[SOLVED] [Satel] Disconnections after Integra mainboard upgrade
Hi! I recently changed mainboard from Integra 64 to Integra 256 plus and now I have problem with disconnections from Satel. Below is log. Hope somebody can help me to fix this. @druciak?
2019-08-03 22:03:36.955 [INFO ] [.satel.internal.protocol.Ethm1Module] - ETHM-1 module connected successfully
2019-08-03 22:03:39.719 [INFO ] [.satel.internal.protocol.SatelModule] - Unhandled exception occurred in communication loop, disconnecting.
java.time.DateTimeException: Invalid value for MonthOfYear (valid values 1 - 12): 23
        at java.time.temporal.ValueRange.checkValidValue(ValueRange.java:311) ~[?:?]
        at java.time.temporal.ChronoField.checkValidValue(ChronoField.java:703) ~[?:?]
        at java.time.LocalDate.of(LocalDate.java:267) ~[?:?]
        at java.time.LocalDateTime.of(LocalDateTime.java:336) ~[?:?]
        at org.openhab.binding.satel.internal.command.IntegraStatusCommand.getIntegraTime(IntegraStatusCommand.java:46) ~[269:org.openhab.binding.satel:2.5.0.M1]        at org.openhab.binding.satel.internal.command.IntegraStatusCommand.handleResponse(IntegraStatusCommand.java:69) ~[269:org.openhab.binding.satel:2.5.0.M1]        at org.openhab.binding.satel.internal.protocol.SatelModule.communicationLoop(SatelModule.java:403) [269:org.openhab.binding.satel:2.5.0.M1]
        at org.openhab.binding.satel.internal.protocol.SatelModule.access$1(SatelModule.java:349) [269:org.openhab.binding.satel:2.5.0.M1]
        at org.openhab.binding.satel.internal.protocol.SatelModule$CommunicationWatchdog$2.run(SatelModule.java:484) [269:org.openhab.binding.satel:2.5.0.M1]
2019-08-03 22:03:39.720 [INFO ] [.satel.internal.protocol.Ethm1Module] - Closing connection to ETHM-1 module
2019-08-03 22:03:39.954 [INFO ] [.satel.internal.protocol.Ethm1Module] - Connecting to ETHM-1 module at 192.168.1.191:7094
2019-08-03 22:03:39.955 [INFO ] [.satel.internal.protocol.Ethm1Module] - ETHM-1 module connected successfully
2019-08-03 22:03:43.439 [INFO ] [.satel.internal.protocol.SatelModule] - Unhandled exception occurred in communication loop, disconnecting.
2019-08-03 22:03:43.441 [INFO ] [.satel.internal.protocol.Ethm1Module] - Closing connection to ETHM-1 module
Hi, please enable DEBUG level and post here logs.
Here you go
2019-08-04 07:32:49.792 [INFO ] [.satel.internal.protocol.Ethm1Module] - Closing connection to ETHM-1 module
2019-08-04 07:32:50.090 [INFO ] [del.script.UPS Runtime Duration is: ] - 01 hours, 21 minutes, 00 seconds
2019-08-04 07:32:50.282 [INFO ] [.satel.internal.protocol.Ethm1Module] - Connecting to ETHM-1 module at 192.168.1.191:7094
2019-08-04 07:32:50.283 [INFO ] [.satel.internal.protocol.Ethm1Module] - ETHM-1 module connected successfully
2019-08-04 07:32:52.546 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: 0928000900C1FEFE0D000000007DF4FE0D
2019-08-04 07:32:52.547 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 0D, payload = 00 00 00 00
2019-08-04 07:32:52.548 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: IntegraStateEvent: command = 0D, extended = true, active = {}
2019-08-04 07:32:52.550 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 0E, payload = 00
2019-08-04 07:32:52.550 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: 95250009AF00FEFE0E00506EFE0D0000
2019-08-04 07:32:52.790 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: A737000A00AFFEFE0E000000007E06FE0D
2019-08-04 07:32:52.791 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 0E, payload = 00 00 00 00
2019-08-04 07:32:52.792 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: IntegraStateEvent: command = 0E, extended = true, active = {}
2019-08-04 07:32:52.793 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 0F, payload = 00
2019-08-04 07:32:52.793 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: 0F8D000A8700FEFE0F00506CFE0D0000
2019-08-04 07:32:52.936 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 7F, payload = 00
2019-08-04 07:32:53.040 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: 022D000B0087FEFE0F000000007E16FE0D
2019-08-04 07:32:53.040 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 0F, payload = 00 00 00 00
2019-08-04 07:32:53.041 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: IntegraStateEvent: command = 0F, extended = true, active = {}
2019-08-04 07:32:53.042 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 10, payload = 00
2019-08-04 07:32:53.042 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: E571000BB000FEFE1000506AFE0D0000
2019-08-04 07:32:53.290 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: B4C0000C00B0FEFE10000000007E26FE0D
2019-08-04 07:32:53.291 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 10, payload = 00 00 00 00
2019-08-04 07:32:53.291 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: IntegraStateEvent: command = 10, extended = true, active = {}
2019-08-04 07:32:53.292 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 11, payload = 00
2019-08-04 07:32:53.293 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: 921F000CD600FEFE11005068FE0D0000
2019-08-04 07:32:53.540 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: 330A000D00D6FEFE11000000007E36FE0D
2019-08-04 07:32:53.540 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 11, payload = 00 00 00 00
