JDBC/MySQL and MySQL issues (including migration MySQL to JDBC/MySQL)
Hi all,
after many days of investigation I need to post my persistence issues here - try to make it brief.
System Setup: Openhab2.1 on Ubuntu (installed via apt, stable version).
Running since some month logging a lot of data.
persistance service: Native MySQL binding (not via JDBC)
MySQL Server running on different VM in the local network.
Persistance Service was working as expected , also no issues with MySQL, beside one - which makes the system essentially unusable in daily operation:
  • In unregular intervals MySQL queries seems to block all persistance actions in openhab
  • It happens during access of pages (BasicUI) with charts querying a lot of history data.
  • Then suddenly the chart is not displayed any more - only the rest of the page is displayed (e.g. other items like text or number items). Then no persistance actions are performed any more (no stores, no queries) by openhab - see logs.
    events are still recieved by Openhab (checked with events.log) - but not processed by persistance any more. Finally also the UI is blocked and not responding any more. Then only openhab restart helped.
  • This issue happend depending on the usage of the sitemap - somtimes after minutes, sometimes after hours when accessing the sitemap e.g. first access in the morning → then UI blocked.
This behaviour I could see over several weeks - however the exact event I could not determine.
It seems however my issue points to following issue: https://community.openhab.org/t/habpanel-gets-completely-broken-by-n3-line-chart-from-mysql-but-no-errors-in-log/34147/4
There is no error in OpenHAB logfile (even with DEBUG and TRACE) of everything:
small excerpt:
2017-11-29 18:05:07.690 [DEBUG] [ce.jetty.internal.HttpServiceContext] - Handling request for [/chart] using http context [DefaultHttpContext [bundle=org.eclipse.smarthome.ui_0.9.0.b5 [136], contextID=default]]
2017-11-29 18:05:07.690 [DEBUG] [y.internal.HttpServiceServletHandler] - handling request org.ops4j.pax.web.service.jetty.internal.HttpServiceRequestWrapper@66735611, org.ops4j.pax.web.service.jetty.internal.HttpServiceResponseWrapper@773c423e
2017-11-29 18:05:07.690 [DEBUG] [sql.internal.MysqlPersistenceService] - mySQL query: item is PelletOvenStatus
2017-11-29 18:05:07.691 [DEBUG] [sql.internal.MysqlPersistenceService] - mySQL: query:SELECT Time, Value FROM Item115 WHERE TIME<'2017-11-26 18:05:07' ORDER BY Time DESC LIMIT 0,1
2017-11-29 18:05:07.691 [DEBUG] [sql.internal.MysqlPersistenceService] - mySQL: query returned 1 rows in 0ms
2017-11-29 18:05:07.692 [DEBUG] [sql.internal.MysqlPersistenceService] - mySQL query: item is PelletOvenStatus
2017-11-29 18:05:07.692 [DEBUG] [sql.internal.MysqlPersistenceService] - mySQL: query:SELECT Time, Value FROM Item115 WHERE TIME>'2017-11-26 18:05:07' AND TIME<'2017-11-29 18:05:07' ORDER BY Time ASC
2017-11-29 18:05:07.693 [DEBUG] [sql.internal.MysqlPersistenceService] - mySQL: query returned 4 rows in 1ms
2017-11-29 18:05:07.694 [DEBUG] [sql.internal.MysqlPersistenceService] - mySQL query: item is Fuel_Pellet_kg
2017-11-29 18:05:07.694 [DEBUG] [sql.internal.MysqlPersistenceService] - mySQL: query:SELECT Time, Value FROM Item110 WHERE TIME<'2017-11-22 18:05:07' ORDER BY Time DESC LIMIT 0,1
2017-11-29 18:05:07.695 [DEBUG] [sql.internal.MysqlPersistenceService] - mySQL: query returned 1 rows in 1ms
2017-11-29 18:05:07.695 [DEBUG] [sql.internal.MysqlPersistenceService] - mySQL query: item is Fuel_Pellet_kg
2017-11-29 18:05:07.695 [DEBUG] [sql.internal.MysqlPersistenceService] - mySQL: query:SELECT Time, Value FROM Item110 WHERE TIME>'2017-11-22 18:05:07' AND TIME<'2017-11-29 18:05:07' ORDER BY Time ASC
2017-11-29 18:05:07.698 [TRACE] [commons.httpclient.methods.GetMethod] - enter GetMethod(String)
2017-11-29 18:05:07.698 [DEBUG] [.httpclient.params.DefaultHttpParams] - Set parameter http.socket.timeout = 5000
2017-11-29 18:05:07.698 [DEBUG] [.httpclient.params.DefaultHttpParams] - Set parameter http.method.retry-handler = org.apache.commons.httpclient.DefaultHttpMethodRetryHandler@17533b47
2017-11-29 18:05:07.699 [TRACE] [apache.commons.httpclient.HttpClient] - enter HttpClient.executeMethod(HttpMethod)
2017-11-29 18:05:07.699 [TRACE] [apache.commons.httpclient.HttpClient] - enter HttpClient.executeMethod(HostConfiguration,HttpMethod,HttpState)
2017-11-29 18:05:07.699 [TRACE] [ommons.httpclient.HttpMethodDirector] - Attempt number 1 to process request
2017-11-29 18:05:07.699 [TRACE] [he.commons.httpclient.HttpConnection] - enter HttpConnection.open()
2017-11-29 18:05:07.699 [DEBUG] [he.commons.httpclient.HttpConnection] - Open connection to raspiPellet1.home.lan:8020
2017-11-29 18:05:07.699 [DEBUG] [sql.internal.MysqlPersistenceService] - mySQL: query returned 562 rows in 4ms
2017-11-29 18:05:07.937 [TRACE] [he.commons.httpclient.HttpMethodBase] - enter HttpMethodBase.execute(HttpState, HttpConnection)
2017-11-29 18:05:07.937 [TRACE] [he.commons.httpclient.HttpMethodBase] - enter HttpMethodBase.writeRequest(HttpState, HttpConnection)
2017-11-29 18:05:07.937 [TRACE] [he.commons.httpclient.HttpMethodBase] - enter HttpMethodBase.writeRequestLine(HttpState, HttpConnection)
2017-11-29 18:05:07.937 [TRACE] [he.commons.httpclient.HttpMethodBase] - enter HttpMethodBase.generateRequestLine(HttpConnection, String, String, String, String)
2017-11-29 18:05:07.937 [DEBUG] [httpclient.wire.header              ] - >> "GET /sensor/temperature/channel_1 HTTP/1.1[\r][\n]"
