Daniel
(Daniel)
November 1, 2016, 2:12pm
1
Hi all,
I´ve just got a new heating unit with a Vaillant VRC 700 (Colormatic 700 ). Now I really would like to get this one integrated into OH.
I looked at the eBus Binding page and did not found my VRC 700 in the supported devices. You my question (specially to @csowada ): is there any chance to get this working with the Binding? What to do and could I help in any way?
Daniel
csowada
(csowada)
November 1, 2016, 2:35pm
2
First you should check the other configurations. Maybe they are compatible with your device. If not you should check your device with the linux daemon ebusd. Then you can idenfify the required commands.
Daniel
(Daniel)
November 2, 2016, 9:49am
3
OK, thx. I´ll try and get back when I got some results…
scantineau
(Scantineau)
November 22, 2016, 10:35am
4
Hi Daniel,
I’m going to do the same than you with a VRC 700 too.
Are you gonna use an eBus coupler USB or RS232 or Ethernet ?
I’m also trying to get my VRC 700 online. I’m using OH 1.8.3 and I’ve had some luck with the deprecated _Vaillant configuration. The following items are already working here:
Number temp_aussen "Aussentemperatur [%.2f C]" { ebus="id:control_v.temp_outdoor" }
Number temp_vorlauf_soll "Vorlaufsolltemperatur [%.2f C]" { ebus="id:burner_v.temp_t_flow" }
Number temp_vorlauf "Vorlauftemperatur [%.2f C]" { ebus="id:burner_v.temp_vessel" }
Number temp_ruecklauf "Ruecklauftemperatur [%.2f C]" { ebus="id:burner_v.temp_return" }
Number temp_ww_solll "WW Solltemperatur [%.2f C]" { ebus="id:burner_v.temp_t_water" }
Number temp_ww_speicher "WW Speichertemperatur [%.2f C]" { ebus="id:burner_v.temp_boiler" }
Number temp_ww_auslauf "WW Temperatur [%.2f C]" { ebus="id:burner_v.temp_water" }
Some of the values, such as pump and burner status are not yet working here. I’d be willing to do some digging, but I have to familiarize myself with the intricacies of the eBus protocol, first.
I’m using the Esera USB eBus Coupler - worked out of the box.
I started analyzing eBus messages today. I was especially interested in the water pressure readings, as those seem to be dropping faster than I’d like in my installation. And I found them, using the brute force logging facility built into the ebus binding:
"comment": "[OK] <Burner> Vaillant: Brenner zu Regler",
"class": "burner_v",
"command": "B5 11",
"data": "00",
"values": {
"pressure_water": {"type": "byte", "pos": 12, "label": "water pressure [bar]", "factor": 0.1 }
Still looking for the messages which give me write access to operation mode and time program, though.
Hello !
It seems that there is a valid config file on john30 repo
Here’s the link :
15.700.csv
I spent 2 hours trying to compile EBusEbusdCsvReader but my last error unresolved is
EBusEbusdCsvReader.java:201: error: cannot access Versioned
mapper.writerWithDefaultPrettyPrinter().writeValue(new File(jsonFilePath), list);
class file for org.codehaus.jackson.Versioned not found
1 error
And I don’t understand why… I learned java at school more than 10 years ago and I have not practiced since today
Maybe @csowada will help us to convert it ?
Update
Finally compiled it…
EBusEbusdCsvReader has been written for an old java version so I had to update it. I will fork on github.
Unfortunatly, a lot of datatypes are not configured in Reader…
Here they are :
calibrationv
date
energy4
EXP
hfrom
HTI
hto
mamode
offmode
opmode
pressv
rcmode
sfmode
shortname
shortphone
slot1-3
tempv
zmapping
zname
zonesel
So only 31 entries are translated.
csowada
(csowada)
April 18, 2017, 6:20am
9
Yes I know that the reader only support the most important data types. I’ve started this simple program more as a proof of concept. I’m working on a new ebus library that allows different configuration types. But currently I’m totally busy to fit out the attic. Also my little daughter is waiting for me. So currently my time for development and help very limited.
