I have searched the log file. The channels of the weather station are updated only once when the sitemap is reloaded (e.g. after editing and then saving).
Thanks for the log. To me it seems that your OH installation does not receive any events from CCU. I can’t see any messages like this in the log (this is an example from my installation):
2022-10-08 10:49:23.983 [TRACE] [nal.communicator.server.XmlRpcServer] - Server parsed XmlRpcMessage:
This means the CCU can not send messages to port 9125 on the machine where OH is running. This is the reason why you don’t get any value updates.
Many thanks for analyzing the log-files. Unfortunately I’m a litle bit confused now. My OpenHab runs on a raspberry PI4 with openhabian. I tought this is an easy setup made especially for openhab. I googled now for I while but was not able to find some tutorials how to check an open ports. May be you can give me a hint.
I think, openHabian is really good for a simple installation of OH but it probably does not now about all ports that may be required by other devices.
I don’t know how the firewall is configured in openHabian, but you can try whether ufw is active with ufw status. If ufw is active it will display all open ports. With ufw allow you can open additional ports.
If ufw is not available, you can use iptables --list to see all rules that are configured.
Many thanks for your reply Martin. It seems there is neither ufw nor iptables installed on my system. So I installed ufw with: sudo apt-get install ufw
Active ufw with: sudo ufw enable
and allowed any connection: sudo ufw default allow
Now any incomming connection or request should be allowed. Shouldn’t it?
If neither ufw nor iptables was installed maybe no firewall was installed at all.
You can check the port status with ufw status verbose.
ufw app list shows only known ports, i.e. standard ports with numbers less then 1024. The binding and Homematic are using non-standard ports.
Maybe there is another possible cause for the problem: how did you connect your raspi to your network? Via WiFi or ethernet cable? I would highly recommend ethernet cable with a fixed ip address.
To verify whether the binding is listening on the correct address and port you can run: netstat -apn | grep 9125
Output should be similar to this:
tcp6 0 0 192.168.2.80:9125 192.168.2.93:59522 ESTABLISHED 12626/java
tcp6 0 0 192.168.2.80:9125 192.168.2.93:37658 ESTABLISHED 12626/java
after that a lot of lines starting with unix are following. But I think they are not relevant.
As I can see there is just one line relted to port 9125 that says the system is listening. It looks to me like there is no connection. Is ist possible that there is a problem with the CCU2? I think I have changed noting. It was working well with OH2.5.
My Raspberry is connected via ethernet cable and has a static IP.
It seems that it is only listining on the tcp6 address :::9125, because there is no entry for “0.0.0.0:9125” or 192.168.8.118:9125. This can cause the problem.
ok I disabled tcp6 but that did not fix the problem. I also disable tcp6 in the settings of OH3.
Now I have an entry like you mentioned:
tcp 0 0 0.0.0.0:9125 0.0.0.0:* LISTEN 1168/java
It seems also not to be a problem of homematic or homematic IP I just changed the setpoint temperature of one of my thermostats (normal homematic) manually, but this changed not the value displayed in the OH app or in the webUI. I realy think that its a special homatic binding problem. I can send commands to the ccu2 but I can not receive data from it. All other devices work well (shelly/tp-link)
The problem is that every binding uses a different technology stack.
I have never seen this kind of problems with the binding before. According to the output the binding is now listening on the correct and waiting for messages from the CCU.
You could try to ssh into the CCU and check the log files in /var/log especially hmserver.log would contain messages if something goes wrong when it tries to send an event to the Homematic binding.
