Hi All,
I am using Modbus binding to control and access my devices. Previously, I was working in simulator HW where Modbus is working properly and able to access devices.
Now, I am working in actual HW and getting error. I have read and implemented other’s solutions. But it is not fixing my issue. Below, I have provided the details,
.things
Bridge modbus:serial:slave04 [port="/dev/ttyACM0",baud=9600,id=4,stopBits="1.0",parity="none",dataBits=8,encoding="rtu"]
// InputControlModule is Manual call point
// Analog Input Register , 30001 + 0x08
Bridge poller inputControlModule[start=8, length=2, refresh=300, type="input"]
Thing data input1[readStart="8",readValueType="int32",readTransform="JS(conversion.js)"]
//slave 0x80 = 128 - First Smoke Detector
Bridge modbus:serial:slave0x80 [port="/dev/ttyACM0",baud=9600,id=128,stopBits="1.0",parity="none",dataBits=8,encoding="rtu"]
//Holding Register = 40001 + 8 = 40009
Bridge poller smokeDetector [start=8, length=2, refresh=1000,type="input"]
Thing data smokeDetector01[readStart="8",readValueType="int32",readTransform="JS(conversion.js)"] //Working one
//Reset the SmokeDetector at register 0xAD
Bridge poller resetSmokeDetector [ start=173, length=2, refresh=0,type="coil"]
Thing data resetSmokeDetector01[writeTransform="01",writeStart="173",writeValueType="bit",writeType="coil"]
//slave 0x40 = 64 - Second Smoke Detector
Bridge modbus:serial:slave0x40 [port="/dev/ttyACM0",baud=9600,id=64,stopBits="1.0",parity="none",dataBits=8,encoding="rtu"]
Thing data smokeDetector02[readStart="8",readValueType="int32",readTransform="JS(conversion.js)"] //Working one
Thing data resetSmokeDetector02[writeTransform="01",writeStart="173",writeValueType="bit",writeType="coil"]
//slave 0x01 - Third Smoke Detector
Bridge modbus:serial:slave0x01 [port="/dev/ttyACM0",baud=9600,id=01,stopBits="1.0",parity="none",dataBits=8,encoding="rtu"]
Thing data smokeDetector03[readStart="8",readValueType="int32",readTransform="JS(conversion.js)"] //Working one
Thing data resetSmokeDetector04[writeTransform="01",writeStart="173",writeValueType="bit",writeType="coil"]
//slave 0x20 = 32 - Fourth Smoke Detector
Bridge modbus:serial:slave0x20 [port="/dev/ttyACM0",baud=9600,id=32,stopBits="1.0",parity="none",dataBits=8,encoding="rtu"]
Thing data smokeDetector04[readStart="8",readValueType="int32",readTransform="JS(conversion.js)"] //Working one
// Fire Alram
//slave 0x10 = 16
Bridge modbus:serial:slave0x10 [port="/dev/ttyACM0",baud=9600,id=16,stopBits="1.0",parity="none",dataBits=8,encoding="rtu"]{
// OutputControlModule is fire alarm or Hooter
// Discrete output Coils
// Discrete register = 0xAC
// 0xAC = 172d
Bridge poller fireAlram [start=172,length=2,refresh=1000,type="holding"]
Thing data fireAlram1[readStart="172",readValueType="int32",writeStart="172",writeValueType="int32",writeType="holding"]
.items
// Fire Alram
Number FireAlarm "FireAlarm_Value [%d]" <fire> {channel="modbus:data:slave0x10:fireAlram:fireAlram1:number"}
Switch FireAlarm_Switch "FireAlarm_Switch" {channel="modbus:data:slave0x10:fireAlram:fireAlram1:switch"}
//Manual Call Point
Number Manual_Value "Manual_Call_Point [%d]" <wallswitch> {channel="modbus:data:slave01:inputControlModule:input1:number"}
Switch Manual_Switch "Manual_CallPoint_Switch [%d]" {channel="modbus:data:slave01:inputControlModule:input1:switch"}
//First Smoke Detector
Number SmokeDetector01 "SmokeDetector01_Value [%d]" <smoke> { channel="modbus:data:slave0x80:smokeDetector:smokeDetector01:number" }
Switch SmokeDetector01_Switch "SmokeDetector01_Switch [%d]" <smoke> { channel="modbus:data:slave0x80:smokeDetector:smokeDetector01:switch" }
Switch ResetSmokeDetector01 "Reseting_SmokeDetector01 [%d]" { channel="modbus:data:slave0x80:resetSmokeDetector:resetSmokeDetector01:switch" }
//Second Smoke Detector
Number SmokeDetector02 "SmokeDetector02_Value [%d]" <smoke> { channel="modbus:data:slave0x40:smokeDetector:smokeDetector02:number" }