2019-08-04 07:32:53.541 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: IntegraStateEvent: command = 11, extended = true, active = {}
2019-08-04 07:32:53.542 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 12, payload = 00
2019-08-04 07:32:53.545 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: E97B000DB700FEFE12005066FE0D0000
2019-08-04 07:32:53.790 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: 5901000E00B7FEFE12000000007E46FE0D
2019-08-04 07:32:53.791 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 12, payload = 00 00 00 00
2019-08-04 07:32:53.791 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: IntegraStateEvent: command = 12, extended = true, active = {}
2019-08-04 07:32:53.792 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 13, payload = 00
2019-08-04 07:32:53.792 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: 7073000EE400FEFE13005064FE0D0000
2019-08-04 07:32:53.938 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 7F, payload = 00
2019-08-04 07:32:54.040 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: DCFF000F00E4FEFE13000000007E56FE0D
2019-08-04 07:32:54.041 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 13, payload = 00 00 00 00
2019-08-04 07:32:54.041 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: IntegraStateEvent: command = 13, extended = true, active = {}
2019-08-04 07:32:54.042 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 15, payload = 00
2019-08-04 07:32:54.043 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: 2376000FAC00FEFE15005060FE0D0000
2019-08-04 07:32:54.290 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: D63A001000ACFEFE15000000007E76FE0D
2019-08-04 07:32:54.291 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 15, payload = 00 00 00 00
2019-08-04 07:32:54.291 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: IntegraStateEvent: command = 15, extended = true, active = {}
2019-08-04 07:32:54.292 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 14, payload = 00
2019-08-04 07:32:54.293 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: 8EF800108700FEFE14005062FE0D0000
2019-08-04 07:32:54.540 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: 3D4C00110087FEFE14000000007E66FE0D
2019-08-04 07:32:54.541 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 14, payload = 00 00 00 00
2019-08-04 07:32:54.541 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: IntegraStateEvent: command = 14, extended = true, active = {}
2019-08-04 07:32:54.542 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 16, payload = 00
2019-08-04 07:32:54.543 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: 114F0011B500FEFE1600505EFE0D0000
2019-08-04 07:32:54.790 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: 6BAB001200B5FEFE16000000007E87FE0D
2019-08-04 07:32:54.791 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 16, payload = 00 00 00 00
2019-08-04 07:32:54.791 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: IntegraStateEvent: command = 16, extended = true, active = {}
2019-08-04 07:32:54.792 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 27, payload = 00
2019-08-04 07:32:54.793 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: 62690012FA00FEFE2700503BFE0D0000
2019-08-04 07:32:54.939 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 7F, payload = 00
2019-08-04 07:32:55.040 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: 9631001300FAFEFE27000000007FA0FE0D
2019-08-04 07:32:55.040 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 27, payload = 00 00 00 00
2019-08-04 07:32:55.041 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: IntegraStateEvent: command = 27, extended = true, active = {}
2019-08-04 07:32:55.042 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 2B, payload = 00
2019-08-04 07:32:55.042 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: 652600139400FEFE2B005033FE0D0000
2019-08-04 07:32:55.290 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: 945700140094FEFE2B000000007FE0FE0D
2019-08-04 07:32:55.290 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 2B, payload = 00 00 00 00
2019-08-04 07:32:55.291 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: IntegraStateEvent: command = 2B, extended = true, active = {}
2019-08-04 07:32:55.292 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 25, payload = 00
2019-08-04 07:32:55.292 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: 9F630014E000FEFE2500503FFE0D0000
2019-08-04 07:32:55.540 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: EE72001500E0FEFE25000000007F80FE0D
2019-08-04 07:32:55.540 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 25, payload = 00 00 00 00
2019-08-04 07:32:55.540 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: IntegraStateEvent: command = 25, extended = true, active = {}
2019-08-04 07:32:55.541 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 1A, payload =
2019-08-04 07:32:55.541 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: D0F900154D00FEFE1AD7FCFE0D000000
2019-08-04 07:32:55.790 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: 35E40016004DFEFE1A20BF1D1706160944A80039FE0D
2019-08-04 07:32:55.791 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 1A, payload = 20 BF 1D 17 06 16 09 44 A8
2019-08-04 07:32:55.791 [INFO ] [.satel.internal.protocol.SatelModule] - Unhandled exception occurred in communication loop, disconnecting.
