Solaredge inverter via Modbus TCP 2
(Part 1/3)
Hi to all,
I have been using the information of this topic by @havaak and the previous one by @tkuehne.
Although the Modbus Sunspec Bundle is now available, I will keep this setup for the while.
I made some modifications to fit my needs and composed it to the following set of files, which I want to share with you.
I am living in Germany, so the most labels are in German.
  • I have a SolarEdge SE2200 inverter and a WattNode WNC-3Y-400-MB meter which is connected to the inverter via RS485 connection. The inverter is connected to the network via LAN.
  • I commented out all values which I do not use or which are not available on my inverter/meter.
  • I added a “scale all values”-rule trigger to prevent openhab from generating errors because of some NULL-values if you e.g. restart openHAB during the night where there is no change in the inverter values.
  • The “scale all values”-rule gets triggered after system start of openHAB automatically.
modbusSolaredge.things
Bridge modbus:tcp:SolarEdgeConverter [ host="192.168.115.164", port=502, id=1, timeBetweenTransactionsMilli=60, timeBetweenReconnectMillis=0, connectMaxTries=3, reconnectAfterMillis=0, connectTimeoutMillis=5000 ] {
    Bridge poller Registers [ start=69, length=50, refresh=5000, type="holding" ] {
        Thing data C_SunSpec_DID        [ readStart="69", readValueType="uint16" ]      // 101 = single phase, 102 = split phase, 103 = three phase
        Thing data C_SunSpec_Length     [ readStart="70", readValueType="uint16" ]      // 50 = Length of model block
        Thing data I_AC_Current         [ readStart="71", readValueType="uint16" ]      // AC Total Current value
        Thing data I_AC_CurrentA        [ readStart="72", readValueType="uint16" ]      // AC Phase A Current value
        //Thing data I_AC_CurrentB        [ readStart="73", readValueType="uint16" ]      // AC Phase B Current value
        //Thing data I_AC_CurrentC        [ readStart="74", readValueType="uint16" ]      // AC Phase C Current value
        Thing data I_AC_Current_SF      [ readStart="75", readValueType="int16"  ]      // AC Current scale factor
        Thing data I_AC_VoltageAB       [ readStart="76", readValueType="uint16" ]      // AC Voltage Phase AB value
        //Thing data I_AC_VoltageBC       [ readStart="77", readValueType="uint16" ]      // AC Voltage Phase BC value
        //Thing data I_AC_VoltageCA       [ readStart="78", readValueType="uint16" ]      // AC Voltage Phase CA value
        //Thing data I_AC_VoltageAN       [ readStart="79", readValueType="uint16" ]      // AC Voltage Phase A to N value
        //Thing data I_AC_VoltageBN       [ readStart="80", readValueType="uint16" ]      // AC Voltage Phase B to N value
        //Thing data I_AC_VoltageCN       [ readStart="81", readValueType="uint16" ]      // AC Voltage Phase C to N value
        Thing data I_AC_Voltage_SF      [ readStart="82", readValueType="int16"  ]      // AC Voltage scale factor
        Thing data I_AC_Power           [ readStart="83", readValueType="int16"  ]      // AC Power value
        Thing data I_AC_Power_SF        [ readStart="84", readValueType="int16"  ]      // AC Power scale factor
        Thing data I_AC_Frequency       [ readStart="85", readValueType="uint16" ]      // AC Frequency value
        Thing data I_AC_Frequency_SF    [ readStart="86", readValueType="int16"  ]      // Scale factor
        Thing data I_AC_VA              [ readStart="87", readValueType="int16"  ]      // Apparent Power
        Thing data I_AC_VA_SF           [ readStart="88", readValueType="int16"  ]      // Scale factor
        Thing data I_AC_VAR             [ readStart="89", readValueType="int16"  ]      // Reactive Power
        Thing data I_AC_VAR_SF          [ readStart="90", readValueType="int16"  ]      // Scale factor
        Thing data I_AC_PF              [ readStart="91", readValueType="int16"  ]      // Power Factor
        Thing data I_AC_PF_SF           [ readStart="92", readValueType="int16"  ]      // Scale factor
        Thing data I_AC_Energy_WH       [ readStart="93", readValueType="uint32" ]      // AC Lifetime Energy Production
        Thing data I_AC_Energy_WH_SF    [ readStart="95", readValueType="uint16" ]      // Scale factor
        Thing data I_DC_Current         [ readStart="96", readValueType="uint16" ]      // DC Current value
        Thing data I_DC_Current_SF      [ readStart="97", readValueType="int16"  ]      // Scale factor
        Thing data I_DC_Voltage         [ readStart="98", readValueType="uint16" ]      // DC Voltage value
        Thing data I_DC_Voltage_SF      [ readStart="99", readValueType="int16"  ]      // Scale factor
        Thing data I_DC_Power           [ readStart="100", readValueType="int16" ]      // DC Power value
        Thing data I_DC_Power_SF        [ readStart="101", readValueType="int16" ]      // Scale factor
        Thing data I_Temp_Sink          [ readStart="103", readValueType="int16" ]      // Heat sink temperature
        Thing data I_Temp_SF            [ readStart="106", readValueType="int16" ]      // Scale factor
        Thing data I_Status             [ readStart="107", readValueType="uint16"]      // Operating state
        Thing data I_Status_Vendor      [ readStart="108", readValueType="uint16"]      // Vendor-defined operating state and error codes
    Bridge poller RegistersMeter [ start=188, length=105, refresh=5000, type="holding" ] {
        Thing data M_C_SunSpec_DID      [ readStart="188", readValueType="uint16" ]     //
        Thing data M_C_SunSpec_Length   [ readStart="189", readValueType="uint16" ]     // 50 = Length of model block
        Thing data M_AC_Current         [ readStart="190", readValueType="int16" ]      // AC Total Current value
        Thing data M_AC_Current_A       [ readStart="191", readValueType="int16" ]      // AC L1 Current value
        Thing data M_AC_Current_B       [ readStart="192", readValueType="int16" ]      // AC L2 Current value
        Thing data M_AC_Current_C       [ readStart="193", readValueType="int16" ]      // AC L3 Current value
        Thing data M_AC_Current_SF      [ readStart="194", readValueType="int16" ]      // AC Total Current scaling factor
        Thing data M_AC_Voltage_LN      [ readStart="195", readValueType="int16" ]      // Line to Neutral AC Voltage (average of active phases)
        Thing data M_AC_Voltage_AN      [ readStart="196", readValueType="int16" ]      // Phase A to Neutral AC Voltage
