Hello everybody,

I couldn’t find a solution by looking through similar posts.

My mqtt and influxdb streams suddenly stop working. I experienced this before, and now I upgraded to 2.4.0 RC1 . After gettingrid of the Z-Wave issues I have the same “old problem” again.

Best to see in the screenshot below - Openhab suddenly stops storing values in the InfluxDB:

It worked the whole night until 8:26 h a.m. Then I restarted openhab by using

sudo /bin/systemctl restart openhab2.service

and so it started to work again at 12:04 p.m. Additionally also the mqtt submission does not work anymore at the same time.
I couldn’t find any error in the log files (just the start of mqtt and influxdb). Previously I also tried to turn on debug logging for the influxdb persistence, but did not see anything obvious.

I am running openhab on an Intel NUC, InfluxDB and Grafana are running in Docker Containers.

My influxdb.persist looks like this:

Strategies {
   //every5seconds : "*/5 * * * * ?"
   everyMinute	: "0 * * * * ?"
   everyHour    : "0 0 * * * ?"
   everyDay     : "0 0 0 * * ?"
   //every5minutes : "0 */5 * * * ?"
   default = everyChange
   
}

Items {
    // persist all items once a day and on every change and restore them from the db at startup
    

    // additionally, persist all temperature and weather values every hour
    gFlatclimate*, gPower* : strategy = everyChange
    gEnergy* : strategy = everyHour
    gEumel* : strategy = everyChange
    gLights* : strategy = everyChange
    
}

my mqtt.persist file looks like this:

Strategies {
  everySecond : "* * * * * ?"
  everyMinute : "0 * * * * ?"
  everyHour   : "0 0 * * * ?"
  everyDay    : "0 0 0 * * ?"
  default     = everySecond
}

Items {
  Fibaro*  : strategy = everyChange
  Qubino*  : strategy = everyChange
  Verbund* : strategy = everyChange
}

If anybody has a hint what kind of logging to turn on or where to go on further with debugging - welcome!

Kind regards,
Herbert

Look in events.log to make sure that you are actually seeing events on these Items during those times. When you have errors like these you need to go back as far as possible to figure out where in the path things are failing.

Are Rules running at these times when nothing is being saved to the DB?

Hi @rlkoshak,

thank you for your reply. Concerning rules: guess not, as it happens at different times, so for the last time at exactly 2:05 am (last datapoint) I do not have a specific rule running.

I do not see any specific issue in the events log:

