Hi Ssalonen,
Thank for the great work your doing.
My log are here http://pastebin.com/xTCA6Nqt and my config http://pastebin.com/n5emH7be
I still get errors…
Do you have any suggestion to try?
Hi Ssalonen,
I still get errors…
Thanks that helps. The delay logic does not work as expected still (you can see “waited 0ms”)
Will look into it
edit: here’s a fixed version : link . Hope it works! @Ferryb4
edit2: noted later that this fixes it only for tcp connection but not serial. Try the v5 for serial fix.
Dear @ssalonen thank you for a great work!
Now I have 5 slaves, 150 ms delay and poll = 4000 ms. It works!
Thank you again.
@ssalonen still no improvement and still there’s this strange performance discrepancy between normal and debug mode:
openhab.cfg: http://pastebin.com/YvjU58j2
logback confs are unchanged.
logs, normal mode: http://pastebin.com/2hj6i6np
logs, debug mode: http://pastebin.com/xWWTzsbP
measured performance, normal mode: 182 transactions per minute
measured performance, debug mode: 1666 transactions per minute
Best regards,
M
EDIT 2: There was still bug with the delays with serial connedctions which basically meant that the delay (50ms) was not exercised in practice (from the logs you can see that Waited 0ms (interBorrowDelayMillis 50ms) before giving returning connection SerialConnection
). Please try the updated version (v5).
If that does not work, can you please try larger interTransactionDelay (the last number that is currently 50ms).
50ms might be too fast for the device, at least it was too much for my siemens plc (which should be industrial grade) which is using modbus tcp (not serial!).
Edit: Small thing but can you please add enable net.wimpi.modbus INFO level in logback.xml. It just basically makes it clear if transactions eventually succeeded…
Hi Ssalonen,
It works with v5.
I set the delay to 500ms
Now I have no more errors.
Thank you very much for your time and energy.
It didn’t work. With version 5 and this configuration for alI devices
modbus:poll=50
onnection=/dev/ttyS0:38400:8:none:1:rtu:280:80
I get a stable performance of 745 transactions per minute. Which sort of makes sense: 60*1000/80 = 750
I’ve added INFO level to the logback.xml. Not a single [ERROR] in the logs.
Although 745 is about four times better than the version openhab currently ships with, it’s still very slow. I’m convinced we can do better than that.
With 70ms transaction delay the performance goes below 300 transactions per minute.
Btw the difference between debug mode and normal mode is gone.
[quote=“ssalonen, post:65, topic:5246”]
[/quote] That can’t be the problem here. The devices I’ve got here have achieved >100 transactions per second (!), when they were connected to a PLC. Of course it also depends on the amount of Registers/Bits that is requested by the PLC, but this still rules out that the problem is with the devices.
In order to show what is possible with a single device I’ve changed my configuration as follows:
modbus:poll=5
modbus:serial.agsBusMasterHolding.connection=/dev/ttyS0:38400:8:none:1:rtu:280:10
modbus:serial.agsBusMasterHolding.id=247
modbus:serial.agsBusMasterHolding.start=42
modbus:serial.agsBusMasterHolding.length=14
modbus:serial.agsBusMasterHolding.type=holding
I get a stable 1864 transactions per minute. Again no [ERROR] in the logs.
Just to clarify: 14 registers is by far the biggest chunk of data I’m requesting among all the devices I have configured. The bottleneck must therefore be somewhere else.
We should make multiple devices work just as well as a single device. ~1900 transactions per minute is what what we should be aiming for (at least ).
If you need any further debug logs with multiple and single devices please say so. I’m willing to help in any way I can.
Thanks for your work!
M
Thank you for the cold hard facts. I’m really satisfied that the binding now at least “works” even though the performance is not yet maximised…
If I understand correctly, you start to get the EOF error with delays of 70ms? Or any other idea why performance decreases?
Now that the basic functionality works, could you try to decrease the read timeout to lower value, say 50ms. I’m thinking It could improve the performance even though the first read might sometimes time out, perhaps it helps to just retry aggressively. Now the binding retries the transactions 3 times.
You could also try to lower transaction delay to the maximum performance you have witnessed, ie 10ms (100 transactions per second).
Looking forward how these tips work!
Now properly understood you single device benchmark. Really illuminating.
Can you share trace level logs with the single slave back multiple slave? How many slaves you have exactly with multi slave configuration? I would like to investigate whether the extra loss is due to overhead cause by the frameworks etc I’m using … We talking about so large performance already…
It might also help that I remove the trace level logging statements, they do incur small overhead. I’ll have a look at this
single device conf: just the six lines I’ve posted in my previous post (1 slave)
single device logs, debug: trace - Pastebin.com (1871 transactions / minute)
multiple device conf: conf multiple - Pastebin.com (13 slaves)
multiple device logs, debug: multipeltrace - Pastebin.com (730 transactions / minute)
The trace level logging doesn’t seem to hurt performance in any way.
I’ll try lowering the timeouts later.
M
Makes things worse. Long transactions, like reading 14 registers, never succeed.
M
OK, to summarize the situation we have now the following (documenting for future generations as well… Perhaps we can snip out something for the wiki in the future as well)
(config) (as reported reported here and here)
(config)
modbus:serial.agsBusMasterHolding.connection=/dev/ttyS0:38400:8:none:1:rtu:280:80
(as reported here)
(same as this config but with different read timeout)
(as reported here)
[1] grepped timestamps with: grep "to allow delay between transactions" single_device.log|cut -d' ' -f1
[2] grepped average wait time using: grep "to allow delay between transactions" multi-device.txt|cut -d' ' -f8
[3] Here’s the corresponding place in code which makes the read block until 1) timeout occurs 2) all message bytes are read
Decreasing the read timeout was a bit poor advice, and definately that is not the issue since the single device configuration works extremely fast with read timeout of 280ms.
Based on the observations I think this might really work with multi device scenario (good general configuration instructions as well):
short poll period, e.g. 5ms. The binding will simply block until previous read is done, and immediately start the new poll round (checked this from openhab core code as well). If there is no requirement to update item status fast, this can be increased ofcourse.
generous read timeout, e.g. 280ms. When the line works, the read returns much faster. In case of errors (e.g. lost bit in transmission for whatever reason), the system waits 280ms before giving up. Default 500ms is pretty good default actually. With a lot of registers, the read timeout likely needs to be increased. If we get EOF errors, the value might be too low.
shorter inter transaction delay, e.g. 10ms. As has been proven by you in the single device scenario, even delay of ~30ms+some seems to work just fine with your device. For high performance requirements, this should be set as low as possible. If we get EOF errors, the value might be too low. This is likely hardest out of all parameters to tune in the sense that it depends on device performance as well.
Summarizing the above advice, can you try this kind of connection string with the multi-slave setup
# - Short poll period (5ms). Binding will simply block until previous read is done, and immediately start the new poll round
modbus:poll=5
# - Read timeout (280ms) needs to be enough for long queries to work out. When the line works, the read returns much faster.
# - Short inter transaction delay (10ms). For high performance requirements, this should be set as low as possible. If we get EOF errors, the value is too low
modbus:serial.X.connection=/dev/ttyS0:38400:8:none:1:rtu:280:10````
Best,
Sami
@ssalonen the summary is a good idea.
I have just tried: http://pastebin.com/5qfiMYG0
There is again a huge performance difference between start.sh and start_debug.sh:
normal: 195 transactions/minute, logs: http://pastebin.com/uPniRYmC
debug: 530 transactions/minute, logs: http://pastebin.com/6kquYwjj
However, there is obviously no improvement - in fact the opposite has happened.
Best regards,
M
Hi @mbs38
Can you try to increase the inter transaction delay, try first with 25ms (binding ensures that there is at least that duration time between transactions. 25ms worked with single slave as explained in the summary) and if you still get errors try even higher value e.g. 35ms.
I would expect it to work eventually, we need to find the smallest value that works. If the delay is too small some bits might be lost it seems and eventually we get EOF error. Performance is naturally decreased since each EOF error means that we have waited the read timeout…
Best
Ssalonen
I have tried 25, 35, 45, 55, 65, 75, 85, 90. The performance is crap below 75 (Errors start to appear at 74). The best performance is at 75ms (783 transactions / minute), no errors. Higher transaction delays make the performance decrease again, the reasons are obvious.
There must be a bug or design error in the binding. There is no technical reason why multiple slaves shouldn’t work just as fast as a single slave.
M
Thank you for trying the different delays! I truly appreciate this and would certainly hope that I could test the thing myself and not bother you…
I’m sorry the hear the performance is not yet there for you although I’m also happy to hear how much the situation has been improved compared to the official version, after all we do get throughput of 13 transactions per second!
But your point is quite valid, and definitely same performance should be expected with many slaves… I will try to investigate more.
Edit : could you please open up what kind of device(s) we are talking about? I noticed that you are using different ids.
Could you paste the logs for 75ms and 35ms inter transaction delay… I could compare the logs to the to single slave version…
EDIT Got new information on performance: I just got “virtual null modem” to work in my linux pc (see pymodbus for the nullmodem implementation). As modbus slave I used diagslave (./diagslave -m rtu -a 1 -b 38400 -d 8 -s 1 -p none -4 10 /dev/pts/7
). Openhab acts as modbus master.
The openhab.cfg is here, items config here.
I have TRACE level logging enabled, and get average performance of 12ms (time between consecutive modbus responses, Response: xx yy ...
log from ModbusRTUTransport
). Most of the time (11ms out of 12ms) of that goes to the actual reading of the response from the server.
This is of course not really comparable to your situation where there is a real serial line, but shows that there is little overhead with the actual binding side. Compared to real life, the java serial binding openhab uses might not be as performant as it could be, for example.
@mbs38 If you can provide the logs I can find out where time goes with your specific case.
13 slaves, settings: 50, 280, 35, start_debug.sh, performance 640
http://pastebin.com/9b8HC9Dn
13 slaves, settings: 50, 280, 35, start.sh, performance 224
http://pastebin.com/dxyNWxBz
(again huge performance difference between debug and non debug…)
13 slaves, settings: 50, 280, 75, start_debug.sh, performance 783
http://pastebin.com/YGqc252E
13 slaves, settings: 50, 280, 75, start.sh, performance 783
logs only contain state updates.
Thank you for trying to make this work better
@mbs38 I can’t seem to find DEBUG log statements from net.wimpi.modbus
. They show better the time that goes to IO.
Using those we can see how much time goes to reading of response. Thanks!
If these don’t give us more information of the root cause, we can try to make up a multi-slave configuration with all the openhab slave definitions querying the same slave id & FC & etc; similar to my expirement (config). It would be interesting to see whether there is any difference in performance then since the configurations should exactly 100% the same thing…
I have added
to my logback_debug.xml and changed modbus:poll to 5.
start_debug.sh: http://pastebin.com/ZCcnTJkE
start.sh: http://pastebin.com/L4GQtGMZ
The performance is now a lot better in debug mode than in normal mode (760 vs 240).