So I was realy able to get access via ssh. I took me a lot of time to find out that umlauts are not working in the password which has to be defined in the CCU2 system configuration. (how to - SSH-Zugang auf CCU2 einrichten - HomeMatic-Dokumentation)
Oct 14 09:02:57 de.eq3.cbcs.server.core.vertx.KeyServerWorker ERROR [vert.x-worker-thread-2] Missing key server configuration parameter (Network.Key) for mode: KEYSERVER_LOCAL
and
Oct 14 09:04:10 de.eq3.cbcs.legacy.bidcos.rpc.internal.InterfaceInitializer ERROR [vert.x-worker-thread-0] IO Exception: Could not add interface: 9e682990-c394-4ce6-8180-e89f18016007
de.eq3.cbcs.legacy.communication.rpc.RpcIOException: java.net.ConnectException: Connection refused (Connection refused)
at de.eq3.cbcs.legacy.communication.rpc.internal.transport.http.HttpTransport.sendRequest(HttpTransport.java:110)
at de.eq3.cbcs.legacy.communication.rpc.internal.rpc.RpcClient.sendRequest(RpcClient.java:94)
at de.eq3.cbcs.legacy.communication.rpc.internal.rpc.RpcClient.invoke(RpcClient.java:82)
at com.sun.proxy.$Proxy19.listDevices(Unknown Source)
at de.eq3.cbcs.legacy.bidcos.rpc.internal.LegacyBackendClient.listDevices(LegacyBackendClient.java:139)
at de.eq3.cbcs.legacy.bidcos.rpc.internal.DeviceUtil.synchronizedBackendDevices(DeviceUtil.java:150)
at de.eq3.cbcs.legacy.bidcos.rpc.internal.InterfaceInitializer.handle(InterfaceInitializer.java:109)
at de.eq3.cbcs.legacy.bidcos.rpc.internal.InterfaceInitializer.handle(InterfaceInitializer.java:26)
at io.vertx.core.eventbus.impl.HandlerRegistration.deliver(HandlerRegistration.java:212)
at io.vertx.core.eventbus.impl.HandlerRegistration.handle(HandlerRegistration.java:191)
at io.vertx.core.eventbus.impl.EventBusImpl.lambda$deliverToHandler$3(EventBusImpl.java:505)
at io.vertx.core.impl.ContextImpl.lambda$wrapTask$2(ContextImpl.java:337)
at io.vertx.core.impl.TaskQueue.lambda$new$0(TaskQueue.java:60)
at java.util.concurrent.ThreadPoolExecutor.runWorker(ThreadPoolExecutor.java:1149)
at java.util.concurrent.ThreadPoolExecutor$Worker.run(ThreadPoolExecutor.java:624)
at java.lang.Thread.run(Thread.java:748)
Caused by: java.net.ConnectException: Connection refused (Connection refused)
at java.net.PlainSocketImpl.socketConnect(Native Method)
at java.net.AbstractPlainSocketImpl.doConnect(AbstractPlainSocketImpl.java:350)
at java.net.AbstractPlainSocketImpl.connectToAddress(AbstractPlainSocketImpl.java:206)
at java.net.AbstractPlainSocketImpl.connect(AbstractPlainSocketImpl.java:188)
at java.net.SocksSocketImpl.connect(SocksSocketImpl.java:392)
at java.net.Socket.connect(Socket.java:589)
at org.apache.http.conn.scheme.PlainSocketFactory.connectSocket(PlainSocketFactory.java:120)
at org.apache.http.impl.conn.DefaultClientConnectionOperator.openConnection(DefaultClientConnectionOperator.java:179)
at org.apache.http.impl.conn.AbstractPoolEntry.open(AbstractPoolEntry.java:144)
at org.apache.http.impl.conn.AbstractPooledConnAdapter.open(AbstractPooledConnAdapter.java:134)
at org.apache.http.impl.client.DefaultRequestDirector.tryConnect(DefaultRequestDirector.java:612)
at org.apache.http.impl.client.DefaultRequestDirector.execute(DefaultRequestDirector.java:447)
at org.apache.http.impl.client.AbstractHttpClient.doExecute(AbstractHttpClient.java:884)
at org.apache.http.impl.client.CloseableHttpClient.execute(CloseableHttpClient.java:82)
at org.apache.http.impl.client.CloseableHttpClient.execute(CloseableHttpClient.java:107)
at org.apache.http.impl.client.CloseableHttpClient.execute(CloseableHttpClient.java:55)
at de.eq3.cbcs.legacy.communication.rpc.internal.transport.http.HttpTransport.sendRequest(HttpTransport.java:106)
... 15 more
and the following warnings:
Oct 14 09:02:59 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-1] SYSTEM ADVICE: pre-conditions for deployment of LocalServerAdapterInitialization still not met - check deployment configuration (still unfulfilled: [persistent.data.loaded])
Oct 14 09:02:59 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-1] SYSTEM ADVICE: pre-conditions for deployment of LocalServerPersistentDataLoader still not met - check deployment configuration
Oct 14 09:02:59 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-1] SYSTEM ADVICE: pre-conditions for deployment of TransactionManagementVerticle still not met - check deployment configuration (still unfulfilled: [persistent.data.loaded])