        Thing data M_AC_Voltage_BN      [ readStart="197", readValueType="int16" ]      // Phase B to Neutral AC Voltage
        Thing data M_AC_Voltage_CN      [ readStart="198", readValueType="int16" ]      // Phase C to Neutral AC Voltage
        //Thing data M_AC_Voltage_LL      [ readStart="199", readValueType="int16" ]      // Line to Line AC Voltage (average of active phases)
        //Thing data M_AC_Voltage_AB      [ readStart="200", readValueType="int16" ]      // Phase A to Phase B AC Voltage
        //Thing data M_AC_Voltage_BC      [ readStart="201", readValueType="int16" ]      // Phase B to Phase C AC Voltage
        //Thing data M_AC_Voltage_CA      [ readStart="202", readValueType="int16" ]      // Phase C to Phase A AC Voltage
        Thing data M_AC_Voltage_SF      [ readStart="203", readValueType="int16" ]      // AC Voltage Scale Factor
        Thing data M_AC_Freq            [ readStart="204", readValueType="int16" ]      // AC Frequency
        Thing data M_AC_Freq_SF         [ readStart="205", readValueType="int16" ]      // AC Frequency Scale Factor
        Thing data M_AC_Power           [ readStart="206", readValueType="int16" ]      // Total Real Power (sum of active phases)
        Thing data M_AC_Power_A         [ readStart="207", readValueType="int16" ]      // Phase A AC Real Power
        Thing data M_AC_Power_B         [ readStart="208", readValueType="int16" ]      // Phase B AC Real Power
        Thing data M_AC_Power_C         [ readStart="209", readValueType="int16" ]      // Phase C AC Real Power
        Thing data M_AC_Power_SF        [ readStart="210", readValueType="int16" ]      // AC Real Power Scale Factor
        Thing data M_AC_VA              [ readStart="211", readValueType="int16" ]      // Total AC Apparent Power (sum of active phases)
        Thing data M_AC_VA_A            [ readStart="212", readValueType="int16" ]      // Phase A AC Apparent Power
        Thing data M_AC_VA_B            [ readStart="213", readValueType="int16" ]      // Phase B AC Apparent Power
        Thing data M_AC_VA_C            [ readStart="214", readValueType="int16" ]      // Phase C AC Apparent Power
        Thing data M_AC_VA_SF           [ readStart="215", readValueType="int16" ]      // AC Apparent Power Scale Factor
        //Thing data M_AC_VAR             [ readStart="216", readValueType="int16" ]      // Total AC Reactive Power (sum of active phases)
        //Thing data M_AC_VAR_A           [ readStart="217", readValueType="int16" ]      // Phase A AC Reactive Power
        //Thing data M_AC_VAR_B           [ readStart="218", readValueType="int16" ]      // Phase B AC Reactive Power
        //Thing data M_AC_VAR_C           [ readStart="219", readValueType="int16" ]      // Phase C AC Reactive Power
        //Thing data M_AC_VAR_SF          [ readStart="220", readValueType="int16" ]      // AC Reactive Power Scale Factor
        Thing data M_AC_PF              [ readStart="221", readValueType="int16" ]      // Average Power Factor (average of active phases)
        Thing data M_AC_PF_A            [ readStart="222", readValueType="int16" ]      // Phase A Power Factor
        Thing data M_AC_PF_B            [ readStart="223", readValueType="int16" ]      // Phase B Power Factor
        Thing data M_AC_PF_C            [ readStart="224", readValueType="int16" ]      // Phase C Power Factor
        Thing data M_AC_PF_SF           [ readStart="225", readValueType="int16" ]      // AC Power Factor Scale Factor
        Thing data M_Exported           [ readStart="226", readValueType="uint32" ]     // Total Exported Real Energy
        Thing data M_Exported_A         [ readStart="228", readValueType="uint32" ]     // Phase A Exported Real Energy
        Thing data M_Exported_B         [ readStart="230", readValueType="uint32" ]     // Phase B Exported Real Energy
        Thing data M_Exported_C         [ readStart="232", readValueType="uint32" ]     // Phase C Exported Real Energy
        Thing data M_Imported           [ readStart="234", readValueType="uint32" ]     // Total Imported Real Energy
        Thing data M_Imported_A         [ readStart="236", readValueType="uint32" ]     // Phase A Imported Real Energy
        Thing data M_Imported_B         [ readStart="238", readValueType="uint32" ]     // Phase B Imported Real Energy
        Thing data M_Imported_C         [ readStart="240", readValueType="uint32" ]     // Phase C Imported Real Energy
        Thing data M_Energy_W_SF        [ readStart="242", readValueType="int16" ]      // Real Energy Scale Factor
        //Thing data M_Exported_VA        [ readStart="243", readValueType="uint32" ]     // Total Exported Apparent Energy
        //Thing data M_Exported_VA_A      [ readStart="245", readValueType="uint32" ]     // Phase A Exported Apparent Energy
        //Thing data M_Exported_VA_B      [ readStart="247", readValueType="uint32" ]     // Phase B Exported Apparent Energy
        //Thing data M_Exported_VA_C      [ readStart="249", readValueType="uint32" ]     // Phase C Exported Apparent Energy
        //Thing data M_Imported_VA        [ readStart="251", readValueType="uint32" ]     // Total Imported Apparent Energy
        //Thing data M_Imported_VA_A      [ readStart="253", readValueType="uint32" ]     // Phase A Imported Apparent Energy
        //Thing data M_Imported_VA_B      [ readStart="255", readValueType="uint32" ]     // Phase B Imported Apparent Energy
        //Thing data M_Imported_VA_C      [ readStart="257", readValueType="uint32" ]     // Phase C Imported Apparent Energy
        //Thing data M_Energy_VA_SF       [ readStart="259", readValueType="int16" ]      // Apparent Energy Scale Factor
        //Thing data M_Import_VARh_Q1     [ readStart="260", readValueType="uint32" ]     // Quadrant 1: Total Imported Reactive Energy
        //Thing data M_Import_VARh_Q1A    [ readStart="262", readValueType="uint32" ]     // Phase A - Quadrant 1: Imported Reactive Energy
        //Thing data M_Import_VARh_Q1B    [ readStart="264", readValueType="uint32" ]     // Phase B - Quadrant 1: Imported Reactive Energy
        //Thing data M_Import_VARh_Q1C    [ readStart="266", readValueType="uint32" ]     // Phase C - Quadrant 1: Imported Reactive Energy
        //Thing data M_Import_VARh_Q2     [ readStart="268", readValueType="uint32" ]     // Quadrant 2: Total Imported Reactive Energy
        //Thing data M_Import_VARh_Q2A    [ readStart="270", readValueType="uint32" ]     // Phase A - Quadrant 2: Imported Reactive Energy