Switch SmokeDetector02_Switch "SmokeDetector02_Switch [%d]" <smoke> { channel="modbus:data:slave0x40:smokeDetector:smokeDetector02:switch" }
Switch ResetSmokeDetector02 "Reseting_SmokeDetector02 [%d]" { channel="modbus:data:slave0x40:resetSmokeDetector:resetSmokeDetector02:switch" }
//Third Smoke Detector
Number SmokeDetector03 "SmokeDetector03_Value [%d]" <smoke> { channel="modbus:data:slave0x01:smokeDetector:smokeDetector03:number" }
Switch SmokeDetector03_Switch "SmokeDetector03_Switch [%d]" <smoke> { channel="modbus:data:slave0x80:smokeDetector:smokeDetector03:switch" }
Switch ResetSmokeDetector03 "Reseting_SmokeDetector03 [%d]" { channel="modbus:data:slave0x01:resetSmokeDetector:resetSmokeDetector03:switch" }
//Fourth Smoke Detector
Number SmokeDetector04 "SmokeDetector04_Value [%d]" <smoke> { channel="modbus:data:slave0x20:smokeDetector:smokeDetector04:number" }
Switch SmokeDetector04_Switch "SmokeDetector04_Switch [%d]" <smoke> { channel="modbus:data:slave0x20:smokeDetector:smokeDetector04:switch" }
Switch ResetSmokeDetector04 "Reseting_SmokeDetector04 [%d]" { channel="modbus:data:slave0x40:resetSmokeDetector:resetSmokeDetector04:switch" }
.log
5:19:09.518 [ERROR] [et.wimpi.modbus.io.ModbusRTUTransport] - Last request: 04 04 00 08 00 02 f0 5c
15:19:09.518 [ERROR] [et.wimpi.modbus.io.ModbusRTUTransport] - failed to read: CRC Error in received frame: 3 bytes: 04 04 00
15:19:09.518 [ERROR] [mpi.modbus.io.ModbusSerialTransaction] - execute try 1/1 error: I/O exception: IOException CRC Error in received frame: 3 bytes: 04 04 00 . Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@24d94233 (unit id 4 & transaction 7396). Serial parameters: SerialParameters@29f6f91c[portName=/dev/ttyACM0,baudRate=9600,flowControlIn=none,flowControlOut=none,databits=8,stopbits=1,parity=none,encoding=rtu,echo=false,receiveTimeoutMillis=1500]
grep: java.nio.file.NoSuchFileException: /var/lib/openhab2/queued15:19:09.518 [ERROR] [mpi.modbus.io.ModbusSerialTransaction] - execute reached max tries 1, throwing last error: I/O exception: IOException CRC Error in received frame: 3 bytes: 04 04 00 . Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@24d94233 (unit id 4 & transaction 7396). Serial parameters: SerialParameters@29f6f91c[portName=/dev/ttyACM0,baudRate=9600,flowControlIn=none,flowControlOut=none,databits=8,stopbits=1,parity=none,encoding=rtu,echo=false,receiveTimeoutMillis=1500]
15:19:09.518 [WARN ] [ort.modbus.internal.ModbusManagerImpl] - Try 2 out of 3 failed when executing request (ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@3e6ecadb[slaveId=4,functionCode=READ_INPUT_REGISTERS,start=8,length=2,maxTries=3]). Will try again soon. Error was I/O error, so reseting the connection. Error details: net.wimpi.modbus.ModbusIOException I/O exception: IOException CRC Error in received frame: 3 bytes: 04 04 00 [operation ID 71bd894e-f23c-47c1-a2ea-da1dcfb9ca5b]
15:19:09.519 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - destroyObject for connection SerialConnection@182eac6d[portName=/dev/ttyACM0,port=/dev/ttyACM0] and endpoint ModbusSerialSlaveEndpoint@7b6c5372[portName=/dev/ttyACM0] -> closing the connection
15:19:09.561 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - Created connection SerialConnection@3ab69fb8[portName=/dev/ttyACM0,port=<null>] for endpoint ModbusSerialSlaveEndpoint@7b6c5372[portName=/dev/ttyACM0]
15:19:09.561 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - Passivating connection SerialConnection@3ab69fb8[portName=/dev/ttyACM0,port=<null>] for endpoint ModbusSerialSlaveEndpoint@7b6c5372[portName=/dev/ttyACM0]...
15:19:09.561 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - (passivate) Connection SerialConnection@3ab69fb8[portName=/dev/ttyACM0,port=<null>] (endpoint ModbusSerialSlaveEndpoint@7b6c5372[portName=/dev/ttyACM0]) age (1554112149561ms) is below the reconnectAfterMillis (-1ms) limit and connection time (0) is after the "disconnectBeforeConnectedMillis"=-1. Keep the connection open.