2018-12-17 02:04:48.513 [me.event.ThingUpdatedEvent] - Thing 'zwave:device:3008c030:node45' has been updated.
2018-12-17 02:04:49.416 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 50.0 to 51.0
2018-12-17 02:04:49.419 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 17.5 to 17.0
2018-12-17 02:04:49.944 [vent.ItemStateChangedEvent] - FibaroNode3_Power changed from 0.6 to 0.5
2018-12-17 02:04:49.945 [vent.ItemStateChangedEvent] - powTV changed from 0.6 to 0.5
2018-12-17 02:04:49.945 [GroupItemStateChangedEvent] - gPower changed from 56.8 to 56.7 through powTV
2018-12-17 02:04:49.993 [arthome.event.BindingEvent] - org.openhab.binding.zwave.event.BindingEvent@418408f0
2018-12-17 02:04:49.996 [me.event.ThingUpdatedEvent] - Thing 'zwave:device:3008c030:node7' has been updated.
2018-12-17 02:04:50.423 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 51.0 to 52.0
2018-12-17 02:04:50.425 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 17.0 to 19.3
2018-12-17 02:04:50.752 [vent.ItemStateChangedEvent] - senTemp_HeatBad changed from 22.3 to 22.4
2018-12-17 02:04:51.433 [vent.ItemStateChangedEvent] - sysNUC_Memused changed from 2342 to 2343
2018-12-17 02:04:51.434 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 52.0 to 51.0
2018-12-17 02:04:51.436 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 19.3 to 16.8
2018-12-17 02:04:52.438 [vent.ItemStateChangedEvent] - sysNUC_Memused changed from 2343 to 2342
2018-12-17 02:04:52.438 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 51.0 to 56.0
2018-12-17 02:04:52.440 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 16.8 to 27.3
2018-12-17 02:04:53.020 [vent.ItemStateChangedEvent] - eumelFreq changed from 49.93000030517578 to 49.939998626708984
2018-12-17 02:04:53.020 [vent.ItemStateChangedEvent] - eumelVA changed from 232.3671112060547 to 232.28109741210938
2018-12-17 02:04:53.021 [vent.ItemStateChangedEvent] - eumelVB changed from 231.91258239746094 to 231.91531372070312
2018-12-17 02:04:53.022 [vent.ItemStateChangedEvent] - eumelVC changed from 231.9753875732422 to 231.93984985351562
2018-12-17 02:04:53.022 [vent.ItemStateChangedEvent] - eumelIA changed from 5.45828914642334 to 5.45745325088501
2018-12-17 02:04:53.023 [vent.ItemStateChangedEvent] - eumelIB changed from 0.7718750238418579 to 0.7729374766349792
2018-12-17 02:04:53.023 [vent.ItemStateChangedEvent] - eumelIC changed from 0.6142265796661377 to 0.6355937719345093
2018-12-17 02:04:53.023 [vent.ItemStateChangedEvent] - eumelPA changed from 1120.81640625 to 1120.19140625
2018-12-17 02:04:53.024 [vent.ItemStateChangedEvent] - eumelPB changed from 99.82421875 to 99.92578125
2018-12-17 02:04:53.024 [vent.ItemStateChangedEvent] - eumelPC changed from 69.91015625 to 73.31640625
2018-12-17 02:04:53.024 [vent.ItemStateChangedEvent] - Verbund_Watt changed from 1290.546875 to 1293.4375
2018-12-17 02:04:53.025 [vent.ItemStateChangedEvent] - eumelPT changed from 1290.546875 to 1293.4375
2018-12-17 02:04:53.025 [vent.ItemStateChangedEvent] - Verbund_PTF changed from 1294.65625 to 1297.484375
2018-12-17 02:04:53.025 [vent.ItemStateChangedEvent] - Verbund_VAR changed from -741.21875 to -741.140625
2018-12-17 02:04:53.027 [vent.ItemStateChangedEvent] - Verbund_VA changed from 1590.46875 to 1594.984375
2018-12-17 02:04:53.028 [vent.ItemStateChangedEvent] - eumelEFAA changed from 1447.170654296875 to 1447.1722412109375
2018-12-17 02:04:53.028 [vent.ItemStateChangedEvent] - eumelEFAB changed from 1085.2142333984375 to 1085.2144775390625
2018-12-17 02:04:53.029 [vent.ItemStateChangedEvent] - eumelEFAT changed from 3122.73828125 to 3122.739990234375
2018-12-17 02:04:53.030 [vent.ItemStateChangedEvent] - eumelEFAC changed from 590.35302734375 to 590.3531494140625
2018-12-17 02:04:53.036 [vent.ItemStateChangedEvent] - eumelEFATKWH changed from 3.12273828 to 3.12273999
2018-12-17 02:04:53.037 [vent.ItemStateChangedEvent] - eumelEFATEURO changed from 0.5620928904 to 0.5620931982
2018-12-17 02:04:53.444 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 56.0 to 52.0
2018-12-17 02:04:53.447 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 27.3 to 36.5
2018-12-17 02:04:54.451 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 52.0 to 51.0
2018-12-17 02:04:54.453 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 36.5 to 16.8
2018-12-17 02:04:55.459 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 16.8 to 17.8
2018-12-17 02:04:55.560 [GroupItemStateChangedEvent] - gPower changed from 56.7 to 57.1 through powKWL
2018-12-17 02:04:55.561 [vent.ItemStateChangedEvent] - powKWL changed from 35.9 to 36.3
2018-12-17 02:04:55.562 [vent.ItemStateChangedEvent] - FibaroNode6_Power changed from 35.9 to 36.3
2018-12-17 02:04:55.793 [vent.ItemStateChangedEvent] - powKWL changed from 36.3 to 35.7
2018-12-17 02:04:55.793 [GroupItemStateChangedEvent] - gPower changed from 57.1 to 56.5 through powKWL
2018-12-17 02:04:55.794 [vent.ItemStateChangedEvent] - FibaroNode6_Power changed from 36.3 to 35.7
2018-12-17 02:04:56.027 [vent.ItemStateChangedEvent] - powKWL changed from 35.7 to 36.3
2018-12-17 02:04:56.027 [GroupItemStateChangedEvent] - gPower changed from 56.5 to 57.1 through powKWL
2018-12-17 02:04:56.028 [vent.ItemStateChangedEvent] - FibaroNode6_Power changed from 35.7 to 36.3
2018-12-17 02:04:56.349 [vent.ItemStateChangedEvent] - eneModem changed from 16.04 to 16.06
2018-12-17 02:04:56.349 [GroupItemStateChangedEvent] - gEnergy changed from 806.65 to 806.67 through eneModem
2018-12-17 02:04:56.463 [vent.ItemStateChangedEvent] - sysNUC_Memused changed from 2342 to 2343
2018-12-17 02:04:56.466 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 17.8 to 17.5
2018-12-17 02:04:57.469 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 51.0 to 50.0
2018-12-17 02:04:57.472 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 17.5 to 16.6
2018-12-17 02:04:58.084 [vent.ItemStateChangedEvent] - eumelFreq changed from 49.939998626708984 to 49.93000030517578
2018-12-17 02:04:58.084 [vent.ItemStateChangedEvent] - eumelVA changed from 232.28109741210938 to 232.3175048828125
2018-12-17 02:04:58.085 [vent.ItemStateChangedEvent] - eumelVB changed from 231.91531372070312 to 231.95492553710938
2018-12-17 02:04:58.086 [vent.ItemStateChangedEvent] - eumelVC changed from 231.93984985351562 to 232.0303192138672
2018-12-17 02:04:58.086 [vent.ItemStateChangedEvent] - eumelIA changed from 5.45745325088501 to 5.450171947479248
2018-12-17 02:04:58.087 [vent.ItemStateChangedEvent] - eumelIB changed from 0.7729374766349792 to 0.7733515501022339
2018-12-17 02:04:58.087 [vent.ItemStateChangedEvent] - eumelIC changed from 0.6355937719345093 to 0.6171562671661377
2018-12-17 02:04:58.087 [vent.ItemStateChangedEvent] - eumelPA changed from 1120.19140625 to 1118.55078125
2018-12-17 02:04:58.088 [vent.ItemStateChangedEvent] - eumelPB changed from 99.92578125 to 100.06640625
2018-12-17 02:04:58.088 [vent.ItemStateChangedEvent] - eumelPC changed from 73.31640625 to 70.37109375
2018-12-17 02:04:58.089 [vent.ItemStateChangedEvent] - Verbund_Watt changed from 1293.4375 to 1288.984375
2018-12-17 02:04:58.089 [vent.ItemStateChangedEvent] - eumelPT changed from 1293.4375 to 1288.984375
2018-12-17 02:04:58.089 [vent.ItemStateChangedEvent] - Verbund_VAR changed from -741.140625 to -740.75
2018-12-17 02:04:58.090 [vent.ItemStateChangedEvent] - Verbund_PTF changed from 1297.484375 to 1293.171875
2018-12-17 02:04:58.091 [vent.ItemStateChangedEvent] - Verbund_VA changed from 1594.984375 to 1589.40625
