT_REGISTERS,start=12548,length=14,maxTries=3]. Description: ModbusSlaveIOException(cause=ModbusIOException, EOF=false, message='I/O exception: SocketTimeoutException Read timed out', cause=null). Message: null

2018-04-12 13:32:34.902 [hingStatusInfoChangedEvent] - 'modbus:data:EPEVER:realtime_data1:3104' changed from OFFLINE: Thing disposed -- bridge initializing? to ONLINE

2018-04-12 13:32:34.909 [hingStatusInfoChangedEvent] - 'modbus:data:EPEVER:realtime_data1:3110' changed from ONLINE to OFFLINE (COMMUNICATION_ERROR): Error (ModbusSlaveIOExceptionImpl) with read. Request: ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@43e080[slaveId=1,functionCode=READ_INPUT_REGISTERS,start=12548,length=14,maxTries=3]. Description: ModbusSlaveIOException(cause=ModbusIOException, EOF=false, message='I/O exception: SocketTimeoutException Read timed out', cause=null). Message: null

2018-04-12 13:32:34.913 [hingStatusInfoChangedEvent] - 'modbus:data:EPEVER:realtime_data1:3111' changed from ONLINE to OFFLINE (COMMUNICATION_ERROR): Error (ModbusSlaveIOExceptionImpl) with read. Request: ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@43e080[slaveId=1,functionCode=READ_INPUT_REGISTERS,start=12548,length=14,maxTries=3]. Description: ModbusSlaveIOException(cause=ModbusIOException, EOF=false, message='I/O exception: SocketTimeoutException Read timed out', cause=null). Message: null

2018-04-12 13:32:34.920 [hingStatusInfoChangedEvent] - 'modbus:data:EPEVER:realtime_data1:3110' changed from OFFLINE (COMMUNICATION_ERROR): Error (ModbusSlaveIOExceptionImpl) with read. Request: ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@43e080[slaveId=1,functionCode=READ_INPUT_REGISTERS,start=12548,length=14,maxTries=3]. Description: ModbusSlaveIOException(cause=ModbusIOException, EOF=false, message='I/O exception: SocketTimeoutException Read timed out', cause=null). Message: null to OFFLINE: Thing disposed -- bridge initializing?

2018-04-12 13:32:34.924 [hingStatusInfoChangedEvent] - 'modbus:poller:EPEVER:realtime_data1' changed from ONLINE to OFFLINE (COMMUNICATION_ERROR): Error with read: org.openhab.io.transport.modbus.internal.ModbusSlaveIOExceptionImpl: null

2018-04-12 13:32:34.931 [hingStatusInfoChangedEvent] - 'modbus:data:EPEVER:realtime_data1:310C' changed from OFFLINE (COMMUNICATION_ERROR): Error (ModbusSlaveIOExceptionImpl) with read. Request: ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@43e080[slaveId=1,functionCode=READ_INPUT_REGISTERS,start=12548,length=14,maxTries=3]. Description: ModbusSlaveIOException(cause=ModbusIOException, EOF=false, message='I/O exception: SocketTimeoutException Read timed out', cause=null). Message: null to OFFLINE: Thing disposed -- bridge initializing?

2018-04-12 13:32:34.936 [hingStatusInfoChangedEvent] - 'modbus:data:EPEVER:realtime_data1:3110' changed from OFFLINE: Thing disposed -- bridge initializing? to ONLINE

2018-04-12 13:32:34.946 [hingStatusInfoChangedEvent] - 'modbus:data:EPEVER:realtime_data1:310C' changed from OFFLINE: Thing disposed -- bridge initializing? to ONLINE

2018-04-12 13:32:34.951 [hingStatusInfoChangedEvent] - 'modbus:data:EPEVER:realtime_data1:3111' changed from OFFLINE (COMMUNICATION_ERROR): Error (ModbusSlaveIOExceptionImpl) with read. Request: ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@43e080[slaveId=1,functionCode=READ_INPUT_REGISTERS,start=12548,length=14,maxTries=3]. Description: ModbusSlaveIOException(cause=ModbusIOException, EOF=false, message='I/O exception: SocketTimeoutException Read timed out', cause=null). Message: null to OFFLINE: Thing disposed -- bridge initializing?