15:19:09.562 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - ...Passivated connection SerialConnection@3ab69fb8[portName=/dev/ttyACM0,port=<null>] for endpoint ModbusSerialSlaveEndpoint@7b6c5372[portName=/dev/ttyACM0]
15:19:09.562 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - invalidating connection for endpoint ModbusSerialSlaveEndpoint@7b6c5372[portName=/dev/ttyACM0] took 43 ms
15:19:09.562 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - Executing task BasicPollTaskImpl@3a515949[request=ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@3e6ecadb[slaveId=4,functionCode=READ_INPUT_REGISTERS,start=8,length=2,maxTries=3],endpoint=ModbusSerialSlaveEndpoint@7b6c5372[portName=/dev/ttyACM0],callback=org.openhab.binding.modbus.internal.handler.ModbusPollerThingHandlerImpl$ReadCallbackDelegator@818e012] (oneOff=false)! Waiting for connection. Idle connections for this endpoint: 0, and active 1 [operation ID 71bd894e-f23c-47c1-a2ea-da1dcfb9ca5b]
15:19:10.501 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - Waited 939ms (interConnectDelayMillis 1000ms, interTransactionDelayMillis 35ms) before connecting disconnected connection SerialConnection@3ab69fb8[portName=/dev/ttyACM0,port=<null>] for endpoint ModbusSerialSlaveEndpoint@22a6ff3d[portName=/dev/ttyACM0], to allow delay between connections re-connects
15:19:10.502 [TRACE] [net.wimpi.modbus.net.SerialConnection] - Got Port Identifier
15:19:10.508 [TRACE] [net.wimpi.modbus.net.SerialConnection] - Got Serial Port
15:19:10.508 [TRACE] [net.wimpi.modbus.net.SerialConnection] - i/o Streams prepared
15:19:10.508 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - Waited 0ms (interTransactionDelayMillis 35ms) before giving returning connection SerialConnection@3ab69fb8[portName=/dev/ttyACM0,port=/dev/ttyACM0] for endpoint ModbusSerialSlaveEndpoint@22a6ff3d[portName=/dev/ttyACM0], to ensure delay between transactions.
15:19:10.509 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - borrowing connection (got Optional[SerialConnection@3ab69fb8[portName=/dev/ttyACM0,port=/dev/ttyACM0]]) for endpoint ModbusSerialSlaveEndpoint@22a6ff3d[portName=/dev/ttyACM0] took 5572 ms
15:19:10.509 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - Executing task BasicPollTaskImpl@5d411317[request=ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@607b1c96[slaveId=32,functionCode=READ_INPUT_REGISTERS,start=8,length=2,maxTries=3],endpoint=ModbusSerialSlaveEndpoint@22a6ff3d[portName=/dev/ttyACM0],callback=org.openhab.binding.modbus.internal.handler.ModbusPollerThingHandlerImpl$ReadCallbackDelegator@329aa566] (oneOff=false)! Connection received in 5572 ms [operation ID f4fddf7d-7f7c-4a51-8c4f-b92a4cf5c76c]
15:19:10.509 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - Try 2 out of 3 [operation ID f4fddf7d-7f7c-4a51-8c4f-b92a4cf5c76c]
15:19:10.509 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - Ensuring that enough time passes before retrying again. Sleeping if necessary [operation ID f4fddf7d-7f7c-4a51-8c4f-b92a4cf5c76c]
15:19:10.509 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - Sleep ended, slept 0 [operation ID f4fddf7d-7f7c-4a51-8c4f-b92a4cf5c76c]
15:19:10.509 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - Going execute transaction with request request (FC=READ_INPUT_REGISTERS): 00 00 00 00 00 06 20 04 00 08 00 02 [operation ID f4fddf7d-7f7c-4a51-8c4f-b92a4cf5c76c]
15:19:10.510 [DEBUG] [et.wimpi.modbus.io.ModbusRTUTransport] - Sent: 20 04 00 08 00 02 f6 b8
15:19:10.523 [TRACE] [et.wimpi.modbus.io.ModbusRTUTransport] - Managed to read at least one byte
15:19:10.527 [DEBUG] [et.wimpi.modbus.io.ModbusRTUTransport] - Response: 20 04 00 02 00
15:19:10.528 [ERROR] [et.wimpi.modbus.io.ModbusRTUTransport] - Last request: 20 04 00 08 00 02 f6 b8
15:19:10.528 [ERROR] [et.wimpi.modbus.io.ModbusRTUTransport] - failed to read: CRC Error in received frame: 3 bytes: 20 04 00
15:19:10.528 [ERROR] [mpi.modbus.io.ModbusSerialTransaction] - execute try 1/1 error: I/O exception: IOException CRC Error in received frame: 3 bytes: 20 04 00 . Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@6af5510c (unit id 32 & transaction 7397). Serial parameters: SerialParameters@18a3aaba[portName=/dev/ttyACM0,baudRate=9600,flowControlIn=none,flowControlOut=none,databits=8,stopbits=1,parity=none,encoding=rtu,echo=false,receiveTimeoutMillis=1500]
15:19:10.528 [ERROR] [mpi.modbus.io.ModbusSerialTransaction] - execute reached max tries 1, throwing last error: I/O exception: IOException CRC Error in received frame: 3 bytes: 20 04 00 . Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@6af5510c (unit id 32 & transaction 7397). Serial parameters: SerialParameters@18a3aaba[portName=/dev/ttyACM0,baudRate=9600,flowControlIn=none,flowControlOut=none,databits=8,stopbits=1,parity=none,encoding=rtu,echo=false,receiveTimeoutMillis=1500]
15:19:10.529 [WARN ] [ort.modbus.internal.ModbusManagerImpl] - Try 2 out of 3 failed when executing request (ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@607b1c96[slaveId=32,functionCode=READ_INPUT_REGISTERS,start=8,length=2,maxTries=3]). Will try again soon. Error was I/O error, so reseting the connection. Error details: net.wimpi.modbus.ModbusIOException I/O exception: IOException CRC Error in received frame: 3 bytes: 20 04 00 [operation ID f4fddf7d-7f7c-4a51-8c4f-b92a4cf5c76c]
15:19:10.529 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - destroyObject for connection SerialConnection@3ab69fb8[portName=/dev/ttyACM0,port=/dev/ttyACM0] and endpoint ModbusSerialSlaveEndpoint@22a6ff3d[portName=/dev/ttyACM0] -> closing the connection
15:19:10.569 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - Created connection SerialConnection@66176eb7[portName=/dev/ttyACM0,port=<null>] for endpoint ModbusSerialSlaveEndpoint@22a6ff3d[portName=/dev/ttyACM0]
15:19:10.570 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - Passivating connection SerialConnection@66176eb7[portName=/dev/ttyACM0,port=<null>] for endpoint ModbusSerialSlaveEndpoint@22a6ff3d[portName=/dev/ttyACM0]...