2018-12-17 02:04:58.092 [vent.ItemStateChangedEvent] - eumelEFAA changed from 1447.1722412109375 to 1447.173828125
2018-12-17 02:04:58.092 [vent.ItemStateChangedEvent] - eumelEFAB changed from 1085.2144775390625 to 1085.214599609375
2018-12-17 02:04:58.093 [vent.ItemStateChangedEvent] - eumelEFAC changed from 590.3531494140625 to 590.3532104492188
2018-12-17 02:04:58.093 [vent.ItemStateChangedEvent] - eumelEFAT changed from 3122.739990234375 to 3122.74169921875
2018-12-17 02:04:58.104 [vent.ItemStateChangedEvent] - eumelEFATKWH changed from 3.12273999 to 3.12274170
2018-12-17 02:04:58.104 [vent.ItemStateChangedEvent] - eumelEFATEURO changed from 0.5620931982 to 0.5620935060
2018-12-17 02:04:58.483 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 16.6 to 17.7
2018-12-17 02:04:59.484 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 50.0 to 49.0
2018-12-17 02:04:59.487 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 17.7 to 16.1
2018-12-17 02:04:59.905 [vent.ItemStateChangedEvent] - powKWL changed from 36.3 to 35.9
2018-12-17 02:04:59.906 [vent.ItemStateChangedEvent] - FibaroNode6_Power changed from 36.3 to 35.9
2018-12-17 02:04:59.906 [GroupItemStateChangedEvent] - gPower changed from 57.1 to 56.7 through powKWL
2018-12-17 02:05:00.019 [vent.ItemStateChangedEvent] - eumelEFATYTD changed from 3.12263452 to 3.12274170
2018-12-17 02:05:00.022 [vent.ItemStateChangedEvent] - eumelEFAT2D changed from 0.00304516 to 0.00315234
2018-12-17 02:05:00.023 [vent.ItemStateChangedEvent] - eumelEFAT2DEURO changed from 0.0005288814 to 0.0005674212
2018-12-17 02:05:00.491 [vent.ItemStateChangedEvent] - sysNUC_Memused changed from 2343 to 2342
2018-12-17 02:05:00.495 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 16.1 to 19.0
2018-12-17 02:05:01.499 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 49.0 to 51.0
2018-12-17 02:05:01.503 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 19.0 to 16.8
2018-12-17 02:05:02.509 [vent.ItemStateChangedEvent] - sysNUC_Memused changed from 2342 to 2343
2018-12-17 02:05:02.510 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 16.8 to 16.9
2018-12-17 02:05:03.155 [vent.ItemStateChangedEvent] - eumelFreq changed from 49.93000030517578 to 49.939998626708984
2018-12-17 02:05:03.157 [vent.ItemStateChangedEvent] - eumelVA changed from 232.3175048828125 to 232.31312561035156
2018-12-17 02:05:03.158 [vent.ItemStateChangedEvent] - eumelVB changed from 231.95492553710938 to 231.9268035888672
2018-12-17 02:05:03.159 [vent.ItemStateChangedEvent] - eumelVC changed from 232.0303192138672 to 231.97882080078125
2018-12-17 02:05:03.159 [vent.ItemStateChangedEvent] - eumelIA changed from 5.450171947479248 to 5.452187538146973
2018-12-17 02:05:03.160 [vent.ItemStateChangedEvent] - eumelIB changed from 0.7733515501022339 to 0.7726718783378601
2018-12-17 02:05:03.166 [vent.ItemStateChangedEvent] - eumelIC changed from 0.6171562671661377 to 0.617382824420929
2018-12-17 02:05:03.167 [vent.ItemStateChangedEvent] - eumelPB changed from 100.06640625 to 99.80078125
2018-12-17 02:05:03.168 [vent.ItemStateChangedEvent] - eumelPA changed from 1118.55078125 to 1119.875
2018-12-17 02:05:03.168 [vent.ItemStateChangedEvent] - Verbund_Watt changed from 1288.984375 to 1290.046875
2018-12-17 02:05:03.169 [vent.ItemStateChangedEvent] - eumelPT changed from 1288.984375 to 1290.046875
2018-12-17 02:05:03.169 [vent.ItemStateChangedEvent] - Verbund_VAR changed from -740.75 to -739.28125
2018-12-17 02:05:03.169 [vent.ItemStateChangedEvent] - eumelEFAA changed from 1447.173828125 to 1447.175537109375
2018-12-17 02:05:03.170 [vent.ItemStateChangedEvent] - eumelEFAC changed from 590.3532104492188 to 590.353271484375
2018-12-17 02:05:03.170 [vent.ItemStateChangedEvent] - Verbund_PTF changed from 1293.171875 to 1294.125
2018-12-17 02:05:03.171 [vent.ItemStateChangedEvent] - Verbund_VA changed from 1589.40625 to 1589.6875
2018-12-17 02:05:03.171 [vent.ItemStateChangedEvent] - eumelEFAB changed from 1085.214599609375 to 1085.2147216796875
2018-12-17 02:05:03.173 [vent.ItemStateChangedEvent] - eumelEFAT changed from 3122.74169921875 to 3122.74365234375
2018-12-17 02:05:03.174 [vent.ItemStateChangedEvent] - eumelEFATKWH changed from 3.12274170 to 3.12274365
2018-12-17 02:05:03.174 [vent.ItemStateChangedEvent] - eumelEFATEURO changed from 0.5620935060 to 0.5620938570
2018-12-17 02:05:03.519 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 16.9 to 17.8
2018-12-17 02:05:03.943 [vent.ItemStateChangedEvent] - FibaroNode3_Power changed from 0.5 to 0.6
2018-12-17 02:05:03.944 [vent.ItemStateChangedEvent] - powTV changed from 0.5 to 0.6
2018-12-17 02:05:03.944 [GroupItemStateChangedEvent] - gPower changed from 56.7 to 56.8 through powTV
2018-12-17 02:05:04.524 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 51.0 to 50.0
2018-12-17 02:05:04.526 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 17.8 to 15.2
2018-12-17 02:05:04.946 [vent.ItemStateChangedEvent] - FibaroNode3_Power changed from 0.6 to 0.5
2018-12-17 02:05:04.947 [GroupItemStateChangedEvent] - gPower changed from 56.8 to 56.7 through powTV
2018-12-17 02:05:04.948 [vent.ItemStateChangedEvent] - powTV changed from 0.6 to 0.5
2018-12-17 02:05:05.533 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 15.2 to 17.4
2018-12-17 02:05:06.539 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 17.4 to 15.0
2018-12-17 02:05:07.543 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 50.0 to 51.0
2018-12-17 02:05:07.545 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 15.0 to 16.4
2018-12-17 02:05:08.258 [vent.ItemStateChangedEvent] - eumelVA changed from 232.31312561035156 to 232.22203063964844
2018-12-17 02:05:08.259 [vent.ItemStateChangedEvent] - eumelVB changed from 231.9268035888672 to 231.849609375
2018-12-17 02:05:08.263 [vent.ItemStateChangedEvent] - eumelVC changed from 231.97882080078125 to 231.72328186035156
2018-12-17 02:05:08.264 [vent.ItemStateChangedEvent] - eumelIA changed from 5.452187538146973 to 5.452070236206055
2018-12-17 02:05:08.265 [vent.ItemStateChangedEvent] - eumelIB changed from 0.7726718783378601 to 0.7759218811988831
2018-12-17 02:05:08.265 [vent.ItemStateChangedEvent] - eumelIC changed from 0.617382824420929 to 0.6152031421661377
2018-12-17 02:05:08.266 [vent.ItemStateChangedEvent] - eumelPA changed from 1119.875 to 1118.53515625
2018-12-17 02:05:08.266 [vent.ItemStateChangedEvent] - eumelPB changed from 99.80078125 to 99.9375
2018-12-17 02:05:08.266 [vent.ItemStateChangedEvent] - eumelPC changed from 70.37109375 to 69.984375
2018-12-17 02:05:08.267 [vent.ItemStateChangedEvent] - Verbund_Watt changed from 1290.046875 to 1288.453125
2018-12-17 02:05:08.267 [vent.ItemStateChangedEvent] - eumelPT changed from 1290.046875 to 1288.453125
2018-12-17 02:05:08.268 [vent.ItemStateChangedEvent] - Verbund_PTF changed from 1294.125 to 1292.734375
2018-12-17 02:05:08.268 [vent.ItemStateChangedEvent] - Verbund_VAR changed from -739.28125 to -739.953125
2018-12-17 02:05:08.268 [vent.ItemStateChangedEvent] - Verbund_VA changed from 1589.6875 to 1589.1875
2018-12-17 02:05:08.269 [vent.ItemStateChangedEvent] - eumelEFAA changed from 1447.175537109375 to 1447.177001953125
2018-12-17 02:05:08.270 [vent.ItemStateChangedEvent] - eumelEFAB changed from 1085.2147216796875 to 1085.21484375
2018-12-17 02:05:08.270 [vent.ItemStateChangedEvent] - eumelEFAC changed from 590.353271484375 to 590.3533935546875