Oct 14 09:02:59 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-1] SYSTEM ADVICE: pre-conditions for deployment of DeviceInclusionAcceptHandler still not met - check deployment configuration (still unfulfilled: [persistent.data.loaded])
Oct 14 09:02:59 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-1] SYSTEM ADVICE: pre-conditions for deployment of KryoPersistenceWorker still not met - check deployment configuration
Oct 14 09:02:59 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-1] SYSTEM ADVICE: pre-conditions for deployment of DeviceBackgroundUpdateSubsystem still not met - check deployment configuration
Oct 14 09:02:59 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-1] SYSTEM ADVICE: pre-conditions for deployment of LegacyNotificationHandler still not met - check deployment configuration (still unfulfilled: [connector.open])
Oct 14 09:02:59 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-1] SYSTEM ADVICE: pre-conditions for deployment of LocalServerFirmwareUpdateInitialization still not met - check deployment configuration (still unfulfilled: [connector.open][firmware.update.subsystem.started][persistent.data.loaded])
Oct 14 09:02:59 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-1] SYSTEM ADVICE: pre-conditions for deployment of LegacyBackendNotificationHandler still not met - check deployment configuration (still unfulfilled: [connector.open])
Oct 14 09:03:06 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-1] SYSTEM ADVICE: pre-conditions for deployment of LocalServerAdapterInitialization still not met - check deployment configuration (still unfulfilled: [persistent.data.loaded])
Oct 14 09:03:06 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-1] SYSTEM ADVICE: pre-conditions for deployment of LocalServerPersistentDataLoader still not met - check deployment configuration
Oct 14 09:03:06 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-1] SYSTEM ADVICE: pre-conditions for deployment of TransactionManagementVerticle still not met - check deployment configuration (still unfulfilled: [persistent.data.loaded])
Oct 14 09:03:06 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-1] SYSTEM ADVICE: pre-conditions for deployment of DeviceInclusionAcceptHandler still not met - check deployment configuration (still unfulfilled: [persistent.data.loaded])
Oct 14 09:03:06 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-1] SYSTEM ADVICE: pre-conditions for deployment of KryoPersistenceWorker still not met - check deployment configuration
Oct 14 09:03:06 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-1] SYSTEM ADVICE: pre-conditions for deployment of DeviceBackgroundUpdateSubsystem still not met - check deployment configuration
Oct 14 09:03:06 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-1] SYSTEM ADVICE: pre-conditions for deployment of LegacyNotificationHandler still not met - check deployment configuration (still unfulfilled: [connector.open])
Oct 14 09:03:06 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-1] SYSTEM ADVICE: pre-conditions for deployment of LocalServerFirmwareUpdateInitialization still not met - check deployment configuration (still unfulfilled: [connector.open][firmware.update.subsystem.started][persistent.data.loaded])
Oct 14 09:03:06 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-1] SYSTEM ADVICE: pre-conditions for deployment of LegacyBackendNotificationHandler still not met - check deployment configuration (still unfulfilled: [connector.open])
Oct 14 09:03:13 de.eq3.cbcs.vertx.management.VertxManager INFO [vert.x-eventloop-thread-1] SYSTEM: start of KryoPersistenceWorker succeeded (67350049-cd01-4282-a534-7e24f420777f)
Oct 14 09:03:13 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-1] SYSTEM ADVICE: pre-conditions for deployment of LocalServerAdapterInitialization still not met - check deployment configuration (still unfulfilled: [persistent.data.loaded])
Oct 14 09:03:13 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-1] SYSTEM ADVICE: pre-conditions for deployment of TransactionManagementVerticle still not met - check deployment configuration (still unfulfilled: [persistent.data.loaded])