No problem
Maybe you already have a table to translate all datatypes ?
If not, I will try to create one and update the reader…
fluppie
(Philippe)
April 24, 2017, 9:46pm
11
I also had some success with the _vaillant parser.
Apr 24 22:23:30 emonpi openhab.sh[18889]: 2017-04-24 22:23:30.317 [DEBUG] [.ebus.internal.parser.Analyses] - 10 08 B5 11 01 01 89 00 09 2B 2C 00 80 2A 29 00 00 FF 0C 00 AA
Apr 24 22:23:30 emonpi openhab.sh[18889]: 2017-04-24 22:23:30.335 [DEBUG] [.ebus.internal.parser.Analyses] - >>> [OK] <Burner> Vaillant: Brenner zu Regler
Apr 24 22:23:30 emonpi openhab.sh[18889]: 2017-04-24 22:23:30.374 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.temp_vessel 21.0 Vorlauftemperatur
Apr 24 22:23:30 emonpi openhab.sh[18889]: 2017-04-24 22:23:30.395 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.temp_return 22.0 Rücklauftemperatur
Apr 24 22:23:30 emonpi openhab.sh[18889]: 2017-04-24 22:23:30.399 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.temp_water 21.0 Brauchwasser Auslauftemperatur
Apr 24 22:23:30 emonpi openhab.sh[18889]: 2017-04-24 22:23:30.434 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.temp_boiler 20.0 Brauchwasser Speichertemperatur
Apr 24 22:23:30 emonpi openhab.sh[18889]: 2017-04-24 22:23:30.437 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.heating_on false Heizen Ein
Apr 24 22:23:30 emonpi openhab.sh[18889]: 2017-04-24 22:23:30.441 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.service_water_on false Brauchwasser Ein
Apr 24 22:23:30 emonpi openhab.sh[18889]: 2017-04-24 22:23:30.493 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.unknown_00 0 Unbekannt immer 00
pi@emonpi:/var/log/openhab$ sudo service openhab status
Apr 24 22:23:31 emonpi openhab.sh[18889]: 2017-04-24 22:23:31.017 [DEBUG] [.ebus.internal.parser.Analyses] - 10 08 B5 10 09 00 00 00 FF FF FF 05 00 00 7E 00 01 01 9A 00 AA
Apr 24 22:23:31 emonpi openhab.sh[18889]: 2017-04-24 22:23:31.039 [DEBUG] [.ebus.internal.parser.Analyses] - >>> [OK] <Regler> Vaillant: Regler zu Brenner
Apr 24 22:23:31 emonpi openhab.sh[18889]: 2017-04-24 22:23:31.048 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.temp_t_flow 0.0 Sollwert Vorlauftemperatur vom Regler
Apr 24 22:23:31 emonpi openhab.sh[18889]: 2017-04-24 22:23:31.064 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.temp_t_water 127.0 Sollwert Brauchwasser vom Regler
Apr 24 22:23:31 emonpi openhab.sh[18889]: 2017-04-24 22:23:31.073 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.bit_heating_off false Heizen aus, vom Regler
Apr 24 22:23:31 emonpi openhab.sh[18889]: 2017-04-24 22:23:31.082 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.bit_brw_off false Brauchwasser aus, vom Regler
Apr 24 22:23:37 emonpi openhab.sh[18889]: 2017-04-24 22:23:37.967 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.unknown_00 0 Unbekannt immer 00
Apr 24 22:23:38 emonpi openhab.sh[18889]: 2017-04-24 22:23:38.386 [DEBUG] [.ebus.internal.parser.Analyses] - 10 FE B5 16 08 00 59 22 23 24 04 01 17 18 AA
Apr 24 22:23:38 emonpi openhab.sh[18889]: 2017-04-24 22:23:38.425 [DEBUG] [.ebus.internal.parser.Analyses] - >>> <Control> Vaillant: Zeit Broadcast
Apr 24 22:23:38 emonpi openhab.sh[18889]: 2017-04-24 22:23:38.429 [TRACE] [.ebus.internal.parser.Analyses] - >>> control_v.time_sec 59 Zeit Sek.