        //Thing data M_Import_VARh_Q2B    [ readStart="272", readValueType="uint32" ]     // Phase B - Quadrant 2: Imported Reactive Energy
        //Thing data M_Import_VARh_Q2C    [ readStart="274", readValueType="uint32" ]     // Phase C - Quadrant 2: Imported Reactive Energy
        //Thing data M_Import_VARh_Q3     [ readStart="276", readValueType="uint32" ]     // Quadrant 3: Total Exported Reactive Energy
        //Thing data M_Import_VARh_Q3A    [ readStart="278", readValueType="uint32" ]     // Phase A - Quadrant 3: Exported Reactive Energy
        //Thing data M_Import_VARh_Q3B    [ readStart="280", readValueType="uint32" ]     // Phase B - Quadrant 3: Exported Reactive Energy
        //Thing data M_Import_VARh_Q3C    [ readStart="282", readValueType="uint32" ]     // Phase C - Quadrant 3: Exported Reactive Energy
        //Thing data M_Import_VARh_Q4     [ readStart="284", readValueType="uint32" ]     // Quadrant 4: Total Exported Reactive Energy
        //Thing data M_Import_VARh_Q4A    [ readStart="286", readValueType="uint32" ]     // Phase A - Quadrant 4: Exported Reactive Energy
        //Thing data M_Import_VARh_Q4B    [ readStart="288", readValueType="uint32" ]     // Phase B - Quadrant 4: Exported Reactive Energy
        //Thing data M_Import_VARh_Q4C    [ readStart="290", readValueType="uint32" ]     // Phase C - Quadrant 4: Exported Reactive Energy
        //Thing data M_Energy_VAR_SF      [ readStart="292", readValueType="int16" ]      // Reactive Energy Scale Factor
solaredgeInverter.items
// ########## SolarEdge General Items ##########
Switch						SE2K_ScaleAll				"Alle SE2K-Skalierungsregeln ausführen"										(gSE2K)				{expire="10s,command=OFF"}
// ########## SolarEdge Wechselrichter Gruppen ##########
// SolarEdge Wechselrichter
Group						gSE2KStat					"Wechselrichter PV-Anlage (Status-Werte, nicht skalierbar)"					(GF_Hwr)
Group						gSE2KInt					"Wechselrichter PV-Anlage (int-Werte, skalierbar)"							(GF_Hwr)
Group						gSE2KSfInt					"Wechselrichter PV-Anlage Skalierungsfaktoren (int-Werte)"					(GF_Hwr)
Group						gSE2K						"Wechselrichter PV-Anlage (float-Werte, skaliert)"							(GF_Hwr)
// ########## ModBus Inverter Items (integer values) ##########
// PV WR ID / ModBus specific items
Number						SE2K_C_SunSpec_DID_int		"PV WR Typ [MAP(solaredgeInverterType.map):%s]"								(gSE2KStat)			{channel="modbus:data:SolarEdgeConverter:Registers:C_SunSpec_DID:number", autoupdate="false"}
Number						SE2K_C_SunSpec_Length_int	"PV WR Sunspec Datensatz Länge (int) [%d]"									(gSE2KStat)			{channel="modbus:data:SolarEdgeConverter:Registers:C_SunSpec_Length:number", autoupdate="false"}
// Current across all phases, Phases A,B,C and scaling factor
//Number SE2K_I_AC_Current_int "PV WR AC Strom gesamt (int) [%d A]" (gSE2Kint)     {channel="modbus:data:SolarEdgeConverter:Registers:I_AC_Current:number" }
Number						SE2K_I_AC_CurrentA_int		"PV WR AC Strom Ph.A (int) [%d A]"											(gSE2Kint)			{channel="modbus:data:SolarEdgeConverter:Registers:I_AC_CurrentA:number"}
//Number SE2K_I_AC_CurrentB_int "PV WR AC Strom Ph.B (int) [%d A]" (gSE2Kint)           {channel="modbus:data:SolarEdgeConverter:Registers:I_AC_CurrentB:number" }
//Number SE2K_I_AC_CurrentC_int "PV WR AC Strom Ph.C (int) [%d A]" (gSE2Kint)           {channel="modbus:data:SolarEdgeConverter:Registers:I_AC_CurrentC:number" }
Number						SE2K_I_AC_Current_SF_int	"PV WR AC Strom Ph.A SF (int) [%d]"											(gSE2KSfInt)		{channel="modbus:data:SolarEdgeConverter:Registers:I_AC_Current_SF:number"}
// Voltage for Phases A,B,C and scaling factor
Number						SE2K_I_AC_VoltageAB_int		"PV WR AC Spannung AB (int) [%d V]"											(gSE2Kint)			{channel="modbus:data:SolarEdgeConverter:Registers:I_AC_VoltageAB:number"}
//Number SE2K_I_AC_VoltageBC_int "PV WR AC Spannung BC (int) [%d V]" (gSE2Kint) {channel="modbus:data:SolarEdgeConverter:Registers:I_AC_VoltageBC:number" }
//Number SE2K_I_AC_VoltageCA_int "PV WR AC Spannung CA (int) [%d V]" (gSE2Kint) {channel="modbus:data:SolarEdgeConverter:Registers:I_AC_VoltageCA:number" }
//Number SE2K_I_AC_VoltageAN_int "PV WR AC Spannung AN (int) [%d V]" (gSE2Kint) {channel="modbus:data:SolarEdgeConverter:Registers:I_AC_VoltageAN:number" }
//Number SE2K_I_AC_VoltageBN_int "PV WR AC Spannung BN (int) [%d V]" (gSE2Kint) {channel="modbus:data:SolarEdgeConverter:Registers:I_AC_VoltageBN:number" }
//Number SE2K_I_AC_VoltageCN_int "PV WR AC Spannung CN (int) [%d V]" (gSE2Kint) {channel="modbus:data:SolarEdgeConverter:Registers:I_AC_VoltageCN:number" }
Number						SE2K_I_AC_Voltage_SF_int	"PV WR AC Spannung SF (int) [%d]"											(gSE2KSfInt)		{channel="modbus:data:SolarEdgeConverter:Registers:I_AC_Voltage_SF:number"}
// Real Power and SF
Number						SE2K_I_AC_Power_int			"PV WR AC Leistung (int) [%d W]"											(gSE2KInt)			{channel="modbus:data:SolarEdgeConverter:Registers:I_AC_Power:number"}
Number						SE2K_I_AC_Power_SF_int		"PV WR AC Leistung SF (int) [%d]"											(gSE2KSfInt)		{channel="modbus:data:SolarEdgeConverter:Registers:I_AC_Power_SF:number"}
// Frequency and SF
Number						SE2K_I_AC_Frequency_int		"PV WR AC Frequenz (int) [%d Hz]"											(gSE2KInt)			{channel="modbus:data:SolarEdgeConverter:Registers:I_AC_Frequency:number"}
Number						SE2K_I_AC_Frequency_SF_int	"PV WR AC Frequenz SF (int) [%d]"											(gSE2KSfInt)		{channel="modbus:data:SolarEdgeConverter:Registers:I_AC_Frequency_SF:number"}
// Apparent Power and SF
Number						SE2K_I_AC_VA_int			"PV WR AC Scheinleistung (int) [%d VA]"										(gSE2KInt)			{channel="modbus:data:SolarEdgeConverter:Registers:I_AC_VA:number"}
Number						SE2K_I_AC_VA_SF_int			"PV WR AC Scheinleistung SF (int) [%d]"										(gSE2KSfInt)		{channel="modbus:data:SolarEdgeConverter:Registers:I_AC_VA_SF:number"}
// Reactive Power and SF
Number						SE2K_I_AC_VAR_int			"PV WR AC Blindleistung (int) [%d var]"										(gSE2KInt)			{channel="modbus:data:SolarEdgeConverter:Registers:I_AC_VAR:number"}
Number						SE2K_I_AC_VAR_SF_int		"PV WR AC Blindleistung SF (int) [%d]"										(gSE2KSfInt)		{channel="modbus:data:SolarEdgeConverter:Registers:I_AC_VAR_SF:number"}
// Power factor
Number						SE2K_I_AC_PF_int			"PV WR AC Leistungsfaktor (int) [%d %%]"									(gSE2KInt)			{channel="modbus:data:SolarEdgeConverter:Registers:I_AC_PF:number"}
Number						SE2K_I_AC_PF_SF_int			"PV WR AC Leistungsfaktor SF (int) [%d]"									(gSE2KSfInt)		{channel="modbus:data:SolarEdgeConverter:Registers:I_AC_PF_SF:number"}
// Lifetime generated energy (acc32-Value / 32-Bit-Wert - im Gegensatz zu allen anderen!)