2019-08-04 07:32:55.792 [INFO ] [.satel.internal.protocol.Ethm1Module] - Closing connection to ETHM-1 module
2019-08-04 07:32:55.793 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: org.openhab.binding.satel.internal.event.ConnectionStatusEvent: connected = false, reason = Unhandled exception: java.time.DateTimeException: Invalid value for MonthOfYear (valid values 1 - 12): 23
2019-08-04 07:32:55.794 [DEBUG] [.satel.internal.protocol.SatelModule] - Communication thread stopped
2019-08-04 07:32:56.282 [DEBUG] [.satel.internal.protocol.SatelModule] - Communication thread started
2019-08-04 07:32:56.283 [INFO ] [.satel.internal.protocol.Ethm1Module] - Connecting to ETHM-1 module at 192.168.1.191:7094
2019-08-04 07:32:56.284 [INFO ] [.satel.internal.protocol.Ethm1Module] - ETHM-1 module connected successfully
2019-08-04 07:32:56.284 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 7F, payload = 00
2019-08-04 07:32:56.285 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: 153B0000C900FEFE7F004F8BFE0D0000
2019-08-04 07:32:56.537 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: C323000100C9FEFE7FFFFFFFFFFFFFFEF08AFE0D
2019-08-04 07:32:56.537 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 7F, payload = FF FF FF FF FF FF
2019-08-04 07:32:56.538 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: org.openhab.binding.satel.internal.event.ConnectionStatusEvent: connected = true, reason = null
2019-08-04 07:32:56.540 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: NewStatesEvent: changed = [00,01,02,03,04,05,06,07,08,09,0A,0B,0C,0D,0E,0F,10,11,12,13,14,15,16,17,18,19,1A,1B,1C,1D,1E,1F,20,21,22,23,24,25,26,27,28,29,2A,2B,2C,2D,2E,2F]
2019-08-04 07:32:56.541 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 00, payload = 00
2019-08-04 07:32:56.543 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 00, payload = 00
2019-08-04 07:32:56.544 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 00, payload = 00
2019-08-04 07:32:56.545 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 00, payload = 00
2019-08-04 07:32:56.546 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 00, payload = 00
2019-08-04 07:32:56.547 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 00, payload = 00
2019-08-04 07:32:56.548 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 00, payload = 00
2019-08-04 07:32:56.551 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 00, payload = 00
2019-08-04 07:32:56.552 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 00, payload = 00
2019-08-04 07:32:56.556 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 00, payload = 00
2019-08-04 07:32:56.557 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 00, payload = 00
2019-08-04 07:32:56.560 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 00, payload = 00
2019-08-04 07:32:56.561 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 00, payload = 00
2019-08-04 07:32:56.562 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 00, payload = 00
2019-08-04 07:32:56.563 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 00, payload = 00
2019-08-04 07:32:56.563 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 17, payload = 00
2019-08-04 07:32:56.564 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 00, payload = 00
2019-08-04 07:32:56.565 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 17, payload = 00
2019-08-04 07:32:56.565 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 00, payload = 00
2019-08-04 07:32:56.566 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 17, payload = 00
2019-08-04 07:32:56.566 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 7F, payload = 00
2019-08-04 07:32:56.567 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: 76770001B600FEFE7F004F8BFE0D0000
2019-08-04 07:32:56.787 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: CE09000200B6FEFE7FFFFFFFFFFFFFFEF08AFE0D
2019-08-04 07:32:56.787 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 7F, payload = FF FF FF FF FF FF
2019-08-04 07:32:56.788 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: NewStatesEvent: changed = [00,01,02,03,04,05,06,07,08,09,0A,0B,0C,0D,0E,0F,10,11,12,13,14,15,16,17,18,19,1A,1B,1C,1D,1E,1F,20,21,22,23,24,25,26,27,28,29,2A,2B,2C,2D,2E,2F]
2019-08-04 07:32:56.789 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 00, payload = 00
2019-08-04 07:32:56.791 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 09, payload = 00
2019-08-04 07:32:56.791 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 0A, payload = 00
2019-08-04 07:32:56.792 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 2A, payload = 00
2019-08-04 07:32:56.792 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 0B, payload = 00
2019-08-04 07:32:56.793 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 0C, payload = 00
2019-08-04 07:32:56.793 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 0D, payload = 00
2019-08-04 07:32:56.793 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 0E, payload = 00
2019-08-04 07:32:56.794 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 0F, payload = 00
