- Platform information:
- Hardware: Pi4
- OS: PiOS
- Java Runtime Environment: 1.8.0_161
- openHAB version: 2.5.11-1
I have a set of rules that run my boiler, heating valves and overall heating system. Late last winter I migrated my valves to homegear, and so I also installed the homematic binding. In general that works excellently. I was however having some issues with rules occassionally not running, which I normally resolved with a restart. Winter ended and it was no longer a problem, so I’ve spent no more time on the problem.
Even though it’s summer, it was a little colder today, and my mother-in-law is visiting, so I turned the heating on. And it didn’t run. And I have pretty good line of sight that the rule didn’t trigger from the event, as when I was last looking at this I turned on all debug logging, and haven’t turned it off.
This looks like some sort of thread stall or failure to fire events to me, as the problem corrects when I reboot with no code change, and the code itself never seems to get to the first debug statement, which is the first statement in the rule - so I think the rule isn’t triggering at all sometimes.
My questions are:
- Has anyone seen anything like this before - is there some obvious thing I’m missing before I spend time chasing?
- Could it be the Homematic binding causing it? I have no real reason to think that other than it was the last major change I made, but thought I’d ask. I can’t really remove the binding without things stopping working, and of course removing the binding requires a reboot, which usually fixes the problem anyway, so difficult to diagnose that way
On to the detail.
I have some items defined as so:
Group:Number:SUM DeviceValves (All)
Switch swMasterHeating "Heating Master" (InternalFlags, Switches, InitSwitchesOn, RestoreGroup)
Number BootValve "Boot Room Valve [%d %%]" (valveBoot, DeviceValves) { channel="homematic:HG-BC-RT-TRX-CyG-3:ABDD5864-8959-5743-FE7A-8ADC71DCD01D:MEQ1344264:1#VALVE_STATE" }
Number MasterValve "Master Valve [%d %%]" (valveMaster, DeviceValves) { channel="homematic:HG-BC-RT-TRX-CyG-3:4BCAAC30-44F5-BBDE-DF54-27D1B87DCE09:LEQ1133856:1#VALVE_STATE" }
# (a number of other valves)
Then a particular rule that should fire:
rule "Adjust heating state and timers whenever the amount of valve opening changes"
Item DeviceValves changed or
Item swMasterHeating changed
logDebug( 'boiler', 'Valve opening changed, deciding what to do, valve opening is ' + DeviceValves)
if ( swInitialisationDone.state == NULL || swInitialisationDone.state != ON ){
logInfo( 'boiler', 'Not running heating state rule - initialisation not done')
} else {
// count how many valves are at 100%
var Number numberValves100 = 0
DeviceValves.members.forEach( valve | {
if( valve.state as Number == 100 ){
numberValves100 = numberValves100 + 1
# - quite a bit of code in here, but ultimately we're not getting to the debug statement, and it compiles, so it's not probably relevant
In my event log I have both a valve change, and a change to swMasterHeating, but I never get the debug message from the rule firing. After rebooting, I do get the debug message, and the rule runs fine. So I believe that the rule itself works, the logic works, and the event usually fires (i.e. this can’t be a syntax problem, if it was a syntax problem it would never run).
That’s leaving me to think it’s some sort of thread stall or other event handling problem that stops the event being fired. Is that a thing that can/does happen in Openhab?