Number						SE2K_I_AC_Energy_WH_int		"PV WR AC Erzeugungszaehler (int) [%d Wh]"									(gSE2KInt)			{channel="modbus:data:SolarEdgeConverter:Registers:I_AC_Energy_WH:number"}
Number						SE2K_I_AC_Energy_WH_SF_int	"PV WR AC Erzeugungszaehler SF (int) [%d]"									(gSE2KSfInt)		{channel="modbus:data:SolarEdgeConverter:Registers:I_AC_Energy_WH_SF:number"}
// DC side current
Number						SE2K_I_DC_Current_int		"PV WR DC Strom (int) [%d A]"												(gSE2KInt)			{channel="modbus:data:SolarEdgeConverter:Registers:I_DC_Current:number"}
Number						SE2K_I_DC_Current_SF_int	"PV WR DC Strom SF (int) [%d]"												(gSE2KSfInt)		{channel="modbus:data:SolarEdgeConverter:Registers:I_DC_Current_SF:number"}
// DC side voltage
Number						SE2K_I_DC_Voltage_int		"PV WR DC Spannung (int) [%d V]"											(gSE2KInt)			{channel="modbus:data:SolarEdgeConverter:Registers:I_DC_Voltage:number"}
Number						SE2K_I_DC_Voltage_SF_int	"PV WR DC Spannung SF (int) [%d]"											(gSE2KSfInt)		{channel="modbus:data:SolarEdgeConverter:Registers:I_DC_Voltage_SF:number"}
// DC side power
Number						SE2K_I_DC_Power_int			"PV WR DC Leistung (int) [%d W]"											(gSE2KInt)			{channel="modbus:data:SolarEdgeConverter:Registers:I_DC_Power:number"}
Number						SE2K_I_DC_Power_SF_int		"PV WR DC Leistung SF (int) [%d]"											(gSE2KSfInt)		{channel="modbus:data:SolarEdgeConverter:Registers:I_DC_Power_SF:number"}
// Temperature heat sink
Number						SE2K_I_TempSink_int			"PV WR Temperatur Kühlplatte (int) [%d °C]"									(gSE2KInt)			{channel="modbus:data:SolarEdgeConverter:Registers:I_Temp_Sink:number"}
Number						SE2K_I_TempSink_SF_int		"PV WR Temperatur Kühlplatte SF (int) [%d]"									(gSE2KSfInt)		{channel="modbus:data:SolarEdgeConverter:Registers:I_Temp_SF:number"}
// Operating state
Number						SE2K_I_Status_int			"PV WR Status [MAP(solaredgeStatus.map):%s]"								(gSE2KStat)			{channel="modbus:data:SolarEdgeConverter:Registers:I_Status:number", autoupdate="false"}
Number						SE2K_I_Status_Vendor_int	"PV WR Status (SE-spezifisch) [%d]"											(gSE2KStat)			{channel="modbus:data:SolarEdgeConverter:Registers:I_Status_Vendor:number", autoupdate="false"}
// ########## ModBus Inverter Items (float values) ##########
// AC Current across all phases
Number:ElectricCurrent		SE2K_I_AC_CurrentA			"PV WR AC Strom gesamt [%.2f A]"							<energy>		(gSE2K)
// AC Voltage for all phases
Number:ElectricPotential	SE2K_I_AC_VoltageAB			"PV WR AC Spannung [%.2f V]"								<energy>		(gSE2K)
// AC Real power
Number:Power				SE2K_I_AC_Power				"PV WR AC Wirkleistung [%.2f W]"							<energy>		(gSE2K)
// AC Frequency
Number:Frequency			SE2K_I_AC_Frequency			"PV WR Netzfrequenz [%.3f Hz]"								<line>			(gSE2K)
// AC Apparent power
Number:Power				SE2K_I_AC_VA				"PV WR AC Scheinleistung [%.2f VA]"							<energy>		(gSE2K)
// AC Reactive power
Number:Power				SE2K_I_AC_VAR				"PV WR AC Blindleistung [%.2f var]"							<energy>		(gSE2K)
// AC Power factor
Number:Dimensionless		SE2K_I_AC_PF				"PV WR AC Leistungsfaktor [%.2f %%]"						<line>			(gSE2K)
Number:Energy				SE2K_I_AC_Energy_WH			"PV WR AC Erzeugungszaehler [%.2f Wh]"						<energy>		(gSE2K)
// DC Current
Number:ElectricCurrent		SE2K_I_DC_Current			"PV WR DC Strom [%.2f A]"									<energy>		(gSE2K)
// DC Voltage
Number:ElectricPotential	SE2K_I_DC_Voltage			"PV WR DC Spannung [%.2f V]"								<energy>		(gSE2K)
// DC Power
Number:Power				SE2K_I_DC_Power				"PV WR DC Leistung [%.2f W]"								<energy>		(gSE2K)
Number:Temperature			SE2K_I_TempSink				"PV WR Temperatur Kühlplatte [%.2f °C]"						<temperature>	(gSE2K)
solaredgeMeter.items
Switch						SE2KM_ScaleAll					"Alle SE2KM-Skalierungsregeln ausführen"									(gSE2KM)					{expire="10s,command=OFF"}
// ########## SolarEdge Meter Gruppen ##########
// SolarEdge Meter
Group						gSE2KMStat						"Meter PV-Anlage (Status-Werte, nicht skalierbar)"							(GF_Hwr)
Group						gSE2KMInt						"Meter PV-Anlage (int-Werte, skalierbar)"									(GF_Hwr)
Group						gSE2KMSfInt						"Meter PV-Anlage Skalierungsfaktoren (int-Werte)"							(GF_Hwr)
Group						gSE2KM							"Meter PV-Anlage (float-Werte, skaliert)"									(GF_Hwr)
Group						gSE2KMMomentan					"Meter PV-Anlage (Momentan-Leistungen)"										(GF_Hwr)
// ########## ModBus Meter Items (integer values) ##########
// PV Meter ID / ModBus specific items
Number						SE2K_M_C_SunSpec_DID_int		"PV Meter Typ [MAP(solaredgeMeterType.map):%s]"								(gSE2KMStat)				{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_C_SunSpec_DID:number", autoupdate="false"}
Number						SE2K_M_C_SunSpec_Length_int		"PV Meter Sunspec Datensatz Länge (int) [%d]"								(gSE2KMStat)				{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_C_SunSpec_Length:number"}
// PV Meter Amps Across all phases, Phases A,B,C and scaling factor
Number						SE2K_M_AC_Current_int			"PV Meter AC Strom (Summe) (int) [%d A]"									(gSE2KMInt)					{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_Current:number"}
Number						SE2K_M_AC_Current_A_int			"PV Meter AC Strom Phase A (int) [%d A]"									(gSE2KMInt)					{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_Current_A:number"}