15:19:10.570 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - (passivate) Connection SerialConnection@66176eb7[portName=/dev/ttyACM0,port=<null>] (endpoint ModbusSerialSlaveEndpoint@22a6ff3d[portName=/dev/ttyACM0]) age (1554112150570ms) is below the reconnectAfterMillis (-1ms) limit and connection time (0) is after the "disconnectBeforeConnectedMillis"=-1. Keep the connection open.
15:19:10.570 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - ...Passivated connection SerialConnection@66176eb7[portName=/dev/ttyACM0,port=<null>] for endpoint ModbusSerialSlaveEndpoint@22a6ff3d[portName=/dev/ttyACM0]
15:19:10.570 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - invalidating connection for endpoint ModbusSerialSlaveEndpoint@22a6ff3d[portName=/dev/ttyACM0] took 41 ms
15:19:10.571 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - Executing task BasicPollTaskImpl@5d411317[request=ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@607b1c96[slaveId=32,functionCode=READ_INPUT_REGISTERS,start=8,length=2,maxTries=3],endpoint=ModbusSerialSlaveEndpoint@22a6ff3d[portName=/dev/ttyACM0],callback=org.openhab.binding.modbus.internal.handler.ModbusPollerThingHandlerImpl$ReadCallbackDelegator@329aa566] (oneOff=false)! Waiting for connection. Idle connections for this endpoint: 0, and active 1 [operation ID f4fddf7d-7f7c-4a51-8c4f-b92a4cf5c76c]
15:19:11.508 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - Waited 937ms (interConnectDelayMillis 1000ms, interTransactionDelayMillis 35ms) before connecting disconnected connection SerialConnection@66176eb7[portName=/dev/ttyACM0,port=<null>] for endpoint ModbusSerialSlaveEndpoint@27d60e81[portName=/dev/ttyACM0], to allow delay between connections re-connects
15:19:11.508 [TRACE] [net.wimpi.modbus.net.SerialConnection] - Got Port Identifier
15:19:11.514 [TRACE] [net.wimpi.modbus.net.SerialConnection] - Got Serial Port
15:19:11.514 [TRACE] [net.wimpi.modbus.net.SerialConnection] - i/o Streams prepared
15:19:11.515 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - Waited 0ms (interTransactionDelayMillis 35ms) before giving returning connection SerialConnection@66176eb7[portName=/dev/ttyACM0,port=/dev/ttyACM0] for endpoint ModbusSerialSlaveEndpoint@27d60e81[portName=/dev/ttyACM0], to ensure delay between transactions.
15:19:11.515 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - borrowing connection (got Optional[SerialConnection@66176eb7[portName=/dev/ttyACM0,port=/dev/ttyACM0]]) for endpoint ModbusSerialSlaveEndpoint@27d60e81[portName=/dev/ttyACM0] took 4034 ms
15:19:11.515 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - Executing task BasicPollTaskImpl@405e49bd[request=ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@65e2d032[slaveId=16,functionCode=READ_MULTIPLE_REGISTERS,start=172,length=2,maxTries=3],endpoint=ModbusSerialSlaveEndpoint@27d60e81[portName=/dev/ttyACM0],callback=org.openhab.binding.modbus.internal.handler.ModbusPollerThingHandlerImpl$ReadCallbackDelegator@49307ecd] (oneOff=false)! Connection received in 4034 ms [operation ID 20790bb3-3d5b-47e3-bc6d-690f140bd0ba]
15:19:11.515 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - Try 2 out of 3 [operation ID 20790bb3-3d5b-47e3-bc6d-690f140bd0ba]
15:19:11.516 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - Ensuring that enough time passes before retrying again. Sleeping if necessary [operation ID 20790bb3-3d5b-47e3-bc6d-690f140bd0ba]
15:19:11.516 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - Sleep ended, slept 0 [operation ID 20790bb3-3d5b-47e3-bc6d-690f140bd0ba]
15:19:11.516 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - Going execute transaction with request request (FC=READ_MULTIPLE_REGISTERS): 00 00 00 00 00 06 10 03 00 ac 00 02 [operation ID 20790bb3-3d5b-47e3-bc6d-690f140bd0ba]
15:19:11.516 [DEBUG] [et.wimpi.modbus.io.ModbusRTUTransport] - Sent: 10 03 00 ac 00 02 07 6b
15:19:13.018 [TRACE] [et.wimpi.modbus.io.ModbusRTUTransport] - Managed to read at least one byte
15:19:13.020 [ERROR] [et.wimpi.modbus.io.ModbusRTUTransport] - Last request: 10 03 00 ac 00 02 07 6b