Apr 24 22:23:38 emonpi openhab.sh[18889]: 2017-04-24 22:23:38.432 [TRACE] [.ebus.internal.parser.Analyses] - >>> control_v.time_min 22 Zeit Min
Apr 24 22:23:38 emonpi openhab.sh[18889]: 2017-04-24 22:23:38.477 [TRACE] [.ebus.internal.parser.Analyses] - >>> control_v.time_hour 23 Zeit Stunde
Apr 24 22:23:38 emonpi openhab.sh[18889]: 2017-04-24 22:23:38.503 [TRACE] [.ebus.internal.parser.Analyses] - >>> control_v.date_day 24 Datum Tag
Apr 24 22:23:38 emonpi openhab.sh[18889]: 2017-04-24 22:23:38.507 [TRACE] [.ebus.internal.parser.Analyses] - >>> control_v.date_month 4 Datum Monat
Apr 24 22:23:38 emonpi openhab.sh[18889]: 2017-04-24 22:23:38.541 [TRACE] [.ebus.internal.parser.Analyses] - >>> control_v.date_weekday 1 Datum Wochentag
Apr 24 22:23:38 emonpi openhab.sh[18889]: 2017-04-24 22:23:38.568 [TRACE] [.ebus.internal.parser.Analyses] - >>> control_v.date_year 17 Datum Jahr
Apr 24 22:23:40 emonpi openhab.sh[18889]: 2017-04-24 22:23:40.349 [DEBUG] [.ebus.internal.parser.Analyses] - 10 08 B5 10 03 05 FF 01 98 00 01 01 9A 00 AA
Apr 24 22:23:40 emonpi openhab.sh[18889]: 2017-04-24 22:23:40.388 [DEBUG] [.ebus.internal.parser.Analyses] - >>> Unknown ----------------------------------------
Apr 24 22:23:40 emonpi openhab.sh[18889]: 2017-04-24 22:23:40.551 [DEBUG] [.ebus.internal.parser.Analyses] - 10 08 B5 12 02 00 00 CA 00 00 00 00 AA
Apr 24 22:23:40 emonpi openhab.sh[18889]: 2017-04-24 22:23:40.561 [DEBUG] [.ebus.internal.parser.Analyses] - >>> [Analyse] <Master> Vaillant: Pumpenstatus 2????
Apr 24 22:23:40 emonpi openhab.sh[18889]: 2017-04-24 22:23:40.575 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.circulating_pump false Zirkulations Pumpe
Apr 24 22:23:40 emonpi openhab.sh[18889]: 2017-04-24 22:23:40.843 [DEBUG] [.ebus.internal.parser.Analyses] - 10 08 B5 12 02 04 FF F4 00 01 01 9A 00 AA
Apr 24 22:23:40 emonpi openhab.sh[18889]: 2017-04-24 22:23:40.875 [DEBUG] [.ebus.internal.parser.Analyses] - >>> Unknown ----------------------------------------
Apr 24 22:23:41 emonpi openhab.sh[18889]: 2017-04-24 22:23:41.228 [DEBUG] [.ebus.internal.parser.Analyses] - 10 FE B5 16 03 01 00 D8 04 AA
Apr 24 22:23:41 emonpi openhab.sh[18889]: 2017-04-24 22:23:41.238 [DEBUG] [.ebus.internal.parser.Analyses] - >>> <Control> Vaillant: Aussentemperatur Broadcast
Apr 24 22:23:41 emonpi openhab.sh[18889]: 2017-04-24 22:23:41.250 [TRACE] [.ebus.internal.parser.Analyses] - >>> control_v.temp_outdoor -40.0 Aussentemperatur Istwert
Apr 24 22:23:48 emonpi openhab.sh[18889]: 2017-04-24 22:23:48.377 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.temp_boiler 20.0 Brauchwasser Speichertemperatur
Apr 24 22:23:48 emonpi openhab.sh[18889]: 2017-04-24 22:23:48.380 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.heating_on false Heizen Ein
Apr 24 22:23:48 emonpi openhab.sh[18889]: 2017-04-24 22:23:48.398 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.service_water_on false Brauchwasser Ein
Apr 24 22:23:48 emonpi openhab.sh[18889]: 2017-04-24 22:23:48.401 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.unknown_00 0 Unbekannt immer 00