Number						SE2K_M_AC_Current_B_int			"PV Meter AC Strom Phase B (int) [%d A]"									(gSE2KMInt)					{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_Current_B:number"}
Number						SE2K_M_AC_Current_C_int			"PV Meter AC Strom Phase C (int) [%d A]"									(gSE2KMInt)					{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_Current_C:number"}
Number						SE2K_M_AC_Current_SF_int		"PV Meter AC Strom SF (int) [%d]"											(gSE2KMSfInt)				{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_Current_SF:number"}
// PV Meter Voltage for Phases A,B,C and scaling factor
Number						SE2K_M_AC_Voltage_LN_int		"PV Meter Spannung LN (Avg.) (int) [%d V]"									(gSE2KMInt)					{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_Voltage_LN:number"}
Number						SE2K_M_AC_Voltage_AN_int		"PV Meter Spannung AN (int) [%d V]"											(gSE2KMInt)					{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_Voltage_AN:number"}
Number						SE2K_M_AC_Voltage_BN_int		"PV Meter Spannung BN (int) [%d V]"											(gSE2KMInt)					{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_Voltage_BN:number"}
Number						SE2K_M_AC_Voltage_CN_int		"PV Meter Spannung CN (int) [%d V]"											(gSE2KMInt)					{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_Voltage_CN:number"}
//Number SE2K_M_AC_Voltage_LL_int "PV Meter Spannung LL (Avg.) (int) [%d V]" (gSE2KMInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_Voltage_LL:number" }
//Number SE2K_M_AC_Voltage_AB_int "PV Meter Spannung AB (int) [%d V]" (gSE2KMInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_Voltage_AB:number" }
//Number SE2K_M_AC_Voltage_BC_int "PV Meter Spannung BC (int) [%d V]" (gSE2KMInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_Voltage_BC:number" }
//Number SE2K_M_AC_Voltage_CA_int "PV Meter Spannung CA (int) [%d V]" (gSE2KMInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_Voltage_CA:number" }
Number						SE2K_M_AC_Voltage_SF_int		"PV Meter Spannung SF (int) [%d]"											(gSE2KMSfInt)				{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_Voltage_SF:number"}
// PV Meter Frequency and SF
Number						SE2K_M_AC_Freq_int				"PV Meter Frequenz (int) [%d Hz]"											(gSE2KMInt)					{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_Freq:number"}
Number						SE2K_M_AC_Freq_SF_int			"PV Meter Frequenz SF (int) [%d]"											(gSE2KMSfInt)				{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_Freq_SF:number"}
Number						SE2K_M_AC_Power_int				"PV Meter Wirkleistung (Summe) (int) [%d W]"								(gSE2KMInt)					{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_Power:number"}
Number						SE2K_M_AC_Power_A_int			"PV Meter Wirkleistung Phase A (int) [%d W]"								(gSE2KMInt)					{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_Power_A:number"}
Number						SE2K_M_AC_Power_B_int			"PV Meter Wirkleistung Phase B (int) [%d W]"								(gSE2KMInt)					{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_Power_B:number"}
Number						SE2K_M_AC_Power_C_int			"PV Meter Wirkleistung Phase C (int) [%d W]"								(gSE2KMInt)					{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_Power_C:number"}
Number						SE2K_M_AC_Power_SF_int			"PV Meter Wirkleistung SF [%d]"												(gSE2KMSfInt)				{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_Power_SF:number"}
Number						SE2K_M_AC_VA_int				"PV Meter Scheinleistung (Summe) (int) [%d VA]"								(gSE2KMInt)					{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_VA:number"}
Number						SE2K_M_AC_VA_A_int				"PV Meter Scheinleistung Phase A (int) [%d VA]"								(gSE2KMInt)					{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_VA_A:number"}
Number						SE2K_M_AC_VA_B_int				"PV Meter Scheinleistung Phase B (int) [%d VA]"								(gSE2KMInt)					{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_VA_B:number"}
Number						SE2K_M_AC_VA_C_int				"PV Meter Scheinleistung Phase C (int) [%d VA]"								(gSE2KMInt)					{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_VA_C:number"}
Number						SE2K_M_AC_VA_SF_int				"PV Meter Scheinleistung SF (int) [%d]"										(gSE2KMSfInt)				{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_VA_SF:number"}
//Number SE2K_M_AC_VAR_int "PV Meter Blindleistung (Summe) (int) [%d var]" (gSE2KMInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_VAR:number" }
//Number SE2K_M_AC_VAR_A_int "PV Meter Blindleistung Phase A (int) [%d var]" (gSE2KMInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_VAR_A:number" }
//Number SE2K_M_AC_VAR_B_int "PV Meter Blindleistung Phase B (int) [%d var]" (gSE2KMInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_VAR_B:number" }
//Number SE2K_M_AC_VAR_C_int "PV Meter Blindleistung Phase C (int) [%d var]" (gSE2KMInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_VAR_C:number" }
//Number SE2K_M_AC_VAR_SF_int "PV Meter Blindleistung SF (int) [%d]" (gSE2KMSfInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_VAR_SF:number" }
// Power factor
Number						SE2K_M_AC_PF_int				"PV Meter Leistungsfaktor (Avg.) (int) [%d %%]"								(gSE2KMInt)					{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_PF:number"}