2018-04-12 13:32:34.958 [hingStatusInfoChangedEvent] - 'modbus:data:EPEVER:realtime_data1:3111' changed from OFFLINE: Thing disposed -- bridge initializing? to ONLINE

==> /var/log/openhab2/openhab.log <==

2018-04-12 13:32:38.303 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute try 1/1 error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@1c5a0c8 (unit id 1 & transaction 1380). Address: /192.168.125.128:502

2018-04-12 13:32:38.310 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute reached max tries 1, throwing last error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@1c5a0c8 (unit id 1 & transaction 1380). Address: /192.168.125.128:502

2018-04-12 13:32:38.315 [WARN ] [rt.modbus.internal.ModbusManagerImpl] - Try 1 out of 3 failed when executing request (ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@1a7eaf3[slaveId=1,functionCode=READ_INPUT_REGISTERS,start=12570,length=1,maxTries=3]). Will try again soon. Error was I/O error, so reseting the connection. Error details: net.wimpi.modbus.ModbusIOException I/O exception: SocketTimeoutException Read timed out [operation ID 797c7f52-d1a5-4ee2-98f7-954589d4229c]

2018-04-12 13:32:41.828 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute try 1/1 error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.ReadCoilsRequest@76a09c (unit id 1 & transaction 1381). Address: /192.168.125.128:502

2018-04-12 13:32:41.830 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute reached max tries 1, throwing last error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.ReadCoilsRequest@76a09c (unit id 1 & transaction 1381). Address: /192.168.125.128:502

2018-04-12 13:32:41.833 [WARN ] [rt.modbus.internal.ModbusManagerImpl] - Try 4 out of 5 failed when executing request (ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@120789[slaveId=1,functionCode=READ_COILS,start=2,length=1,maxTries=5]). Will try again soon. Error was I/O error, so reseting the connection. Error details: net.wimpi.modbus.ModbusIOException I/O exception: SocketTimeoutException Read timed out [operation ID 514012bb-82d2-4df6-a91c-d89314f1864a]

2018-04-12 13:32:45.347 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute try 1/1 error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@104b945 (unit id 1 & transaction 1382). Address: /192.168.125.128:502

2018-04-12 13:32:45.351 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute reached max tries 1, throwing last error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@104b945 (unit id 1 & transaction 1382). Address: /192.168.125.128:502

2018-04-12 13:32:45.355 [WARN ] [rt.modbus.internal.ModbusManagerImpl] - Try 1 out of 3 failed when executing request (ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@43e080[slaveId=1,functionCode=READ_INPUT_REGISTERS,start=12548,length=14,maxTries=3]). Will try again soon. Error was I/O error, so reseting the connection. Error details: net.wimpi.modbus.ModbusIOException I/O exception: SocketTimeoutException Read timed out [operation ID ae28db66-88a7-4193-922e-eb0154efea0b]

2018-04-12 13:32:48.868 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute try 1/1 error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@218dbe (unit id 1 & transaction 1383). Address: /192.168.125.128:502

2018-04-12 13:32:48.870 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute reached max tries 1, throwing last error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@218dbe (unit id 1 & transaction 1383). Address: /192.168.125.128:502

2018-04-12 13:32:48.874 [WARN ] [rt.modbus.internal.ModbusManagerImpl] - Try 2 out of 3 failed when executing request (ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@1a7eaf3[slaveId=1,functionCode=READ_INPUT_REGISTERS,start=12570,length=1,maxTries=3]). Will try again soon. Error was I/O error, so reseting the connection. Error details: net.wimpi.modbus.ModbusIOException I/O exception: SocketTimeoutException Read timed out [operation ID 797c7f52-d1a5-4ee2-98f7-954589d4229c]

2018-04-12 13:32:52.396 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute try 1/1 error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.ReadCoilsRequest@4a33cb (unit id 1 & transaction 1384). Address: /192.168.125.128:502

2018-04-12 13:32:52.401 [ERROR] [wimpi.modbus.io.ModbusTCPTransaction] - execute reached max tries 1, throwing last error: I/O exception: SocketTimeoutException Read timed out. Request: net.wimpi.modbus.msg.ReadCoilsRequest@4a33cb (unit id 1 & transaction 1384). Address: /192.168.125.128:502

