2020-12-12T13:23:01Z
2020-12-12T13:23:51Z
14.00
13620
26085
30375
1440
False
False
1: Vendor - Kohler Company |
549: Ats Contactor Position - Source2 |
1221: Value - False |
1543: Value - 9.5 |
2: Controller Type - DC2 |
550: Ats Sources Available - 3 |
1222: Event - Low Fuel Pressure |
1544: Relative Value - 9.57 |
3: Current Firmware - 6.12.2 |
563: Source1 Rotation Actual - Disabled |
1224: Switch Type - Normally Open |
1545: Low Protective Inhibit Delay - 0 |
4: Engine Speed - 3606 R/min |
585: Source1 Voltage AB - 244.1 V |
1225: Value - False |
1546: High Protective Inhibit Delay - 0 |
5: Engine Target Speed - 3600 R/min |
586: Source1 Voltage BC - 0.0 V |
1226: Enabled - True |
1547: Normal Delay - 0 |
6: Engine Oil Pressure - 0 Psi |
587: Source1 Voltage CA - 0.0 V |
1227: Event - Auxiliary Input Value Fault |
1548: Low Warning Delay - 0 |
7: Engine Coolant Temperature - 32 F |
588: Source1 Voltage Average Line To Line - 244.1 V |
1229: Switch Type - Normally Open |
1549: Critically Low Warning Delay - 0 |
11: Battery Voltage - 13.2 V |
597: Source1 Frequency - 60.0 Hz |
1230: Value - False |
1550: High Warning Delay - 0 |
18: Lube Oil Temperature - 176 F |
598: Source2 Rotation Actual - Disabled |
1231: Enabled - True |
1551: Critically High Warning Delay - 0 |
20: Generator Controller Temperature - 86 F |
620: Source2 Voltage AB - 230.6 V |
1232: Event - Battery Charger Fault Value |
1552: Low Shutdown Delay - 0 |
26: Engine Low Oil Pressure Switch - Off |
621: Source2 Voltage BC - 0.0 V |
1234: Switch Type - Normally Open |
1553: High Shutdown Delay - 0 |
32: Engine Compartment Temperature - 32 F |
622: Source2 Voltage CA - 0.0 V |
1289: Value - False |
1554: Low Warning Limit - 0.0 |
33: Engine Speed Adjustment - 50 |
623: Source2 Voltage Average Line To Line - 230.6 V |
1290: Enabled - False |
1555: Critically Low Warning Limit - 0.0 |
34: Engine Speed Gain Adjustment - 50 |
632: Source2 Frequency - 60.0 Hz |
1291: Event - None Value |
1556: Low Shutdown Limit - 0.0 |
35: Generator Rotation Actual - Disabled |
661: Ats Total Hours Of Operation - 1982.0 h |
1292: Value - False |
1557: High Warning Limit - 0.0 |
36: Generator Current Lead Lag A - 0 |
662: Ats Total Hours Not In Preferred - 19.1 h |
1293: Enabled - False |
1558: Critically High Warning Limit - 0.0 |
37: Generator Current Lead Lag B - 0 |
663: Ats Total Hours In Standby - 19.1 h |
1294: Event - None Value |
1559: High Shutdown Limit - 0.0 |
38: Generator Current Lead Lag C - 0 |
664: Ats Total Switch Transfers - 4.9 |
1315: Value - False |
1560: Deadband - 0.0 |
39: Generator Current Total Lead Lag - 0 |
666: Ats Total Loss Of Preferred Transfers - 1.8 |
1316: Event - Nfpa110 Alarm Active Value Warning |
1615: Serial Number - 51078 |
40: Generator Power Factor A - 0.0 |
672: Ats Hours Of Operation Since Maintenance - 1982.0 h |
1319: Value - True |
1616: Type - Load Control |
41: Generator Power Factor B - 0.0 |
673: Ats Hours Not In Preferred Since Maintenance - 19.1 h |
1320: Event - Generator Running Value |
1617: Communication Errors - 0 |
42: Generator Power Factor C - 0.0 |
674: Ats Hours In Standby Since Maintenance - 19.1 h |
1321: Value - False |
1618: Communication Timeouts - 2 |
43: Generator Total Power Factor - 0.0 |
675: Ats Switch Transfers Since Maintenance - 49 |
1322: Event - Common Fault Value |
1619: Modbus Id - 1 |
44: Generator Apparent Power A - 0.0 VA |
677: Ats Loss Of Preferred Transfers Since Maintenance - 18 |
1323: Value - False |
1620: Last Connection Date - 0001-01-03 00:00:00 |
45: Generator Apparent Power B - 0.0 VA |
689: Ats Source - Local |
1324: Event - Low Battery Voltage |
1621: Firmware Version - 1.2.0 |
46: Generator Apparent Power C - 0.0 VA |
696: Source1 System Voltage - 240.0 V |
1325: Value - False |
1622: Connected - True |
47: Generator Total Apparent Power - 0.0 VA |
697: Source1 System Frequency - 60.0 Hz |
1326: Event - Not In Auto Value Fault |
1623: Serial Number - -1 |
48: Generator Reactive Power A - 0.0 VAR |
700: Source1 Voltage Debounce Delay - 0.5 s |
1327: Value - True |
1624: Type - Invalid |