Number						SE2K_M_AC_PF_A_int				"PV Meter Leistungsfaktor Phase A (int) [%d %%]"							(gSE2KMInt)					{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_PF_A:number"}
Number						SE2K_M_AC_PF_B_int				"PV Meter Leistungsfaktor Phase B (int) [%d %%]"							(gSE2KMInt)					{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_PF_B:number"}
Number						SE2K_M_AC_PF_C_int				"PV Meter Leistungsfaktor Phase C (int) [%d %%]"							(gSE2KMInt)					{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_PF_C:number"}
Number						SE2K_M_AC_PF_SF_int				"PV Meter Leistungsfaktor SF (int) [%d %%]"									(gSE2KMSfInt)				{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_AC_PF_SF:number"}
// Accumulated Energy (Real Energy)
Number						SE2K_M_Exported_int				"PV Meter Einspeisezähler Wirkenergie (Summe) (int) [%d Wh]"				(gSE2KMInt)					{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Exported:number"}
Number						SE2K_M_Exported_A_int			"PV Meter Einspeisezähler Wirkenergie Phase A (int) [%d Wh]"				(gSE2KMInt)					{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Exported_A:number"}
Number						SE2K_M_Exported_B_int			"PV Meter Einspeisezähler Wirkenergie Phase B (int) [%d Wh]"				(gSE2KMInt)					{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Exported_B:number"}
Number						SE2K_M_Exported_C_int			"PV Meter Einspeisezähler Wirkenergie Phase C (int) [%d Wh]"				(gSE2KMInt)					{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Exported_C:number"}
Number						SE2K_M_Imported_int				"PV Meter Bezugszähler Wirkenergie (Summe) (int) [%d Wh]"					(gSE2KMInt)					{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Imported:number"}
Number						SE2K_M_Imported_A_int			"PV Meter Bezugszähler Wirkenergie Phase A (int) [%d Wh]"					(gSE2KMInt)					{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Imported_A:number"}
Number						SE2K_M_Imported_B_int			"PV Meter Bezugszähler Wirkenergie Phase B (int) [%d Wh]"					(gSE2KMInt)					{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Imported_B:number"}
Number						SE2K_M_Imported_C_int			"PV Meter Bezugszähler Wirkenergie Phase C (int) [%d Wh]"					(gSE2KMInt)					{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Imported_C:number"}
Number						SE2K_M_Energy_W_SF_int			"PV Meter Zähler Wirkenergie SF (int) [%d]"									(gSE2KMSfInt)				{channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Energy_W_SF:number"}
// Accumulated Energy (Apparent Energy)
//Number SE2K_M_Exported_VA_int "PV Meter Einspeisezähler Scheinenergie (Summe) (int) [%d VAh]" (gSE2KMInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Exported_VA:number" }
//Number SE2K_M_Exported_VA_A_int "PV Meter Einspeisezähler Scheinenergie Phase A (int) [%d VAh]" (gSE2KMInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Exported_VA_A:number" }
//Number SE2K_M_Exported_VA_B_int "PV Meter Einspeisezähler Scheinenergie Phase B (int) [%d VAh]" (gSE2KMInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Exported_VA_B:number" }
//Number SE2K_M_Exported_VA_C_int "PV Meter Einspeisezähler Scheinenergie Phase C (int) [%d VAh]" (gSE2KMInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Exported_VA_C:number" }
//Number SE2K_M_Imported_VA_int "PV Meter Bezugszähler Scheinenergie (Summe) (int) [%d VAh]" (gSE2KMInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Imported_VA:number" }
//Number SE2K_M_Imported_VA_A_int "PV Meter Bezugszähler Scheinenergie Phase A (int) [%d VAh]" (gSE2KMInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Imported_VA_A:number" }
//Number SE2K_M_Imported_VA_B_int "PV Meter Bezugszähler Scheinenergie Phase B (int) [%d VAh]" (gSE2KMInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Imported_VA_B:number" }
//Number SE2K_M_Imported_VA_C_int "PV Meter Bezugszähler Scheinenergie Phase C (int) [%d VAh]" (gSE2KMInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Imported_VA_C:number" }
//Number SE2K_M_Energy_VA_SF_int "PV Meter Zähler Scheinenergie SF (int) [%d]" (gSE2KMSfInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Energy_VA_SF:number" }
// Accumulated Energy (Reactive Energy)
//Number SE2K_M_Import_VARh_Q1_int "PV Meter Bezugszähler Blindenergie Q1 (Summe) (int) [%d VARh]" (gSE2KMInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Import_VARh_Q1:number" }
//Number SE2K_M_Import_VARh_Q1A_int "PV Meter Bezugszähler Blindenergie Ph. A Q1 (Summe) (int) [%d VARh]" (gSE2KMInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Import_VARh_Q1A:number" }
//Number SE2K_M_Import_VARh_Q1B_int "PV Meter Bezugszähler Blindenergie Ph. B Q1 (Summe) (int) [%d VARh]" (gSE2KMInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Import_VARh_Q1B:number" }
//Number SE2K_M_Import_VARh_Q1C_int "PV Meter Bezugszähler Blindenergie Ph. C Q1 (Summe) (int) [%d VARh]" (gSE2KMInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Import_VARh_Q1C:number" }
//Number SE2K_M_Import_VARh_Q2_int "PV Meter Bezugszähler Blindenergie Q2 (Summe) (int) [%d VARh]" (gSE2KMInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Import_VARh_Q2:number" }
//Number SE2K_M_Import_VARh_Q2A_int "PV Meter Bezugszähler Blindenergie Ph. A Q2 (Summe) (int) [%d VARh]" (gSE2KMInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Import_VARh_Q2A:number" }