Apr 24 22:23:48 emonpi openhab.sh[18889]: 2017-04-24 22:23:48.977 [DEBUG] [.ebus.internal.parser.Analyses] - 10 08 B5 10 09 00 00 00 FF FF FF 05 00 00 7E 00 01 01 9A 00 AA
Apr 24 22:23:48 emonpi openhab.sh[18889]: 2017-04-24 22:23:48.983 [DEBUG] [.ebus.internal.parser.Analyses] - >>> [OK] <Regler> Vaillant: Regler zu Brenner
Apr 24 22:23:49 emonpi openhab.sh[18889]: 2017-04-24 22:23:49.013 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.temp_t_flow 0.0 Sollwert Vorlauftemperatur vom Regler
Apr 24 22:23:49 emonpi openhab.sh[18889]: 2017-04-24 22:23:49.017 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.temp_t_water 127.0 Sollwert Brauchwasser vom Regler
Apr 24 22:23:49 emonpi openhab.sh[18889]: 2017-04-24 22:23:49.020 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.bit_heating_off false Heizen aus, vom Regler
Apr 24 22:23:49 emonpi openhab.sh[18889]: 2017-04-24 22:23:49.054 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.bit_brw_off false Brauchwasser aus, vom Regler
Apr 24 22:23:56 emonpi openhab.sh[18889]: 2017-04-24 22:23:56.179 [DEBUG] [.ebus.internal.parser.Analyses] - 10 08 B5 11 01 01 89 00 09 2B 2C 00 80 2A 29 00 00 FF 0C 00 AA
Apr 24 22:23:56 emonpi openhab.sh[18889]: 2017-04-24 22:23:56.182 [DEBUG] [.ebus.internal.parser.Analyses] - >>> [OK] <Burner> Vaillant: Brenner zu Regler
Apr 24 22:23:56 emonpi openhab.sh[18889]: 2017-04-24 22:23:56.237 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.temp_vessel 21.0 Vorlauftemperatur
Apr 24 22:23:56 emonpi openhab.sh[18889]: 2017-04-24 22:23:56.270 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.temp_return 22.0 Rücklauftemperatur
Apr 24 22:23:56 emonpi openhab.sh[18889]: 2017-04-24 22:23:56.279 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.temp_water 21.0 Brauchwasser Auslauftemperatur
Apr 24 22:23:56 emonpi openhab.sh[18889]: 2017-04-24 22:23:56.314 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.temp_boiler 20.0 Brauchwasser Speichertemperatur
Apr 24 22:23:56 emonpi openhab.sh[18889]: 2017-04-24 22:23:56.317 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.heating_on false Heizen Ein
Apr 24 22:23:56 emonpi openhab.sh[18889]: 2017-04-24 22:23:56.327 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.service_water_on false Brauchwasser Ein
Apr 24 22:23:56 emonpi openhab.sh[18889]: 2017-04-24 22:23:56.355 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.unknown_00 0 Unbekannt immer 00
Apr 24 22:32:40 emonpi openhab.sh[18889]: 2017-04-24 22:32:40.602 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.unknown_00 0 Unbekannt immer 00
Apr 24 22:32:41 emonpi openhab.sh[18889]: 2017-04-24 22:32:41.346 [DEBUG] [.ebus.internal.parser.Analyses] - 10 FE B5 16 08 00 01 32 23 24 04 01 17 E4 AA
Apr 24 22:32:41 emonpi openhab.sh[18889]: 2017-04-24 22:32:41.361 [DEBUG] [.ebus.internal.parser.Analyses] - >>> <Control> Vaillant: Zeit Broadcast
Apr 24 22:32:41 emonpi openhab.sh[18889]: 2017-04-24 22:32:41.371 [TRACE] [.ebus.internal.parser.Analyses] - >>> control_v.time_sec 1 Zeit Sek.