2019-08-04 07:32:56.794 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 10, payload = 00
2019-08-04 07:32:56.794 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 11, payload = 00
2019-08-04 07:32:56.795 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 12, payload = 00
2019-08-04 07:32:56.795 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 13, payload = 00
2019-08-04 07:32:56.795 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 15, payload = 00
2019-08-04 07:32:56.796 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 14, payload = 00
2019-08-04 07:32:56.796 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 16, payload = 00
2019-08-04 07:32:56.796 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 27, payload = 00
2019-08-04 07:32:56.797 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 2B, payload = 00
2019-08-04 07:32:56.797 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 25, payload = 00
2019-08-04 07:32:56.798 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 00, payload = 00
2019-08-04 07:32:56.799 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 00, payload = 00
2019-08-04 07:32:56.800 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 00, payload = 00
2019-08-04 07:32:56.800 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 1A, payload =
2019-08-04 07:32:56.801 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 00, payload = 00
2019-08-04 07:32:56.802 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 00, payload = 00
2019-08-04 07:32:56.803 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 00, payload = 00
2019-08-04 07:32:56.804 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 00, payload = 00
2019-08-04 07:32:56.805 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 00, payload = 00
2019-08-04 07:32:56.805 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 17, payload = 00
2019-08-04 07:32:56.806 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 17, payload = 00
2019-08-04 07:32:56.806 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 00, payload = 00
2019-08-04 07:32:56.807 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 17, payload = 00
2019-08-04 07:32:56.807 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 00, payload = 00
2019-08-04 07:32:56.808 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 00, payload = 00
2019-08-04 07:32:56.808 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: 2CEA0002F200FEFE0000508AFE0D0000
2019-08-04 07:32:57.037 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: F04C000300F2FEFE00000000000000000000000000000000000000000000000000000000000000000077DEFE0D
2019-08-04 07:32:57.038 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 00, payload = 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
2019-08-04 07:32:57.038 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: IntegraStateEvent: command = 00, extended = true, active = {}
2019-08-04 07:32:57.042 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 09, payload = 00
2019-08-04 07:32:57.043 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: 1D9900031600FEFE09005078FE0D0000
2019-08-04 07:32:57.288 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: 9F0600040016FEFE09000000007DB4FE0D
2019-08-04 07:32:57.288 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 09, payload = 00 00 00 00
2019-08-04 07:32:57.289 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: IntegraStateEvent: command = 09, extended = true, active = {}
2019-08-04 07:32:57.290 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 0A, payload = 00
2019-08-04 07:32:57.290 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: DE0F00049100FEFE0A005076FE0D0000
2019-08-04 07:32:57.538 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: B52D00050091FEFE0A000000007DC4FE0D
2019-08-04 07:32:57.538 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 0A, payload = 00 00 00 00
2019-08-04 07:32:57.539 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: IntegraStateEvent: command = 0A, extended = true, active = {}
2019-08-04 07:32:57.539 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 2A, payload = 00
2019-08-04 07:32:57.540 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: 25AB00050F00FEFE2A005035FE0D0000
2019-08-04 07:32:57.787 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: E81B0006000FFEFE2A000000007FD0FE0D
2019-08-04 07:32:57.788 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 2A, payload = 00 00 00 00
2019-08-04 07:32:57.788 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: IntegraStateEvent: command = 2A, extended = true, active = {}
2019-08-04 07:32:57.789 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 0B, payload = 00
2019-08-04 07:32:57.790 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: 444900062300FEFE0B005074FE0D0000
2019-08-04 07:32:57.940 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 7F, payload = 00
2019-08-04 07:32:58.038 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: 520600070023FEFE0B000000007DD4FE0D
2019-08-04 07:32:58.038 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 0B, payload = 00 00 00 00