Event log:
2021-02-15 12:01:54.751 [vent.ItemStateChangedEvent] - numberFridgesEnergyUsage changed from 34.972 to 34.973
2021-02-15 12:02:01.099 [ome.event.ItemCommandEvent] - Item 'numberHeatingReturnTemp' received command 23
2021-02-15 12:02:01.105 [vent.ItemStateChangedEvent] - numberHeatingReturnTemp changed from 22.9 to 23
2021-02-15 12:02:24.926 [vent.ItemStateChangedEvent] - numberFridgesPower changed from 200.443 to 201.485
2021-02-15 12:02:24.934 [vent.ItemStateChangedEvent] - numberFridgesEnergyUsage changed from 34.973 to 34.975
2021-02-15 12:02:31.131 [ome.event.ItemCommandEvent] - Item 'BootValve' received command 10
2021-02-15 12:02:31.187 [nt.ItemStatePredictedEvent] - BootValve predicted to become 10
2021-02-15 12:02:31.219 [vent.ItemStateChangedEvent] - BootValve changed from 0 to 10
2021-02-15 12:02:31.228 [GroupItemStateChangedEvent] - DeviceValves changed from 236 to 246 through BootValve
2021-02-15 12:02:31.738 [ome.event.ItemCommandEvent] - Item 'numberDHWUpperCylinderTemp' received command 43.5
2021-02-15 12:02:31.749 [vent.ItemStateChangedEvent] - numberDHWUpperCylinderTemp changed from 43.6 to 43.5
2021-02-15 12:02:32.777 [ome.event.ItemCommandEvent] - Item 'numberHeatingReturnTemp' received command 22.9
2021-02-15 12:02:32.789 [vent.ItemStateChangedEvent] - numberHeatingReturnTemp changed from 23 to 22.9
2021-02-15 12:02:45.536 [ome.event.ItemCommandEvent] - Item 'BootValve' received command 0
2021-02-15 12:02:45.581 [nt.ItemStatePredictedEvent] - BootValve predicted to become 0
2021-02-15 12:02:45.627 [GroupItemStateChangedEvent] - DeviceValves changed from 246 to 236 through BootValve
2021-02-15 12:02:45.629 [vent.ItemStateChangedEvent] - BootValve changed from 10 to 0
2021-02-15 12:02:48.156 [ome.event.ItemCommandEvent] - Item 'numberHeatingReturnTemp' received command 23
2021-02-15 12:02:48.172 [vent.ItemStateChangedEvent] - numberHeatingReturnTemp changed from 22.9 to 23
2021-02-15 12:02:55.163 [vent.ItemStateChangedEvent] - numberFridgesPower changed from 201.485 to 201.216
2021-02-15 12:02:55.166 [vent.ItemStateChangedEvent] - numberFridgesEnergyUsage changed from 34.975 to 34.977
2021-02-15 12:03:15.276 [ome.event.ItemCommandEvent] - Item 'numberDHWLowerCylinderTemp' received command 28
2021-02-15 12:03:15.298 [vent.ItemStateChangedEvent] - numberDHWLowerCylinderTemp changed from 28.1 to 28
2021-02-15 12:03:22.398 [ome.event.ItemCommandEvent] - Item 'numberDHWUpperCylinderTemp' received command 44
2021-02-15 12:03:22.423 [vent.ItemStateChangedEvent] - numberDHWUpperCylinderTemp changed from 43.5 to 44
2021-02-15 12:03:25.360 [vent.ItemStateChangedEvent] - numberFridgesPower changed from 201.216 to 201.246
2021-02-15 12:03:25.371 [vent.ItemStateChangedEvent] - numberFridgesEnergyUsage changed from 34.977 to 34.979
2021-02-15 12:03:37.036 [ome.event.ItemCommandEvent] - Item 'numberDHWUpperCylinderTemp' received command 44.3
2021-02-15 12:03:37.049 [vent.ItemStateChangedEvent] - numberDHWUpperCylinderTemp changed from 44 to 44.3
2021-02-15 12:07:16.717 [ome.event.ItemCommandEvent] - Item 'numberDHWLowerCylinderTemp' received command 27.9
2021-02-15 12:07:16.733 [vent.ItemStateChangedEvent] - numberDHWLowerCylinderTemp changed from 28 to 27.9
2021-02-15 12:07:18.557 [ome.event.ItemCommandEvent] - Item 'numberHeatingReturnTemp' received command 23.1
2021-02-15 12:07:18.571 [vent.ItemStateChangedEvent] - numberHeatingReturnTemp changed from 23 to 23.1
2021-02-15 12:07:25.391 [ome.event.ItemCommandEvent] - Item 'swMasterHeating' received command OFF
2021-02-15 12:07:25.406 [vent.ItemStateChangedEvent] - swMasterHeating changed from ON to OFF
2021-02-15 12:07:26.943 [vent.ItemStateChangedEvent] - numberFridgesPower changed from 201.077 to 200.87
2021-02-15 12:07:26.946 [vent.ItemStateChangedEvent] - numberFridgesEnergyUsage changed from 34.991 to 34.992