2018-12-17 02:05:08.270 [vent.ItemStateChangedEvent] - eumelEFAT changed from 3122.74365234375 to 3122.74560546875
2018-12-17 02:05:08.271 [vent.ItemStateChangedEvent] - eumelEFATKWH changed from 3.12274365 to 3.12274561
2018-12-17 02:05:08.271 [vent.ItemStateChangedEvent] - eumelEFATEURO changed from 0.5620938570 to 0.5620942098
2018-12-17 02:05:08.510 [me.event.ThingUpdatedEvent] - Thing 'zwave:device:3008c030:node14' has been updated.
2018-12-17 02:05:08.550 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 16.4 to 16.1
2018-12-17 02:05:09.554 [vent.ItemStateChangedEvent] - sysNUC_Memav changed from 5483 to 5482
2018-12-17 02:05:09.558 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 16.1 to 16.6
2018-12-17 02:05:10.563 [vent.ItemStateChangedEvent] - sysNUC_Memav changed from 5482 to 5483
2018-12-17 02:05:10.563 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 51.0 to 49.0
2018-12-17 02:05:10.567 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 16.6 to 16.1
2018-12-17 02:05:11.568 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 49.0 to 51.0
2018-12-17 02:05:11.570 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 16.1 to 15.3
2018-12-17 02:05:12.575 [vent.ItemStateChangedEvent] - sysNUC_Memav changed from 5483 to 5482
2018-12-17 02:05:12.576 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 51.0 to 50.0
2018-12-17 02:05:12.579 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 15.3 to 16.3
2018-12-17 02:05:13.330 [vent.ItemStateChangedEvent] - eumelVA changed from 232.22203063964844 to 232.37149047851562
2018-12-17 02:05:13.330 [vent.ItemStateChangedEvent] - eumelVB changed from 231.849609375 to 232.07789611816406
2018-12-17 02:05:13.330 [vent.ItemStateChangedEvent] - eumelVC changed from 231.72328186035156 to 232.02391052246094
2018-12-17 02:05:13.331 [vent.ItemStateChangedEvent] - eumelIA changed from 5.452070236206055 to 5.463679790496826
2018-12-17 02:05:13.331 [vent.ItemStateChangedEvent] - eumelIB changed from 0.7759218811988831 to 0.7754218578338623
2018-12-17 02:05:13.332 [vent.ItemStateChangedEvent] - eumelIC changed from 0.6152031421661377 to 0.6173437237739563
2018-12-17 02:05:13.332 [vent.ItemStateChangedEvent] - eumelPA changed from 1118.53515625 to 1122.22265625
2018-12-17 02:05:13.334 [vent.ItemStateChangedEvent] - eumelPB changed from 99.9375 to 99.8046875
2018-12-17 02:05:13.334 [vent.ItemStateChangedEvent] - eumelPC changed from 69.984375 to 70.3671875
2018-12-17 02:05:13.335 [vent.ItemStateChangedEvent] - Verbund_Watt changed from 1288.453125 to 1292.390625
2018-12-17 02:05:13.336 [vent.ItemStateChangedEvent] - eumelPT changed from 1288.453125 to 1292.390625
2018-12-17 02:05:13.337 [vent.ItemStateChangedEvent] - Verbund_PTF changed from 1292.734375 to 1296.796875
2018-12-17 02:05:13.337 [vent.ItemStateChangedEvent] - Verbund_VAR changed from -739.953125 to -741.359375
2018-12-17 02:05:13.338 [vent.ItemStateChangedEvent] - Verbund_VA changed from 1589.1875 to 1593.453125
2018-12-17 02:05:13.338 [vent.ItemStateChangedEvent] - eumelEFAA changed from 1447.177001953125 to 1447.1785888671875
2018-12-17 02:05:13.339 [vent.ItemStateChangedEvent] - eumelEFAB changed from 1085.21484375 to 1085.2149658203125
2018-12-17 02:05:13.340 [vent.ItemStateChangedEvent] - eumelEFAC changed from 590.3533935546875 to 590.353515625
2018-12-17 02:05:13.342 [vent.ItemStateChangedEvent] - eumelEFAT changed from 3122.74560546875 to 3122.747314453125
2018-12-17 02:05:13.343 [vent.ItemStateChangedEvent] - eumelEFATKWH changed from 3.12274561 to 3.12274731
2018-12-17 02:05:13.343 [vent.ItemStateChangedEvent] - eumelEFATEURO changed from 0.5620942098 to 0.5620945158
2018-12-17 02:05:13.588 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 50.0 to 51.0
2018-12-17 02:05:13.589 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 16.3 to 17.2
2018-12-17 02:05:14.580 [vent.ItemStateChangedEvent] - FibaroNode3_Power changed from 0.5 to 0.6
2018-12-17 02:05:14.581 [vent.ItemStateChangedEvent] - powTV changed from 0.5 to 0.6
2018-12-17 02:05:14.591 [vent.ItemStateChangedEvent] - sysNUC_Memav changed from 5482 to 5483
2018-12-17 02:05:14.593 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 17.2 to 16.1
2018-12-17 02:05:15.595 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 51.0 to 49.0
2018-12-17 02:05:15.597 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 16.1 to 16.7
2018-12-17 02:05:15.867 [vent.ItemStateChangedEvent] - FibaroNode3_Power changed from 0.6 to 0.5
2018-12-17 02:05:15.867 [vent.ItemStateChangedEvent] - powTV changed from 0.6 to 0.5
2018-12-17 02:05:15.953 [vent.ItemStateChangedEvent] - FibaroNode3_Power changed from 0.5 to 0.6
2018-12-17 02:05:15.954 [vent.ItemStateChangedEvent] - powTV changed from 0.5 to 0.6
2018-12-17 02:05:16.604 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 16.7 to 15.9
2018-12-17 02:05:16.942 [vent.ItemStateChangedEvent] - FibaroNode3_Power changed from 0.6 to 0.5
2018-12-17 02:05:16.943 [vent.ItemStateChangedEvent] - powTV changed from 0.6 to 0.5
2018-12-17 02:05:17.609 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 15.9 to 17.0
2018-12-17 02:05:18.418 [vent.ItemStateChangedEvent] - eumelVA changed from 232.37149047851562 to 232.26820373535156
2018-12-17 02:05:18.419 [vent.ItemStateChangedEvent] - eumelVB changed from 232.07789611816406 to 231.9678192138672
2018-12-17 02:05:18.420 [vent.ItemStateChangedEvent] - eumelVC changed from 232.02391052246094 to 231.9297637939453
2018-12-17 02:05:18.424 [vent.ItemStateChangedEvent] - eumelIA changed from 5.463679790496826 to 5.456265449523926
2018-12-17 02:05:18.424 [vent.ItemStateChangedEvent] - eumelIB changed from 0.7754218578338623 to 0.7737343907356262
2018-12-17 02:05:18.425 [vent.ItemStateChangedEvent] - eumelIC changed from 0.6173437237739563 to 0.6159843802452087
2018-12-17 02:05:18.425 [vent.ItemStateChangedEvent] - eumelPA changed from 1122.22265625 to 1120.83984375
2018-12-17 02:05:18.425 [vent.ItemStateChangedEvent] - eumelPB changed from 99.8046875 to 99.42578125
2018-12-17 02:05:18.426 [vent.ItemStateChangedEvent] - eumelPC changed from 70.3671875 to 70.08203125
2018-12-17 02:05:18.426 [vent.ItemStateChangedEvent] - Verbund_Watt changed from 1292.390625 to 1290.34375
2018-12-17 02:05:18.426 [vent.ItemStateChangedEvent] - eumelPT changed from 1292.390625 to 1290.34375
2018-12-17 02:05:18.426 [vent.ItemStateChangedEvent] - Verbund_PTF changed from 1296.796875 to 1294.4375
2018-12-17 02:05:18.427 [vent.ItemStateChangedEvent] - Verbund_VAR changed from -741.359375 to -739.265625
2018-12-17 02:05:18.427 [vent.ItemStateChangedEvent] - Verbund_VA changed from 1593.453125 to 1590.3125
2018-12-17 02:05:18.427 [vent.ItemStateChangedEvent] - eumelEFAA changed from 1447.1785888671875 to 1447.18017578125
2018-12-17 02:05:18.428 [vent.ItemStateChangedEvent] - eumelEFAB changed from 1085.2149658203125 to 1085.215087890625
2018-12-17 02:05:18.428 [vent.ItemStateChangedEvent] - eumelEFAC changed from 590.353515625 to 590.3536376953125
2018-12-17 02:05:18.428 [vent.ItemStateChangedEvent] - eumelEFAT changed from 3122.747314453125 to 3122.7490234375
2018-12-17 02:05:18.620 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 17.0 to 16.5
2018-12-17 02:05:19.621 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 49.0 to 50.0
2018-12-17 02:05:19.623 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 16.5 to 16.6
2018-12-17 02:05:19.921 [vent.ItemStateChangedEvent] - FibaroNode3_Power changed from 0.5 to 0.6