49: Generator Reactive Power B - 0.0 VAR |
706: Source1 Low Voltage Pickup - 90 % |
1328: Event - Engine Cool Down Active Value |
1625: Communication Errors - 0 |
50: Generator Reactive Power C - 0.0 VAR |
707: Source1 Low Voltage Dropout - 90 % |
1329: Value - False |
1626: Communication Timeouts - 0 |
51: Generator Total Reactive Power - 0.0 VAR |
713: Source1 Calibration Factor Voltage AB - 1.0 |
1330: Event - Normal Power Source Unavailable Value |
1627: Modbus Id - 0 |
52: Generator True Power A - 0.0 W |
714: Source1 Calibration Factor Voltage BC - 1.0 |
1331: Value - False |
1628: Last Connection Date - 0001-01-03 00:00:00 |
53: Generator True Power B - 0.0 W |
715: Source1 Calibration Factor Voltage CA - 1.0 |
1332: Event - Load Priority 2 Shed Value |
1629: Firmware Version - 0.0.0 |
54: Generator True Power C - 0.0 W |
722: Source2 System Voltage - 240.0 V |
1333: Value - False |
1630: Connected - False |
55: Generator True Total Power - 0.0 W |
723: Source2 System Frequency - 60.0 Hz |
1334: Event - Load Priority 5 Shed Value Fault |
1631: Serial Number - -1 |
56: Generator True Percent Of Rated Power - 0 % |
726: Source2 Voltage Debounce Delay - 0.5 s |
1335: Value - False |
1632: Type - Invalid |
57: Generator Voltage AB - 240.4 V |
732: Source2 Low Voltage Pickup - 90 % |
1336: Event - Load Priority 1 Shed Value Fault |
1633: Communication Errors - 0 |
58: Generator Voltage BC - 0.0 V |
733: Source2 Low Voltage Dropout - 90 % |
1337: Value - False |
1634: Communication Timeouts - 0 |
59: Generator Voltage CA - 0.0 V |
739: Source2 Calibration Factor Voltage AB - 1.0 |
1338: Event - Load Priority 3 Shed Value |
1635: Modbus Id - 0 |
60: Generator Voltage Average Line To Line - 240.4 V |
740: Source2 Calibration Factor Voltage BC - 1.0 |
1339: Value - False |
1636: Last Connection Date - 0001-01-03 00:00:00 |
61: Generator Voltage AN - 0.0 V |
741: Source2 Calibration Factor Voltage CA - 1.0 |
1340: Event - Load Priority 4 Shed Value Warning |
1637: Firmware Version - 0.0.0 |
65: Generator Current A - 0.0 A |
748: Exercise Interval - Every Other Week |
1341: Value - False |
1638: Connected - False |
66: Generator Current B - 0.0 A |
749: Exercise Run Duration - 15 min |
1342: Event - Load Priority 6 Shed Value |
1639: Serial Number - -1 |
67: Generator Current C - 0.0 A |
750: Exercise Mode - Loaded Full Speed |
1395: Protectives Enabled - 0 |
1640: Type - Invalid |
68: Generator Current Average - 12.2 A |
751: Exercise Warning Enabled - True |
1398: Event - Engine Fuel Level |
1641: Communication Errors - 0 |
69: Generator Frequency - 60.2 Hz |
752: Ats Transfer From Preferred Delay - 3 s |
1399: Sensor - Fuel Level |
1642: Communication Timeouts - 0 |
91: Genset Model Number Select - 20 RESA |
753: Ats Transfer From Standby Delay - 120 s |
1412: Protectives Enabled - 0 |
1643: Modbus Id - 0 |
93: Generator Serial Number - sgm142hdr |
756: Ats Source2 Engine Start Delay - 3 s |
1413: Event - None Value |
1644: Last Connection Date - 0001-01-03 00:00:00 |
94: Alternator Part Number - |
852: Is Modbus Master - False |
1414: Sensor - None |
1645: Firmware Version - 0.0.0 |
95: Generator Controller Serial Number - 1309738773 |
857: Dhcp Enabled - True |
1424: Inhibit Delay - 0 |
1646: Connected - False |
96: Engine Part Number - |
858: Static IP Address - 192.168.2.30 |
1425: Delay - 0 |
1647: Serial Number - -1 |
97: Engine Model Number - CH-1000 |
859: Static Subnet Mask - 255.255.255.0 |
1426: Inhibit Delay - 0 |
1648: Type - Invalid |
98: Engine Serial Number - |
860: Static Default Gateway - 192.168.2.1 |
1427: Delay - 0 |
1649: Communication Errors - 0 |
102: Generator State - Performing Loaded Exercise |
861: Static Dns Server1 - 8.8.8.8 |
1428: Inhibit Delay - 0 |
1650: Communication Timeouts - 0 |
113: Generator Controller Clock Time - 2013-03-25 20:38:06 |
862: Static Dns Server2 - 8.8.4.4 |
1429: Delay - 0 |
1651: Modbus Id - 0 |
114: Generator Controller Total Operation Time - 19556.6 h |
863: Server Host Name - devices.kohler.com |
1474: Value - 0.0 |
1652: Last Connection Date - 0001-01-03 00:00:00 |