2017-11-29 18:05:07.937 [TRACE] [he.commons.httpclient.HttpConnection] - enter HttpConnection.print(String)
with corresponding mySQL log entries:
2017-11-29T18:05:07.691848+01:00	    4 Query	SELECT Time, Value FROM Item115 WHERE TIME<'2017-11-26 18:05:07' ORDER BY Time DESC LIMIT 0,1
2017-11-29T18:05:07.693174+01:00	    4 Query	SELECT Time, Value FROM Item115 WHERE TIME>'2017-11-26 18:05:07' AND TIME<'2017-11-29 18:05:07' ORDER BY Time ASC
2017-11-29T18:05:07.695356+01:00	    4 Query	SELECT Time, Value FROM Item110 WHERE TIME<'2017-11-22 18:05:07' ORDER BY Time DESC LIMIT 0,1
2017-11-29T18:05:07.696694+01:00	    4 Query	SELECT Time, Value FROM Item110 WHERE TIME>'2017-11-22 18:05:07' AND TIME<'2017-11-29 18:05:07' ORDER BY Time ASC
2017-11-29T18:05:25.463682+01:00	    4 Query	select @@session.tx_read_only
2017-11-29T18:05:25.465062+01:00	    4 Query	INSERT INTO Item108 (TIME, VALUE) VALUES('2017-11-29 18:05:25.462','137.60') ON DUPLICATE KEY UPDATE VALUE='137.60'
2017-11-29T18:05:25.522226+01:00	    4 Query	select @@session.tx_read_only
2017-11-29T18:05:25.522603+01:00	    4 Query	INSERT INTO Item140 (TIME, VALUE) VALUES('2017-11-29 18:05:25.521','20,1 % | 39,2 kg | Ofen=AUS') ON DUPLICATE KEY UPDATE VALUE='20,1 % | 39,2 kg | Ofen=AUS'
2017-11-29T18:05:25.545577+01:00	    4 Query	select @@session.tx_read_only
2017-11-29T18:05:25.545889+01:00	    4 Query	INSERT INTO Item109 (TIME, VALUE) VALUES('2017-11-29 18:05:25.544','20.09') ON DUPLICATE KEY UPDATE VALUE='20.09'
2017-11-29T18:05:25.572746+01:00	    4 Query	SELECT Time, Value FROM Item110 WHERE TIME<'2017-11-22 18:05:25' ORDER BY Time DESC LIMIT 0,1
2017-11-29T18:05:25.574043+01:00	    4 Query	SELECT Time, Value FROM Item110 WHERE TIME>'2017-11-22 18:05:25' AND TIME<'2017-11-29 18:05:25' ORDER BY Time ASC
2017-11-29T18:05:25.575333+01:00	    4 Query	SELECT Time, Value FROM Item110 WHERE TIME<'2017-11-28 18:05:25' ORDER BY Time DESC LIMIT 0,1
2017-11-29T18:05:25.576662+01:00	    4 Query	SELECT Time, Value FROM Item110 WHERE TIME>'2017-11-28 18:05:25' AND TIME<'2017-11-29 18:05:25' ORDER BY Time ASC
2017-11-29T18:05:25.577192+01:00	    4 Query	select @@session.tx_read_only
2017-11-29T18:05:25.577472+01:00	    4 Query	INSERT INTO Item110 (TIME, VALUE) VALUES('2017-11-29 18:05:25.575','39.18') ON DUPLICATE KEY UPDATE VALUE='39.18'
Then no entries any more in mysql.log ==> corresponding to openhab/persistance logging entries.
The entry "2017-11-29T18:05:25.577472+01:00 " is the last entry in the mySQL logfile - this is consistant with Openhab logfile where the last persitence entry is at “2017-11-29 18:05:07.695 [DEBUG] [sql.internal.MysqlPersistenceService] - mySQL: query:SELECT Time, Value FROM Item110 WHERE TIME>‘2017-11-22 18:05:07’ AND TIME<‘2017-11-29 18:05:07’ ORDER BY Time ASC”.
I could post the logfiles but they are quite big.
Mitigation:
In order to get rid of this issue I tried to switch to JDBC/mySQL connectivity - as suggested i the thread above - but the migration failed ==> this the next issue:
changed mysql.cfg to jdbc.cfg:
############################ jdbc Persistence Service ##################################
# the database url like 'jdbc:mysql://<host>:<port>/<database>'
#url=jdbc:mysql://homeserver2.home.lan:3306/OpenHAB
url=jdbc:mysql://homeserver2.home.lan:3306/OpenHABJDBC
# the database user
user=openhab
# the database password
password=*****
tableNamePrefix=Item
tableUseRealItemNames=false
tableIdDigitCount=0
errReconnectThreshold=10
# the reconnection counter
#reconnectCnt=5
# the connection timeout (in seconds)
#mysql:waitTimeout=28800
# optional tweaking of mysql datatypes
# example as described in https://github.com/openhab/openhab/issues/710
sqltype.string=VARCHAR(20000)
# Use MySQL Server time to store item values (=false) or use openHAB Server time (=true).
# For new installations, its recommend to set "mysql:localtime=true".
# (available since 1.9, optional, defaults to false)
#localtime=true
# enable logtime
enableLogTime=true
I also respected the mySQL to jdbc/mysql documentation in Openhab documentation (Items vs items, …)
Changed mysql.persist to jdbc.persist (Note that exactly the same .persist file was working with native mySQL persistance service without issue - so do not expect issue here)
// persistance strategy definition for homeserver2 mysql database
//  following Strategies are defined:
//  1) Restore states on startup
Strategies {
   everyMinute	: "0 * * * * ?"
   everyHour    : "0 0 * * * ?"
   everyDay     : "0 0 0 * * ?"
   // next line is not allowed - it must be a cron strategy, of "everyChange" should be used this must be used directly at the items
   //EnergyTarifStrategy : everyChange
   EnergyTarifStrategy : "0 */15 * * * ?"
   // every 15 min
   EnergyConsumptionStrategy : "0 */15 * * * ?"
   //EnergyConsumptionStrategy : "0 */1 * * * ?"
   // Pellet strategies
   // <<<< TO BE DEFINED >>>>
   // Weather strategies
   WeatherStrategy : "0 */15 * * * ?"
    // Sprinkler strategies
    //SprinklerStrategyParameters : everyChange
	// default = everyUpdate
    default = everyChange
// items lower case?
Items {
    // persist all items on every change and restore them from the MapDB at startup
    //* : strategy = everyChange, restoreOnStartup
    gAlert* : strategy = everyChange, restoreOnStartup
    // items for electrical Meter Energy
    // using the group name gEnergy
    gEnergy* : strategy = EnergyTarifStrategy, restoreOnStartup
    gEnergyConsumption* : strategy = EnergyConsumptionStrategy, restoreOnStartup
	// should be removed if the group definition is used.
	//Tarif1_Energy_Plus : strategy = EnergyTarifStrategy, restoreOnStartup
	//Tarif1_Energy_Minus : strategy = EnergyTarifStrategy, restoreOnStartup
	//InstantVoltageL1 : strategy = EnergyTarifStrategy, restoreOnStartup
	//InstantVoltageL2 : strategy = EnergyTarifStrategy, restoreOnStartup
	//InstantVoltageL3 : strategy = EnergyTarifStrategy, restoreOnStartup
	/* Testing of Yahoo Weather binding
	Test_TemperatureMYSQL : strategy = everyMinute, restoreOnStartup
	Test_HumidityMYSQL : strategy = everyMinute, restoreOnStartup
	Test_PressureMYSQL : strategy = everyMinute, restoreOnStartup
	// Wheather items
	gWetter* : strategy = WeatherStrategy, restoreOnStartup
	gWheatherUnderground* : strategy = WeatherStrategy, restoreOnStartup
	// Pellet items
	// gPellet* : strategy = everyChange, everyUpdate, restoreOnStartup
	gPellet* : strategy = everyChange, restoreOnStartup
	// Sprinkler items
	gWaterSource* 				: strategy = everyChange, restoreOnStartup
	gWaterShaft*					: strategy = everyChange, restoreOnStartup
	gCistern*					: strategy = everyChange, restoreOnStartup
	SprTimeScalingFactor 		: strategy = everyChange, restoreOnStartup
	SprGlobalState 				: strategy = everyChange, restoreOnStartup
	SprStartingGroup_1_StartTime_Hour : strategy = everyChange, restoreOnStartup
	SprStartingGroup_1_StartTime_Min : strategy = everyChange, restoreOnStartup
	SprStartingGroup_2_StartTime_Hour : strategy = everyChange, restoreOnStartup
	SprStartingGroup_2_StartTime_Min : strategy = everyChange, restoreOnStartup
	SprStartingGroup_3_StartTime_Hour : strategy = everyChange, restoreOnStartup
	SprStartingGroup_3_StartTime_Min : strategy = everyChange, restoreOnStartup
	itemStartingGroup_1_TotalDurationTime : strategy = everyChange, restoreOnStartup
	itemStartingGroup_2_TotalDurationTime : strategy = everyChange, restoreOnStartup
	itemStartingGroup_3_TotalDurationTime : strategy = everyChange, restoreOnStartup
	// Sprinkler groups
	gCh* 						: strategy = everyChange, restoreOnStartup
After deinstalling mysql binding and installding jdbc/mysql binding the persistance was not working any more.
Excerpt of logfile:
2017-12-04 21:23:59.262 [DEBUG] [org.openhab.persistence.jdbc        ] - BundleEvent STARTING - org.openhab.persistence.jdbc
2017-12-04 21:23:59.274 [DEBUG] [jdbc.internal.JdbcPersistenceService] - JDBC::setItemRegistry
2017-12-04 21:23:59.274 [DEBUG] [jdbc.internal.JdbcPersistenceService] - JDBC::activate: persistence service activated
2017-12-04 21:23:59.276 [DEBUG] [jdbc.internal.JdbcPersistenceService] - JDBC::updateConfig
2017-12-04 21:23:59.294 [DEBUG] [ence.jdbc.internal.JdbcConfiguration] - JDBC::JdbcConfiguration
2017-12-04 21:23:59.296 [DEBUG] [ence.jdbc.internal.JdbcConfiguration] - JDBC::updateConfig: configuration size = 16
2017-12-04 21:23:59.298 [DEBUG] [ence.jdbc.internal.JdbcConfiguration] - JDBC::updateConfig: user=openhab
2017-12-04 21:23:59.298 [DEBUG] [ence.jdbc.internal.JdbcConfiguration] - JDBC::updateConfig: password exists? true
2017-12-04 21:23:59.300 [DEBUG] [ence.jdbc.internal.JdbcConfiguration] - JDBC::updateConfig: url=jdbc:mysql://homeserver2.home.lan:3306/OpenHAB
2017-12-04 21:23:59.301 [DEBUG] [ence.jdbc.internal.JdbcConfiguration] - JDBC::updateConfig: found serviceName = 'mysql'
2017-12-04 21:23:59.301 [DEBUG] [ence.jdbc.internal.JdbcConfiguration] - JDBC::updateConfig: Init Data Access Object Class: 'org.openhab.persistence.jdbc.db.JdbcMysqlDAO'
2017-12-04 21:23:59.334 [DEBUG] [nhab.persistence.jdbc.db.JdbcBaseDAO] - JDBC::initSqlTypes: Initialize the type array
2017-12-04 21:23:59.341 [DEBUG] [nhab.persistence.jdbc.db.JdbcBaseDAO] - JDBC::initSqlQueries: 'JdbcMysqlDAO'
2017-12-04 21:23:59.342 [DEBUG] [hab.persistence.jdbc.db.JdbcMysqlDAO] - JDBC::initSqlTypes: Initialize the type array
2017-12-04 21:23:59.344 [DEBUG] [hab.persistence.jdbc.db.JdbcMysqlDAO] - JDBC::initSqlQueries: 'JdbcMysqlDAO'
2017-12-04 21:23:59.354 [DEBUG] [ence.jdbc.internal.JdbcConfiguration] - JDBC::updateConfig: dBDAO ClassName=org.openhab.persistence.jdbc.db.JdbcMysqlDAO
2017-12-04 21:23:59.359 [DEBUG] [ence.jdbc.internal.JdbcConfiguration] - JDBC::updateConfig: set sqlTypes: itemType=STRINGITEM value=VARCHAR(20000)
2017-12-04 21:23:59.361 [DEBUG] [ence.jdbc.internal.JdbcConfiguration] - JDBC::updateConfig: errReconnectThreshold=5
2017-12-04 21:23:59.374 [DEBUG] [ence.jdbc.internal.JdbcConfiguration] - JDBC::updateConfig: tableNamePrefix=Item
2017-12-04 21:23:59.376 [DEBUG] [ence.jdbc.internal.JdbcConfiguration] - JDBC::updateConfig: tableUseRealItemNames=false
2017-12-04 21:23:59.378 [DEBUG] [ence.jdbc.internal.JdbcConfiguration] - JDBC::updateConfig: tableIdDigitCount=0
2017-12-04 21:23:59.379 [DEBUG] [ence.jdbc.internal.JdbcConfiguration] - JDBC::updateConfig: enableLogTime true
2017-12-04 21:23:59.448 [DEBUG] [ence.jdbc.internal.JdbcConfiguration] - JDBC::updateConfig: load JDBC-driverClass was successful: 'com.mysql.jdbc.Driver'
2017-12-04 21:23:59.457 [DEBUG] [ence.jdbc.internal.JdbcConfiguration] - JDBC::updateConfig: configuration complete. service=jdbc
2017-12-04 21:23:59.458 [DEBUG] [persistence.jdbc.internal.JdbcMapper] - JDBC::pingDB
2017-12-04 21:23:59.458 [DEBUG] [persistence.jdbc.internal.JdbcMapper] - JDBC::openConnection isDriverAvailable: true
2017-12-04 21:23:59.459 [INFO ] [persistence.jdbc.internal.JdbcMapper] - JDBC::openConnection: Driver is available::Yank setupDataSource
2017-12-04 21:23:59.494 [INFO ] [com.zaxxer.hikari.HikariDataSource  ] - yank-default - Started.
2017-12-04 21:24:00.420 [INFO ] [org.knowm.yank.YankPoolManager      ] - Initialized pool 'yank-default'
2017-12-04 21:24:00.421 [DEBUG] [ence.jdbc.internal.JdbcConfiguration] - JDBC::setDbConnected true
2017-12-04 21:24:00.421 [DEBUG] [hab.persistence.jdbc.db.JdbcMysqlDAO] - JDBC::initAfterFirstDbConnection: Initializing step, after db is connected.
2017-12-04 21:24:00.446 [DEBUG] [ab.persistence.jdbc.utils.DbMetaData] - dbMajorVersion = '5'
2017-12-04 21:24:00.446 [DEBUG] [ab.persistence.jdbc.utils.DbMetaData] - dbMinorVersion = '7'
2017-12-04 21:24:00.447 [DEBUG] [ab.persistence.jdbc.utils.DbMetaData] - driverMajorVersion = '5'
2017-12-04 21:24:00.447 [DEBUG] [ab.persistence.jdbc.utils.DbMetaData] - driverMinorVersion = '1'
2017-12-04 21:24:00.447 [DEBUG] [ab.persistence.jdbc.utils.DbMetaData] - dbProductName = 'MySQL'
2017-12-04 21:24:00.447 [DEBUG] [ab.persistence.jdbc.utils.DbMetaData] - dbProductVersion = '5.7.19-0ubuntu0.16.04.1-log'
2017-12-04 21:24:00.447 [DEBUG] [ence.jdbc.internal.JdbcConfiguration] - JDBC::updateConfig: set sqlTypes: itemType=STRINGITEM value=VARCHAR(20000)
2017-12-04 21:24:00.449 [DEBUG] [persistence.jdbc.internal.JdbcMapper] - JDBC::pingDB asking db for name as absolutely first db action, after connection is established.
2017-12-04 21:24:00.569 [INFO ] [persistence.jdbc.internal.JdbcMapper] - JDBC::logTime: 'pingDB':
 afterAccess     = 1111 ms
 timeAverage50  = 1111 ms
 timeAverage100 = 1111 ms
 timeAverage200 = 1111 ms
 afterAccessMin  = 1111 ms
 afterAccessMax  = 1111 ms
 1000Statements = 0 sec
 statementCount = 1
2017-12-04 21:24:00.570 [DEBUG] [persistence.jdbc.internal.JdbcMapper] - JDBC::checkDBAcessability, first try connection: true
2017-12-04 21:24:00.570 [DEBUG] [jdbc.internal.JdbcPersistenceService] - JDBC::getName: returning name 'jdbc' for queryable persistence service.
2017-12-04 21:24:00.571 [DEBUG] [jdbc.internal.JdbcPersistenceService] - JDBC::updateConfig: configuration complete for service=jdbc.
2017-12-04 21:24:00.583 [DEBUG] [jdbc.internal.JdbcPersistenceService] - JDBC::getName: returning name 'jdbc' for queryable persistence service.
2017-12-04 21:24:00.589 [DEBUG] [jdbc.internal.JdbcPersistenceService] - JDBC::getName: returning name 'jdbc' for queryable persistence service.
2017-12-04 21:24:00.592 [DEBUG] [jdbc.internal.JdbcPersistenceService] - JDBC::getName: returning name 'jdbc' for queryable persistence service.
2017-12-04 21:24:00.600 [DEBUG] [persistence.jdbc.internal.JdbcMapper] - JDBC::pingDB
2017-12-04 21:24:00.600 [DEBUG] [persistence.jdbc.internal.JdbcMapper] - JDBC::openConnection isDriverAvailable: true
2017-12-04 21:24:00.604 [INFO ] [persistence.jdbc.internal.JdbcMapper] - JDBC::logTime: 'pingDB':
 afterAccess     = 4 ms
 timeAverage50  = 557 ms
 timeAverage100 = 557 ms
 timeAverage200 = 557 ms
 afterAccessMin  = 4 ms
 statementCount = 2
2017-12-04 21:24:00.605 [DEBUG] [persistence.jdbc.internal.JdbcMapper] - JDBC::checkDBAcessability, first try connection: true
2017-12-04 21:24:00.605 [WARN ] [jdbc.internal.JdbcPersistenceService] - JDBC::query: database not connected, query aborted for item 'GlobalInfoString'
2017-12-04 21:24:00.607 [DEBUG] [persistence.jdbc.internal.JdbcMapper] - JDBC::pingDB
2017-12-04 21:24:00.607 [DEBUG] [persistence.jdbc.internal.JdbcMapper] - JDBC::openConnection isDriverAvailable: true
2017-12-04 21:24:00.611 [INFO ] [persistence.jdbc.internal.JdbcMapper] - JDBC::logTime: 'pingDB':
 afterAccess     = 4 ms
 timeAverage50  = 373 ms
 timeAverage100 = 373 ms
 timeAverage200 = 373 ms
 statementCount = 3
2017-12-04 21:24:00.615 [DEBUG] [persistence.jdbc.internal.JdbcMapper] - JDBC::checkDBAcessability, first try connection: true
2017-12-04 21:24:00.619 [WARN ] [jdbc.internal.JdbcPersistenceService] - JDBC::query: database not connected, query aborted for item 'Tarif1_Energy_Minus'
2017-12-04 21:24:00.620 [DEBUG] [persistence.jdbc.internal.JdbcMapper] - JDBC::pingDB
2017-12-04 21:24:00.620 [DEBUG] [persistence.jdbc.internal.JdbcMapper] - JDBC::openConnection isDriverAvailable: true
2017-12-04 21:24:00.624 [INFO ] [persistence.jdbc.internal.JdbcMapper] - JDBC::logTime: 'pingDB':
 afterAccess     = 4 ms
 timeAverage50  = 280 ms
 timeAverage100 = 280 ms
 timeAverage200 = 280 ms
 statementCount = 4
corresponding mySQL logfile:
2017-12-04T21:24:00.367236+01:00	 1663 Connect	openhab@10.0.1.59 on OpenHAB using TCP/IP
2017-12-04T21:24:00.375101+01:00	 1663 Query	/* mysql-connector-java-5.1.38 ( Revision: fe541c166cec739c74cc727c5da96c1028b4834a ) */SELECT  @@session.auto_increment_increment AS auto_increment_increment, @@character_set_client AS character_set_client, @@character_set_connection AS character_set_connection, @@character_set_results AS character_set_results, @@character_set_server AS character_set_server, @@init_connect AS init_connect, @@interactive_timeout AS interactive_timeout, @@license AS license, @@lower_case_table_names AS lower_case_table_names, @@max_allowed_packet AS max_allowed_packet, @@net_buffer_length AS net_buffer_length, @@net_write_timeout AS net_write_timeout, @@query_cache_size AS query_cache_size, @@query_cache_type AS query_cache_type, @@sql_mode AS sql_mode, @@system_time_zone AS system_time_zone, @@time_zone AS time_zone, @@tx_isolation AS tx_isolation, @@wait_timeout AS wait_timeout
2017-12-04T21:24:00.407367+01:00	 1663 Query	SET NAMES latin1
2017-12-04T21:24:00.407930+01:00	 1663 Query	SET character_set_results = NULL
2017-12-04T21:24:00.408902+01:00	 1663 Query	SET autocommit=1
2017-12-04T21:24:00.410734+01:00	 1663 Query	set session transaction read write
2017-12-04T21:24:00.411056+01:00	 1663 Query	SET autocommit=1
2017-12-04T21:24:00.411878+01:00	 1663 Query	SELECT @@session.tx_isolation
2017-12-04T21:24:00.413030+01:00	 1663 Quit
2017-12-04T21:24:00.427955+01:00	 1664 Connect	openhab@10.0.1.59 on OpenHAB using TCP/IP
2017-12-04T21:24:00.428443+01:00	 1664 Query	/* mysql-connector-java-5.1.38 ( Revision: fe541c166cec739c74cc727c5da96c1028b4834a ) */SELECT  @@session.auto_increment_increment AS auto_increment_increment, @@character_set_client AS character_set_client, @@character_set_connection AS character_set_connection, @@character_set_results AS character_set_results, @@character_set_server AS character_set_server, @@init_connect AS init_connect, @@interactive_timeout AS interactive_timeout, @@license AS license, @@lower_case_table_names AS lower_case_table_names, @@max_allowed_packet AS max_allowed_packet, @@net_buffer_length AS net_buffer_length, @@net_write_timeout AS net_write_timeout, @@query_cache_size AS query_cache_size, @@query_cache_type AS query_cache_type, @@sql_mode AS sql_mode, @@system_time_zone AS system_time_zone, @@time_zone AS time_zone, @@tx_isolation AS tx_isolation, @@wait_timeout AS wait_timeout
2017-12-04T21:24:00.430414+01:00	 1664 Query	SET NAMES latin1
2017-12-04T21:24:00.430729+01:00	 1664 Query	SET character_set_results = NULL
2017-12-04T21:24:00.431042+01:00	 1664 Query	SET autocommit=1
2017-12-04T21:24:00.431369+01:00	 1664 Query	set session transaction read write
2017-12-04T21:24:00.431933+01:00	 1664 Query	SET autocommit=1
2017-12-04T21:24:00.469888+01:00	 1665 Connect	openhab@10.0.1.59 on OpenHAB using TCP/IP
2017-12-04T21:24:00.471825+01:00	 1665 Query	/* mysql-connector-java-5.1.38 ( Revision: fe541c166cec739c74cc727c5da96c1028b4834a ) */SELECT  @@session.auto_increment_increment AS auto_increment_increment, @@character_set_client AS character_set_client, @@character_set_connection AS character_set_connection, @@character_set_results AS character_set_results, @@character_set_server AS character_set_server, @@init_connect AS init_connect, @@interactive_timeout AS interactive_timeout, @@license AS license, @@lower_case_table_names AS lower_case_table_names, @@max_allowed_packet AS max_allowed_packet, @@net_buffer_length AS net_buffer_length, @@net_write_timeout AS net_write_timeout, @@query_cache_size AS query_cache_size, @@query_cache_type AS query_cache_type, @@sql_mode AS sql_mode, @@system_time_zone AS system_time_zone, @@time_zone AS time_zone, @@tx_isolation AS tx_isolation, @@wait_timeout AS wait_timeout
2017-12-04T21:24:00.474943+01:00	 1665 Query	SET NAMES latin1
2017-12-04T21:24:00.477611+01:00	 1665 Query	SET character_set_results = NULL
2017-12-04T21:24:00.480441+01:00	 1665 Query	SET autocommit=1
2017-12-04T21:24:00.483073+01:00	 1665 Query	set session transaction read write
2017-12-04T21:24:00.484641+01:00	 1665 Query	SET autocommit=1
2017-12-04T21:24:00.520709+01:00	 1666 Connect	openhab@10.0.1.59 on OpenHAB using TCP/IP
2017-12-04T21:24:00.522873+01:00	 1666 Query	/* mysql-connector-java-5.1.38 ( Revision: fe541c166cec739c74cc727c5da96c1028b4834a ) */SELECT  @@session.auto_increment_increment AS auto_increment_increment, @@character_set_client AS character_set_client, @@character_set_connection AS character_set_connection, @@character_set_results AS character_set_results, @@character_set_server AS character_set_server, @@init_connect AS init_connect, @@interactive_timeout AS interactive_timeout, @@license AS license, @@lower_case_table_names AS lower_case_table_names, @@max_allowed_packet AS max_allowed_packet, @@net_buffer_length AS net_buffer_length, @@net_write_timeout AS net_write_timeout, @@query_cache_size AS query_cache_size, @@query_cache_type AS query_cache_type, @@sql_mode AS sql_mode, @@system_time_zone AS system_time_zone, @@time_zone AS time_zone, @@tx_isolation AS tx_isolation, @@wait_timeout AS wait_timeout
2017-12-04T21:24:00.525601+01:00	 1666 Query	SET NAMES latin1
2017-12-04T21:24:00.528064+01:00	 1666 Query	SET character_set_results = NULL
2017-12-04T21:24:00.530399+01:00	 1666 Query	SET autocommit=1
2017-12-04T21:24:00.531839+01:00	 1666 Query	set session transaction read write
2017-12-04T21:24:00.537766+01:00	 1666 Query	SET autocommit=1
2017-12-04T21:24:00.542791+01:00	 1665 Query	SELECT DATABASE()
2017-12-04T21:24:00.596468+01:00	 1665 Query	SELECT 1
2017-12-04T21:24:00.603515+01:00	 1665 Query	SELECT 1
2017-12-04T21:24:00.616624+01:00	 1665 Query	SELECT 1
2017-12-04T21:24:00.623959+01:00	 1665 Query	SELECT 1
2017-12-04T21:24:00.632228+01:00	 1665 Query	SELECT 1
2017-12-04T21:24:00.637018+01:00	 1665 Query	SELECT 1
2017-12-04T21:24:00.693115+01:00	 1665 Query	SELECT 1
2017-12-04T21:24:00.703445+01:00	 1665 Query	SELECT 1
2017-12-04T21:24:00.709578+01:00	 1665 Query	SELECT 1
2017-12-04T21:24:00.734161+01:00	 1665 Query	SELECT 1
2017-12-04T21:24:00.740954+01:00	 1665 Query	SELECT 1
2017-12-04T21:24:00.764671+01:00	 1665 Query	SELECT 1
2017-12-04T21:24:00.769624+01:00	 1665 Query	SELECT 1
2017-12-04T21:24:00.775768+01:00	 1665 Query	SELECT 1
I also tried to drop the database completely that the tables are newly creaed - but also not successfull.
From the logfile entries in OpenHAB I tried to do some reverse engineering with the jdbc/openhab source code (in pseudo code below):
Class JdbcPersistanceService.java
	execute class constructor
		 public  void updateConfig(Map<Object, Object> configuration) {
				logger.debug("JDBC::updateConfig");
				conf = new JdbcConfiguration(configuration);
				if (checkDBAccessability()) {
					checkDBSchema();
					// connection has been established ... initialization completed!
					initialized = true;
				} else {
					initialized = false;
				logger.debug("JDBC::updateConfig: configuration complete for service={}.", getName());
then execute
	   public  void setDbConnected(boolean dbConnected) {
        logger.debug("JDBC::setDbConnected {}", dbConnected);
        // Initializing step, after db is connected.
        // Initialize sqlTypes, depending on DB version for example
        dBDAO.initAfterFirstDbConnection();
        // Running once again to prior external configured SqlTypes!
        setSqlTypes();
        this.dbConnected = dbConnected;
	==> then exectute
	  public  void initAfterFirstDbConnection() {
        logger.debug("JDBC::initAfterFirstDbConnection: Initializing step, after db is connected.");
        dbMeta = new DbMetaData();// get DB information
	==> then execute DbMetaData()    ==> this is in   import org.openhab.persistence.jdbc.utils.DbMetaData;
	==> then execute  (once again)
	  JdbcConfiguration::setSqlTypes();
	==> then setDbConnected  exit
	==> then   checkDBAccessability()
			==> within: exec  pingDB()
				within PingdB:
					check Dbname == null =>   "JDBC::pingDB asking db for name as absolutely first db action, after connection is established.")
					set DBname
						SELECT DATABASE()  command is executed
						>>>>>>>>>>Question: Is correct Database name given back???!!!!!!!!!!!!<<<<<<
	==> then checkDBSchema();
			==> within  execture createItemsTableIfNot()
			==> there is no DEBUG logfile entry any more  (like >>>> logger.debug("JDBC::createItemsTableIfNot"); <<<<<)
It seems the database connectivity is always checked but not stored correctly or not percieved correctly from the DB.
Or either the DB-name is not received correctly or the tables could not be checked correctly (with checkDBSchema() frrom the existing DB.
Unfortunately there is no error seen. I do not know how to debug further… (hope the explanations above are somehow clear).
Any hint is appreciated.
Thanks a lot!
------- EDIT -------
One additional addon:
I found in this post https://github.com/openhab/openhab1-addons/issues/5112 a debug log file showing the follogin log:
2017-03-05 14:05:23.638 [DEBUG] [org.openhab.persistence.jdbc        ] - BundleEvent STARTED - org.openhab.persistence.jdbc
2017-03-05 14:05:23.645 [DEBUG] [jdbc.internal.JdbcPersistenceService] - JDBC::setItemRegistry
2017-03-05 14:05:23.646 [DEBUG] [jdbc.internal.JdbcPersistenceService] - JDBC::activate: persistence service activated
2017-03-05 14:05:23.646 [DEBUG] [jdbc.internal.JdbcPersistenceService] - JDBC::updateConfig
2017-03-05 14:05:23.649 [DEBUG] [ence.jdbc.internal.JdbcConfiguration] - JDBC::JdbcConfiguration
2017-03-05 14:05:23.649 [DEBUG] [ence.jdbc.internal.JdbcConfiguration] - JDBC::updateConfig: configuration size = 11
2017-03-05 14:05:23.652 [DEBUG] [ence.jdbc.internal.JdbcConfiguration] - JDBC::updateConfig: user=lewie
2017-03-05 14:05:23.652 [DEBUG] [ence.jdbc.internal.JdbcConfiguration] - JDBC::updateConfig: password exists? true
2017-03-05 14:05:23.653 [DEBUG] [ence.jdbc.internal.JdbcConfiguration] - JDBC::updateConfig: url=jdbc:mysql://192.168.0.181:3306/ItemTypeTest4
2017-03-05 14:05:23.653 [DEBUG] [ence.jdbc.internal.JdbcConfiguration] - JDBC::updateConfig: found serviceName = 'mysql'
2017-03-05 14:05:23.653 [DEBUG] [ence.jdbc.internal.JdbcConfiguration] - JDBC::updateConfig: Init Data Access Object Class: 'org.openhab.persistence.jdbc.db.JdbcMysqlDAO'
2017-03-05 14:05:23.688 [DEBUG] [nhab.persistence.jdbc.db.JdbcBaseDAO] - JDBC::initSqlTypes: Initialize the type array
2017-03-05 14:05:23.702 [DEBUG] [nhab.persistence.jdbc.db.JdbcBaseDAO] - JDBC::initSqlQueries: 'JdbcMysqlDAO'
2017-03-05 14:05:23.704 [DEBUG] [hab.persistence.jdbc.db.JdbcMysqlDAO] - JDBC::initSqlTypes: Initialize the type array
2017-03-05 14:05:23.704 [DEBUG] [hab.persistence.jdbc.db.JdbcMysqlDAO] - JDBC::initSqlQueries: 'JdbcMysqlDAO'
2017-03-05 14:05:23.704 [DEBUG] [ence.jdbc.internal.JdbcConfiguration] - JDBC::updateConfig: dBDAO ClassName=org.openhab.persistence.jdbc.db.JdbcMysqlDAO
2017-03-05 14:05:23.705 [DEBUG] [ence.jdbc.internal.JdbcConfiguration] - JDBC::updateConfig: numberDecimalcount=1
2017-03-05 14:05:23.705 [DEBUG] [ence.jdbc.internal.JdbcConfiguration] - JDBC::updateConfig: tableUseRealItemNames=false
2017-03-05 14:05:23.705 [DEBUG] [ence.jdbc.internal.JdbcConfiguration] - JDBC::updateConfig: enableLogTime false
2017-03-05 14:05:23.713 [DEBUG] [ence.jdbc.internal.JdbcConfiguration] - JDBC::updateConfig: load JDBC-driverClass was successful: 'com.mysql.jdbc.Driver'
2017-03-05 14:05:23.713 [DEBUG] [ence.jdbc.internal.JdbcConfiguration] - JDBC::updateConfig: configuration complete. service=jdbc
2017-03-05 14:05:23.713 [DEBUG] [persistence.jdbc.internal.JdbcMapper] - JDBC::pingDB
2017-03-05 14:05:23.713 [DEBUG] [persistence.jdbc.internal.JdbcMapper] - JDBC::openConnection isDriverAvailable: true
2017-03-05 14:05:23.713 [INFO ] [persistence.jdbc.internal.JdbcMapper] - JDBC::openConnection: Driver is available::Yank setupDataSource
2017-03-05 14:05:24.452 [DEBUG] [ence.jdbc.internal.JdbcConfiguration] - JDBC::setDbConnected true
2017-03-05 14:05:24.452 [DEBUG] [hab.persistence.jdbc.db.JdbcMysqlDAO] - JDBC::initAfterFirstDbConnection: Initializing step, after db is connected.
2017-03-05 14:05:24.561 [DEBUG] [ab.persistence.jdbc.utils.DbMetaData] - dbMajorVersion = '5'
2017-03-05 14:05:24.562 [DEBUG] [ab.persistence.jdbc.utils.DbMetaData] - dbMinorVersion = '7'
2017-03-05 14:05:24.564 [DEBUG] [ab.persistence.jdbc.utils.DbMetaData] - driverMajorVersion = '5'
2017-03-05 14:05:24.564 [DEBUG] [ab.persistence.jdbc.utils.DbMetaData] - driverMinorVersion = '1'
2017-03-05 14:05:24.564 [DEBUG] [ab.persistence.jdbc.utils.DbMetaData] - dbProductName = 'MySQL'
2017-03-05 14:05:24.564 [DEBUG] [ab.persistence.jdbc.utils.DbMetaData] - dbProductVersion = '5.7.17'
2017-03-05 14:05:24.565 [DEBUG] [persistence.jdbc.internal.JdbcMapper] - JDBC::pingDB asking db for name as absolutely first db action, after connection is established.
2017-03-05 14:05:24.705 [DEBUG] [persistence.jdbc.internal.JdbcMapper] - JDBC::checkDBAcessability, first try connection: true
2017-03-05 14:05:24.707 [DEBUG] [persistence.jdbc.internal.JdbcMapper] - JDBC::createItemsTableIfNot
2017-03-05 14:05:24.708 [DEBUG] [nhab.persistence.jdbc.db.JdbcBaseDAO] - JDBC::doCreateItemsTableIfNot sql=CREATE TABLE IF NOT EXISTS items (ItemId INT NOT NULL AUTO_INCREMENT,itemname VARCHAR(500) NOT NULL,PRIMARY KEY (ItemId))
2017-03-05 14:05:24.797 [DEBUG] [persistence.jdbc.internal.JdbcMapper] - JDBC::getItemIDTableNames
2017-03-05 14:05:24.797 [DEBUG] [nhab.persistence.jdbc.db.JdbcBaseDAO] - JDBC::doGetItemIDTableNames sql=SELECT itemid, itemname FROM items
2017-03-05 14:05:24.801 [DEBUG] [jdbc.internal.JdbcPersistenceService] - JDBC::getName: returning name 'jdbc' for queryable persistence service.
2017-03-05 14:05:24.802 [DEBUG] [jdbc.internal.JdbcPersistenceService] - JDBC::updateConfig: configuration complete for service=jdbc.
2017-03-05 14:05:24.802 [DEBUG] [jdbc.internal.JdbcPersistenceService] - JDBC::getName: returning name 'jdbc' for queryable persistence service.
2017-03-05 14:05:24.804 [DEBUG] [jdbc.internal.JdbcPersistenceService] - JDBC::getName: returning name 'jdbc' for queryable persistence service.
2017-03-05 14:05:24.805 [DEBUG] [jdbc.internal.JdbcPersistenceService] - JDBC::getName: returning name 'jdbc' for queryable persistence service.
2017-03-05 14:05:24.833 [DEBUG] [jdbc.internal.JdbcPersistenceService] - JDBC::getName: returning name 'jdbc' for queryable persistence service.
2017-03-05 14:05:24.834 [DEBUG] [jdbc.internal.JdbcPersistenceService] - JDBC::getName: returning name 'jdbc' for queryable persistence service.
2017-03-05 14:05:24.836 [DEBUG] [org.openhab.persistence.jdbc        ] - ServiceEvent REGISTERED - {org.openhab.core.persistence.PersistenceService, org.openhab.core.persistence.QueryablePersistenceService}={url=jdbc:mysql://192.168.0.181:3306/ItemTypeTest4, component.name=org.openhab.persistence.jdbc, tableUseRealItemNames=false, service.config.category=persistence, service.config.description.uri=persistence:jdbc, user=lewie, service.pid=org.openhab.jdbc, service.config.label=JDBC Persistence, component.id=158, numberDecimalcount=1, password=VRCLq7ED9GQJ7xEy, service.id=287, service.bundleid=193, service.scope=bundle} - org.openhab.persistence.jdbc
2017-03-05 14:05:30.672 [DEBUG] [persistence.jdbc.internal.JdbcMapper] - JDBC::storeItemValue: item=testItem (Type=NumberItem, State=1)
2017-03-05 14:05:30.673 [DEBUG] [persistence.jdbc.internal.JdbcMapper] - JDBC::getTable: no table found for item 'testItem' in sqlTables
2017-03-05 14:05:30.673 [DEBUG] [persistence.jdbc.internal.JdbcMapper] - JDBC::createNewEntryInItemsTable
2017-03-05 14:05:30.673 [DEBUG] [nhab.persistence.jdbc.db.JdbcBaseDAO] - JDBC::doCreateNewEntryInItemsTable sql=INSERT INTO items (ItemName) VALUES ('testItem')
2017-03-05 14:05:30.688 [DEBUG] [persistence.jdbc.internal.JdbcMapper] - JDBC::getTable: getTableName with rowId=1 itemName=testItem
2017-03-05 14:05:30.688 [DEBUG] [nhab.persistence.jdbc.db.JdbcBaseDAO] - JDBC::getItemType: Try to use ItemType NUMBERITEM for Item testItem
2017-03-05 14:05:30.689 [DEBUG] [penhab.persistence.jdbc.model.ItemVO] - JDBC:ItemVO tableName=item0001; newTableName=testItem;
2017-03-05 14:05:30.690 [DEBUG] [persistence.jdbc.internal.JdbcMapper] - JDBC::createItemTable
2017-03-05 14:05:30.776 [DEBUG] [persistence.jdbc.internal.JdbcMapper] - JDBC::getTable: Table created for item 'testItem' with dataType DOUBLE in SQL database.
2017-03-05 14:05:30.776 [DEBUG] [penhab.persistence.jdbc.model.ItemVO] - JDBC:ItemVO tableName=item0001; newTableName=null;
2017-03-05 14:05:30.776 [DEBUG] [nhab.persistence.jdbc.db.JdbcBaseDAO] - JDBC::getItemType: Try to use ItemType NUMBERITEM for Item testItem
2017-03-05 14:05:30.777 [DEBUG] [nhab.persistence.jdbc.db.JdbcBaseDAO] - JDBC::storeItemValueProvider: item 'testItem' as Type 'NUMBERITEM' in 'item0001' with state '1'
2017-03-05 14:05:30.777 [DEBUG] [nhab.persistence.jdbc.db.JdbcBaseDAO] - JDBC::storeItemValueProvider: getState: '1'
2017-03-05 14:05:30.777 [DEBUG] [penhab.persistence.jdbc.model.ItemVO] - JDBC:ItemVO setValueTypes dbType=DOUBLE; javaType=class java.lang.Double;
2017-03-05 14:05:30.777 [DEBUG] [nhab.persistence.jdbc.db.JdbcBaseDAO] - JDBC::storeItemValueProvider: newVal.doubleValue: '1.0'
2017-03-05 14:05:30.777 [DEBUG] [nhab.persistence.jdbc.db.JdbcBaseDAO] - JDBC::doStoreItemValue sql=INSERT INTO item0001 (TIME, VALUE) VALUES( NOW(3), ? ) ON DUPLICATE KEY UPDATE VALUE= ? value='1.0'
2017-03-05 14:05:30.790 [DEBUG] [jdbc.internal.JdbcPersistenceService] - JDBC: Stored item 'testItem' as '1' in SQL database at Sun Mar 05 14:05:30 CET 2017 in 118 ms.
2017-03-05 14:05:35.009 [DEBUG] [persistence.jdbc.internal.JdbcMapper] - JDBC::storeItemValue: item=testSwitch (Type=SwitchItem, State=OFF)
2017-03-05 14:05:35.009 [DEBUG] [persistence.jdbc.internal.JdbcMapper] - JDBC::getTable: no table found for item 'testSwitch' in sqlTables
2017-03-05 14:05:35.009 [DEBUG] [persistence.jdbc.internal.JdbcMapper] - JDBC::createNewEntryInItemsTable
2017-03-05 14:05:35.009 [DEBUG] [nhab.persistence.jdbc.db.JdbcBaseDAO] - JDBC::doCreateNewEntryInItemsTable sql=INSERT INTO items (ItemName) VALUES ('testSwitch')
2017-03-05 14:05:35.032 [DEBUG] [persistence.jdbc.internal.JdbcMapper] - JDBC::getTable: getTableName with rowId=2 itemName=testSwitch
2017-03-05 14:05:35.032 [DEBUG] [nhab.persistence.jdbc.db.JdbcBaseDAO] - JDBC::getItemType: Try to use ItemType SWITCHITEM for Item testSwitch
2017-03-05 14:05:35.032 [DEBUG] [penhab.persistence.jdbc.model.ItemVO] - JDBC:ItemVO tableName=item0002; newTableName=testSwitch;
2017-03-05 14:05:35.032 [DEBUG] [persistence.jdbc.internal.JdbcMapper] - JDBC::createItemTable
2017-03-05 14:05:35.103 [DEBUG] [persistence.jdbc.internal.JdbcMapper] - JDBC::getTable: Table created for item 'testSwitch' with dataType VARCHAR(6) in SQL database.
2017-03-05 14:05:35.104 [DEBUG] [penhab.persistence.jdbc.model.ItemVO] - JDBC:ItemVO tableName=item0002; newTableName=null;
2017-03-05 14:05:35.104 [DEBUG] [nhab.persistence.jdbc.db.JdbcBaseDAO] - JDBC::getItemType: Try to use ItemType SWITCHITEM for Item testSwitch
2017-03-05 14:05:35.104 [DEBUG] [nhab.persistence.jdbc.db.JdbcBaseDAO] - JDBC::storeItemValueProvider: item 'testSwitch' as Type 'SWITCHITEM' in 'item0002' with state 'OFF'
2017-03-05 14:05:35.104 [DEBUG] [nhab.persistence.jdbc.db.JdbcBaseDAO] - JDBC::storeItemValueProvider: getState: 'OFF'
2017-03-05 14:05:35.104 [DEBUG] [penhab.persistence.jdbc.model.ItemVO] - JDBC:ItemVO setValueTypes dbType=VARCHAR(6); javaType=class java.lang.String;
2017-03-05 14:05:35.104 [DEBUG] [nhab.persistence.jdbc.db.JdbcBaseDAO] - JDBC::storeItemValueProvider: other: item.getState().toString(): 'OFF'
2017-03-05 14:05:35.104 [DEBUG] [nhab.persistence.jdbc.db.JdbcBaseDAO] - JDBC::doStoreItemValue sql=INSERT INTO item0002 (TIME, VALUE) VALUES( NOW(3), ? ) ON DUPLICATE KEY UPDATE VALUE= ? value='OFF'
2017-03-05 14:05:35.110 [DEBUG] [jdbc.internal.JdbcPersistenceService] - JDBC: Stored item 'testSwitch' as 'OFF' in SQL database at Sun Mar 05 14:05:35 CET 2017 in 101 ms.
2017-03-05 14:06:00.004 [DEBUG] [persistence.jdbc.internal.JdbcMapper] - JDBC::storeItemValue: item=testItem (Type=NumberItem, State=2)
2017-03-05 14:06:00.005 [DEBUG] [penhab.persistence.jdbc.model.ItemVO] - JDBC:ItemVO tableName=item0001; newTableName=null;
The interesting part is the following part:
which means that the function “createItemsTableIfNot” is see in the DEBUG log. I do not see this entering in my case ==> thus the DB seems never “initialized” in the JDBC driver in this function:
					checkDBSchema();
					initialized = true;
				} else {
For other people having potentially the same issue during migration from mysql persistance to jdbc/mysql persistance see following solutions:
In jdbc.cfg I changed errReconnectThreshold=5 to errReconnectThreshold=0 ===> but no change in behaviour after restart
But following entries seen in /var/lib/openhab2/config/org/openhab/jdbc.config
$:/var/lib/openhab2/config/org/openhab$ more jdbc.config
enableLogTime="true"
errReconnectThreshold="0"
password="******"
reconnectCnt="5"
service.pid="org.openhab.jdbc"
sqltype.string="VARCHAR(20000)"
tableIdDigitCount="0"
tableNamePrefix="Item"
tableUseRealItemNames="false"
url="jdbc:mysql://homeserver2.home.lan:3306/openhab"
user="openhab"
So still the parameter reconnectCnt="5" was set even if it was set to 0 in the /etc/openhab2/persistance/jdbc.cfg file
Finally I replaced errReconnectThreshold=0 to reconnectCnt=0 in /etc/openhab2/persistance/jdbc.cfg ==> THIS provided the solution
This then also changed the the file /var/lib/openhab2/config/org/openhab/jdbc.config
password="******"
reconnectCnt="0"
user="openhab"
Now the Parameter reconnectCnt="0" was really set to 0 and it seems this parameter IS taken into account in the jdbc driver.
The parameter reconnectCnt seemed to be still active from some old config file (either jdbc.cfg or mysql.cfg).
Thus I recommend to change the documenation at
https://docs.openhab.org/v2.1.0/addons/persistence/jdbc/readme.html
to add a hint for the parameter reconnectCnt. This should be set to 0 (if it was ever used before,
especially for the Migration section from mysql persistance to jdbc/mysql persistance)
In addition:
The item management table is named different when using native mysql connector compared to the jdbc/mysql connector:
mysql native persistance: the items manage table within the database is named “Items
jdbc/mysql persistance: the items manage table within the database is named “items
In the source code file: org.openhab.persistance.jdbc/java/org/openhab/persistance/jdbc/model/ItemsVO.java
The itemsManageTable seems to be hardcoded:
	private String itemsManageTable = "items";
Solution: Rename in the existing MySQL Database the managetable from “Items” to “items
I also suggest to add this hint into the migration section https://docs.openhab.org/v2.1.0/addons/persistence/jdbc/readme.html#migration-from-mysql-to-jdbc-persistence-services that also the item management table needs to be renamed directly in the database.
I observed the same problem and a switch from mysql to jdbc solved it.
After migrating vom openHAB1 to openHAB2, the execution of rules stopped after some time. After a restart of openHAB it works some time, but then it stopped again. I run openHAB in DEBUG mode. In the debug messages I saw a sql select without an answer as last message from the mysql addon.
I followed Jo’s proposal and this solved the problem.
In my case I used mariadb with openHAB 1 and therfore I deciced to switch to the jdbc-mariadb persistence service.
Thank you very much @jrieder! After setting reconnectCnt=0, it worked perfectly! Would be interesting to know why…