2019-08-04 07:32:58.039 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: IntegraStateEvent: command = 0B, extended = true, active = {}
2019-08-04 07:32:58.040 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 0C, payload = 00
2019-08-04 07:32:58.040 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: 97BF00078900FEFE0C005072FE0D0000
2019-08-04 07:32:58.288 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: E98800080089FEFE0C000000007DE4FE0D
2019-08-04 07:32:58.288 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 0C, payload = 00 00 00 00
2019-08-04 07:32:58.289 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: IntegraStateEvent: command = 0C, extended = true, active = {}
2019-08-04 07:32:58.290 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 0D, payload = 00
2019-08-04 07:32:58.290 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: 5BC000088500FEFE0D005070FE0D0000
2019-08-04 07:32:58.538 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: 171E00090085FEFE0D000000007DF4FE0D
2019-08-04 07:32:58.538 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 0D, payload = 00 00 00 00
2019-08-04 07:32:58.539 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: IntegraStateEvent: command = 0D, extended = true, active = {}
2019-08-04 07:32:58.540 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 0E, payload = 00
2019-08-04 07:32:58.540 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: FC1E00092A00FEFE0E00506EFE0D0000
2019-08-04 07:32:58.787 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: 8D25000A002AFEFE0E000000007E06FE0D
2019-08-04 07:32:58.788 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 0E, payload = 00 00 00 00
2019-08-04 07:32:58.788 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: IntegraStateEvent: command = 0E, extended = true, active = {}
2019-08-04 07:32:58.789 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 0F, payload = 00
2019-08-04 07:32:58.790 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: 578C000A8600FEFE0F00506CFE0D0000
2019-08-04 07:32:58.941 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 7F, payload = 00
2019-08-04 07:32:59.038 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: A073000B0086FEFE0F000000007E16FE0D
2019-08-04 07:32:59.038 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 0F, payload = 00 00 00 00
2019-08-04 07:32:59.039 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: IntegraStateEvent: command = 0F, extended = true, active = {}
2019-08-04 07:32:59.040 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 10, payload = 00
2019-08-04 07:32:59.040 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: B148000B0C00FEFE1000506AFE0D0000
2019-08-04 07:32:59.288 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: 6A3E000C000CFEFE10000000007E26FE0D
2019-08-04 07:32:59.288 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 10, payload = 00 00 00 00
2019-08-04 07:32:59.289 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: IntegraStateEvent: command = 10, extended = true, active = {}
2019-08-04 07:32:59.290 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 11, payload = 00
2019-08-04 07:32:59.290 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: 7A57000CB700FEFE11005068FE0D0000
2019-08-04 07:32:59.537 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: E120000D00B7FEFE11000000007E36FE0D
2019-08-04 07:32:59.538 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 11, payload = 00 00 00 00
2019-08-04 07:32:59.538 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: IntegraStateEvent: command = 11, extended = true, active = {}
2019-08-04 07:32:59.539 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 12, payload = 00
2019-08-04 07:32:59.540 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: 2F39000DAF00FEFE12005066FE0D0000
2019-08-04 07:32:59.787 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: 5F8F000E00AFFEFE12000000007E46FE0D
2019-08-04 07:32:59.788 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 12, payload = 00 00 00 00
2019-08-04 07:32:59.788 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: IntegraStateEvent: command = 12, extended = true, active = {}
2019-08-04 07:32:59.789 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 13, payload = 00
2019-08-04 07:32:59.790 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: 5540000E8400FEFE13005064FE0D0000
2019-08-04 07:32:59.942 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 7F, payload = 00
2019-08-04 07:33:00.039 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: 1A65000F0084FEFE13000000007E56FE0D
2019-08-04 07:33:00.039 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 13, payload = 00 00 00 00
2019-08-04 07:33:00.040 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: IntegraStateEvent: command = 13, extended = true, active = {}
2019-08-04 07:33:00.041 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 15, payload = 00
2019-08-04 07:33:00.041 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: BAEE000F3100FEFE15005060FE0D0000
2019-08-04 07:33:00.289 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: AC5800100031FEFE15000000007E76FE0D
2019-08-04 07:33:00.289 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 15, payload = 00 00 00 00