115: Engine Total Run Time - 55.6 h |
864: IP Address - 47.16.240.87:1182 |
1475: Relative Value - 0.0 |
1653: Firmware Version - 0.0.0 |
116: Engine Total Run Time Loaded - 27.1 h |
865: Subnet Mask - 255.255.255.0 |
1476: Low Protective Inhibit Delay - 0 |
1654: Connected - False |
118: Engine Total Number Of Starts - 143 |
866: Default Gateway - 192.168.2.1 |
1477: High Protective Inhibit Delay - 0 |
1655: Serial Number - -1 |
119: Genset Total Energy - 1.1986518E7 kWh |
867: Dns Server1 - 10.105.2.50 |
1481: Normal Delay - 0 |
1656: Type - Invalid |
121: Genset Date Time Of Last Maintenance - 2012-11-03 01:23:31 |
868: Dns Server2 - 8.8.8.8 |
1482: Low Warning Delay - 30 |
1657: Communication Errors - 0 |
122: Engine Run Time At Reset Maintenance - 22.8 h |
869: Mac Address - 146022421884574 |
1483: Critically Low Warning Delay - 0 |
1658: Communication Timeouts - 0 |
123: Engine Run Time Until Maintenance - 123.4 h |
870: Connected Server IP Address - 40.117.195.28 |
1484: High Warning Delay - 0 |
1659: Modbus Id - 0 |
124: Genset Controller Hours Of Operation Since Maintenance - 19556.6 h |
872: Network Connection Established - True |
1485: Critically High Warning Delay - 0 |
1660: Last Connection Date - 0001-01-03 00:00:00 |
125: Engine Run Time Since Maintenance - 26.6 h |
873: Media Connected - True |
1486: Low Shutdown Delay - 10 |
1661: Firmware Version - 0.0.0 |
126: Engine Run Time Loaded Since Maintenance - 27.1 h |
903: Rbus Active - True |
1487: High Shutdown Delay - 0 |
1662: Connected - False |
128: Engine Number Of Starts Since Maintenance - 143 |
904: Rbus Connection Count - 2 |
1488: Low Warning Limit - 35.0 |
1663: Serial Number - -1 |
129: Genset Energy Since Maintenance - 1.1986518E7 kWh |
905: Rbus Net Cycle Time - 200 ms |
1489: Critically Low Warning Limit - 0.0 |
1664: Type - Invalid |
136: Genset Controller Date Format - Month Date Year |
906: Rbus Timeouts - 20 |
1490: Low Shutdown Limit - 5.0 |
1665: Communication Errors - 0 |
137: Genset Controller Time Format - Hr12 |
907: Rbus Errors - 0 |
1491: High Warning Limit - 90.0 |
1666: Communication Timeouts - 0 |
138: Genset Date Timeof Next Maintenance - 0001-08-13 04:51:25 |
908: Serial Number - 26981 |
1492: Critically High Warning Limit - 95.0 |
1667: Modbus Id - 0 |
139: Maintenance Period In Days - 365 days |
909: Type - Single Phase Ats |
1493: High Shutdown Limit - 0.0 |
1668: Last Connection Date - 0001-01-03 00:00:00 |
140: Maintenance Period Remaining - 19197720 s |
910: Communication Errors - 0 |
1494: Deadband - 0.0 |
1669: Firmware Version - 0.0.0 |
141: Genset Controller Clock Time Zone Offset - 0001-01-03 00:00:00 |
911: Communication Timeouts - 18 |
1670: Connected - False |
142: Ecm Model - No Ecm |
912: Modbus Id - 2 |
1671: Latest Firmware - 6.12.2 |
143: Maximum Alternator Current - 75 A |
913: Last Connection Date - 0001-01-03 00:00:00 |
144: Engine Number Of Flywheel Teeth - 1 |
914: Firmware Version - 1.2.0 |
145: Engine Warmed Up Temperature - 89.6 F |
915: Connected - True |
146: Engine Cooled Down Temperature - 174.2 F |
147: Engine Crank Disconnect Speed - 750 R/min |
148: Engine Idle Speed - 2700 R/min |
149: Engine Run Speed - 3600 R/min |
150: Engine Coolant Temperature Protectives Enabled - Low Warning |
151: Engine Coolant Temperature Sensor - None |
153: Engine High Coolant Temperature Inhibit Delay - 0 s |
154: Engine Low Coolant Temperature Warning Delay - 5 s |
155: Engine High Coolant Temperature Warning Delay - 0 s |
156: Engine Low Coolant Temperature Shutdown Delay - 0 s |
157: Engine High Coolant Temperature Shutdown Delay - 0 s |
158: Engine Low Coolant Temperature Warning Limit - 60.08 F |
159: Engine High Coolant Temperature Warning Limit - 32 F |
161: Engine High Coolant Temperature Shutdown Limit - 32 F |
162: Engine Coolant Temperature Deadband - 33.8 F |
163: Personality Alternator Manufacturer - Marathon |
164: Personality Alternator Toc Time Constant - 203 s |
165: Personality Alternator Number Of Poles - -1 |
166: Personality Alternator Type - Old Reconnectable Or Dual |
167: Personality Fixed Voltage50 Hz - 0 V |