2021-02-15 12:07:33.036 [ome.event.ItemCommandEvent] - Item 'numberDHWUpperCylinderTemp' received command 44.3
2021-02-15 12:07:33.050 [vent.ItemStateChangedEvent] - numberDHWUpperCylinderTemp changed from 44.5 to 44.3
2021-02-15 12:07:38.848 [ome.event.ItemCommandEvent] - Item 'swMasterHeating' received command ON
2021-02-15 12:07:38.865 [vent.ItemStateChangedEvent] - swMasterHeating changed from OFF to ON
2021-02-15 12:07:49.276 [ome.event.ItemCommandEvent] - Item 'numberHeatingReturnTemp' received command 23
2021-02-15 12:07:49.290 [vent.ItemStateChangedEvent] - numberHeatingReturnTemp changed from 23.1 to 23
2021-02-15 12:07:57.130 [vent.ItemStateChangedEvent] - numberFridgesPower changed from 200.87 to 200.377
2021-02-15 12:07:57.133 [vent.ItemStateChangedEvent] - numberFridgesEnergyUsage changed from 34.992 to 34.994
Openhab.log around that time period (there’s lots of debug logging, so quite a bit going on, but nothing that looks like this rule):
2021-02-15 12:01:47.461 [DEBUG] [eclipse.smarthome.model.script.zones] - Set to summer, use summerSetpoint
2021-02-15 12:01:47.478 [DEBUG] [eclipse.smarthome.model.script.zones] - Calculating setpoint for zoneLoggia at time 1201
2021-02-15 12:01:47.491 [DEBUG] [eclipse.smarthome.model.script.zones] - Checking time 600 against currentTime 1201
2021-02-15 12:01:47.495 [DEBUG] [eclipse.smarthome.model.script.zones] - Was less than or equal
2021-02-15 12:01:47.499 [DEBUG] [eclipse.smarthome.model.script.zones] - Checking time 900 against currentTime 1201
2021-02-15 12:01:47.504 [DEBUG] [eclipse.smarthome.model.script.zones] - Was less than or equal
2021-02-15 12:01:47.508 [DEBUG] [eclipse.smarthome.model.script.zones] - Checking time 1800 against currentTime 1201
2021-02-15 12:01:47.513 [DEBUG] [eclipse.smarthome.model.script.zones] - Checking time 2130 against currentTime 1201
2021-02-15 12:01:47.541 [DEBUG] [eclipse.smarthome.model.script.zones] - Calculated setpoint for zone zoneLoggia is setpointNumber 2 with value of 18.5, including adjustor of -0.5,
old setpoint was setCurrentLoggia (Type=NumberItem, State=14, Label=Loggia Zone Current Setpoint, Category=temperature, Groups=[zoneSettingsLoggia, InitCurrentSetpoints, ZoneSetpoin
ts])
2021-02-15 12:01:47.552 [DEBUG] [eclipse.smarthome.model.script.zones] - Set to summer, use summerSetpoint
2021-02-15 12:02:31.226 [WARN ] [ommunicator.AbstractHomematicGateway] - Datapoint is readOnly, it is not published to the gateway with id 'ABDD5864-8959-5743-FE7A-8ADC71DCD01D': 'M
EQ1344264:1#VALVE_STATE'
2021-02-15 12:02:45.598 [WARN ] [ommunicator.AbstractHomematicGateway] - Datapoint is readOnly, it is not published to the gateway with id 'ABDD5864-8959-5743-FE7A-8ADC71DCD01D': 'M
2021-02-15 12:06:47.032 [DEBUG] [eclipse.smarthome.model.script.zones] - Running zone settings
2021-02-15 12:06:47.055 [DEBUG] [eclipse.smarthome.model.script.zones] - Calculating setpoint for zoneBoot at time 1206
2021-02-15 12:06:47.102 [DEBUG] [eclipse.smarthome.model.script.zones] - Checking time 600 against currentTime 1206
2021-02-15 12:06:47.111 [DEBUG] [eclipse.smarthome.model.script.zones] - Was less than or equal
2021-02-15 12:06:47.121 [DEBUG] [eclipse.smarthome.model.script.zones] - Checking time 900 against currentTime 1206
2021-02-15 12:06:47.130 [DEBUG] [eclipse.smarthome.model.script.zones] - Was less than or equal
2021-02-15 12:06:47.140 [DEBUG] [eclipse.smarthome.model.script.zones] - Checking time 1800 against currentTime 1206
2021-02-15 12:06:47.151 [DEBUG] [eclipse.smarthome.model.script.zones] - Checking time 2130 against currentTime 1206
2021-02-15 12:06:47.362 [DEBUG] [eclipse.smarthome.model.script.zones] - Calculating setpoint for zoneGuest at time 1206
2021-02-15 12:06:47.389 [DEBUG] [eclipse.smarthome.model.script.zones] - Checking time 600 against currentTime 1206