15:19:13.021 [ERROR] [et.wimpi.modbus.io.ModbusRTUTransport] - failed to read: Error reading response (EOF)
15:19:13.022 [ERROR] [mpi.modbus.io.ModbusSerialTransaction] - execute try 1/1 error: I/O exception: IOException Error reading response (EOF). Request: net.wimpi.modbus.msg.ReadMultipleRegistersRequest@42789b96 (unit id 16 & transaction 7398). Serial parameters: SerialParameters@64dfe7f[portName=/dev/ttyACM0,baudRate=9600,flowControlIn=none,flowControlOut=none,databits=8,stopbits=1,parity=none,encoding=rtu,echo=false,receiveTimeoutMillis=1500]
15:19:13.024 [ERROR] [mpi.modbus.io.ModbusSerialTransaction] - execute reached max tries 1, throwing last error: I/O exception: IOException Error reading response (EOF). Request: net.wimpi.modbus.msg.ReadMultipleRegistersRequest@42789b96 (unit id 16 & transaction 7398). Serial parameters: SerialParameters@64dfe7f[portName=/dev/ttyACM0,baudRate=9600,flowControlIn=none,flowControlOut=none,databits=8,stopbits=1,parity=none,encoding=rtu,echo=false,receiveTimeoutMillis=1500]
15:19:13.024 [WARN ] [ort.modbus.internal.ModbusManagerImpl] - Try 2 out of 3 failed when executing request (ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@65e2d032[slaveId=16,functionCode=READ_MULTIPLE_REGISTERS,start=172,length=2,maxTries=3]). Will try again soon. Error was I/O error, so reseting the connection. Error details: net.wimpi.modbus.ModbusIOException I/O exception: IOException Error reading response (EOF) [operation ID 20790bb3-3d5b-47e3-bc6d-690f140bd0ba]
15:19:13.025 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - destroyObject for connection SerialConnection@66176eb7[portName=/dev/ttyACM0,port=/dev/ttyACM0] and endpoint ModbusSerialSlaveEndpoint@27d60e81[portName=/dev/ttyACM0] -> closing the connection
15:19:13.121 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - Created connection SerialConnection@3d76cd3a[portName=/dev/ttyACM0,port=<null>] for endpoint ModbusSerialSlaveEndpoint@27d60e81[portName=/dev/ttyACM0]
15:19:13.122 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - Passivating connection SerialConnection@3d76cd3a[portName=/dev/ttyACM0,port=<null>] for endpoint ModbusSerialSlaveEndpoint@27d60e81[portName=/dev/ttyACM0]...
15:19:13.123 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - (passivate) Connection SerialConnection@3d76cd3a[portName=/dev/ttyACM0,port=<null>] (endpoint ModbusSerialSlaveEndpoint@27d60e81[portName=/dev/ttyACM0]) age (1554112153123ms) is below the reconnectAfterMillis (-1ms) limit and connection time (0) is after the "disconnectBeforeConnectedMillis"=-1. Keep the connection open.
15:19:13.124 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - ...Passivated connection SerialConnection@3d76cd3a[portName=/dev/ttyACM0,port=<null>] for endpoint ModbusSerialSlaveEndpoint@27d60e81[portName=/dev/ttyACM0]
15:19:13.124 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - invalidating connection for endpoint ModbusSerialSlaveEndpoint@27d60e81[portName=/dev/ttyACM0] took 99 ms
15:19:13.125 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - Executing task BasicPollTaskImpl@405e49bd[request=ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@65e2d032[slaveId=16,functionCode=READ_MULTIPLE_REGISTERS,start=172,length=2,maxTries=3],endpoint=ModbusSerialSlaveEndpoint@27d60e81[portName=/dev/ttyACM0],callback=org.openhab.binding.modbus.internal.handler.ModbusPollerThingHandlerImpl$ReadCallbackDelegator@49307ecd] (oneOff=false)! Waiting for connection. Idle connections for this endpoint: 0, and active 1 [operation ID 20790bb3-3d5b-47e3-bc6d-690f140bd0ba]
15:19:13.125 [TRACE] [net.wimpi.modbus.net.SerialConnection] - Got Port Identifier
15:19:13.134 [TRACE] [net.wimpi.modbus.net.SerialConnection] - Got Serial Port
15:19:13.135 [TRACE] [net.wimpi.modbus.net.SerialConnection] - i/o Streams prepared
15:19:13.159 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - Waited 21ms (interTransactionDelayMillis 35ms) before giving returning connection SerialConnection@3d76cd3a[portName=/dev/ttyACM0,port=/dev/ttyACM0] for endpoint ModbusSerialSlaveEndpoint@501d49b1[portName=/dev/ttyACM0], to ensure delay between transactions.