168: Personality Power Rating Single Phase50 Hz10 PF - 0 kW |
169: Personality Power Rating Single Phase50 Hz8 PF - 10 kW |
170: Personality Power Rating Fixed Volt50 Hz - 0 kW |
171: Personality Power Rating50 Hz_220_440 - 0 kW |
172: Personality Power Rating50 Hz_208_415 - 0 kW |
173: Personality Power Rating50 Hz_200_400 - 0 kW |
174: Personality Power Rating50 Hz_190_380 - 0 kW |
175: Personality Power Rating50 Hz_173_346 - 9995 kW |
176: Personality Power Rating50 Hz Delta - 0 kW |
177: Personality Fixed Voltage60 Hz - 3597 V |
178: Personality Power Rating Single Phase60 Hz10 PF - 0 kW |
179: Personality Power Rating Single Phase60 Hz8 PF - 0 kW |
180: Personality Power Rating Fixed Volt60 Hz - 0 kW |
181: Personality Power Rating60 Hz_240_480 - 0 kW |
182: Personality Power Rating60 Hz_230_460 - 0 kW |
183: Personality Power Rating60 Hz_220_440 - 0 kW |
184: Personality Power Rating60 Hz_208_416 - 0 kW |
185: Personality Power Rating60 Hz_190_380 - 0 kW |
186: Personality Power Rating60 Hz Delta - 0 kW |
188: Personality Installed Options - 0 |
190: Genset System Voltage - 240.0 V |
191: Genset System Frequency - 60.0 Hz |
192: Genset Voltage Phase Connection - Single Phase |
193: Genset Power Rating - 18.0 kW |
194: Genset Rated Current - 75.0 A |
195: Genset System Battery Voltage - Twelve Volts |
196: Prime Power Application - Standby |
197: Current Transformer Ratio - 400 |
198: Local Start Mode - Off |
199: Measurement System - English |
200: Ecm Power - Off |
206: Display Contrast - 50 |
208: Genset System Language - English |
209: Genset Maximum Percent Capacity - 70.0 % |
210: Generator Overloaded Percent - 85.0 % |
211: Genset Fuel Type - Natural Gas |
212: Automatic Start Minimum Voltage - 51.0 V |
213: Automatic Stop Minimum Percent Load - 20.0 % |
215: Automatic Start Minimum Voltage Delay - 180.0 s |
216: Automatic Stop Minimum Load Delay - 180.0 s |
219: Genset Calibration Factor Voltage AB - 1.015808 |
220: Genset Calibration Factor Voltage BC - 0.9745 |
221: Genset Calibration Factor Voltage CA - 0.915 |
222: Genset Calibration Factor Voltage AN - 1.0 |
225: Genset Calibration Factor Current A - 1.0 |
226: Genset Calibration Factor Current B - 1.0 |
227: Genset Calibration Factor Current C - 1.0 |
228: Current Transformer Calibration At No Load - 3.5 |
229: Current Transformer Calibration At Full Load - 121.5 |
239: Proportional Gain - 1.0 |
240: Transient Integral Gain - 1.0 |
241: Derivative Gain - 1.0 |
242: Slow Correction Integral Gain - 1.0 |
243: Diagnostic Derivative Gain - 1.0 |
244: Diagnostic Transient Integral Gain - 1.0 |
245: Voltage Regulator Average Voltage Adjustment - 240.0 V |
246: Voltage Regulator Volts Per Hertz Slope - 5 % |
247: Voltage Regulator Volts Per Hertz Cut In Frequency - 59.0 Hz |
248: Voltage Regulator Gain - 128 |
265: Engine Start Delay - 0 s |
267: Engine Cool Down Delay - 300 s |
270: Engine Crank On Delay - 15 s |
271: Engine Crank Pause Delay - 15 s |
272: Engine Number Of Crank Cycles - 3 |
274: Genset Low Battery Voltage Warning Delay - 90 s |
275: Genset High Battery Voltage Warning Delay - 10 s |
276: Genset Low Battery Voltage Warning Limit - 100 % |
277: Genset High Battery Voltage Warning Limit - 125 % |
278: Genset Battery Low Cranking Voltage Warning Delay - 6 s |
279: Genset Battery Low Cranking Voltage Warning Limit - 60 % |
292: Engine Locked Rotor Shutdown Delay - 3 s |
294: Genset Low Engine Speed Shutdown Limit - 85 % |
295: Genset High Engine Speed Shutdown Limit - 115 % |
303: Engine Low Oil Pressure Warning Limit - 0 Psi |
306: Engine High Oil Pressure Shutdown Limit - 0 Psi |
308: Loss Of ACSensing Shutdown Delay - 3 s |
309: Genset Low Voltage Shutdown Delay - 10 s |
310: Genset High Voltage Shutdown Delay - 2 s |
311: Genset Low Voltage Shutdown Limit - 80 % |
312: Genset High Voltage Shutdown Limit - 120 % |
313: Genset Short Term Low Frequency Shutdown Delay - 10 s |
314: Genset Long Term Low Frequency Shutdown Delay - 60 s |
315: Genset High Frequency Shutdown Delay - 10 s |
316: Genset Low Frequency Shutdown Limit - 90 % |
317: Genset High Frequency Shutdown Limit - 110 % |
