eBUS binding 5.x + Vaillant VRC 470: can DHW mode / “1 x tank charge” be triggered from the bus? (writes to 0x42 ignored)
Setup
openHAB 5.x, eBUS binding 5.0.0 (ebus-configuration 1.1.10, ebus-core 1.1.14), self-built eBUS adapter. Vaillant ecoTEC (BAI00, addr 08), calorMATIC VRC 470/4 (addr 15), VR61 mixer module (addr 50), VR81 (addr 75), DHW cylinder.
Goal
Trigger a one-time DHW charge outside the time program from openHAB (the panel function “1 x ładowanie zasobnika” / “1 x tank charge”), and ideally switch the DHW mode Auto / Day / Off.
What works
Reads of everything I tried, and writes of ordinary parameters: HC1 day setpoint (0D/0E 27 00), DHW setpoint (0x44), controller time. Changes reach the VRC display within ~20–30 s.
What I found (from raw logs and panel changes)
  1. Register 0x42 (B5 09 0D 42 00, built-in dhw.program_dhw_circuit) follows the panel: Off = 0, Auto = 2, and 6 during the panel’s “1 x tank charge” (I added a raw uchar channel without min/max to see it; the built-in mapping returns null for 6).
  2. Writing to 0x42 from the bus has no effect. I tried values 0, 1, 2 and 6, both through the binding SET and as raw telegrams from the adhoc field (e.g. FF 15 B5 09 04 0E 42 00 06 00). The write is ACKed, the register briefly echoes, then returns to the panel state within one poll. The boiler does not start.
  3. Register 0x5D (HC1 special mode) stays 0 during “1 x tank charge”; writing 9 or 0 does nothing.
  4. Register 0x2A (“Is in single DHW loading mode” from the old VRS620 eBUS document) is readable but stays 0 during the panel-initiated charge. Writing 1 is accepted for a few seconds, then back to 0, no effect.
  5. The real gate is in the VRC → boiler telegram B5 10 (boiler.control.setopdata), sent every ~10 s. Its bit turnoffservice_water_heating is true in Auto outside the program, and false when the panel selects Day mode or “1 x tank charge” (boiler starts within ~1 min). At activation the VRC also sends 10 08 B5 12 02 00 64 (circulation pump per the old doc) and 10 50 B5 09 04 0E 01 00 01 (VR61 reg 01 = 1).
  6. I injected my own setopdata with that bit cleared (FF 08 B5 10 09 00 00 2E FF FF FF 00 00 00). It is ACKed, but the VRC’s next telegram 10 s later restores true, so the boiler never reacts. Sending it cyclically would fight the controller and risk burner short-cycling, so I did not pursue that.
  7. Side note: the VRC cancels the one-time charge within seconds if the cylinder is already warmer than the setpoint, and the boiler needs the cylinder several kelvin below the setpoint (hysteresis). I had to rule that out first.
Conclusion so far
On this VRC 470 the DHW mode registers (0x42, 0x2A) behave as read-only mirrors of the panel state. Writes from the binding’s source address (FF) are accepted at bus level but not acted on. Only the panel changes the mode.
Questions
  • Has anyone found a register or telegram that actually changes the DHW mode / triggers the one-time charge on a VRC 470/430 (e.g. a B5 04 message, or a different source address that the VRC accepts, like a remote controller)?
  • Are the DHW time-program registers writable over the bus (that would be a clean workaround by shifting the window)?
  • Does the write acceptance depend on the sender address?
Happy to post raw logs (poll responses, setopdata fields, telegrams around the activation).
I have probably not fully understood what you intent to do. But looking to the Vaillant app, there is one limitation for “hot water fast” outside the time program: the actual temperature needs to be lower than the setpoint minus the defined hysteresis for a new loading cycle.
Otherwise the command will not be accepted.
Example: i have a setpoint of 48°C and a hysteresis for a new loading of 8 Kelvin. Means that a new loading command will not be realized before the tank is below 40°C.
If i have e.g. 40.5°C and want to trigger a new loading cycle, i either switch on the circulation pump (drops the temperature quickly by another 2 degrees and triggers loading) or i set the defined hysteresis temporarily to e.g. 6 Kelvin in order to be able to trigger a “hot water fast” outside the time program having still 40.5°C.
Does this help you?
The command from the ebus binding for “hot water fast” is HWC SFmode = “load” (Special Functions, usually set to “auto”).
Have just verified it again: if i command “load” at actually 44.5°C storage temperature, nothing happens except that the circulation pump is switched on. The command is accepted but would not be executed before the temperature is below setpoint minus hysteresis as a said in my last post.
Let me know if you need the ebus telegram for that command. I could try to retrieve it.
Thanks, that helps a lot, and it points at a flaw in my tests.
I have a VRC 470/4 (the older B5 09 register protocol, binding config vrc430), not a VRC 700/720, so I don’t have a “HWC SF mode” channel. What I found so far:
  • Register 0x42 (B5 09 0D 42 00) follows the VRC panel: Off = 0, Auto = 2, and 6 while the panel’s “1 x tank charge” (one-time DHW load) is active. I only found the 6 by adding a raw uchar channel; the built-in mapping (0/1/2) returns null for it.