2019-08-04 07:33:00.290 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: IntegraStateEvent: command = 15, extended = true, active = {}
2019-08-04 07:33:00.290 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 14, payload = 00
2019-08-04 07:33:00.291 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: 910200108700FEFE14005062FE0D0000
2019-08-04 07:33:00.538 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: 8B8200110087FEFE14000000007E66FE0D
2019-08-04 07:33:00.539 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 14, payload = 00 00 00 00
2019-08-04 07:33:00.539 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: IntegraStateEvent: command = 14, extended = true, active = {}
2019-08-04 07:33:00.540 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 16, payload = 00
2019-08-04 07:33:00.541 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: 4E260011BC00FEFE1600505EFE0D0000
2019-08-04 07:33:00.788 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: 91D9001200BCFEFE16000000007E87FE0D
2019-08-04 07:33:00.789 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 16, payload = 00 00 00 00
2019-08-04 07:33:00.789 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: IntegraStateEvent: command = 16, extended = true, active = {}
2019-08-04 07:33:00.790 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 27, payload = 00
2019-08-04 07:33:00.791 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: A55500121B00FEFE2700503BFE0D0000
2019-08-04 07:33:00.943 [DEBUG] [.satel.internal.protocol.SatelModule] - Command already in the queue: Message: command = 7F, payload = 00
2019-08-04 07:33:01.038 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: 74B70013001BFEFE27000000007FA0FE0D
2019-08-04 07:33:01.039 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 27, payload = 00 00 00 00
2019-08-04 07:33:01.040 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: IntegraStateEvent: command = 27, extended = true, active = {}
2019-08-04 07:33:01.041 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 2B, payload = 00
2019-08-04 07:33:01.041 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: B76D00133E00FEFE2B005033FE0D0000
2019-08-04 07:33:01.289 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: 4E520014003EFEFE2B000000007FE0FE0D
2019-08-04 07:33:01.289 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 2B, payload = 00 00 00 00
2019-08-04 07:33:01.290 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: IntegraStateEvent: command = 2B, extended = true, active = {}
2019-08-04 07:33:01.291 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 25, payload = 00
2019-08-04 07:33:01.291 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: 229400143000FEFE2500503FFE0D0000
2019-08-04 07:33:01.538 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: 441000150030FEFE25000000007F80FE0D
2019-08-04 07:33:01.539 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 25, payload = 00 00 00 00
2019-08-04 07:33:01.539 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: IntegraStateEvent: command = 25, extended = true, active = {}
2019-08-04 07:33:01.540 [DEBUG] [.satel.internal.protocol.SatelModule] - Sending message: Message: command = 1A, payload =
2019-08-04 07:33:01.541 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Encrypting data: 365500155F00FEFE1AD7FCFE0D000000
2019-08-04 07:33:01.789 [DEBUG] [.satel.internal.protocol.Ethm1Module] - Decrypted data: 039A0016005FFEFE1A20BF1D1706161544A80069FE0D
2019-08-04 07:33:01.789 [DEBUG] [.satel.internal.protocol.SatelModule] - Got response: Message: command = 1A, payload = 20 BF 1D 17 06 16 15 44 A8
2019-08-04 07:33:01.790 [INFO ] [.satel.internal.protocol.SatelModule] - Unhandled exception occurred in communication loop, disconnecting.
2019-08-04 07:33:01.790 [INFO ] [.satel.internal.protocol.Ethm1Module] - Closing connection to ETHM-1 module
2019-08-04 07:33:01.791 [DEBUG] [satel.internal.event.EventDispatcher] - Distributing event: org.openhab.binding.satel.internal.event.ConnectionStatusEvent: connected = false, reason = Unhandled exception: java.time.DateTimeException: Invalid value for MonthOfYear (valid values 1 - 12): 23
2019-08-04 07:33:01.792 [DEBUG] [.satel.internal.protocol.SatelModule] - Communication thread stopped
2019-08-04 07:33:02.282 [DEBUG] [.satel.internal.protocol.SatelModule] - Communication thread started
2019-08-04 07:33:02.283 [INFO ] [.satel.internal.protocol.Ethm1Module] - Connecting to ETHM-1 module at 192.168.1.191:7094
2019-08-04 07:33:02.283 [INFO ] [.satel.internal.protocol.Ethm1Module] - ETHM-1 module connected successfully
Is there a date-time or zone/locale that needs setting on the new board, or something?
So here is interesting part:
First 7 bytes should be date and time in BCD: 20BF-1D-17 06:16:09
As you can see both date and time are corrupted, they look like random bytes.
Could you make sure (using DloadX or panel) you have correct date and time set?
It would make sense to ignore corrupted values in such case, so I will prepare a fix for this in my spare time.
I am not aware of any zone with 23 months in year :wink: