[SOLVED] NUT-Client Items
Hello guys,
I have a problem:
I want to run this command “upsc ups@IP-NutServer” and split the Output to different Items.
This is for example the Output:
Init SSL without certificate database
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 50
battery.date: not set
battery.mfr.date: 2019/04/25
battery.runtime: 2302
battery.runtime.low: 120
battery.type: PbAc
battery.voltage: 13.6
battery.voltage.nominal: 12.0
device.mfr: APC
device.model: Back-UPS ES 700G
device.serial: XXXXXXXXXX
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 5
driver.parameter.port: auto
driver.version: XXXXXXXXX
driver.version.data: APC HID 0.95
driver.version.internal: 0.38
input.sensitivity: medium
input.transfer.high: 266
input.transfer.low: 180
input.voltage: 238.0
input.voltage.nominal: 230
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.firmware: 871.O4 .I
ups.firmware.aux: O4
ups.load: 0
ups.mfr: APC
ups.mfr.date: 2019/04/25
ups.model: Back-UPS ES 700G
ups.productid: 0000
ups.serial: XXXXXXX
ups.status: OL
ups.timer.reboot: 0
ups.timer.shutdown: -1
ups.vendorid: 00XX0
Now i want to transfer every single value like “Back-UPS ES 700G” or “medium” to different OpenHab Items
This is my Items-File:
    Number        USV_APC_BattProz                                              "Akku: [%.1f %%]"                                             <battery>                   (influx)
    Number        USV_APC_BattLowProz                                           "Akku Low bei: [%.1f %%]"                                     <battery>
    Number        USV_APC_BattWarnProz                                          "Akku Warn bei: [%.1f %%]"                                    <battery>
    String        USV_APC_BattManFacDate                                        "Akku Herstellungsdat: [%s]"                                  <calendar>
    Number        USV_APC_BattRuntime                                           "Akku Laufzeit: [%.1f s]"                                     <clock>                     (influx)
    Number        USV_APC_BattRuntimeLow                                        "Akku Runt Low: [%.1f s]"                                     <clock>
    String        USV_APC_BattType                                              "Akkutyp: [%s]"                                               <battery>
    Number        USV_APC_BattVolt                                              "Akkuspng: [%.1f V]"                                          <battery>                   (influx)
    Number        USV_APC_BattVoltNorm                                          "Akkuspng Normal: [%.1f V]"                                   <battery>
    String        USV_APC_DevMfr                                                "Hersteller: [%s]"                                            <battery>
    String        USV_APC_DevModel                                              "Model: [%s]"                                                 <battery>
    String        USV_APC_DevSerNr                                              "Seriennummer: [%s]"                                          <battery>
    String        USV_APC_DevTyp                                                "Typ: [%s]"                                                   <battery>
    String        USV_APC_DriverName                                            "Treibername: [%s]"                                           <battery>
    Number        USV_APC_DriverPollFr                                          "Pollfreq: [%s]"                                              <clock>
    Number        USV_APC_DriverPollInt                                         "Pollinter: [%s]"                                             <clock>
    String        USV_APC_DriverPort                                            "Port: [%s]"                                                  <battery>
    String        USV_APC_DriverVers                                            "Treibervers: [%s]"                                           <battery>
    String        USV_APC_DriverData                                            "Treiberdata: [%s]"                                           <battery>
    String        USV_APC_DriverVersInt                                         "Treibervers intern: [%s]"                                    <battery>
    String        USV_APC_InpSens                                               "Eingangssensib: [%s]"                                        <battery>
    Number        USV_APC_InpTransH                                             "Eingangsspng High: [%.1f V]"                                 <battery>
    Number        USV_APC_InpTransL                                             "Eingangsspng Low: [%.1f V]"                                  <battery>
    Number        USV_APC_InpVolt                                               "Eingangsspng: [%.1f V]"                                      <battery>
    Number        USV_APC_InpVoltNorm                                           "Eingangsspng Normal: [%.1f V]"                               <battery>
    String        USV_APC_UpsBeep                                               "Piepser: [%s"                                                <battery>
    Number        USV_APC_UpsShutdDelay                                         "Herunterfahrverzö: [%.1f s]"                                 <battery>
    String        USV_APC_UpsFirmware                                           "Firmware: [%s]"                                              <battery>
    String        USV_APC_UpsFirmwareAux                                        "Firmware Aux: [%s]"                                          <battery>
    Number        USV_APC_UpsLoad                                               "Last: [%.1f W]"                                              <light>
    String        USV_APC_UpsMfr                                                "Ups Hersteller: [%s]"                                        <battery>
    String        USV_APC_UpsManFacDate                                         "Ups Herstellungsdat: [%s]"                                   <battery>
    String        USV_APC_UpsModel                                              "Ups Model: [%s]"                                             <battery>
    String        USV_APC_UpsProductId                                          "Ups Product Id: [%s]"                                        <battery>
    String        USV_APC_UpsSerNr                                              "Ups Seriennummer: [%s]"                                      <battery>
    String        USV_APC_UpsStatus                                             "Ups Status: [%s]"                                            <battery>
    Number        USV_APC_UpsTimerReboot                                        "Ups Timer Reboot: [%.1f s]"                                  <battery>
    Number        USV_APC_UpsTimerShutdown                                      "Ups Timer Shutdown: [%.1f s]"                                <battery>
    String        USV_APC_UpsVendorId                                           "Ups Vendor Id: [%s]"                                         <battery>
And my Rules -File:
rule "Alle 20 Sekunden UPS Status abfragen und auswerten"
    Time cron "0/20 * * ? * * *"
    var String CommandOutput = executeCommandLine("upsc ups@IP-NutServer", 120*1000)
    if (CommandOutput.startsWith("Init SSL")) {
        var String[] results = CommandOutput.split("\\r?\\n")
        var Arg0 = results.get(0).split(" ").get(1)
        var Arg1 = results.get(1).split(" ").get(2)
        var Arg2 = results.get(2).split(" ").get(1)
        var Arg3 = results.get(3).split(" ").get(1)
        var Arg4 = results.get(4).split(" ").get(1)
        var Arg5 = results.get(5).split(" ").get(1)
        var Arg6 = results.get(6).split(" ").get(1)
        var Arg7 = results.get(7).split(" ").get(1)
        var Arg8 = results.get(8).split(" ").get(1)
        var Arg9 = results.get(9).split(" ").get(1)
        var Arg10 = results.get(10).split(" ").get(1)
        var Arg11 = results.get(11).split(" ").get(1)
        var Arg12 = results.get(12).split(" ").get(1)
        var Arg13 = results.get(13).split(" ").get(1)
        var Arg14 = results.get(14).split(" ").get(1)
        var Arg15 = results.get(15).split(" ").get(1)
        var Arg16 = results.get(16).split(" ").get(1)
        var Arg17 = results.get(17).split(" ").get(1)
        var Arg18 = results.get(18).split(" ").get(1)
        var Arg19 = results.get(19).split(" ").get(1)
        var Arg20 = results.get(20).split(" ").get(1)
        var Arg21 = results.get(21).split(" ").get(1)
        var Arg22 = results.get(22).split(" ").get(1)
        var Arg23 = results.get(23).split(" ").get(1)
        var Arg24 = results.get(24).split(" ").get(1)
        var Arg25 = results.get(25).split(" ").get(1)
        var Arg26 = results.get(26).split(" ").get(1)
        var Arg27 = results.get(27).split(" ").get(1)
        var Arg28 = results.get(28).split(" ").get(1)
        var Arg29 = results.get(29).split(" ").get(1)
        var Arg30 = results.get(30).split(" ").get(1)
        var Arg31 = results.get(31).split(" ").get(1)
        var Arg32 = results.get(32).split(" ").get(1)
        var Arg33 = results.get(33).split(" ").get(1)
        var Arg34 = results.get(34).split(" ").get(1)
        var Arg35 = results.get(35).split(" ").get(1)
        var Arg36 = results.get(36).split(" ").get(1)
        var Arg37 = results.get(37).split(" ").get(1)
        var Arg38 = results.get(38).split(" ").get(1)
        var Arg39 = results.get(39).split(" ").get(1)
        USV_APC_BattProz.sendCommand(Arg1)
        USV_APC_BattLowProz.sendCommand(Arg2)
        USV_APC_BattWarnProz.sendCommand(Arg3)
        USV_APC_BattManFacDate.sendCommand(Arg4)
        USV_APC_BattRuntime.sendCommand(Arg5)
        USV_APC_BattRuntimeLow.sendCommand(Arg6)
        USV_APC_BattType.sendCommand(Arg7)
        USV_APC_BattVolt.sendCommand(Arg8)
        USV_APC_BattVoltNorm.sendCommand(Arg9)
        USV_APC_DevMfr.sendCommand(Arg10)
        USV_APC_DevModel.sendCommand(Arg11)
        USV_APC_DevSerNr.sendCommand(Arg12)
        USV_APC_DevTyp.sendCommand(Arg13)
        USV_APC_DriverName.sendCommand(Arg14)
        USV_APC_DriverPollFr.sendCommand(Arg15)
        USV_APC_DriverPollInt.sendCommand(Arg16)
        USV_APC_DriverPort.sendCommand(Arg17)
        USV_APC_DriverVers.sendCommand(Arg18)
        USV_APC_DriverData.sendCommand(Arg19)
        USV_APC_DriverVersInt.sendCommand(Arg20)
        USV_APC_InpSens.sendCommand(Arg21)
        USV_APC_InpTransH.sendCommand(Arg22)
        USV_APC_InpTransL.sendCommand(Arg23)
        USV_APC_InpVolt.sendCommand(Arg24)
        USV_APC_InpVoltNorm.sendCommand(Arg25)
        USV_APC_UpsBeep.sendCommand(Arg26)
        USV_APC_UpsShutdDelay.sendCommand(Arg27)
        USV_APC_UpsFirmware.sendCommand(Arg28)
        USV_APC_UpsFirmwareAux.sendCommand(Arg29)
        USV_APC_UpsLoad.sendCommand(Arg30)
        USV_APC_UpsMfr.sendCommand(Arg31)
        USV_APC_UpsManFacDate.sendCommand(Arg32)
        USV_APC_UpsModel.sendCommand(Arg33)
        USV_APC_UpsProductId.sendCommand(Arg34)
        USV_APC_UpsSerNr.sendCommand(Arg35)
        USV_APC_UpsStatus.sendCommand(Arg36)
        USV_APC_UpsTimerReboot.sendCommand(Arg37)
        USV_APC_UpsTimerShutdown.sendCommand(Arg38)
        USV_APC_UpsVendorId.sendCommand(Arg39)
But it’s not working.
Can someone help me with this Problem? Thanks!
Does your rule file load successfully? Look into your openhab.log
Are there any runtime errors? See openhab.log
Does the rule fire? Add a logInfo to find out.
Does your data fetch return anything? Add a logInfo to find out.
2019-08-24 13:28:00.130 [ERROR] [ntime.internal.engine.ExecuteRuleJob] - Error during the execution of rule 'Alle 20 Sekunden UPS Status abfragen und auswerten': 2
This is in the Log
The Rule loaded successfully
I’m almost certain that means the results string is not what you expect, and there is no element 2 for get(2)
I have corrected the error where Arg1 is.
Now i get errors that the format doesn’t match
Are you aware that there is a NUT binding? Russel posted a pretty thorough tutorial to get it up and working with openHAB. Beginner's Guide to Network UPS Tools (NUT) on a Raspberry Pi
One thing I don’t know is whether the NUT output is guaranteed to always be in the same order. Just in case I would change the approach a little and use a Map. Then you can use a nice for loop to process each line as well.