2018-12-17 02:05:19.921 [vent.ItemStateChangedEvent] - powTV changed from 0.5 to 0.6
2018-12-17 02:05:20.048 [arthome.event.BindingEvent] - org.openhab.binding.zwave.event.BindingEvent@6366457e
2018-12-17 02:05:20.049 [me.event.ThingUpdatedEvent] - Thing 'zwave:device:3008c030:node8' has been updated.
2018-12-17 02:05:20.626 [vent.ItemStateChangedEvent] - sysNUC_Memav changed from 5483 to 5482
2018-12-17 02:05:20.629 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 16.6 to 19.0
2018-12-17 02:05:21.636 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 19.0 to 16.0
2018-12-17 02:05:22.641 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 16.0 to 16.8
2018-12-17 02:05:23.527 [vent.ItemStateChangedEvent] - eumelVA changed from 232.26820373535156 to 232.3933563232422
2018-12-17 02:05:23.527 [vent.ItemStateChangedEvent] - eumelVB changed from 231.9678192138672 to 232.0849151611328
2018-12-17 02:05:23.529 [vent.ItemStateChangedEvent] - eumelVC changed from 231.9297637939453 to 232.03562927246094
2018-12-17 02:05:23.529 [vent.ItemStateChangedEvent] - eumelIA changed from 5.456265449523926 to 5.463507652282715
2018-12-17 02:05:23.530 [vent.ItemStateChangedEvent] - eumelIB changed from 0.7737343907356262 to 0.7749609351158142
2018-12-17 02:05:23.531 [vent.ItemStateChangedEvent] - eumelIC changed from 0.6159843802452087 to 0.6146015524864197
2018-12-17 02:05:23.531 [vent.ItemStateChangedEvent] - eumelPA changed from 1120.83984375 to 1121.73046875
2018-12-17 02:05:23.532 [vent.ItemStateChangedEvent] - eumelPB changed from 99.42578125 to 99.8046875
2018-12-17 02:05:23.532 [vent.ItemStateChangedEvent] - eumelPC changed from 70.08203125 to 70.03125
2018-12-17 02:05:23.532 [vent.ItemStateChangedEvent] - Verbund_Watt changed from 1290.34375 to 1291.5625
2018-12-17 02:05:23.533 [vent.ItemStateChangedEvent] - eumelPT changed from 1290.34375 to 1291.5625
2018-12-17 02:05:23.533 [vent.ItemStateChangedEvent] - Verbund_PTF changed from 1294.4375 to 1295.828125
2018-12-17 02:05:23.534 [vent.ItemStateChangedEvent] - Verbund_VAR changed from -739.265625 to -742.0
2018-12-17 02:05:23.534 [vent.ItemStateChangedEvent] - Verbund_VA changed from 1590.3125 to 1592.796875
2018-12-17 02:05:23.535 [vent.ItemStateChangedEvent] - eumelEFAA changed from 1447.18017578125 to 1447.1817626953125
2018-12-17 02:05:23.535 [vent.ItemStateChangedEvent] - eumelEFAB changed from 1085.215087890625 to 1085.2152099609375
2018-12-17 02:05:23.536 [vent.ItemStateChangedEvent] - eumelEFAC changed from 590.3536376953125 to 590.3536987304688
2018-12-17 02:05:23.536 [vent.ItemStateChangedEvent] - eumelEFAT changed from 3122.7490234375 to 3122.7509765625
2018-12-17 02:05:23.647 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 50.0 to 51.0
2018-12-17 02:05:23.648 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 16.8 to 16.9
2018-12-17 02:05:24.656 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 16.9 to 15.8
2018-12-17 02:05:25.660 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 51.0 to 50.0
2018-12-17 02:05:25.664 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 15.8 to 16.8
2018-12-17 02:05:26.668 [vent.ItemStateChangedEvent] - sysNUC_Memav changed from 5482 to 5483
2018-12-17 02:05:26.669 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 50.0 to 49.0
2018-12-17 02:05:26.672 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 16.8 to 16.3
2018-12-17 02:05:27.072 [vent.ItemStateChangedEvent] - powKWL changed from 35.9 to 36.1
2018-12-17 02:05:27.073 [vent.ItemStateChangedEvent] - FibaroNode6_Power changed from 35.9 to 36.1
2018-12-17 02:05:27.328 [vent.ItemStateChangedEvent] - FibaroNode3_Power changed from 0.6 to 0.5
2018-12-17 02:05:27.329 [vent.ItemStateChangedEvent] - powTV changed from 0.6 to 0.5
2018-12-17 02:05:27.677 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 49.0 to 50.0
2018-12-17 02:05:27.680 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 16.3 to 16.4
2018-12-17 02:05:27.862 [vent.ItemStateChangedEvent] - FibaroNode3_Power changed from 0.5 to 0.6
2018-12-17 02:05:27.863 [vent.ItemStateChangedEvent] - powTV changed from 0.5 to 0.6
2018-12-17 02:05:28.598 [vent.ItemStateChangedEvent] - eumelVA changed from 232.3933563232422 to 232.43218994140625
2018-12-17 02:05:28.599 [vent.ItemStateChangedEvent] - eumelVB changed from 232.0849151611328 to 232.15211486816406
2018-12-17 02:05:28.600 [vent.ItemStateChangedEvent] - eumelVC changed from 232.03562927246094 to 232.00320434570312
2018-12-17 02:05:28.601 [vent.ItemStateChangedEvent] - eumelIA changed from 5.463507652282715 to 5.457843780517578
2018-12-17 02:05:28.601 [vent.ItemStateChangedEvent] - eumelIB changed from 0.7749609351158142 to 0.7758906483650208
2018-12-17 02:05:28.602 [vent.ItemStateChangedEvent] - eumelIC changed from 0.6146015524864197 to 0.6150546669960022
2018-12-17 02:05:28.602 [vent.ItemStateChangedEvent] - eumelPB changed from 99.8046875 to 99.94140625
2018-12-17 02:05:28.603 [vent.ItemStateChangedEvent] - eumelPC changed from 70.03125 to 70.06640625
2018-12-17 02:05:28.603 [vent.ItemStateChangedEvent] - eumelPA changed from 1121.73046875 to 1121.08984375
2018-12-17 02:05:28.604 [vent.ItemStateChangedEvent] - Verbund_Watt changed from 1291.5625 to 1291.09375
2018-12-17 02:05:28.604 [vent.ItemStateChangedEvent] - eumelPT changed from 1291.5625 to 1291.09375
2018-12-17 02:05:28.605 [vent.ItemStateChangedEvent] - Verbund_PTF changed from 1295.828125 to 1295.390625
2018-12-17 02:05:28.605 [vent.ItemStateChangedEvent] - Verbund_VAR changed from -742.0 to -740.9375
2018-12-17 02:05:28.606 [vent.ItemStateChangedEvent] - Verbund_VA changed from 1592.796875 to 1592.046875
2018-12-17 02:05:28.606 [vent.ItemStateChangedEvent] - eumelEFAA changed from 1447.1817626953125 to 1447.1832275390625
2018-12-17 02:05:28.607 [vent.ItemStateChangedEvent] - eumelEFAB changed from 1085.2152099609375 to 1085.2154541015625
2018-12-17 02:05:28.608 [vent.ItemStateChangedEvent] - eumelEFAC changed from 590.3536987304688 to 590.353759765625
2018-12-17 02:05:28.608 [vent.ItemStateChangedEvent] - eumelEFAT changed from 3122.7509765625 to 3122.752685546875
2018-12-17 02:05:28.689 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 16.4 to 17.0
2018-12-17 02:05:29.028 [arthome.event.BindingEvent] - org.openhab.binding.zwave.event.BindingEvent@5be26150
2018-12-17 02:05:29.030 [me.event.ThingUpdatedEvent] - Thing 'zwave:device:3008c030:node14' has been updated.
2018-12-17 02:05:29.693 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 50.0 to 56.0
2018-12-17 02:05:29.694 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 17.0 to 21.4
2018-12-17 02:05:30.698 [vent.ItemStateChangedEvent] - sysNUC_Memused changed from 2343 to 2342
2018-12-17 02:05:30.699 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 56.0 to 51.0
2018-12-17 02:05:30.701 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 21.4 to 28.4
2018-12-17 02:05:31.173 [vent.ItemStateChangedEvent] - FibaroNode3_Power changed from 0.6 to 0.5
2018-12-17 02:05:31.174 [vent.ItemStateChangedEvent] - powTV changed from 0.6 to 0.5
2018-12-17 02:05:31.706 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 28.4 to 16.3
2018-12-17 02:05:32.157 [vent.ItemStateChangedEvent] - sysNUC_CPUload5 changed from 0.8 to 0.9
2018-12-17 02:05:32.161 [vent.ItemStateChangedEvent] - sysNUC_CPUload1 changed from 0.6 to 1.1
2018-12-17 02:05:32.170 [vent.ItemStateChangedEvent] - sysNUC_Packetssent changed from 67916 to 67919