2021-02-15 12:06:47.394 [DEBUG] [eclipse.smarthome.model.script.zones] - Was less than or equal
2021-02-15 12:06:47.401 [DEBUG] [eclipse.smarthome.model.script.zones] - Checking time 900 against currentTime 1206
2021-02-15 12:06:47.407 [DEBUG] [eclipse.smarthome.model.script.zones] - Was less than or equal
2021-02-15 12:06:47.412 [DEBUG] [eclipse.smarthome.model.script.zones] - Checking time 1800 against currentTime 1206
2021-02-15 12:06:47.420 [DEBUG] [eclipse.smarthome.model.script.zones] - Checking time 2130 against currentTime 1206
2021-02-15 12:06:47.460 [DEBUG] [eclipse.smarthome.model.script.zones] - Calculated setpoint for zone zoneGuest is setpointNumber 2 with value of 18.5, including adjustor of -0.5, old setpoint was setCurrentGuest (Type=NumberItem, State=10, Label=Guest Zone Current Setpoint, Category=temperature, Groups=[zoneSettingsGuest, InitCurrentSetpoints, ZoneSetpoints])
2021-02-15 12:06:47.471 [DEBUG] [eclipse.smarthome.model.script.zones] - Zone zoneGuest is switched off, setting setpoint to away setpoint
2021-02-15 12:06:47.483 [DEBUG] [eclipse.smarthome.model.script.zones] - Calculating setpoint for zoneLiving at time 1206
2021-02-15 12:06:47.500 [DEBUG] [eclipse.smarthome.model.script.zones] - Checking time 600 against currentTime 1206
2021-02-15 12:06:47.504 [DEBUG] [eclipse.smarthome.model.script.zones] - Was less than or equal
2021-02-15 12:06:47.508 [DEBUG] [eclipse.smarthome.model.script.zones] - Checking time 900 against currentTime 1206
2021-02-15 12:06:47.513 [DEBUG] [eclipse.smarthome.model.script.zones] - Was less than or equal
2021-02-15 12:06:47.517 [DEBUG] [eclipse.smarthome.model.script.zones] - Checking time 1800 against currentTime 1206
2021-02-15 12:06:47.522 [DEBUG] [eclipse.smarthome.model.script.zones] - Checking time 2130 against currentTime 1206
2021-02-15 12:06:47.551 [DEBUG] [eclipse.smarthome.model.script.zones] - Calculated setpoint for zone zoneLiving is setpointNumber 2 with value of 18.5, including adjustor of -0.5, old setpoint was setCurrentLiving (Type=NumberItem, State=14, Label=Living Zone Current Setpoint, Category=temperature, Groups=[zoneSettingsLiving, InitCurrentSetpoints, ZoneSetpoints])
2021-02-15 12:06:47.567 [DEBUG] [eclipse.smarthome.model.script.zones] - Set to summer, use summerSetpoint
2021-02-15 12:06:47.577 [DEBUG] [eclipse.smarthome.model.script.zones] - Calculating setpoint for zoneLoggia at time 1206
2021-02-15 12:06:47.592 [DEBUG] [eclipse.smarthome.model.script.zones] - Checking time 600 against currentTime 1206
2021-02-15 12:06:47.597 [DEBUG] [eclipse.smarthome.model.script.zones] - Was less than or equal
2021-02-15 12:06:47.601 [DEBUG] [eclipse.smarthome.model.script.zones] - Checking time 900 against currentTime 1206
2021-02-15 12:06:47.605 [DEBUG] [eclipse.smarthome.model.script.zones] - Was less than or equal
2021-02-15 12:06:47.609 [DEBUG] [eclipse.smarthome.model.script.zones] - Checking time 1800 against currentTime 1206
2021-02-15 12:06:47.614 [DEBUG] [eclipse.smarthome.model.script.zones] - Checking time 2130 against currentTime 1206
2021-02-15 12:06:47.640 [DEBUG] [eclipse.smarthome.model.script.zones] - Calculated setpoint for zone zoneLoggia is setpointNumber 2 with value of 18.5, including adjustor of -0.5, old setpoint was setCurrentLoggia (Type=NumberItem, State=14, Label=Loggia Zone Current Setpoint, Category=temperature, Groups=[zoneSettingsLoggia, InitCurrentSetpoints, ZoneSetpoints])
2021-02-15 12:06:47.650 [DEBUG] [eclipse.smarthome.model.script.zones] - Set to summer, use summerSetpoint
2021-02-15 12:11:47.032 [DEBUG] [eclipse.smarthome.model.script.zones] - Running zone settings
2021-02-15 12:11:47.053 [DEBUG] [eclipse.smarthome.model.script.zones] - Calculating setpoint for zoneBoot at time 1211
2021-02-15 12:11:47.088 [DEBUG] [eclipse.smarthome.model.script.zones] - Checking time 600 against currentTime 1211