15:19:13.160 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - borrowing connection (got Optional[SerialConnection@3d76cd3a[portName=/dev/ttyACM0,port=/dev/ttyACM0]]) for endpoint ModbusSerialSlaveEndpoint@501d49b1[portName=/dev/ttyACM0] took 5580 ms
15:19:13.162 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - Executing task BasicPollTaskImpl@3d3f7eaa[request=ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@69880c34[slaveId=128,functionCode=READ_INPUT_REGISTERS,start=8,length=2,maxTries=3],endpoint=ModbusSerialSlaveEndpoint@501d49b1[portName=/dev/ttyACM0],callback=org.openhab.binding.modbus.internal.handler.ModbusPollerThingHandlerImpl$ReadCallbackDelegator@329abbec] (oneOff=false)! Connection received in 5582 ms [operation ID 1b815eb9-58ff-4136-85f1-92488104ab99]
15:19:13.163 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - Try 2 out of 3 [operation ID 1b815eb9-58ff-4136-85f1-92488104ab99]
15:19:13.168 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - Ensuring that enough time passes before retrying again. Sleeping if necessary [operation ID 1b815eb9-58ff-4136-85f1-92488104ab99]
15:19:13.168 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - Sleep ended, slept 0 [operation ID 1b815eb9-58ff-4136-85f1-92488104ab99]
15:19:13.169 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - Going execute transaction with request request (FC=READ_INPUT_REGISTERS): 00 00 00 00 00 06 80 04 00 08 00 02 [operation ID 1b815eb9-58ff-4136-85f1-92488104ab99]
15:19:13.169 [DEBUG] [et.wimpi.modbus.io.ModbusRTUTransport] - Sent: 80 04 00 08 00 02 ee 18
15:19:13.183 [TRACE] [et.wimpi.modbus.io.ModbusRTUTransport] - Managed to read at least one byte
15:19:13.187 [DEBUG] [et.wimpi.modbus.io.ModbusRTUTransport] - Response: 80 04 00 02 00
15:19:13.188 [ERROR] [et.wimpi.modbus.io.ModbusRTUTransport] - Last request: 80 04 00 08 00 02 ee 18
15:19:13.188 [ERROR] [et.wimpi.modbus.io.ModbusRTUTransport] - failed to read: CRC Error in received frame: 3 bytes: 80 04 00
15:19:13.189 [ERROR] [mpi.modbus.io.ModbusSerialTransaction] - execute try 1/1 error: I/O exception: IOException CRC Error in received frame: 3 bytes: 80 04 00 . Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@3fe0ed76 (unit id 128 & transaction 7399). Serial parameters: SerialParameters@61fc8efc[portName=/dev/ttyACM0,baudRate=9600,flowControlIn=none,flowControlOut=none,databits=8,stopbits=1,parity=none,encoding=rtu,echo=false,receiveTimeoutMillis=1500]
15:19:13.189 [ERROR] [mpi.modbus.io.ModbusSerialTransaction] - execute reached max tries 1, throwing last error: I/O exception: IOException CRC Error in received frame: 3 bytes: 80 04 00 . Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@3fe0ed76 (unit id 128 & transaction 7399). Serial parameters: SerialParameters@61fc8efc[portName=/dev/ttyACM0,baudRate=9600,flowControlIn=none,flowControlOut=none,databits=8,stopbits=1,parity=none,encoding=rtu,echo=false,receiveTimeoutMillis=1500]
15:19:13.190 [WARN ] [ort.modbus.internal.ModbusManagerImpl] - Try 2 out of 3 failed when executing request (ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@69880c34[slaveId=128,functionCode=READ_INPUT_REGISTERS,start=8,length=2,maxTries=3]). Will try again soon. Error was I/O error, so reseting the connection. Error details: net.wimpi.modbus.ModbusIOException I/O exception: IOException CRC Error in received frame: 3 bytes: 80 04 00 [operation ID 1b815eb9-58ff-4136-85f1-92488104ab99]
15:19:13.190 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - destroyObject for connection SerialConnection@3d76cd3a[portName=/dev/ttyACM0,port=/dev/ttyACM0] and endpoint ModbusSerialSlaveEndpoint@501d49b1[portName=/dev/ttyACM0] -> closing the connection
15:19:13.224 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - Created connection SerialConnection@3d75375e[portName=/dev/ttyACM0,port=<null>] for endpoint ModbusSerialSlaveEndpoint@501d49b1[portName=/dev/ttyACM0]
15:19:13.225 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - Passivating connection SerialConnection@3d75375e[portName=/dev/ttyACM0,port=<null>] for endpoint ModbusSerialSlaveEndpoint@501d49b1[portName=/dev/ttyACM0]...
15:19:13.226 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - (passivate) Connection SerialConnection@3d75375e[portName=/dev/ttyACM0,port=<null>] (endpoint ModbusSerialSlaveEndpoint@501d49b1[portName=/dev/ttyACM0]) age (1554112153226ms) is below the reconnectAfterMillis (-1ms) limit and connection time (0) is after the "disconnectBeforeConnectedMillis"=-1. Keep the connection open.