//Number SE2K_M_Import_VARh_Q2B_int "PV Meter Bezugszähler Blindenergie Ph. B Q2 (Summe) (int) [%d VARh]" (gSE2KMInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Import_VARh_Q2B:number" }
//Number SE2K_M_Import_VARh_Q2C_int "PV Meter Bezugszähler Blindenergie Ph. C Q2 (Summe) (int) [%d VARh]" (gSE2KMInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Import_VARh_Q2C:number" }
//Number SE2K_M_Import_VARh_Q3_int "PV Meter Bezugszähler Blindenergie Q3 (Summe) (int) [%d VARh]" (gSE2KMInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Import_VARh_Q3:number" }
//Number SE2K_M_Import_VARh_Q3A_int "PV Meter Bezugszähler Blindenergie Ph. A Q3 (Summe) (int) [%d VARh]" (gSE2KMInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Import_VARh_Q3A:number" }
//Number SE2K_M_Import_VARh_Q3B_int "PV Meter Bezugszähler Blindenergie Ph. B Q3 (Summe) (int) [%d VARh]" (gSE2KMInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Import_VARh_Q3B:number" }
//Number SE2K_M_Import_VARh_Q3C_int "PV Meter Bezugszähler Blindenergie Ph. C Q3 (Summe) (int) [%d VARh]" (gSE2KMInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Import_VARh_Q3C:number" }
//Number SE2K_M_Import_VARh_Q4_int "PV Meter Bezugszähler Blindenergie Q4 (Summe) (int) [%d VARh]" (gSE2KMInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Import_VARh_Q4:number" }
//Number SE2K_M_Import_VARh_Q4A_int "PV Meter Bezugszähler Blindenergie Ph. A Q4 (Summe) (int) [%d VARh]" (gSE2KMInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Import_VARh_Q4A:number" }
//Number SE2K_M_Import_VARh_Q4B_int "PV Meter Bezugszähler Blindenergie Ph. B Q4 (Summe) (int) [%d VARh]" (gSE2KMInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Import_VARh_Q4B:number" }
//Number SE2K_M_Import_VARh_Q4C_int "PV Meter Bezugszähler Blindenergie Ph. C Q4 (Summe) (int) [%d VARh]" (gSE2KMInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Import_VARh_Q4C:number" }
//Number SE2K_M_Energy_VAR_SF_int "PV Meter Zähler Blindenergie SF (int) [%d]" (gSE2KMSfInt) {channel="modbus:data:SolarEdgeConverter:RegistersMeter:M_Energy_VAR_SF:number" }
// PV Meter Events
Number						SE2K_M_Events_int				"PV Meter Events [%h]"														(gSE2KMStat)				{channel="modbus:data:SolarEdgeConverter:Registers:M_Events:number"}
// ########## ModBus Meter Items (float values) ##########
Number:ElectricCurrent		SE2K_M_AC_Current				"PV Meter AC Strom (Summe) [%.2f A]"							<energy>	(gSE2KM)
Number:ElectricCurrent		SE2K_M_AC_Current_A				"PV Meter AC Strom Phase A [%.2f A]"							<energy>	(gSE2KM)
Number:ElectricCurrent		SE2K_M_AC_Current_B				"PV Meter AC Strom Phase B [%.2f A]"							<energy>	(gSE2KM)
Number:ElectricCurrent		SE2K_M_AC_Current_C				"PV Meter AC Strom Phase C [%.2f A]"							<energy>	(gSE2KM)
// PV Amps calculated from Power and Voltage
Number:ElectricCurrent		SE2K_M_AC_Current_calc			"PV Meter AC Strom (Summe, berechnet) [%.2f A]"					<energy>	(gSE2KM)
Number:ElectricCurrent		SE2K_M_AC_Current_A_calc		"PV Meter AC Strom Phase A (berechnet) [%.2f A]"				<energy>	(gSE2KM)
Number:ElectricCurrent		SE2K_M_AC_Current_B_calc		"PV Meter AC Strom Phase B (berechnet) [%.2f A]"				<energy>	(gSE2KM)
Number:ElectricCurrent		SE2K_M_AC_Current_C_calc		"PV Meter AC Strom Phase C (berechnet) [%.2f A]"				<energy>	(gSE2KM)
Number:ElectricPotential	SE2K_M_AC_Voltage_LN			"PV Meter Spannung LN (Avg.) [%.2f V]"							<energy>	(gSE2KM)
Number:ElectricPotential	SE2K_M_AC_Voltage_AN			"PV Meter Spannung AN [%.2f V]"									<energy>	(gSE2KM)
Number:ElectricPotential	SE2K_M_AC_Voltage_BN			"PV Meter Spannung BN [%.2f V]"									<energy>	(gSE2KM)
Number:ElectricPotential	SE2K_M_AC_Voltage_CN			"PV Meter Spannung CN [%.2f V]"									<energy>	(gSE2KM)
//Number:ElectricPotential SE2K_M_AC_Voltage_LL "PV Meter Spannung LL (Avg.) [%.2f V]" <energy> (gSE2KM)
//Number:ElectricPotential SE2K_M_AC_Voltage_AB "PV Meter Spannung AB [%.2f V]" <energy> (gSE2KM)
//Number:ElectricPotential SE2K_M_AC_Voltage_BC "PV Meter Spannung BC [%.2f V]" <energy> (gSE2KM)
//Number:ElectricPotential SE2K_M_AC_Voltage_CA "PV Meter Spannung CA [%.2f V]" <energy> (gSE2KM)
Number:Frequency			SE2K_M_AC_Freq					"PV Meter Frequenz [%.3f Hz]"									<line>		(gSE2KM)
Number:Power				SE2K_M_AC_Power					"PV Meter Wirkleistung (Summe) [%.2f W]"						<energy>	(gSE2KM)
Number:Power				SE2K_M_AC_Power_A				"PV Meter Wirkleistung Phase A [%.2f W]"						<energy>	(gSE2KM)
Number:Power				SE2K_M_AC_Power_B				"PV Meter Wirkleistung Phase B [%.2f W]"						<energy>	(gSE2KM)
Number:Power				SE2K_M_AC_Power_C				"PV Meter Wirkleistung Phase C [%.2f W]"						<energy>	(gSE2KM)
Number:Power				SE2K_M_AC_VA					"PV Meter Scheinleistung (Summe) [%.2f VA]"						<energy>	(gSE2KM)
Number:Power				SE2K_M_AC_VA_A					"PV Meter Scheinleistung Phase A [%.2f VA]"						<energy>	(gSE2KM)
Number:Power				SE2K_M_AC_VA_B					"PV Meter Scheinleistung Phase B [%.2f VA]"						<energy>	(gSE2KM)
Number:Power				SE2K_M_AC_VA_C					"PV Meter Scheinleistung Phase C [%.2f VA]"						<energy>	(gSE2KM)
//Number:Power SE2K_M_AC_VAR "PV Meter Blindleistung (Summe) [%.2f var]" <energy> (gSE2KM)