2018-04-12 13:32:52.407 [ERROR] [rt.modbus.internal.ModbusManagerImpl] - Last try 5 failed when executing request (ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@120789[slaveId=1,functionCode=READ_COILS,start=2,length=1,maxTries=5]). Aborting. Error was I/O error, so reseting the connection. Error details: net.wimpi.modbus.ModbusIOException I/O exception: SocketTimeoutException Read timed out [operation ID 514012bb-82d2-4df6-a91c-d89314f1864a]

2018-04-12 13:32:52.422 [ERROR] [odbus.handler.ModbusDataThingHandler] - Thing modbus:data:EPEVER:switch_value:0002 'Modbus data' had ModbusSlaveIOExceptionImpl error on read: ModbusSlaveIOException(cause=ModbusIOException, EOF=false, message='I/O exception: SocketTimeoutException Read timed out', cause=null)

==> /var/log/openhab2/events.log <==

2018-04-12 13:32:52.440 [vent.ItemStateChangedEvent] - EPEVER_0002_lastReadError changed from 2018-04-12T13:21:34.739+0200 to 2018-04-12T13:32:52.426+0200

2018-04-12 13:32:52.451 [hingStatusInfoChangedEvent] - 'modbus:data:EPEVER:switch_value:0002' changed from OFFLINE (COMMUNICATION_ERROR): Error (ModbusSlaveIOExceptionImpl) with read. Request: ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@120789[slaveId=1,functionCode=READ_COILS,start=2,length=1,maxTries=5]. Description: ModbusSlaveIOException(cause=ModbusIOException, EOF=false, message='I/O exception: SocketTimeoutException Read timed out', cause=null). Message: null to OFFLINE: Thing disposed -- bridge initializing?

2018-04-12 13:32:52.456 [hingStatusInfoChangedEvent] - 'modbus:data:EPEVER:switch_value:0002' changed from OFFLINE (COMMUNICATION_ERROR): Error (ModbusSlaveIOExceptionImpl) with write. Request: ModbusWriteCoilRequestBlueprintImpl@16cfbe8[slaveId=1,reference=2,functionCode=WRITE_COIL,bits=SingleBitArray(true),maxTries=3]. Description: ModbusSlaveIOException(cause=ModbusIOException, EOF=false, message='I/O exception: SocketTimeoutException Read timed out', cause=null). Message: null to OFFLINE (COMMUNICATION_ERROR): Error (ModbusSlaveIOExceptionImpl) with read. Request: ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@120789[slaveId=1,functionCode=READ_COILS,start=2,length=1,maxTries=5]. Description: ModbusSlaveIOException(cause=ModbusIOException, EOF=false, message='I/O exception: SocketTimeoutException Read timed out', cause=null). Message: null

2018-04-12 13:32:52.462 [hingStatusInfoChangedEvent] - 'modbus:data:EPEVER:switch_value:0002' changed from OFFLINE: Thing disposed -- bridge initializing? to ONLINE

After 5 Minutes off errors i restartet the Tracer - everything working well again.

Any hints here?

Thank you - Tom

As you probably know, this means that data would not be updated. Is that what you want?

“Bridge poller switch_value” and the “EPEVER_0002_switch” in the logs do not tell the corresponding thing and channel. Please paste the item configuration as well.

I’m afraid I do not know how to help you, sounds like problems with the device (Tracer?).

sry, here are all of them…
“Bridge poller switch_value” and the “EPEVER_0002_switch” they belong together.