600
600
3
10
3
False
False
1: Vendor - Kohler Company |
549: Ats Contactor Position - Source1 |
1221: Value - False |
1543: Value - 9.5 |
2: Controller Type - DC2 |
550: Ats Sources Available - Source1 |
1222: Event - Low Fuel Pressure |
1544: Relative Value - 9.57 |
3: Current Firmware - 6.12.2 |
563: Source1 Rotation Actual - Disabled |
1224: Switch Type - Normally Open |
1545: Low Protective Inhibit Delay - 0 |
4: Engine Speed - 0 R/min |
585: Source1 Voltage AB - 241.0 V |
1225: Value - False |
1546: High Protective Inhibit Delay - 0 |
5: Engine Target Speed - 0 R/min |
586: Source1 Voltage BC - 0.0 V |
1226: Enabled - True |
1547: Normal Delay - 0 |
6: Engine Oil Pressure - 0 Psi |
587: Source1 Voltage CA - 0.0 V |
1227: Event - Auxiliary Input Value Fault |
1548: Low Warning Delay - 0 |
7: Engine Coolant Temperature - 32 F |
588: Source1 Voltage Average Line To Line - 241.0 V |
1229: Switch Type - Normally Open |
1549: Critically Low Warning Delay - 0 |
11: Battery Voltage - 13.4 V |
597: Source1 Frequency - 60.0 Hz |
1230: Value - False |
1550: High Warning Delay - 0 |
18: Lube Oil Temperature - 168.8 F |
598: Source2 Rotation Actual - Disabled |
1231: Enabled - True |
1551: Critically High Warning Delay - 0 |
20: Generator Controller Temperature - 91.4 F |
620: Source2 Voltage AB - 0.0 V |
1232: Event - Battery Charger Fault Value |
1552: Low Shutdown Delay - 0 |
26: Engine Low Oil Pressure Switch - Off |
621: Source2 Voltage BC - 0.0 V |
1234: Switch Type - Normally Open |
1553: High Shutdown Delay - 0 |
32: Engine Compartment Temperature - 32 F |
622: Source2 Voltage CA - 0.0 V |
1289: Value - False |
1554: Low Warning Limit - 0.0 |
33: Engine Speed Adjustment - 50 |
623: Source2 Voltage Average Line To Line - 0.0 V |
1290: Enabled - False |
1555: Critically Low Warning Limit - 0.0 |
34: Engine Speed Gain Adjustment - 50 |
632: Source2 Frequency - 0.0 Hz |
1291: Event - None Value |
1556: Low Shutdown Limit - 0.0 |
35: Generator Rotation Actual - Disabled |
661: Ats Total Hours Of Operation - 1982.4 h |
1292: Value - False |
1557: High Warning Limit - 0.0 |
36: Generator Current Lead Lag A - 0 |
662: Ats Total Hours Not In Preferred - 19.2 h |
1293: Enabled - False |
1558: Critically High Warning Limit - 0.0 |
37: Generator Current Lead Lag B - 0 |
663: Ats Total Hours In Standby - 19.1 h |
1294: Event - None Value |
1559: High Shutdown Limit - 0.0 |
38: Generator Current Lead Lag C - 0 |
664: Ats Total Switch Transfers - 5.0 |
1315: Value - False |
1560: Deadband - 0.0 |
39: Generator Current Total Lead Lag - 0 |
666: Ats Total Loss Of Preferred Transfers - 1.8 |
1316: Event - Nfpa110 Alarm Active Value Warning |
1615: Serial Number - 51078 |
40: Generator Power Factor A - 0.0 |
672: Ats Hours Of Operation Since Maintenance - 1982.4 h |
1319: Value - False |
1616: Type - Load Control |
41: Generator Power Factor B - 0.0 |
673: Ats Hours Not In Preferred Since Maintenance - 19.2 h |
1320: Event - Generator Running Value |
1617: Communication Errors - 0 |
42: Generator Power Factor C - 0.0 |
674: Ats Hours In Standby Since Maintenance - 19.1 h |
1321: Value - False |
1618: Communication Timeouts - 2 |
43: Generator Total Power Factor - 0.0 |
675: Ats Switch Transfers Since Maintenance - 50 |
1322: Event - Common Fault Value |
1619: Modbus Id - 1 |
44: Generator Apparent Power A - 0.0 VA |
677: Ats Loss Of Preferred Transfers Since Maintenance - 18 |
1323: Value - False |
1620: Last Connection Date - 0001-01-03 00:00:00 |
45: Generator Apparent Power B - 0.0 VA |
689: Ats Source - Local |
1324: Event - Low Battery Voltage |
1621: Firmware Version - 1.2.0 |
46: Generator Apparent Power C - 0.0 VA |
696: Source1 System Voltage - 240.0 V |
1325: Value - False |
1622: Connected - True |
47: Generator Total Apparent Power - 0.0 VA |
697: Source1 System Frequency - 60.0 Hz |
1326: Event - Not In Auto Value Fault |
1623: Serial Number - -1 |
48: Generator Reactive Power A - 0.0 VAR |
700: Source1 Voltage Debounce Delay - 0.5 s |
1327: Value - False |
1624: Type - Invalid |
49: Generator Reactive Power B - 0.0 VAR |
