NibeGW, Nibe Heat Pump binding, Nibe F730

Hi,

does anyone know if nibegw (mentioned in Nibe Heatpump - Bindings | openHAB) should work with a Nibe F730? Also, should the binding work with it? Only the F750 is mentioned.

I got a RS485 USB adapter connect to a Raspberry Pi and connected that to my F730. Unfortunately, there seem to be a lot of checksum errors and the Nibe goes into Alarm 251 right away.

Any idea? I just updated by Nibe F730 to try to fix this checksum issue. Unfortunately, that didn’t change anything. I still get those checksum errors.

Would really like to get that NibeGW to work :slight_smile:

NibeGW doesn’t receive all the bytes from the serial port, which cause checksum errors. New frame start with 5C byte. Long frame which have checksum error should have 80 bytes of data. After 80 bytes of data is received, NibeGW calculate the checksum which does not match the checksum byte of the received frame. Data seems to contain other short frames (e.g. 5C 00 20 6B 00 4B) included to the data, which indicates that some bytes was not received.

What could that be caused by? Not the correct cabling? I am not using a resistor. Might have to find some better cabling (shielded CAT cable might be still around somewhere). I don’t (yet) have resistors yet, though.

Or could there be some other issue that causes this?

I had the same problem with F470.

Turned out that the pump was sending “too much” info which caused some buffer (in the RS485 adapter or in the driver? Dunno.) to fill up. When nibegw read from the serial port, it didn’t get the full message (which probably causes those solo chars in your screenshot right after long message) and determined that the checksum is wrong.

I modified the pump message to contain only 1 coil by using ModbusManager which shortened the message enough and I don’t get checksum errors anymore.

Have to check what is the limit and is it enough for my usage or should nibegw be modified to better handle a situation where message is split between serial port reads.

What does that mean exactly? Haven’t used ModbusManager before (maybe that’s an issue as well, maybe my Nibe doesn’t send any “relevant” data yet?).

I just installed it and added a few variables to my selection, saved the file to LOG.SET and opened that file. I don’t see anything where I could set “the pump message to contain only 1 coil”:

[NIBL;20221106;8310]
Divisors		1	1	1	10
Date	Time	SG Ready hot water	SG Ready heating	Hot water comfort mode	BT1 Outdoor Temperature [°C]
48284
48282
47041
40004