Number		EPEVER_3104_number			"Spannung Batterie: [%s V]"											(gEPEVER, gPVTrend, gPV)	{channel="modbus:data:EPEVER:realtime_data1:3104:number"}
DateTime	EPEVER_3104_lastReadSuccess	"realtime_data1 last read [%1$td.%1$tm.%1$tY %1$tH:%1$tM:%1$tS]"	<time>	(gEPEVER)					{channel="modbus:data:EPEVER:realtime_data1:3104:lastReadSuccess"}
DateTime	EPEVER_3104_lastReadError	"realtime_data1 last error [%1$td.%1$tm.%1$tY %1$tH:%1$tM:%1$tS]"	<error>	(gEPEVER)					{channel="modbus:data:EPEVER:realtime_data1:3104:lastReadError"}

Number		EPEVER_310C_number			"Load voltage: [%s V]"												(gEPEVER, gPV)	{channel="modbus:data:EPEVER:realtime_data1:310C:number"}

Number		EPEVER_3110_number			"Temperatur Batterie: [%.2f °C]"									<temperature>	(gEPEVER, gPV)	{channel="modbus:data:EPEVER:realtime_data1:3110:number"}
Number		EPEVER_3111_number			"Temperatur Tracer: [%.2f °C]"										<temperature>	(gEPEVER, gPV)	{channel="modbus:data:EPEVER:realtime_data1:3111:number"}

Number		EPEVER_311A_number			"Battery SOC: [%d %%]"												<bat>	(gEPEVER, gPV)	{channel="modbus:data:EPEVER:realtime_data3:311A:number"}
DateTime	EPEVER_311A_lastReadSuccess	"realtime_data3 last read [%1$td.%1$tm.%1$tY %1$tH:%1$tM:%1$tS]"	<time>	(gEPEVER)	{channel="modbus:data:EPEVER:realtime_data3:311A:lastReadSuccess"}
DateTime	EPEVER_311A_lastReadError	"realtime_data3 last error [%1$td.%1$tm.%1$tY %1$tH:%1$tM:%1$tS]"	<error>	(gEPEVER)	{channel="modbus:data:EPEVER:realtime_data3:311A:lastReadError"}

Switch EPEVER_0002_switch      "[%s]"   (gEPEVER)    {channel="modbus:data:EPEVER:switch_value:0002:switch" }	
DateTime	EPEVER_0002_lastReadSuccess	"switch_value last read [%1$td.%1$tm.%1$tY %1$tH:%1$tM:%1$tS]"	<time>	(gEPEVER)	{channel="modbus:data:EPEVER:switch_value:0002:lastReadSuccess"}
DateTime	EPEVER_0002_lastReadError	"switch_value last error [%1$td.%1$tm.%1$tY %1$tH:%1$tM:%1$tS]"	<error>	(gEPEVER)	{channel="modbus:data:EPEVER:switch_value:0002:lastReadError"}
String EPEVER_0002_string      "[%s]"   (gEPEVER)    { channel="modbus:data:EPEVER:switch_value:0002:string" }

refresh=0 is not what i want - it was only to test the switch…

To get out of this errors it is helping to restart the Tracer.
It is NOT helping to cut the connection between OH an the Tracer (unpluging the USR) or restarting OH or…

Greetings, Tom

One last question - i hope…
What about sending a command - is this made “between” the pollers or simultaneously?

The EPEVER software is able to collect data and send it to the Tracer - so maybe they stop polling before sending?!

Regards

Same with commands, the binding makes sure only one connection and one transaction is active to the same device.

I suggest to open new thread regarding this device. Perhaps someone has practical experience with this device.

It certainly sounds that nothing on binding side can help here.

Anyone can help to make the Modbus RTU serial work? Please…

I recommend opening a new thread regarding this this, it’s a bit buried in this thread.

The binding supports modbus RTU. I am happy to help there when you have the rest ready (arduino etc)

Sami

New version available up (23/4) with some fixes and improvements:

  • grouped logging messages

  • update only linked channels (performance optimization)

  • throttling REFRESH commands. This is performance optimization for slower PCs (e.g. raspberry pi 3). When openHAB starts, all channels receive a REFRESH command which will translate to many modbus read requests which are queued. Clearing the queue takes quite some time, which leads to slow updates. UPDATE Apr 23: this was not needed after all – it seems that updating all the channels always was the thing that really suffocated openHAB. Throttling of REFRESH has been removed.

  • Sometimes the transport bundle was not operating properly, and raised the below error [1] (first reported by @gitMiguel here). This error was quite likely when updating the addon.