706: Source1 Low Voltage Pickup - 90 % |
1328: Event - Engine Cool Down Active Value |
1625: Communication Errors - 0 |
50: Generator Reactive Power C - 0.0 VAR |
707: Source1 Low Voltage Dropout - 90 % |
1329: Value - False |
1626: Communication Timeouts - 0 |
51: Generator Total Reactive Power - 0.0 VAR |
713: Source1 Calibration Factor Voltage AB - 1.0 |
1330: Event - Normal Power Source Unavailable Value |
1627: Modbus Id - 0 |
52: Generator True Power A - 0.0 W |
714: Source1 Calibration Factor Voltage BC - 1.0 |
1331: Value - False |
1628: Last Connection Date - 0001-01-03 00:00:00 |
53: Generator True Power B - 0.0 W |
715: Source1 Calibration Factor Voltage CA - 1.0 |
1332: Event - Load Priority 2 Shed Value |
1629: Firmware Version - 0.0.0 |
54: Generator True Power C - 0.0 W |
722: Source2 System Voltage - 240.0 V |
1333: Value - False |
1630: Connected - False |
55: Generator True Total Power - 0.0 W |
723: Source2 System Frequency - 60.0 Hz |
1334: Event - Load Priority 5 Shed Value Fault |
1631: Serial Number - -1 |
56: Generator True Percent Of Rated Power - 0 % |
726: Source2 Voltage Debounce Delay - 0.5 s |
1335: Value - False |
1632: Type - Invalid |
57: Generator Voltage AB - 0.0 V |
732: Source2 Low Voltage Pickup - 90 % |
1336: Event - Load Priority 1 Shed Value Fault |
1633: Communication Errors - 0 |
58: Generator Voltage BC - 0.0 V |
733: Source2 Low Voltage Dropout - 90 % |
1337: Value - False |
1634: Communication Timeouts - 0 |
59: Generator Voltage CA - 0.0 V |
739: Source2 Calibration Factor Voltage AB - 1.0 |
1338: Event - Load Priority 3 Shed Value |
1635: Modbus Id - 0 |
60: Generator Voltage Average Line To Line - 0.0 V |
740: Source2 Calibration Factor Voltage BC - 1.0 |
1339: Value - False |
1636: Last Connection Date - 0001-01-03 00:00:00 |
61: Generator Voltage AN - 0.0 V |
741: Source2 Calibration Factor Voltage CA - 1.0 |
1340: Event - Load Priority 4 Shed Value Warning |
1637: Firmware Version - 0.0.0 |
65: Generator Current A - 0.0 A |
748: Exercise Interval - Every Other Week |
1341: Value - False |
1638: Connected - False |
66: Generator Current B - 0.0 A |
749: Exercise Run Duration - 15 min |
1342: Event - Load Priority 6 Shed Value |
1639: Serial Number - -1 |
67: Generator Current C - 0.0 A |
750: Exercise Mode - Loaded Full Speed |
1395: Protectives Enabled - 0 |
1640: Type - Invalid |
68: Generator Current Average - 0.0 A |
751: Exercise Warning Enabled - True |
1398: Event - Engine Fuel Level |
1641: Communication Errors - 0 |
69: Generator Frequency - 0.0 Hz |
752: Ats Transfer From Preferred Delay - 3 s |
1399: Sensor - Fuel Level |
1642: Communication Timeouts - 0 |
91: Genset Model Number Select - 20 RESA |
753: Ats Transfer From Standby Delay - 120 s |
1412: Protectives Enabled - 0 |
1643: Modbus Id - 0 |
93: Generator Serial Number - sgm142hdr |
756: Ats Source2 Engine Start Delay - 3 s |
1413: Event - None Value |
1644: Last Connection Date - 0001-01-03 00:00:00 |
94: Alternator Part Number - |
852: Is Modbus Master - False |
1414: Sensor - None |
1645: Firmware Version - 0.0.0 |
95: Generator Controller Serial Number - 1309738773 |
857: Dhcp Enabled - True |
1424: Inhibit Delay - 0 |
1646: Connected - False |
96: Engine Part Number - |
858: Static IP Address - 192.168.2.30 |
1425: Delay - 0 |
1647: Serial Number - -1 |
97: Engine Model Number - CH-1000 |
859: Static Subnet Mask - 255.255.255.0 |
1426: Inhibit Delay - 0 |
1648: Type - Invalid |
98: Engine Serial Number - |
860: Static Default Gateway - 192.168.2.1 |
1427: Delay - 0 |
1649: Communication Errors - 0 |
102: Generator State - Standby |
861: Static Dns Server1 - 8.8.8.8 |
1428: Inhibit Delay - 0 |
1650: Communication Timeouts - 0 |
113: Generator Controller Clock Time - 2013-03-25 20:51:44 |
862: Static Dns Server2 - 8.8.4.4 |
1429: Delay - 0 |
1651: Modbus Id - 0 |
114: Generator Controller Total Operation Time - 19556.8 h |
863: Server Host Name - devices.kohler.com |
1474: Value - 0.0 |
1652: Last Connection Date - 0001-01-03 00:00:00 |
115: Engine Total Run Time - 55.7 h |
864: IP Address - 47.16.240.87:1182 |