2021-02-15 12:11:47.097 [DEBUG] [eclipse.smarthome.model.script.zones] - Was less than or equal
2021-02-15 12:11:47.107 [DEBUG] [eclipse.smarthome.model.script.zones] - Checking time 900 against currentTime 1211
2021-02-15 12:11:47.113 [DEBUG] [eclipse.smarthome.model.script.zones] - Was less than or equal
2021-02-15 12:11:47.118 [DEBUG] [eclipse.smarthome.model.script.zones] - Checking time 1800 against currentTime 1211
2021-02-15 12:11:47.124 [DEBUG] [eclipse.smarthome.model.script.zones] - Checking time 2130 against currentTime 1211
2021-02-15 12:11:47.157 [DEBUG] [eclipse.smarthome.model.script.zones] - Calculated setpoint for zone zoneBoot is setpointNumber 2 with value of 18.5, including adjustor of -0.5, old setpoint was setCurrentBoot (Type=NumberItem, State=14, Label=Boot Zone Current Setpoint, Category=temperature, Groups=[zoneSettingsBoot, InitCurrentSetpoints, ZoneSetpoints])
2021-02-15 12:11:47.170 [DEBUG] [eclipse.smarthome.model.script.zones] - Set to summer, use summerSetpoint
2021-02-15 12:11:47.180 [DEBUG] [eclipse.smarthome.model.script.zones] - Calculating setpoint for zoneBed at time 1211
So there are other rules and timers firing, but not these particular events, which seems unusual.
Finally, a log from after the reboot, where it’s working properly.
2021-02-15 19:09:59.855 [DEBUG] [lipse.smarthome.model.script.devices] - A valve changed value: Kitchen
2021-02-15 19:09:59.921 [DEBUG] [lipse.smarthome.model.script.devices] - Releasing lock
2021-02-15 19:09:59.927 [DEBUG] [clipse.smarthome.model.script.boiler] - Valve opening changed, deciding what to do, valve opening is DeviceValves (Type=GroupItem, BaseType=NumberIt
em, Members=12, State=76, Label=null, Category=null, Groups=[All])
2021-02-15 19:09:59.964 [DEBUG] [clipse.smarthome.model.script.boiler] - Already running, valves have changed so need to adjust run timer
2021-02-15 19:09:59.969 [DEBUG] [clipse.smarthome.model.script.boiler] - setRunTimer with type of update
2021-02-15 19:09:59.979 [DEBUG] [clipse.smarthome.model.script.boiler] - Heating run timer calculated as 1990.00000000 based on numberHeatingRunBaseMinutes (Type=NumberItem, State=3
0, Label=Base Run Minutes, Category=clock, Groups=[InternalFlags, RestoreGroup])DeviceValves (Type=GroupItem, BaseType=NumberItem, Members=12, State=76, Label=null, Category=null, G
roups=[All])numberHeatingRunFactor (Type=NumberItem, State=250, Label=Run Factor, Category=waterpump, Groups=[InternalFlags, RestoreGroup])
2021-02-15 19:09:59.983 [DEBUG] [clipse.smarthome.model.script.boiler] - Timer was present, cancelled it
2021-02-15 19:09:59.999 [DEBUG] [clipse.smarthome.model.script.boiler] - Valves changed, creating a new run timer, timer will end at dtTimerEnd (Type=DateTimeItem, State=2021-02-15T
19:26:59.227+1300, Label=Current Timer End, Category=clock, Groups=[InternalFlags, RestoreGroup])
2021-02-15 19:10:00.008 [DEBUG] [model.script.actions.ScriptExecution] - Scheduled code for execution at 2021-02-15T19:26:59.227+13:00
2021-02-15 19:10:00.015 [DEBUG] [clipse.smarthome.model.script.boiler] - Run timer is org.eclipse.smarthome.model.script.internal.actions.TimerImpl@b06bf6
2021-02-15 19:10:00.022 [DEBUG] [lipse.smarthome.model.script.devices] - Timer called: ValveTimerSet (Type=StringItem, State=Kitchen, Label=Valve Timer, Category=null)
2021-02-15 19:10:00.063 [DEBUG] [lipse.smarthome.model.script.devices] - Cancelling existing timer for Kitchen
2021-02-15 19:10:00.079 [DEBUG] [lipse.smarthome.model.script.devices] - Timer called: ValveTimerSet (Type=StringItem, State=, Label=Valve Timer, Category=null)
2021-02-15 19:10:00.082 [DEBUG] [lipse.smarthome.model.script.devices] - Timer called, string is empty meaning its an unset not a set
2021
Any information or ideas gratefully received.