    Turns out this is an open issue/bug with the 3rd party library Apache pool (for more info POOL-338). It will be fixed eventually upstream, but until then I was able to make a workaround for the bug.

    java.lang.IllegalArgumentException: [org.apache.commons.pool2.impl.DefaultEvictionPolicy] does not implement EvictionPolicy
    

Best,
Sami

2 Likes

Hi All

I have been trying to access my SMA Solar inverter - I have no issues so far using a plain Modbus Poller, but with Modbus bindings for Openhab 2 (The very latest) i’m getting those in my logs:

16:34:07.550 [INFO ] [del.core.internal.ModelRepositoryImpl] - Refreshing model 'sma.things'
16:34:07.564 [INFO ] [ort.modbus.internal.ModbusManagerImpl] - Unregistering regular poll task PollTaskImpl@1ef66b81[request=ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@17ea7119[slaveId=3,functionCode=READ_INPUT_REGISTERS,start=30769,length=6,maxTries=3],endpoint=ModbusTCPSlaveEndpoint@773beafa[address=192.168.100.141,port=502],callback=org.openhab.binding.modbus.handler.ModbusPollerThingHandlerImpl$ReadCallbackDelegator@aff81b6b] (interrupting if necessary)
16:34:07.565 [INFO ] [ort.modbus.internal.ModbusManagerImpl] - Poll task PollTaskImpl@1ef66b81[request=ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@17ea7119[slaveId=3,functionCode=READ_INPUT_REGISTERS,start=30769,length=6,maxTries=3],endpoint=ModbusTCPSlaveEndpoint@773beafa[address=192.168.100.141,port=502],callback=org.openhab.binding.modbus.handler.ModbusPollerThingHandlerImpl$ReadCallbackDelegator@aff81b6b] canceled
16:34:07.574 [INFO ] [ome.event.ThingStatusInfoChangedEvent] - 'modbus:poller:endpointSMA:SMA_Power_A' changed from ONLINE to OFFLINE
16:34:07.593 [INFO ] [ort.modbus.internal.ModbusManagerImpl] - Unregistering regular poll task PollTaskImpl@3a46300b[request=ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@8f04dfe[slaveId=3,functionCode=READ_INPUT_REGISTERS,start=30957,length=6,maxTries=3],endpoint=ModbusTCPSlaveEndpoint@773beafa[address=192.168.100.141,port=502],callback=org.openhab.binding.modbus.handler.ModbusPollerThingHandlerImpl$ReadCallbackDelegator@aff81b6c] (interrupting if necessary)
16:34:07.593 [INFO ] [ort.modbus.internal.ModbusManagerImpl] - Poll task PollTaskImpl@3a46300b[request=ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@8f04dfe[slaveId=3,functionCode=READ_INPUT_REGISTERS,start=30957,length=6,maxTries=3],endpoint=ModbusTCPSlaveEndpoint@773beafa[address=192.168.100.141,port=502],callback=org.openhab.binding.modbus.handler.ModbusPollerThingHandlerImpl$ReadCallbackDelegator@aff81b6c] canceled
16:34:07.599 [INFO ] [smarthome.event.ThingUpdatedEvent    ] - Thing 'modbus:poller:endpointSMA:SMA_Power_A' has been updated.
16:34:07.606 [INFO ] [ome.event.ThingStatusInfoChangedEvent] - 'modbus:data:endpointSMA:SMA_Power_A:SMA_Power_A' changed from ONLINE to OFFLINE: Thing disposed -- bridge initializing?
16:34:07.606 [INFO ] [ome.event.ThingStatusInfoChangedEvent] - 'modbus:data:endpointSMA:SMA_Power_A:SMA_Power_A' changed from OFFLINE: Thing disposed -- bridge initializing? to ONLINE
16:34:07.606 [INFO ] [ome.event.ThingStatusInfoChangedEvent] - 'modbus:data:endpointSMA:SMA_Power_B:SMA_Power_B' changed from ONLINE to OFFLINE: Thing disposed -- bridge initializing?
16:34:07.607 [INFO ] [ome.event.ThingStatusInfoChangedEvent] - 'modbus:data:endpointSMA:SMA_Power_B:SMA_Power_B' changed from OFFLINE: Thing disposed -- bridge initializing? to OFFLINE (BRIDGE_OFFLINE): Poller modbus:poller:endpointSMA:SMA_Power_B 'Regular poll' has no poll task
16:34:07.611 [INFO ] [ome.event.ThingStatusInfoChangedEvent] - 'modbus:poller:endpointSMA:SMA_Power_B' changed from ONLINE to OFFLINE
16:34:07.612 [INFO ] [smarthome.event.ThingUpdatedEvent    ] - Thing 'modbus:poller:endpointSMA:SMA_Power_B' has been updated.
16:34:07.613 [INFO ] [ort.modbus.internal.ModbusManagerImpl] - Unregistering regular poll task PollTaskImpl@6024a064[request=ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@2a737eb3[slaveId=3,functionCode=READ_INPUT_REGISTERS,start=30537,length=2,maxTries=3],endpoint=ModbusTCPSlaveEndpoint@773beafa[address=192.168.100.141,port=502],callback=org.openhab.binding.modbus.handler.ModbusPollerThingHandlerImpl$ReadCallbackDelegator@556609ab] (interrupting if necessary)
16:34:07.613 [INFO ] [ort.modbus.internal.ModbusManagerImpl] - Poll task PollTaskImpl@6024a064[request=ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@2a737eb3[slaveId=3,functionCode=READ_INPUT_REGISTERS,start=30537,length=2,maxTries=3],endpoint=ModbusTCPSlaveEndpoint@773beafa[address=192.168.100.141,port=502],callback=org.openhab.binding.modbus.handler.ModbusPollerThingHandlerImpl$ReadCallbackDelegator@556609ab] canceled
16:34:07.617 [INFO ] [ome.event.ThingStatusInfoChangedEvent] - 'modbus:data:endpointSMA:SMA_Daily_Yield:SMA_Daily_Yield' changed from ONLINE to OFFLINE: Thing disposed -- bridge initializing?
16:34:07.617 [INFO ] [ome.event.ThingStatusInfoChangedEvent] - 'modbus:poller:endpointSMA:SMA_Daily_Yield' changed from ONLINE to OFFLINE
16:34:07.617 [INFO ] [ome.event.ThingStatusInfoChangedEvent] - 'modbus:data:endpointSMA:SMA_Daily_Yield:SMA_Daily_Yield' changed from OFFLINE: Thing disposed -- bridge initializing? to OFFLINE (BRIDGE_OFFLINE): Poller modbus:poller:endpointSMA:SMA_Daily_Yield 'Regular poll' has no poll task
16:34:07.618 [INFO ] [smarthome.event.ThingUpdatedEvent    ] - Thing 'modbus:poller:endpointSMA:SMA_Daily_Yield' has been updated.