1475: Relative Value - 0.0 |
1653: Firmware Version - 0.0.0 |
116: Engine Total Run Time Loaded - 27.2 h |
865: Subnet Mask - 255.255.255.0 |
1476: Low Protective Inhibit Delay - 0 |
1654: Connected - False |
118: Engine Total Number Of Starts - 143 |
866: Default Gateway - 192.168.2.1 |
1477: High Protective Inhibit Delay - 0 |
1655: Serial Number - -1 |
119: Genset Total Energy - 1.2022309E7 kWh |
867: Dns Server1 - 10.105.2.50 |
1481: Normal Delay - 0 |
1656: Type - Invalid |
121: Genset Date Time Of Last Maintenance - 2012-11-03 01:23:31 |
868: Dns Server2 - 8.8.8.8 |
1482: Low Warning Delay - 30 |
1657: Communication Errors - 0 |
122: Engine Run Time At Reset Maintenance - 22.8 h |
869: Mac Address - 146022421884574 |
1483: Critically Low Warning Delay - 0 |
1658: Communication Timeouts - 0 |
123: Engine Run Time Until Maintenance - 123.2 h |
870: Connected Server IP Address - 40.117.195.28 |
1484: High Warning Delay - 0 |
1659: Modbus Id - 0 |
124: Genset Controller Hours Of Operation Since Maintenance - 19556.8 h |
872: Network Connection Established - True |
1485: Critically High Warning Delay - 0 |
1660: Last Connection Date - 0001-01-03 00:00:00 |
125: Engine Run Time Since Maintenance - 26.8 h |
873: Media Connected - True |
1486: Low Shutdown Delay - 10 |
1661: Firmware Version - 0.0.0 |
126: Engine Run Time Loaded Since Maintenance - 27.2 h |
903: Rbus Active - True |
1487: High Shutdown Delay - 0 |
1662: Connected - False |
128: Engine Number Of Starts Since Maintenance - 143 |
904: Rbus Connection Count - 2 |
1488: Low Warning Limit - 35.0 |
1663: Serial Number - -1 |
129: Genset Energy Since Maintenance - 1.2022309E7 kWh |
905: Rbus Net Cycle Time - 200 ms |
1489: Critically Low Warning Limit - 0.0 |
1664: Type - Invalid |
136: Genset Controller Date Format - Month Date Year |
906: Rbus Timeouts - 20 |
1490: Low Shutdown Limit - 5.0 |
1665: Communication Errors - 0 |
137: Genset Controller Time Format - Hr12 |
907: Rbus Errors - 0 |
1491: High Warning Limit - 90.0 |
1666: Communication Timeouts - 0 |
138: Genset Date Timeof Next Maintenance - 0001-08-13 04:37:06 |
908: Serial Number - 26981 |
1492: Critically High Warning Limit - 95.0 |
1667: Modbus Id - 0 |
139: Maintenance Period In Days - 365 days |
909: Type - Single Phase Ats |
1493: High Shutdown Limit - 0.0 |
1668: Last Connection Date - 0001-01-03 00:00:00 |
140: Maintenance Period Remaining - 19197000 s |
910: Communication Errors - 0 |
1494: Deadband - 0.0 |
1669: Firmware Version - 0.0.0 |
141: Genset Controller Clock Time Zone Offset - 0001-01-03 00:00:00 |
911: Communication Timeouts - 18 |
1670: Connected - False |
142: Ecm Model - No Ecm |
912: Modbus Id - 2 |
1671: Latest Firmware - 6.12.2 |
143: Maximum Alternator Current - 75 A |
913: Last Connection Date - 0001-01-03 00:00:00 |
144: Engine Number Of Flywheel Teeth - 1 |
914: Firmware Version - 1.2.0 |
145: Engine Warmed Up Temperature - 89.6 F |
915: Connected - True |
146: Engine Cooled Down Temperature - 174.2 F |
147: Engine Crank Disconnect Speed - 750 R/min |
148: Engine Idle Speed - 2700 R/min |
149: Engine Run Speed - 3600 R/min |
150: Engine Coolant Temperature Protectives Enabled - Low Warning |
151: Engine Coolant Temperature Sensor - None |
153: Engine High Coolant Temperature Inhibit Delay - 0 s |
154: Engine Low Coolant Temperature Warning Delay - 5 s |
155: Engine High Coolant Temperature Warning Delay - 0 s |
156: Engine Low Coolant Temperature Shutdown Delay - 0 s |
157: Engine High Coolant Temperature Shutdown Delay - 0 s |
158: Engine Low Coolant Temperature Warning Limit - 60.08 F |
159: Engine High Coolant Temperature Warning Limit - 32 F |
161: Engine High Coolant Temperature Shutdown Limit - 32 F |
162: Engine Coolant Temperature Deadband - 33.8 F |
163: Personality Alternator Manufacturer - Marathon |
164: Personality Alternator Toc Time Constant - -20 s |
165: Personality Alternator Number Of Poles - -1 |
166: Personality Alternator Type - Old Reconnectable Or Dual |
167: Personality Fixed Voltage50 Hz - 0 V |
168: Personality Power Rating Single Phase50 Hz10 PF - 0 kW |
169: Personality Power Rating Single Phase50 Hz8 PF - 10 kW |
170: Personality Power Rating Fixed Volt50 Hz - 0 kW |
171: Personality Power Rating50 Hz_220_440 - 0 kW |
172: Personality Power Rating50 Hz_208_415 - 0 kW |
173: Personality Power Rating50 Hz_200_400 - 0 kW |
174: Personality Power Rating50 Hz_190_380 - 0 kW |
175: Personality Power Rating50 Hz_173_346 - 10026 kW |
176: Personality Power Rating50 Hz Delta - 0 kW |
177: Personality Fixed Voltage60 Hz - 3603 V |
178: Personality Power Rating Single Phase60 Hz10 PF - 0 kW |
179: Personality Power Rating Single Phase60 Hz8 PF - 0 kW |
180: Personality Power Rating Fixed Volt60 Hz - 0 kW |
181: Personality Power Rating60 Hz_240_480 - 0 kW |
182: Personality Power Rating60 Hz_230_460 - 0 kW |
183: Personality Power Rating60 Hz_220_440 - 0 kW |
184: Personality Power Rating60 Hz_208_416 - 0 kW |
185: Personality Power Rating60 Hz_190_380 - 0 kW |
186: Personality Power Rating60 Hz Delta - 0 kW |
188: Personality Installed Options - 0 |
190: Genset System Voltage - 240.0 V |
191: Genset System Frequency - 60.0 Hz |
192: Genset Voltage Phase Connection - Single Phase |
193: Genset Power Rating - 18.0 kW |
194: Genset Rated Current - 75.0 A |
195: Genset System Battery Voltage - Twelve Volts |
196: Prime Power Application - Standby |
197: Current Transformer Ratio - 400 |
198: Local Start Mode - Off |
199: Measurement System - English |
200: Ecm Power - Off |
206: Display Contrast - 50 |
208: Genset System Language - English |
209: Genset Maximum Percent Capacity - 70.0 % |
210: Generator Overloaded Percent - 85.0 % |
211: Genset Fuel Type - Natural Gas |
212: Automatic Start Minimum Voltage - 51.0 V |
213: Automatic Stop Minimum Percent Load - 20.0 % |
215: Automatic Start Minimum Voltage Delay - 180.0 s |
216: Automatic Stop Minimum Load Delay - 180.0 s |
219: Genset Calibration Factor Voltage AB - 1.015808 |
220: Genset Calibration Factor Voltage BC - 0.9745 |
221: Genset Calibration Factor Voltage CA - 0.915 |
222: Genset Calibration Factor Voltage AN - 1.0 |
225: Genset Calibration Factor Current A - 1.0 |
226: Genset Calibration Factor Current B - 1.0 |
227: Genset Calibration Factor Current C - 1.0 |
228: Current Transformer Calibration At No Load - 3.5 |
229: Current Transformer Calibration At Full Load - 121.5 |
239: Proportional Gain - 1.0 |
240: Transient Integral Gain - 1.0 |
241: Derivative Gain - 1.0 |
242: Slow Correction Integral Gain - 1.0 |
243: Diagnostic Derivative Gain - 1.0 |
244: Diagnostic Transient Integral Gain - 1.0 |
245: Voltage Regulator Average Voltage Adjustment - 240.0 V |
246: Voltage Regulator Volts Per Hertz Slope - 5 % |
247: Voltage Regulator Volts Per Hertz Cut In Frequency - 59.0 Hz |
248: Voltage Regulator Gain - 128 |
265: Engine Start Delay - 0 s |
267: Engine Cool Down Delay - 300 s |
270: Engine Crank On Delay - 15 s |
271: Engine Crank Pause Delay - 15 s |
272: Engine Number Of Crank Cycles - 3 |
274: Genset Low Battery Voltage Warning Delay - 90 s |
275: Genset High Battery Voltage Warning Delay - 10 s |
276: Genset Low Battery Voltage Warning Limit - 100 % |
277: Genset High Battery Voltage Warning Limit - 125 % |
278: Genset Battery Low Cranking Voltage Warning Delay - 6 s |
279: Genset Battery Low Cranking Voltage Warning Limit - 60 % |
292: Engine Locked Rotor Shutdown Delay - 3 s |
294: Genset Low Engine Speed Shutdown Limit - 85 % |
295: Genset High Engine Speed Shutdown Limit - 115 % |
303: Engine Low Oil Pressure Warning Limit - 0 Psi |
306: Engine High Oil Pressure Shutdown Limit - 0 Psi |
308: Loss Of ACSensing Shutdown Delay - 3 s |
309: Genset Low Voltage Shutdown Delay - 10 s |
310: Genset High Voltage Shutdown Delay - 2 s |
311: Genset Low Voltage Shutdown Limit - 80 % |
312: Genset High Voltage Shutdown Limit - 120 % |
313: Genset Short Term Low Frequency Shutdown Delay - 10 s |
314: Genset Long Term Low Frequency Shutdown Delay - 60 s |
315: Genset High Frequency Shutdown Delay - 10 s |
316: Genset Low Frequency Shutdown Limit - 90 % |
317: Genset High Frequency Shutdown Limit - 110 % |
600
600
24
3
2
1
False
False