Hi, I am running OH since 2020 and it was always working fine, but since the last few days (maybe a week) I am experiencing regular instabilities. It is not completely dead but seems like the rules stop working.
Yesterday I rebooted and upgraded the system but today it happened again.
I also note the CPU load is on high side.
Last change I did, is I added one device with about 100 Modbus registers (things).
Any ideas what to look for in the logs?
After restart I checked the running processes and the OH is taking the most resources 25-35%
Well the only way to see if your SSD via usb can keep up is by installing iotop on your openhabian and look what happens when modbus is active. But normally if you don’t need the values so often to be changed then increase the time and also careful with persistence of those items can put a big strain.
Thanks for the heads up. Those 600ms were mistake. I increased the poll rate to 10s and I see the CPU load doesn’t go above 25%, so this might solve the problem.
It just happened again. I noted the log stopped logging item updates and no other error can be seen
2022-03-22 20:02:53.145 [INFO ] [openhab.event.ItemStateChangedEvent ] - Item 'Memory_Used' changed from 1460 to 1461
2022-03-22 20:02:53.400 [INFO ] [openhab.event.ItemStateChangedEvent ] - Item 'PANEL_MESSAGE' changed from 650: Partition can now be armed. to 609: General status of the zone - open.
2022-03-22 20:02:53.402 [INFO ] [openhab.event.ItemStateChangedEvent ] - Item 'ZONE2_STATUS' changed from CLOSED to OPEN
2022-03-22 20:02:53.404 [INFO ] [hab.event.GroupItemStateChangedEvent] - Item 'grpDSCAlarmMotion' changed from CLOSED to OPEN through ZONE2_STATUS
2022-03-22 20:02:53.405 [INFO ] [openhab.event.ItemStateChangedEvent ] - Item 'ZONE2_MESSAGE' changed from to 609: General status of the zone - open.
==> /var/log/openhab/openhab.log <==
2022-03-22 20:03:09.506 [WARN ] [p.internal.http.HttpResponseListener] - Requesting 'http://192.168.4.221/real_time_data.xml' (method='GET', content='null') failed: Total timeout 3000 ms elapsed
2022-03-22 20:03:39.513 [WARN ] [p.internal.http.HttpResponseListener] - Requesting 'http://192.168.4.221/real_time_data.xml' (method='GET', content='null') failed: Total timeout 3000 ms elapsed
I can also see OpenHAB Java process is using almost 100% cpu
Once you get beyond non-trivial Modbus configurations, you should pay attention to consequences. It is quite possible to poll at 600mS periods, using methods to reduce knock-on workload.
Te usual effect of neglecting this is hammering the persistence service(s), which impacts system performance overall.
My Modbus polls are every 5 or 10 seconds now and I also deleted about 50% of the items that were in the original post.
Polling every 600ms would probably work since I have 4 slaves daisy chained.
But I do admit there is place to optimise the system so I will have a look in it.