My configuration is:

        Bridge modbus:tcp:endpointSMA [ host="192.168.100.141", port=502, id=3, connectMaxTries=3] {



	Bridge poller SMA_Power_A [ start=30769, length=6, refresh=5000, type="input" ] {
	    
	    	 Thing data SMA_Power_A [ readStart="30773", readValueType="int32", readTransform="JS(divide1000.js)" ]
	    
	   	 
	   	 }



	Bridge poller SMA_Power_B [ start=30957, length=6, refresh=5000, type="input" ] {
	    
	    	 Thing data SMA_Power_B [ readStart="30961", readValueType="int32", readTransform="JS(divide1000.js)" ]
	    	   	 
	   	 }

	Bridge poller SMA_Daily_Yield [ start=30537, length=2, refresh=5000, type="input" ] {
	    
	    	 Thing data SMA_Daily_Yield[ readStart="30537", readValueType="uint32", readTransform="JS(divide1000.js)" ]
	       	 
	   	 }

}

Anyone have an Idea?

I don’t see any error really, just things updating which causes things to go OFFLINE momentarily (no ERRORs just INFO)…

What is the final status of things?

Please paste the output or

smarthome:things list 

or alternatively screenshot of paper UI things section

66 % is offline, and communication with the device are very slow - when I access the device from ModbusPoll (Test Util) there are no issues.

Can you please open one of the data things and take a screenshot of the status message?

and can you do the same for Poller modbus:poller:endpointSMA:SMA_Power_B?