15:19:13.226 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - ...Passivated connection SerialConnection@3d75375e[portName=/dev/ttyACM0,port=<null>] for endpoint ModbusSerialSlaveEndpoint@501d49b1[portName=/dev/ttyACM0]
15:19:13.226 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - invalidating connection for endpoint ModbusSerialSlaveEndpoint@501d49b1[portName=/dev/ttyACM0] took 36 ms
15:19:13.227 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - Executing task BasicPollTaskImpl@3d3f7eaa[request=ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@69880c34[slaveId=128,functionCode=READ_INPUT_REGISTERS,start=8,length=2,maxTries=3],endpoint=ModbusSerialSlaveEndpoint@501d49b1[portName=/dev/ttyACM0],callback=org.openhab.binding.modbus.internal.handler.ModbusPollerThingHandlerImpl$ReadCallbackDelegator@329abbec] (oneOff=false)! Waiting for connection. Idle connections for this endpoint: 0, and active 1 [operation ID 1b815eb9-58ff-4136-85f1-92488104ab99]
15:19:14.137 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - Waited 910ms (interConnectDelayMillis 1000ms, interTransactionDelayMillis 35ms) before connecting disconnected connection SerialConnection@3d75375e[portName=/dev/ttyACM0,port=<null>] for endpoint ModbusSerialSlaveEndpoint@17072183[portName=/dev/ttyACM0], to allow delay between connections re-connects
15:19:14.138 [TRACE] [net.wimpi.modbus.net.SerialConnection] - Got Port Identifier
15:19:14.145 [TRACE] [net.wimpi.modbus.net.SerialConnection] - Got Serial Port
15:19:14.146 [TRACE] [net.wimpi.modbus.net.SerialConnection] - i/o Streams prepared
15:19:14.146 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - Waited 0ms (interTransactionDelayMillis 35ms) before giving returning connection SerialConnection@3d75375e[portName=/dev/ttyACM0,port=/dev/ttyACM0] for endpoint ModbusSerialSlaveEndpoint@17072183[portName=/dev/ttyACM0], to ensure delay between transactions.
15:19:14.147 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - borrowing connection (got Optional[SerialConnection@3d75375e[portName=/dev/ttyACM0,port=/dev/ttyACM0]]) for endpoint ModbusSerialSlaveEndpoint@17072183[portName=/dev/ttyACM0] took 5590 ms
15:19:14.148 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - Executing task BasicPollTaskImpl@6f9a43ba[request=ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@c19d0d4[slaveId=64,functionCode=READ_INPUT_REGISTERS,start=8,length=2,maxTries=3],endpoint=ModbusSerialSlaveEndpoint@17072183[portName=/dev/ttyACM0],callback=org.openhab.binding.modbus.internal.handler.ModbusPollerThingHandlerImpl$ReadCallbackDelegator@329aace8] (oneOff=false)! Connection received in 5591 ms [operation ID 452bab5e-5eff-49aa-872e-7add789af404]
15:19:14.148 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - Try 3 out of 3 [operation ID 452bab5e-5eff-49aa-872e-7add789af404]
15:19:14.148 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - Ensuring that enough time passes before retrying again. Sleeping if necessary [operation ID 452bab5e-5eff-49aa-872e-7add789af404]
15:19:14.149 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - Sleep ended, slept 0 [operation ID 452bab5e-5eff-49aa-872e-7add789af404]
15:19:14.153 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - Going execute transaction with request request (FC=READ_INPUT_REGISTERS): 00 00 00 00 00 06 40 04 00 08 00 02 [operation ID 452bab5e-5eff-49aa-872e-7add789af404]
15:19:14.154 [DEBUG] [et.wimpi.modbus.io.ModbusRTUTransport] - Sent: 40 04 00 08 00 02 ff 18
15:19:14.173 [TRACE] [et.wimpi.modbus.io.ModbusRTUTransport] - Managed to read at least one byte
15:19:14.178 [DEBUG] [et.wimpi.modbus.io.ModbusRTUTransport] - Response: 40 04 00 02 00
15:19:14.180 [ERROR] [et.wimpi.modbus.io.ModbusRTUTransport] - Last request: 40 04 00 08 00 02 ff 18
15:19:14.182 [ERROR] [et.wimpi.modbus.io.ModbusRTUTransport] - failed to read: CRC Error in received frame: 3 bytes: 40 04 00
15:19:14.184 [ERROR] [mpi.modbus.io.ModbusSerialTransaction] - execute try 1/1 error: I/O exception: IOException CRC Error in received frame: 3 bytes: 40 04 00 . Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@cdc247e (unit id 64 & transaction 7400). Serial parameters: SerialParameters@22ec164a[portName=/dev/ttyACM0,baudRate=9600,flowControlIn=none,flowControlOut=none,databits=8,stopbits=1,parity=none,encoding=rtu,echo=false,receiveTimeoutMillis=1500]
15:19:14.185 [ERROR] [mpi.modbus.io.ModbusSerialTransaction] - execute reached max tries 1, throwing last error: I/O exception: IOException CRC Error in received frame: 3 bytes: 40 04 00 . Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@cdc247e (unit id 64 & transaction 7400). Serial parameters: SerialParameters@22ec164a[portName=/dev/ttyACM0,baudRate=9600,flowControlIn=none,flowControlOut=none,databits=8,stopbits=1,parity=none,encoding=rtu,echo=false,receiveTimeoutMillis=1500]
15:19:14.185 [ERROR] [ort.modbus.internal.ModbusManagerImpl] - Last try 3 failed when executing request (ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@c19d0d4[slaveId=64,functionCode=READ_INPUT_REGISTERS,start=8,length=2,maxTries=3]). Aborting. Error was I/O error, so reseting the connection. Error details: net.wimpi.modbus.ModbusIOException I/O exception: IOException CRC Error in received frame: 3 bytes: 40 04 00 [operation ID 452bab5e-5eff-49aa-872e-7add789af404]
15:19:14.185 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - destroyObject for connection SerialConnection@3d75375e[portName=/dev/ttyACM0,port=/dev/ttyACM0] and endpoint ModbusSerialSlaveEndpoint@17072183[portName=/dev/ttyACM0] -> closing the connection
15:19:14.215 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - Created connection SerialConnection@18e7b414[portName=/dev/ttyACM0,port=<null>] for endpoint ModbusSerialSlaveEndpoint@17072183[portName=/dev/ttyACM0]
15:19:14.217 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - Passivating connection SerialConnection@18e7b414[portName=/dev/ttyACM0,port=<null>] for endpoint ModbusSerialSlaveEndpoint@17072183[portName=/dev/ttyACM0]...