Apr 24 22:32:41 emonpi openhab.sh[18889]: 2017-04-24 22:32:41.398 [TRACE] [.ebus.internal.parser.Analyses] - >>> control_v.time_min 32 Zeit Min
Apr 24 22:32:41 emonpi openhab.sh[18889]: 2017-04-24 22:32:41.400 [TRACE] [.ebus.internal.parser.Analyses] - >>> control_v.time_hour 23 Zeit Stunde
Apr 24 22:32:41 emonpi openhab.sh[18889]: 2017-04-24 22:32:41.412 [TRACE] [.ebus.internal.parser.Analyses] - >>> control_v.date_day 24 Datum Tag
Apr 24 22:32:41 emonpi openhab.sh[18889]: 2017-04-24 22:32:41.425 [TRACE] [.ebus.internal.parser.Analyses] - >>> control_v.date_month 4 Datum Monat
Apr 24 22:32:41 emonpi openhab.sh[18889]: 2017-04-24 22:32:41.427 [TRACE] [.ebus.internal.parser.Analyses] - >>> control_v.date_weekday 1 Datum Wochentag
Apr 24 22:32:41 emonpi openhab.sh[18889]: 2017-04-24 22:32:41.455 [TRACE] [.ebus.internal.parser.Analyses] - >>> control_v.date_year 17 Datum Jahr
● openhab.service - Starts and stops the openHAB Home Automation Bus
Loaded: loaded (/usr/lib/systemd/system/openhab.service; disabled)
Active: active (running) since Mon 2017-04-24 22:16:38 BST; 16min ago
Docs: http://www.openhab.org
Process: 18818 ExecStartPre=/usr/share/openhab/bin/setpermissions.sh (code=exited, status=0/SUCCESS)
Main PID: 18889 (openhab.sh)
CGroup: /system.slice/openhab.service
├─18889 /bin/sh /usr/share/openhab/bin/openhab.sh -o
└─18908 /usr/bin/java -Dlogback.configurationFile=/etc/openhab/logback.xml -Dosgi.clean=true -Declipse.ignoreApp=true -Dosgi.noShutdown=true -Djetty.port=8080 -Dopenhab.configfile=/etc/openhab/...
Apr 24 22:32:41 emonpi openhab.sh[18889]: 2017-04-24 22:32:41.847 [DEBUG] [.ebus.internal.parser.Analyses] - 10 08 B5 10 09 00 00 00 FF FF FF 05 00 00 7E 00 01 01 9A 00 AA
Apr 24 22:32:41 emonpi openhab.sh[18889]: 2017-04-24 22:32:41.849 [DEBUG] [.ebus.internal.parser.Analyses] - >>> [OK] <Regler> Vaillant: Regler zu Brenner
Apr 24 22:32:41 emonpi openhab.sh[18889]: 2017-04-24 22:32:41.852 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.temp_t_flow 0.0 Sollwert Vorlauftemperatur vom Regler
Apr 24 22:32:41 emonpi openhab.sh[18889]: 2017-04-24 22:32:41.941 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.temp_t_water 127.0 Sollwert Brauchwasser vom Regler
Apr 24 22:32:41 emonpi openhab.sh[18889]: 2017-04-24 22:32:41.965 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.bit_heating_off false Heizen aus, vom Regler
Apr 24 22:32:41 emonpi openhab.sh[18889]: 2017-04-24 22:32:41.968 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.bit_brw_off false Brauchwasser aus, vom Regler
Apr 24 22:32:42 emonpi openhab.sh[18889]: 2017-04-24 22:32:42.839 [DEBUG] [.ebus.internal.parser.Analyses] - 10 08 B5 11 01 00 88 00 08 5C 01 0F 00 1F 10 00 00 1D 00 AA
Apr 24 22:32:42 emonpi openhab.sh[18889]: 2017-04-24 22:32:42.857 [DEBUG] [.ebus.internal.parser.Analyses] - >>> Unknown ----------------------------------------