2018-12-17 02:05:32.545 [vent.ItemStateChangedEvent] - FibaroNode3_Power changed from 0.5 to 0.6
2018-12-17 02:05:32.545 [vent.ItemStateChangedEvent] - powTV changed from 0.5 to 0.6
2018-12-17 02:05:32.709 [vent.ItemStateChangedEvent] - sysNUC_Memused changed from 2342 to 2343
2018-12-17 02:05:32.712 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 16.3 to 19.4
2018-12-17 02:05:33.243 [vent.ItemStateChangedEvent] - FibaroNode3_Power changed from 0.6 to 0.7
2018-12-17 02:05:33.243 [vent.ItemStateChangedEvent] - powTV changed from 0.6 to 0.7
2018-12-17 02:05:33.668 [vent.ItemStateChangedEvent] - eumelVA changed from 232.43218994140625 to 232.21163940429688
2018-12-17 02:05:33.669 [vent.ItemStateChangedEvent] - eumelVB changed from 232.15211486816406 to 232.01397705078125
2018-12-17 02:05:33.669 [vent.ItemStateChangedEvent] - eumelVC changed from 232.00320434570312 to 232.60116577148438
2018-12-17 02:05:33.672 [vent.ItemStateChangedEvent] - eumelIA changed from 5.457843780517578 to 5.462320327758789
2018-12-17 02:05:33.672 [vent.ItemStateChangedEvent] - eumelIB changed from 0.7758906483650208 to 0.7728593945503235
2018-12-17 02:05:33.673 [vent.ItemStateChangedEvent] - eumelIC changed from 0.6150546669960022 to 0.6157265901565552
2018-12-17 02:05:33.673 [vent.ItemStateChangedEvent] - eumelPA changed from 1121.08984375 to 1121.2421875
2018-12-17 02:05:33.674 [vent.ItemStateChangedEvent] - eumelPB changed from 99.94140625 to 99.16015625
2018-12-17 02:05:33.674 [vent.ItemStateChangedEvent] - eumelPC changed from 70.06640625 to 70.3828125
2018-12-17 02:05:33.674 [vent.ItemStateChangedEvent] - Verbund_Watt changed from 1291.09375 to 1290.78125
2018-12-17 02:05:33.674 [vent.ItemStateChangedEvent] - eumelPT changed from 1291.09375 to 1290.78125
2018-12-17 02:05:33.675 [vent.ItemStateChangedEvent] - Verbund_PTF changed from 1295.390625 to 1294.953125
2018-12-17 02:05:33.675 [vent.ItemStateChangedEvent] - Verbund_VAR changed from -740.9375 to -741.28125
2018-12-17 02:05:33.675 [vent.ItemStateChangedEvent] - Verbund_VA changed from 1592.046875 to 1591.59375
2018-12-17 02:05:33.675 [vent.ItemStateChangedEvent] - eumelEFAA changed from 1447.1832275390625 to 1447.184814453125
2018-12-17 02:05:33.676 [vent.ItemStateChangedEvent] - eumelEFAC changed from 590.353759765625 to 590.3538818359375
2018-12-17 02:05:33.676 [vent.ItemStateChangedEvent] - eumelEFAT changed from 3122.752685546875 to 3122.75439453125
2018-12-17 02:05:33.715 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 51.0 to 52.0
2018-12-17 02:05:33.718 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 19.4 to 18.0
2018-12-17 02:05:34.721 [vent.ItemStateChangedEvent] - sysNUC_Memused changed from 2343 to 2342
2018-12-17 02:05:34.722 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 52.0 to 50.0
2018-12-17 02:05:34.723 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 18.0 to 16.0
2018-12-17 02:05:35.726 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 50.0 to 51.0
2018-12-17 02:05:35.729 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 16.0 to 16.2
2018-12-17 02:05:36.731 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 51.0 to 50.0
2018-12-17 02:05:36.734 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 16.2 to 15.4
2018-12-17 02:05:37.033 [arthome.event.BindingEvent] - org.openhab.binding.zwave.event.BindingEvent@6611f56d
2018-12-17 02:05:37.036 [me.event.ThingUpdatedEvent] - Thing 'zwave:device:3008c030:node9' has been updated.
2018-12-17 02:05:37.738 [vent.ItemStateChangedEvent] - sysNUC_Memused changed from 2342 to 2343
2018-12-17 02:05:37.739 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 50.0 to 51.0
2018-12-17 02:05:37.741 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 15.4 to 18.0
2018-12-17 02:05:38.745 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 51.0 to 50.0
2018-12-17 02:05:38.749 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 18.0 to 16.4
2018-12-17 02:05:38.769 [vent.ItemStateChangedEvent] - eumelVA changed from 232.21163940429688 to 232.23452758789062
2018-12-17 02:05:38.771 [vent.ItemStateChangedEvent] - eumelVB changed from 232.01397705078125 to 232.0439910888672
2018-12-17 02:05:38.772 [vent.ItemStateChangedEvent] - eumelVC changed from 232.60116577148438 to 232.62547302246094
2018-12-17 02:05:38.775 [vent.ItemStateChangedEvent] - eumelIA changed from 5.462320327758789 to 5.4598517417907715
2018-12-17 02:05:38.775 [vent.ItemStateChangedEvent] - eumelIB changed from 0.7728593945503235 to 0.7767968773841858
2018-12-17 02:05:38.775 [vent.ItemStateChangedEvent] - eumelIC changed from 0.6157265901565552 to 0.6171796917915344
2018-12-17 02:05:38.776 [vent.ItemStateChangedEvent] - eumelPA changed from 1121.2421875 to 1120.20703125
2018-12-17 02:05:38.776 [vent.ItemStateChangedEvent] - eumelPB changed from 99.16015625 to 99.84765625
2018-12-17 02:05:38.777 [vent.ItemStateChangedEvent] - eumelPC changed from 70.3828125 to 70.5703125
2018-12-17 02:05:38.777 [vent.ItemStateChangedEvent] - Verbund_Watt changed from 1290.78125 to 1290.625
2018-12-17 02:05:38.777 [vent.ItemStateChangedEvent] - eumelPT changed from 1290.78125 to 1290.625
2018-12-17 02:05:38.778 [vent.ItemStateChangedEvent] - Verbund_PTF changed from 1294.953125 to 1294.875
2018-12-17 02:05:38.778 [vent.ItemStateChangedEvent] - Verbund_VAR changed from -741.28125 to -742.328125
2018-12-17 02:05:38.779 [vent.ItemStateChangedEvent] - Verbund_VA changed from 1591.59375 to 1592.4375
2018-12-17 02:05:38.779 [vent.ItemStateChangedEvent] - eumelEFAA changed from 1447.184814453125 to 1447.1865234375
2018-12-17 02:05:38.780 [vent.ItemStateChangedEvent] - eumelEFAB changed from 1085.2154541015625 to 1085.2156982421875
2018-12-17 02:05:38.780 [vent.ItemStateChangedEvent] - eumelEFAC changed from 590.3538818359375 to 590.35400390625
2018-12-17 02:05:38.780 [vent.ItemStateChangedEvent] - eumelEFAT changed from 3122.75439453125 to 3122.756591796875
2018-12-17 02:05:39.107 [vent.ItemStateChangedEvent] - FibaroNode3_Power changed from 0.7 to 0.5
2018-12-17 02:05:39.107 [vent.ItemStateChangedEvent] - powTV changed from 0.7 to 0.5
2018-12-17 02:05:39.753 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 50.0 to 49.0
2018-12-17 02:05:39.755 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 16.4 to 17.6
2018-12-17 02:05:40.759 [vent.ItemStateChangedEvent] - sysNUC_Memused changed from 2343 to 2342
2018-12-17 02:05:40.759 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 49.0 to 50.0
2018-12-17 02:05:40.761 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 17.6 to 17.0
2018-12-17 02:05:41.600 [me.event.ThingUpdatedEvent] - Thing 'zwave:device:3008c030:node16' has been updated.
2018-12-17 02:05:41.763 [vent.ItemStateChangedEvent] - sysNUC_Memused changed from 2342 to 2343
2018-12-17 02:05:41.766 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 17.0 to 17.4
2018-12-17 02:05:42.770 [vent.ItemStateChangedEvent] - sysNUC_Memused changed from 2343 to 2342
2018-12-17 02:05:42.771 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 50.0 to 51.0
2018-12-17 02:05:42.774 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 17.4 to 16.8
2018-12-17 02:05:43.780 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 16.8 to 17.0
2018-12-17 02:05:43.841 [vent.ItemStateChangedEvent] - eumelVA changed from 232.23452758789062 to 232.22500610351562
2018-12-17 02:05:43.841 [vent.ItemStateChangedEvent] - eumelVB changed from 232.0439910888672 to 232.02178955078125