//Number:Power SE2K_M_AC_VAR_A "PV Meter Blindleistung Phase A [%.2f var]" <energy> (gSE2KM)
//Number:Power SE2K_M_AC_VAR_B "PV Meter Blindleistung Phase B [%.2f var]" <energy> (gSE2KM)
//Number:Power SE2K_M_AC_VAR_C "PV Meter Blindleistung Phase C [%.2f var]" <energy> (gSE2KM)
// Power factor
Number:Dimensionless		SE2K_M_AC_PF					"PV Meter Leistungsfaktor (Avg.) [%.2f %%]"						<line>		(gSE2KM)
Number:Dimensionless		SE2K_M_AC_PF_A					"PV Meter Leistungsfaktor Phase A [%.2f %%]"					<line>		(gSE2KM)
Number:Dimensionless		SE2K_M_AC_PF_B					"PV Meter Leistungsfaktor Phase B [%.2f %%]"					<line>		(gSE2KM)
Number:Dimensionless		SE2K_M_AC_PF_C					"PV Meter Leistungsfaktor Phase C [%.2f %%]"					<line>		(gSE2KM)
Number:Energy				SE2K_M_Exported					"PV Meter Einspeisezähler Wirkenergie (Summe) [%.2f Wh]"		<energy>	(gSE2KM)
Number:Energy				SE2K_M_Exported_A				"PV Meter Einspeisezähler Wirkenergie Phase A [%.2f Wh]"		<energy>	(gSE2KM)
Number:Energy				SE2K_M_Exported_B				"PV Meter Einspeisezähler Wirkenergie Phase B [%.2f Wh]"		<energy>	(gSE2KM)
Number:Energy				SE2K_M_Exported_C				"PV Meter Einspeisezähler Wirkenergie Phase C [%.2f Wh]"		<energy>	(gSE2KM)
Number:Energy				SE2K_M_Imported					"PV Meter Bezugszähler Wirkenergie (Summe) [%.2f Wh]"			<energy>	(gSE2KM)
Number:Energy				SE2K_M_Imported_A				"PV Meter Bezugszähler Wirkenergie Phase A [%.2f Wh]"			<energy>	(gSE2KM)
Number:Energy				SE2K_M_Imported_B				"PV Meter Bezugszähler Wirkenergie Phase B [%.2f Wh]"			<energy>	(gSE2KM)
Number:Energy				SE2K_M_Imported_C				"PV Meter Bezugszähler Wirkenergie Phase C [%.2f Wh]"			<energy>	(gSE2KM)
//Number:Energy SE2K_M_Exported_VA "PV Meter Einspeisezähler Scheinenergie (Summe) [%.2f VAh]" <energy> (gSE2KM)
//Number:Energy SE2K_M_Exported_VA_A "PV Meter Einspeisezähler Scheinenergie Phase A [%.2f VAh]" <energy> (gSE2KM)
//Number:Energy SE2K_M_Exported_VA_B "PV Meter Einspeisezähler Scheinenergie Phase B [%.2f VAh]" <energy> (gSE2KM)
//Number:Energy SE2K_M_Exported_VA_C "PV Meter Einspeisezähler Scheinenergie Phase C [%.2f VAh]" <energy> (gSE2KM)
//Number:Energy SE2K_M_Imported_VA "PV Meter Bezugszähler Scheinenergie (Summe) [%.2f VAh]" <energy> (gSE2KM)
//Number:Energy SE2K_M_Imported_VA_A "PV Meter Bezugszähler Scheinenergie Phase A [%.2f VAh]" <energy> (gSE2KM)
//Number:Energy SE2K_M_Imported_VA_B "PV Meter Bezugszähler Scheinenergie Phase B [%.2f VAh]" <energy> (gSE2KM)
//Number:Energy SE2K_M_Imported_VA_C "PV Meter Bezugszähler Scheinenergie Phase C [%.2f VAh]" <energy> (gSE2KM)
//Number:Energy SE2K_M_Import_VARh_Q1 "PV Meter Bezugszähler Blindenergie Q1 (Summe) [%.2f VARh]" <energy> (gSE2KM)
//Number:Energy SE2K_M_Import_VARh_Q1A "PV Meter Bezugszähler Blindenergie Ph. A Q1 (Summe) [%.2f VARh]" <energy> (gSE2KM)
//Number:Energy SE2K_M_Import_VARh_Q1B "PV Meter Bezugszähler Blindenergie Ph. B Q1 (Summe) [%.2f VARh]" <energy> (gSE2KM)
//Number:Energy SE2K_M_Import_VARh_Q1C "PV Meter Bezugszähler Blindenergie Ph. C Q1 (Summe) [%.2f VARh]" <energy> (gSE2KM)
//Number:Energy SE2K_M_Import_VARh_Q2 "PV Meter Bezugszähler Blindenergie Q2 (Summe) [%.2f VARh]" <energy> (gSE2KM)
//Number:Energy SE2K_M_Import_VARh_Q2A "PV Meter Bezugszähler Blindenergie Ph. A Q2 (Summe) [%.2f VARh]" <energy> (gSE2KM)
//Number:Energy SE2K_M_Import_VARh_Q2B "PV Meter Bezugszähler Blindenergie Ph. B Q2 (Summe) [%.2f VARh]" <energy> (gSE2KM)
//Number:Energy SE2K_M_Import_VARh_Q2C "PV Meter Bezugszähler Blindenergie Ph. C Q2 (Summe) [%.2f VARh]" <energy> (gSE2KM)
//Number:Energy SE2K_M_Import_VARh_Q3 "PV Meter Bezugszähler Blindenergie Q3 (Summe) [%.2f VARh]" <energy> (gSE2KM)
//Number:Energy SE2K_M_Import_VARh_Q3A "PV Meter Bezugszähler Blindenergie Ph. A Q3 (Summe) [%.2f VARh]" <energy> (gSE2KM)
//Number:Energy SE2K_M_Import_VARh_Q3B "PV Meter Bezugszähler Blindenergie Ph. B Q3 (Summe) [%.2f VARh]" <energy> (gSE2KM)
//Number:Energy SE2K_M_Import_VARh_Q3C "PV Meter Bezugszähler Blindenergie Ph. C Q3 (Summe) [%.2f VARh]" <energy> (gSE2KM)
//Number:Energy SE2K_M_Import_VARh_Q4 "PV Meter Bezugszähler Blindenergie Q4 (Summe) [%.2f VARh]" <energy> (gSE2KM)
//Number:Energy SE2K_M_Import_VARh_Q4A "PV Meter Bezugszähler Blindenergie Ph. A Q4 (Summe) [%.2f VARh]" <energy> (gSE2KM)
//Number:Energy SE2K_M_Import_VARh_Q4B "PV Meter Bezugszähler Blindenergie Ph. B Q4 (Summe) [%.2f VARh]" <energy> (gSE2KM)
//Number:Energy SE2K_M_Import_VARh_Q4C "PV Meter Bezugszähler Blindenergie Ph. C Q4 (Summe) [%.2f VARh]" <energy> (gSE2KM)
// Other calculated Items
Number:Power				SE2KM_EigenverbrauchGesamt		"Eigenverbrauch Gesamt [%.2f Wh]"								<energy>	(gSE2KM)
Number:Power				SE2KM_GesamtverbrauchGesamt		"Gesamtverbrauch Gesamt [%.2f Wh]"								<energy>	(gSE2KM)
Number:Dimensionless		SE2KM_SolarerDeckungsgradGesamt	"SolarerDeckungsgrad Gesamt [%.2f %%]"							<line>		(gSE2KM)
Number:Power				SE2KM_DirektverbrauchMomentan	"Direktverbrauch Momentan [%.2f W]"								<energy>	(gSE2KM,gSE2KMMomentan)
Number:Power				SE2KM_HausverbrauchMomentan		"Hausverbrauch Momentan [%.2f W]"								<energy>	(gSE2KM,gSE2KMMomentan)
Number:Power				SE2KM_NetzleistungMomentan		"Netzleistung Momentan [%.2f W]"								<energy>	(gSE2KM,gSE2KMMomentan)