Apr 24 22:35:25 emonpi openhab.sh[18889]: at java.lang.Thread.run(Thread.java:745) [na:1.7.0_60]
Apr 24 22:35:31 emonpi openhab.sh[18889]: 2017-04-24 22:35:31.560 [DEBUG] [.ebus.internal.parser.Analyses] - 10 08 B5 11 01 01 89 00 09 2B 2C 00 80 2A 29 00 00 FF 0C 00 AA
Apr 24 22:35:31 emonpi openhab.sh[18889]: 2017-04-24 22:35:31.573 [DEBUG] [.ebus.internal.parser.Analyses] - >>> [OK] <Burner> Vaillant: Brenner zu Regler
Apr 24 22:35:31 emonpi openhab.sh[18889]: 2017-04-24 22:35:31.581 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.temp_vessel 21.0 Vorlauftemperatur
Apr 24 22:35:31 emonpi openhab.sh[18889]: 2017-04-24 22:35:31.669 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.temp_return 22.0 Rücklauftemperatur
Apr 24 22:35:31 emonpi openhab.sh[18889]: 2017-04-24 22:35:31.678 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.temp_water 21.0 Brauchwasser Auslauftemperatur
Apr 24 22:35:31 emonpi openhab.sh[18889]: 2017-04-24 22:35:31.686 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.temp_boiler 20.0 Brauchwasser Speichertemperatur
Apr 24 22:35:31 emonpi openhab.sh[18889]: 2017-04-24 22:35:31.689 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.heating_on false Heizen Ein
Apr 24 22:35:31 emonpi openhab.sh[18889]: 2017-04-24 22:35:31.691 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.service_water_on false Brauchwasser Ein
Apr 24 22:35:31 emonpi openhab.sh[18889]: 2017-04-24 22:35:31.704 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.unknown_00 0 Unbekannt immer 00
Apr 24 22:35:32 emonpi openhab.sh[18889]: 2017-04-24 22:35:32.297 [DEBUG] [.ebus.internal.parser.Analyses] - 10 08 B5 10 09 00 00 00 FF FF FF 05 00 00 7E 00 01 01 9A 00 AA
Apr 24 22:35:32 emonpi openhab.sh[18889]: 2017-04-24 22:35:32.328 [DEBUG] [.ebus.internal.parser.Analyses] - >>> [OK] <Regler> Vaillant: Regler zu Brenner
Apr 24 22:35:32 emonpi openhab.sh[18889]: 2017-04-24 22:35:32.355 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.temp_t_flow 0.0 Sollwert Vorlauftemperatur vom Regler
Apr 24 22:35:32 emonpi openhab.sh[18889]: 2017-04-24 22:35:32.357 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.temp_t_water 127.0 Sollwert Brauchwasser vom Regler
Apr 24 22:35:32 emonpi openhab.sh[18889]: 2017-04-24 22:35:32.360 [TRACE] [.ebus.internal.parser.Analyses] - >>> burner_v.bit_heating_off false Heizen aus, vom Regler
fluppie
(Philippe)
June 26, 2017, 1:42pm
12
@nikoraes @csowada
Is there already a better parser for the Multimatic 700? I also have the vr900 internet module connected.
mikulaos
(Sinisa Mikulandra)
January 7, 2018, 4:35pm
13
scantineau:
No problem
@scantineau , @csowada : Any progress?
scantineau
(Scantineau)
January 8, 2018, 8:40am
14
Hi @mikulaos !
Indeed but not this way…
I have installed :
john30’s ebusd daemon 3.0 (with ebusd-configuration)
mqtt server
mqtt binding
And this way everything is working fine.