    Time cron 0/20 * * ? * * *"
    // This Rule executes every 20 seconds. You must not let the Rule take more than 20 seconds to complete
    // The original timeout of two minutes creates a really likely risk that you run out of Quartz threads
    // and all your cron triggered Rules and Astro binding will stop functioning
    val commandOutput = executeCommandLine("upsc ups@IP-NutServer", 15*1000)
    if(!commandOutput.startsWith("Init SSL")) return; // fail fast
    val values = newHashMap
    commandOutput.split("\\r?\\n").forEach[ line |
        val parts = line.split(": ")
        values.put(parts.get(0), parts.get(1))
    // since you are just changing OH state and not causing something to happen, use postUpdate
    USV_APC_BattProz.postUpdate(values.get("battery.charge"))
Please don’t describe the error. Post the actual error.
I’ve forgott an item so that they where all shifted.
The binding is not working for me.
Thats now my solution:
Follow this guide to setup the NUT-Client: Click
Then configure this Openhab-Files:
Items-File:
    String        USV_APC_BattDate                                              "Akku Datum: [%s]"                                            <calendar>
    String        USV_APC_UpsBeep                                               "Piepser: [%s]"                                               <battery>
    String        USV_APC_UpsStatus                                             "Ups Status: [MAP(USV_Status.map):%s]"                        <battery>
Rules-File:
rule "Alle 20 Sekunden USV Status abfragen und auswerten"
        if(parts.size > 1) values.put(parts.get(0), parts.get(1))
    USV_APC_BattProz.sendCommand(values.get("battery.charge"))
    USV_APC_BattLowProz.sendCommand(values.get("battery.charge.low"))
    USV_APC_BattWarnProz.sendCommand(values.get("battery.charge.warning"))
    USV_APC_BattDate.sendCommand(values.get("battery.date"))
    USV_APC_BattManFacDate.sendCommand(values.get("battery.mfr.date"))
    USV_APC_BattRuntime.sendCommand(values.get("battery.runtime"))
    USV_APC_BattRuntimeLow.sendCommand(values.get("battery.runtime.low"))
    USV_APC_BattType.sendCommand(values.get("battery.type"))
    USV_APC_BattVolt.sendCommand(values.get("battery.voltage"))
    USV_APC_BattVoltNorm.sendCommand(values.get("battery.voltage.nominal"))
    USV_APC_DevMfr.sendCommand(values.get("device.mfr"))
    USV_APC_DevModel.sendCommand(values.get("device.model"))
    USV_APC_DevSerNr.sendCommand(values.get("device.serial"))
    USV_APC_DevTyp.sendCommand(values.get("device.type"))
    USV_APC_DriverName.sendCommand(values.get("driver.name"))
    USV_APC_DriverPollFr.sendCommand(values.get("driver.parameter.pollfreq"))
    USV_APC_DriverPollInt.sendCommand(values.get("driver.parameter.pollinterval"))
    USV_APC_DriverPort.sendCommand(values.get("driver.parameter.port"))
    USV_APC_DriverVers.sendCommand(values.get("driver.version"))
    USV_APC_DriverData.sendCommand(values.get("driver.version.data"))
    USV_APC_DriverVersInt.sendCommand(values.get("driver.version.internal"))
    USV_APC_InpSens.sendCommand(values.get("input.sensitivity"))
    USV_APC_InpTransH.sendCommand(values.get("input.transfer.high"))
    USV_APC_InpTransL.sendCommand(values.get("input.transfer.low"))
    USV_APC_InpVolt.sendCommand(values.get("input.voltage"))
    USV_APC_InpVoltNorm.sendCommand(values.get("input.voltage.nominal"))
    USV_APC_UpsBeep.sendCommand(values.get("ups.beeper.status"))
    USV_APC_UpsShutdDelay.sendCommand(values.get("ups.delay.shutdown"))
    USV_APC_UpsFirmware.sendCommand(values.get("ups.firmware"))
    USV_APC_UpsFirmwareAux.sendCommand(values.get("ups.firmware.aux"))
    USV_APC_UpsLoad.sendCommand(values.get("ups.load"))
    USV_APC_UpsMfr.sendCommand(values.get("ups.mfr"))
    USV_APC_UpsManFacDate.sendCommand(values.get("ups.mfr.date"))
    USV_APC_UpsModel.sendCommand(values.get("ups.model"))
    USV_APC_UpsProductId.sendCommand(values.get("ups.productid"))
    USV_APC_UpsSerNr.sendCommand(values.get("ups.serial"))
    USV_APC_UpsStatus.sendCommand(values.get("ups.status"))
    USV_APC_UpsTimerReboot.sendCommand(values.get("ups.timer.reboot"))
    USV_APC_UpsTimerShutdown.sendCommand(values.get("ups.timer.shutdown"))
    USV_APC_UpsVendorId.sendCommand(values.get("ups.vendorid"))
rule "Wenn USV in Batteriemodus wechselt"
    Item USV_APC_UpsStatus changed to 'OB DISCHRG'
        logInfo("Nachricht", "00 USV in Batteriebetrieb")
    Item USV_APC_UpsStatus changed to 'OL'
        logInfo("Nachricht", "00 USV in Netzbetrieb")
    Item USV_APC_UpsStatus changed to 'OL CHRG'
        logInfo("Nachricht", "00 USV Laedt")
Here i coded “.sendCommand” because of the Actions
Sitemap:
    Frame label="USV"{
	  Text label="USV" icon="battery" {
        Text item=USV_APC_BattProz
        Text item=USV_APC_BattLowProz
        Text item=USV_APC_BattWarnProz
        Text item=USV_APC_BattDate
        Text item=USV_APC_BattManFacDate
        Text item=USV_APC_BattRuntime
        Text item=USV_APC_BattRuntimeLow
        Text item=USV_APC_BattType
        Text item=USV_APC_BattVolt
        Text item=USV_APC_BattVoltNorm
        Text item=USV_APC_DevMfr
        Text item=USV_APC_DevModel
        Text item=USV_APC_DevSerNr
        Text item=USV_APC_DevTyp
        Text item=USV_APC_DriverName
        Text item=USV_APC_DriverPollFr
        Text item=USV_APC_DriverPollInt
        Text item=USV_APC_DriverPort
        Text item=USV_APC_DriverVers
        Text item=USV_APC_DriverData
        Text item=USV_APC_DriverVersInt
        Text item=USV_APC_InpSens
        Text item=USV_APC_InpTransH
        Text item=USV_APC_InpTransL
        Text item=USV_APC_InpVolt
        Text item=USV_APC_InpVoltNorm
        Text item=USV_APC_UpsBeep
        Text item=USV_APC_UpsShutdDelay
        Text item=USV_APC_UpsFirmware
        Text item=USV_APC_UpsFirmwareAux
        Text item=USV_APC_UpsLoad
        Text item=USV_APC_UpsMfr
        Text item=USV_APC_UpsManFacDate
        Text item=USV_APC_UpsModel
        Text item=USV_APC_UpsProductId
        Text item=USV_APC_UpsSerNr
        Text item=USV_APC_UpsStatus
        Text item=USV_APC_UpsTimerReboot
        Text item=USV_APC_UpsTimerShutdown
        Text item=USV_APC_UpsVendorId
Map File “USV_Status.map”:
OB \DISCHRG=Batteriemodus
OL \CHRG=Lädt auf
OL=Netzbetrieb
Did you file an issue? It can’t be fixed if we don’t know it’s broken.
It says “Nut processing error” “org.networkupstools.jnut.NutException: UNKNOWN-UPS”
But i configured it with the correct password
Yout solution above is smart but it gives me the error: “Error during the execution of rule ‘Alle 20 Sekunden UPS Status abfragen und auswerten’: 1”
Oh, I know what’s wrong. The first line doesn’t have the ": " because it’s the Init SSL line.
Change
For the error, that has nothing to do with the password. That looks like you had the wrong path to the nut server. But if you are sure you configured everything correctly, file an issue so the developers can fix the problem if there is one.
Your solution is working perfectly thanks!
Can it be that if I run the Nut client in the background a second instance of the nut client (from the binding) is not possible?
I don’t know but that will but my understanding is the binding does exactly what your rule does. It just calls upsc, or more likely implements the same protocol as upsc to get the information. I’ve been using the binding for quite some time and can confirm that at least in my environment it works just fine. So it can work. There open question is why it doesn’t work for you.
I don’t know. But it is not so bad. The version above works great for me