  • When the panel starts the charge, the VRC changes the turnoffservice_water_heating bit in its B5 10 (boiler.control.setopdata) telegram to the boiler from true to false (sent every ~10 s), the boiler starts within about a minute, and the VRC also sends 10 08 B5 12 02 00 64 (circulation pump) and 10 50 B5 09 04 0E 01 00 01 to the VR61.
  • My attempts to write 0x42 (values 0, 1, 2, 6) from the bus as raw telegrams, e.g. FF 15 B5 09 04 0E 42 00 06 00, were ACKed but had no visible effect, and the register returned to the panel state within one poll.
Your point about the hysteresis is exactly what I missed: in the tests that mattered the cylinder was only 5 K below the setpoint, so according to what you describe the VRC would not have accepted a “load” command anyway. My conclusion that writes to 0x42 are ignored is therefore not reliable. I’m repeating the test with the cylinder well below setpoint minus hysteresis (about 12 K below), watching the setopdata bit and the circulation pump telegram, and I’ll report back.
Two questions, if you can check:
  1. Is your “HWC SF mode” = load a plain write of a single value to a register (and which one, the B5 24 family used by vrc700)? If you can retrieve the raw telegram, that would help me judge whether anything similar exists on the 470.
  2. In your experience, does the VRC show any sign that the “load” command was accepted but deferred (apart from the circulation pump switching on)?
Will post the result of the repeat test.
Did you look on Github “ebusd configuration” here: archived/de/vaillant/15.470.csv ?
15.470.txt (16.8 KB) please rename back to .csv
Line 93 shows a “HwcOPMode” (but obviously no HwcSFmode) which can be set to 0=off;1=on;2=auto;3=autosunday;4=party;5=load;7=holiday with ebusd data format UCH,
but this seems to be read only acc. to the file?
This could be the following ebus telegram in openHAB: “FF 15 B5 09 03 0D 42 00” (read)
Will come back with my telegrams for the VRC720 later today.
Edit: found “Hc1Sfmode” within the same file where 8=onetimewater, but this seems also to be read only if these informations are right?
0=none;1=party;2=onedaybankholiday;3=onedayholiday;4=holiday;5=bankholiday;6=quickveto;7=onetimeventilation;8=onetimewater
This could be the appropriate ebus telegram in openHAB: “FF 15 B5 09 03 0D 5D 00” (read)
Thanks for pointing me to archived/de/vaillant/15.470.csv, that was the missing piece. Summary of what I found on a VRC 470/4 (binding 5.0.0, B5 09 register protocol):
What did NOT work (writes to the DHW “mode” registers from the bus, source address FF):
  • 0x42 (HwcOPMode): reading follows the panel (0 = off, 2 = auto, and 6 while the panel’s “1 x tank charge” is active; the csv lists 5 = load, on my unit it is 6). The csv comment says “set implicitly”, which matches what I saw: writes are ACKed but have no effect.
  • 0x5D (HC1 special mode) stays 0 during the one-time charge, 0x2A (“single DHW loading”, from an old VRS620 document) stays 0 as well. Writing to them does nothing.
  • Injecting my own B5 10 telegram with the “disable DHW tank loading” bit cleared is overwritten by the VRC every ~10 s (it sends B5 10 that often), so that is a dead end.
What works: the register 0x0B (TestVarActivateFunction), line 92 of the csv, which lists paired ON/OFF values per special function, e.g. 9 = 1xDHWLoad ON, 10 = OFF. Despite being marked read-only in the csv, writing it works on my VRC 470/4:
FF 15 B5 09 04 0E 0B 00 09    (CRC 73, the adhoc field calculates it)   -> one-time DHW load, boiler starts
FF 15 B5 09 04 0E 0B 00 0A    (CRC 70)                                  -> stop
This triggers exactly what the panel’s “1 x charge” does: the VRC clears the disable DHW tank loading bit in its B5 10 telegram and the boiler starts within about a minute.
Important condition (thanks for pointing it out earlier in this thread): the load is only executed if the cylinder temperature is below setpoint minus hysteresis. My first tests failed because the cylinder was only ~5 K below the setpoint; the VRC then discards the request immediately. I needed a difference of roughly 12 K to be sure.
I am happy that you found a solution and that my hints have been helpful.
I also found an AI search result where the following is stated: the openHAB ebus binding should provide a channel dhw_onetimewater / dhw_charging for a VRC470 thing which is a switch type. Did you see such channel?
The problem is that we can’t believe everything :winking_face_with_tongue:, either within the ebusd files (read/write) from John30 or from an AI agent.
No, I did not see such a channel. I checked the built-in vaillant-vrc-configuration.json of the binding (ebus-configuration 1.1.10): the DHW commands are only dhw.temp_d_holiday, dhw.program_dhw_circuit (reg 0x42) and dhw.temp_d_dhw (reg 0x44), and nothing called dhw_onetimewater or dhw_charging; there is also no Switch-type channel for this. The closest thing is heating.program_heating_circuit_special (reg 0x5D, with “9 = LoadDHW” in its mapping), but on my VRC 470/4 that register stays 0 during the one-time charge and writing to it has no effect. I agree we shouldn’t trust AI summaries or the read/write flags in the ebusd files without testing; I only trusted 0x0B after I tested it on the actual hardware, and I even had to figure out the hysteresis condition. The onetimewater name exists only in 15.470.csv (value 8 of 0x5D), so the AI probably mixed that up.
Okay, thanks, that was for my interest only because we never stop to learn about ebus :slight_smile: .