Oct 14 09:03:13 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-1] SYSTEM ADVICE: pre-conditions for deployment of DeviceInclusionAcceptHandler still not met - check deployment configuration (still unfulfilled: [persistent.data.loaded])
Oct 14 09:03:13 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-1] SYSTEM ADVICE: pre-conditions for deployment of LegacyNotificationHandler still not met - check deployment configuration (still unfulfilled: [connector.open])
Oct 14 09:03:13 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-1] SYSTEM ADVICE: pre-conditions for deployment of LocalServerFirmwareUpdateInitialization still not met - check deployment configuration (still unfulfilled: [connector.open][firmware.update.subsystem.started][persistent.data.loaded])
Oct 14 09:03:13 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-1] SYSTEM ADVICE: pre-conditions for deployment of LegacyBackendNotificationHandler still not met - check deployment configuration (still unfulfilled: [connector.open])
Oct 14 09:03:14 de.eq3.cbcs.server.core.otau.AbstractUpdateSubsystem INFO [vert.x-eventloop-thread-0] SYSTEM: DeviceLiveUpdateSubsystem Verticle or Worker started
Oct 14 09:03:14 de.eq3.cbcs.server.core.live_otau.DeviceLiveUpdateSubsystem INFO [vert.x-eventloop-thread-0] SYSTEM: DeviceLiveUpdateSubsystem started
Oct 14 09:03:14 de.eq3.cbcs.vertx.management.VertxManager INFO [vert.x-eventloop-thread-0] SYSTEM: start of HMIPTRXWriterWorker succeeded (d9f5f808-9583-4848-90d6-e48a7eae3293)
Oct 14 09:03:14 de.eq3.cbcs.vertx.management.VertxManager INFO [vert.x-eventloop-thread-0] SYSTEM: start of KeyServerWorker succeeded (8a4068e7-b14c-4395-b752-b125f1373f7e)
Oct 14 09:03:14 de.eq3.cbcs.vertx.management.VertxManager INFO [vert.x-eventloop-thread-0] SYSTEM: start of CyclicSmokeDetectorAwakening succeeded (a91fa1f2-072f-410a-a3da-d8cc00592352)
Oct 14 09:03:14 de.eq3.cbcs.server.core.otau.AbstractUpdateSubsystem INFO [vert.x-eventloop-thread-0] SYSTEM: DeviceBackgroundUpdateSubsystem Verticle or Worker started
Oct 14 09:03:15 de.eq3.cbcs.server.local.base.internal.LocalServerPersistentDataLoader INFO [vert.x-eventloop-thread-0] SYSTEM: LocalServerPersistentDataLoader Verticle or Worker started
Oct 14 09:03:15 de.eq3.cbcs.vertx.management.VertxManager INFO [vert.x-eventloop-thread-1] SYSTEM: start of LocalServerPersistentDataLoader succeeded (14649a6a-6e4c-492c-a742-8a2e7735e6fe)
Oct 14 09:03:15 de.eq3.cbcs.vertx.management.VertxManager INFO [vert.x-eventloop-thread-0] SYSTEM: start of DeviceLiveUpdateSubsystem succeeded (6be745e8-1ae4-4875-9d0f-a810bc53ee5a)
Oct 14 09:03:15 de.eq3.cbcs.vertx.management.VertxManager INFO [vert.x-eventloop-thread-0] SYSTEM: start of DeviceBackgroundUpdateSubsystem succeeded (45ebd11a-1aa4-4796-ab92-125eabc688b8)
Oct 14 09:03:15 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-0] SYSTEM ADVICE: pre-conditions for deployment of FirmwareLoaderFileSystem still not met - check deployment configuration (still unfulfilled: [persistent.data.loaded])
Oct 14 09:03:15 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-0] SYSTEM ADVICE: pre-conditions for deployment of BackendCommandHandler still not met - check deployment configuration (still unfulfilled: [transaction.management.ready])
Oct 14 09:03:15 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-0] SYSTEM ADVICE: pre-conditions for deployment of IncomingHMIPFrameHandler still not met - check deployment configuration (still unfulfilled: [persistent.data.loaded])
Oct 14 09:03:15 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-0] SYSTEM ADVICE: pre-conditions for deployment of LegacyAPIWorker still not met - check deployment configuration (still unfulfilled: [connector.open])
Oct 14 09:03:15 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-0] SYSTEM ADVICE: pre-conditions for deployment of LegacyInitializion still not met - check deployment configuration (still unfulfilled: [legacy.api.worker][connector.open][persistent.data.loaded])
Oct 14 09:03:15 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-0] SYSTEM ADVICE: long-lasting deployment, check deployment configuration - currently deployed 11 out of 22
Oct 14 09:03:18 de.eq3.cbcs.server.core.vertx.IncomingHMIPFrameHandler INFO [vert.x-eventloop-thread-0] SYSTEM: IncomingHMIPFrameHandler Verticle or Worker started