2018-12-17 02:05:43.843 [vent.ItemStateChangedEvent] - eumelVC changed from 232.62547302246094 to 232.55914306640625
2018-12-17 02:05:43.844 [vent.ItemStateChangedEvent] - eumelIA changed from 5.4598517417907715 to 5.461671829223633
2018-12-17 02:05:43.845 [vent.ItemStateChangedEvent] - eumelIB changed from 0.7767968773841858 to 0.7748827934265137
2018-12-17 02:05:43.846 [vent.ItemStateChangedEvent] - eumelIC changed from 0.6171796917915344 to 0.616335928440094
2018-12-17 02:05:43.846 [vent.ItemStateChangedEvent] - eumelPA changed from 1120.20703125 to 1120.796875
2018-12-17 02:05:43.847 [vent.ItemStateChangedEvent] - eumelPB changed from 99.84765625 to 99.37890625
2018-12-17 02:05:43.847 [vent.ItemStateChangedEvent] - eumelPC changed from 70.5703125 to 70.4296875
2018-12-17 02:05:43.847 [vent.ItemStateChangedEvent] - Verbund_Watt changed from 1290.625 to 1290.609375
2018-12-17 02:05:43.848 [vent.ItemStateChangedEvent] - eumelPT changed from 1290.625 to 1290.609375
2018-12-17 02:05:43.848 [vent.ItemStateChangedEvent] - Verbund_PTF changed from 1294.875 to 1294.671875
2018-12-17 02:05:43.849 [vent.ItemStateChangedEvent] - Verbund_VAR changed from -742.328125 to -741.40625
2018-12-17 02:05:43.849 [vent.ItemStateChangedEvent] - Verbund_VA changed from 1592.4375 to 1592.109375
2018-12-17 02:05:43.850 [vent.ItemStateChangedEvent] - eumelEFAA changed from 1447.1865234375 to 1447.1881103515625
2018-12-17 02:05:43.851 [vent.ItemStateChangedEvent] - eumelEFAB changed from 1085.2156982421875 to 1085.2158203125
2018-12-17 02:05:43.851 [vent.ItemStateChangedEvent] - eumelEFAC changed from 590.35400390625 to 590.3541259765625
2018-12-17 02:05:43.852 [vent.ItemStateChangedEvent] - eumelEFAT changed from 3122.756591796875 to 3122.75830078125
2018-12-17 02:05:44.785 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 51.0 to 49.0
2018-12-17 02:05:44.788 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 17.0 to 16.1
2018-12-17 02:05:45.791 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 49.0 to 50.0
2018-12-17 02:05:46.203 [vent.ItemStateChangedEvent] - powKWL changed from 36.1 to 36
2018-12-17 02:05:46.204 [vent.ItemStateChangedEvent] - FibaroNode6_Power changed from 36.1 to 36
2018-12-17 02:05:46.798 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 16.1 to 16.3
2018-12-17 02:05:47.801 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 50.0 to 49.0
2018-12-17 02:05:48.808 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 49.0 to 50.0
2018-12-17 02:05:48.811 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 16.3 to 16.9
2018-12-17 02:05:48.913 [vent.ItemStateChangedEvent] - eumelVA changed from 232.22500610351562 to 232.2372589111328
2018-12-17 02:05:48.914 [vent.ItemStateChangedEvent] - eumelVB changed from 232.02178955078125 to 232.02554321289062
2018-12-17 02:05:48.915 [vent.ItemStateChangedEvent] - eumelVC changed from 232.55914306640625 to 232.56227111816406
2018-12-17 02:05:48.917 [vent.ItemStateChangedEvent] - eumelIA changed from 5.461671829223633 to 5.458796977996826
2018-12-17 02:05:48.917 [vent.ItemStateChangedEvent] - eumelIB changed from 0.7748827934265137 to 0.7758906483650208
2018-12-17 02:05:48.918 [vent.ItemStateChangedEvent] - eumelIC changed from 0.616335928440094 to 0.6161015629768372
2018-12-17 02:05:48.919 [vent.ItemStateChangedEvent] - eumelPA changed from 1120.796875 to 1120.77734375
2018-12-17 02:05:48.919 [vent.ItemStateChangedEvent] - eumelPB changed from 99.37890625 to 99.6484375
2018-12-17 02:05:48.919 [vent.ItemStateChangedEvent] - eumelPC changed from 70.4296875 to 70.5078125
2018-12-17 02:05:48.920 [vent.ItemStateChangedEvent] - Verbund_Watt changed from 1290.609375 to 1290.9375
2018-12-17 02:05:48.920 [vent.ItemStateChangedEvent] - eumelPT changed from 1290.609375 to 1290.9375
2018-12-17 02:05:48.920 [vent.ItemStateChangedEvent] - Verbund_VAR changed from -741.40625 to -740.453125
2018-12-17 02:05:48.921 [vent.ItemStateChangedEvent] - Verbund_PTF changed from 1294.671875 to 1295.15625
2018-12-17 02:05:48.921 [vent.ItemStateChangedEvent] - Verbund_VA changed from 1592.109375 to 1591.6875
2018-12-17 02:05:48.922 [vent.ItemStateChangedEvent] - eumelEFAA changed from 1447.1881103515625 to 1447.189697265625
2018-12-17 02:05:48.922 [vent.ItemStateChangedEvent] - eumelEFAB changed from 1085.2158203125 to 1085.2159423828125
2018-12-17 02:05:48.922 [vent.ItemStateChangedEvent] - eumelEFAC changed from 590.3541259765625 to 590.3541870117188
2018-12-17 02:05:48.923 [vent.ItemStateChangedEvent] - eumelEFAT changed from 3122.75830078125 to 3122.760009765625
2018-12-17 02:05:48.979 [vent.ItemStateChangedEvent] - FibaroNode3_Power changed from 0.5 to 0.6
2018-12-17 02:05:48.980 [vent.ItemStateChangedEvent] - powTV changed from 0.5 to 0.6
2018-12-17 02:05:49.816 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 16.9 to 17.5
2018-12-17 02:05:50.819 [vent.ItemStateChangedEvent] - sysNUC_Memav changed from 5483 to 5484
2018-12-17 02:05:50.820 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 50.0 to 49.0
2018-12-17 02:05:50.823 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 17.5 to 17.4
2018-12-17 02:05:50.837 [vent.ItemStateChangedEvent] - senTemp_HeatBad changed from 22.4 to 22.3
2018-12-17 02:05:50.943 [vent.ItemStateChangedEvent] - FibaroNode3_Power changed from 0.6 to 0.5
2018-12-17 02:05:50.944 [vent.ItemStateChangedEvent] - powTV changed from 0.6 to 0.5
2018-12-17 02:05:51.827 [vent.ItemStateChangedEvent] - sysNUC_Memav changed from 5484 to 5483
2018-12-17 02:05:51.828 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 49.0 to 50.0
2018-12-17 02:05:51.831 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 17.4 to 16.1
2018-12-17 02:05:52.833 [vent.ItemStateChangedEvent] - sysNUC_Memav changed from 5483 to 5475
2018-12-17 02:05:52.834 [vent.ItemStateChangedEvent] - sysNUC_Memused changed from 2342 to 2350
2018-12-17 02:05:52.834 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 50.0 to 59.0
2018-12-17 02:05:52.836 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 16.1 to 40.4
2018-12-17 02:05:53.839 [vent.ItemStateChangedEvent] - sysNUC_Memused changed from 2350 to 2351
2018-12-17 02:05:53.840 [vent.ItemStateChangedEvent] - sysNUC_CPUtemp changed from 59.0 to 51.0
2018-12-17 02:05:53.842 [vent.ItemStateChangedEvent] - sysNUC_CPUload changed from 40.4 to 33.4
2018-12-17 02:05:54.017 [vent.ItemStateChangedEvent] - eumelVA changed from 232.2372589111328 to 232.255859375
2018-12-17 02:05:54.018 [vent.ItemStateChangedEvent] - eumelVB changed from 232.02554321289062 to 232.10366821289062
2018-12-17 02:05:54.018 [vent.ItemStateChangedEvent] - eumelVC changed from 232.56227111816406 to 232.5340576171875
2018-12-17 02:05:54.019 [vent.ItemStateChangedEvent] - eumelIA changed from 5.458796977996826 to 5.4585466384887695
2018-12-17 02:05:54.019 [vent.ItemStateChangedEvent] - eumelIB changed from 0.7758906483650208 to 0.7737656235694885
2018-12-17 02:05:54.019 [vent.ItemStateChangedEvent] - eumelIC changed from 0.6161015629768372 to 0.6123281121253967
2018-12-17 02:05:54.020 [vent.ItemStateChangedEvent] - eumelPA changed from 1120.77734375 to 1120.93359375
2018-12-17 02:05:54.020 [vent.ItemStateChangedEvent] - eumelPB changed from 99.6484375 to 99.4375
2018-12-17 02:05:54.020 [vent.ItemStateChangedEvent] - eumelPC changed from 70.5078125 to 69.90234375
2018-12-17 02:05:54.021 [vent.ItemStateChangedEvent] - Verbund_Watt changed from 1290.9375 to 1290.28125

The only rules I found which could occur at 5 minutes past 2 a.m are:

var Number varStromkosten = 0.18

rule "Wh in kWh" //divide by 1000 for better visualization
    when   
       Item eumelEFAT received update or Time cron "0 */5 * * * ?"
    then   
      var Number WhBezug = eumelEFAT.state as DecimalType   
      var Number kWhBezug = WhBezug/1000
      var Number EuroBezug = kWhBezug*varStromkosten
      postUpdate(eumelEFATKWH, kWhBezug)
      postUpdate(eumelEFATEURO, EuroBezug)
      logInfo("Rules", "Euro und kWh Bezug updated to: "+eumelEFATKWH.state)
    end


rule "YTD energy values"
  when
    Time cron "0 */5 * * * ?"
  then
   
    val Yearbeginn = now.withTimeAtStartOfDay.withDayOfYear(1)
      logInfo("Rules", "Datum: "+Yearbeginn)

    var Number YTDBezug = eumelEFATKWH.deltaSince(Yearbeginn)
    logInfo("Rules", "YTD Bezug updated to: "+YTDBezug)
    if (YTDBezug == null) {
      eumelEFATYTD.postUpdate(eumelEFATKWH.state)
    }

    else  {
    postUpdate(eumelEFATYTD,YTDBezug)
   
    }
    logInfo("Rules", "EFATYTD updated to: "+eumelEFATYTD.state)
end 

rule "Day energy values"
when
  Time cron "0 */5 * * * ?"
then
  var Number Energycons2day = eumelEFATKWH.deltaSince(now.withTimeAtStartOfDay())
  postUpdate(eumelEFAT2D,Energycons2day)
  logInfo("Rules","Energy consumption today updated to"+eumelEFAT2D.state)
  var Number Energycost2day = ((eumelEFAT2D.state as DecimalType)*varStromkosten)
  postUpdate(eumelEFAT2DEURO,Energycost2day)
  logInfo("Rules","Energy cost today updated to"+eumelEFAT2DEURO.state)
end

I will deactivate these rules…just a guess..

Anything obvious in your eyes?

Regards,
Herbert

I don’t think it’s the Rules. I think the Rules might be a symptom of the same problem. Something is happening, perhaps a flurry of events, that is causing OH to run out of threads or something like that and preventing it from processing the events.

any hint how to proceed - what kind of logging could point me to a solution (problem)?
I just restarted the openhab service → working again

thank you

Look at your system usage and start to systematically disable Rules or addon’s and the like until the problem stops happening. I don’t have any good suggestions.

OK - thank you! Concerning sytem usage, I did not find anything suspicious…will post an update, if I can find anything.

Since I know a bit about your installation Herbert, I would like to point out that some of the things connected send events as fast as once every second, and you have more than 10 of them. so it’s not unreasonable to assume that the controller and OpenHAB will be receiving data at a rate of 10 events per second or more.

Hi Zisis,

thank you for the hint - I reduced the zwave traffic for single nodes → did not help. If you mean the “eumel” and “sysNUC” Item changes → that shouldn’t be the issue, as it should be normal to update different channels of the same thing…
Next step: trying to deactivate mqtt → see if that helps (more tomorrow).