Oct 14 09:03:18 de.eq3.cbcs.vertx.management.VertxManager INFO [vert.x-eventloop-thread-1] SYSTEM: start of IncomingHMIPFrameHandler succeeded (34bc0525-72e5-4d80-8ef5-7c36a3b71a84)
Oct 14 09:03:19 de.eq3.cbcs.server.core.otau.util.FirmwareLoaderFileSystem INFO [vert.x-worker-thread-0] SYSTEM: Firmware update directory is set to /etc/config/firmware
Oct 14 09:03:19 de.eq3.cbcs.server.core.otau.util.FirmwareLoaderFileSystem INFO [vert.x-worker-thread-0] SYSTEM: FirmwareLoaderFileSystem Verticle or Worker started
Oct 14 09:03:19 de.eq3.cbcs.vertx.management.VertxManager INFO [vert.x-eventloop-thread-1] SYSTEM: start of FirmwareLoaderFileSystem succeeded (aca13c63-3170-40c1-8397-ec687a14e432)
Oct 14 09:03:20 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-1] SYSTEM ADVICE: pre-conditions for deployment of LegacyNotificationHandler still not met - check deployment configuration (still unfulfilled: [connector.open])
Oct 14 09:03:20 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-1] SYSTEM ADVICE: pre-conditions for deployment of LocalServerFirmwareUpdateInitialization still not met - check deployment configuration (still unfulfilled: [connector.open])
Oct 14 09:03:20 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-1] SYSTEM ADVICE: pre-conditions for deployment of LegacyBackendNotificationHandler still not met - check deployment configuration (still unfulfilled: [connector.open])
Oct 14 09:03:21 de.eq3.cbcs.server.local.base.internal.LocalServerAdapterInitialization INFO [vert.x-eventloop-thread-0] SYSTEM: LocalServerAdapterInitialization Verticle or Worker started
Oct 14 09:03:21 de.eq3.cbcs.vertx.management.VertxManager INFO [vert.x-eventloop-thread-1] SYSTEM: start of LocalServerAdapterInitialization succeeded (678d4a6a-724e-477d-b3b6-003e60687bab)
Oct 14 09:03:21 de.eq3.cbcs.server.core.vertx.DeviceInclusionAcceptHandler INFO [vert.x-eventloop-thread-0] SYSTEM: DeviceInclusionAcceptHandler Verticle or Worker started
Oct 14 09:03:21 de.eq3.cbcs.vertx.management.VertxManager INFO [vert.x-eventloop-thread-1] SYSTEM: start of DeviceInclusionAcceptHandler succeeded (4434579b-64ff-410f-98bb-0f73cc2ef1a4)
Oct 14 09:03:21 de.eq3.cbcs.server.core.transaction.TransactionManagementVerticle INFO [vert.x-eventloop-thread-0] SYSTEM: TransactionManagementVerticle Verticle or Worker started
Oct 14 09:03:21 de.eq3.cbcs.vertx.management.VertxManager INFO [vert.x-eventloop-thread-0] SYSTEM: start of TransactionManagementVerticle succeeded (d3207821-2e5c-451e-8b68-5df6fa62d070)
Oct 14 09:03:21 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-0] SYSTEM ADVICE: long-lasting deployment, check deployment configuration - currently deployed 16 out of 22
Oct 14 09:03:21 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-0] SYSTEM ADVICE: pre-conditions for deployment of BackendCommandHandler still not met - check deployment configuration (still unfulfilled: [transaction.management.ready])
Oct 14 09:03:21 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-0] SYSTEM ADVICE: pre-conditions for deployment of LegacyAPIWorker still not met - check deployment configuration (still unfulfilled: [connector.open])
Oct 14 09:03:21 de.eq3.cbcs.vertx.management.VertxManager WARN [vert.x-eventloop-thread-0] SYSTEM ADVICE: pre-conditions for deployment of LegacyInitializion still not met - check deployment configuration (still unfulfilled: [legacy.api.worker][connector.open])
I think these lines contain the relevant information:
The exception clearly shows that the CCU can not connect to openHAB. Something seems to block the connection.
But the first line is also a bit strange. Normally there should be issued the name of interface (like HmIP-RF).
There is one idea left that you can check and try. I saw this in your bridge configuration:
This was the problem!
I thought callbackHost is some kind of alternate address where you usually put the same address or zero.
Of course the 192.168.8.135 was not the address of the Raspi but the address of the CCU2. This would probably have been noticed immediately if I had not overwritten the first address with x.
In the logs I see now incoming values of the CCU2 and the data of the weather station update now also.