15:19:14.218 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - (passivate) Connection SerialConnection@18e7b414[portName=/dev/ttyACM0,port=<null>] (endpoint ModbusSerialSlaveEndpoint@17072183[portName=/dev/ttyACM0]) age (1554112154218ms) is below the reconnectAfterMillis (-1ms) limit and connection time (0) is after the "disconnectBeforeConnectedMillis"=-1. Keep the connection open.
15:19:14.220 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - ...Passivated connection SerialConnection@18e7b414[portName=/dev/ttyACM0,port=<null>] for endpoint ModbusSerialSlaveEndpoint@17072183[portName=/dev/ttyACM0]
15:19:14.221 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - invalidating connection for endpoint ModbusSerialSlaveEndpoint@17072183[portName=/dev/ttyACM0] took 36 ms
15:19:14.221 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - Calling write response callback org.openhab.binding.modbus.internal.handler.ModbusPollerThingHandlerImpl$ReadCallbackDelegator@329aace8 for request ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@c19d0d4[slaveId=64,functionCode=READ_INPUT_REGISTERS,start=8,length=2,maxTries=3]. Error was org.openhab.io.transport.modbus.internal.ModbusSlaveIOExceptionImpl Modbus IO Error with cause=ModbusIOException, EOF=false, message='I/O exception: IOException CRC Error in received frame: 3 bytes: 40 04 00 ', cause2=null
15:19:14.222 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - Called write response callback org.openhab.binding.modbus.internal.handler.ModbusPollerThingHandlerImpl$ReadCallbackDelegator@329aace8 for request ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@c19d0d4[slaveId=64,functionCode=READ_INPUT_REGISTERS,start=8,length=2,maxTries=3]. Error was org.openhab.io.transport.modbus.internal.ModbusSlaveIOExceptionImpl Modbus IO Error with cause=ModbusIOException, EOF=false, message='I/O exception: IOException CRC Error in received frame: 3 bytes: 40 04 00 ', cause2=null
15:19:14.222 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - returning connection for endpoint ModbusSerialSlaveEndpoint@17072183[portName=/dev/ttyACM0] took 0 ms
15:19:14.222 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - Connection was returned to the pool, ending operation [operation ID 452bab5e-5eff-49aa-872e-7add789af404]
15:19:14.223 [DEBUG] [ort.modbus.internal.ModbusManagerImpl] - Modbus operation ended, timing info: {total: 16929 ms, connection: 16844, transaction=74, callback=1} [operation ID 452bab5e-5eff-49aa-872e-7add789af404]
15:19:14.223 [DEBUG] [ort.modbus.internal.ModbusManagerImpl] - Execution of scheduled (1000ms) poll task BasicPollTaskImpl@6f9a43ba[request=ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@c19d0d4[slaveId=64,functionCode=READ_INPUT_REGISTERS,start=8,length=2,maxTries=3],endpoint=ModbusSerialSlaveEndpoint@17072183[portName=/dev/ttyACM0],callback=org.openhab.binding.modbus.internal.handler.ModbusPollerThingHandlerImpl$ReadCallbackDelegator@329aace8] finished at 1554112154223. Was started at millis: 1554112137294 (=duration of 16929 millis)
15:19:14.223 [DEBUG] [ort.modbus.internal.ModbusManagerImpl] - Executing scheduled (1000ms) poll task BasicPollTaskImpl@7b24be69[request=ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@399ec2a9[slaveId=1,functionCode=READ_INPUT_REGISTERS,start=8,length=2,maxTries=3],endpoint=ModbusSerialSlaveEndpoint@38c4b77[portName=/dev/ttyACM0],callback=org.openhab.binding.modbus.internal.handler.ModbusPollerThingHandlerImpl$ReadCallbackDelegator@329a9e03]. Current millis: 1554112154223
15:19:14.223 [INFO ] [smarthome.event.ThingStatusInfoEvent ] - 'modbus:data:slave0x40:smokeDetector:smokeDetector02' updated: OFFLINE (COMMUNICATION_ERROR): Error (ModbusSlaveIOExceptionImpl) with read. Request: ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@c19d0d4[slaveId=64,functionCode=READ_INPUT_REGISTERS,start=8,length=2,maxTries=3]. Description: ModbusSlaveIOException(cause=ModbusIOException, EOF=false, message='I/O exception: IOException CRC Error in received frame: 3 bytes: 40 04 00 ', cause2=null). Message: Modbus IO Error with cause=ModbusIOException, EOF=false, message='I/O exception: IOException CRC Error in received frame: 3 bytes: 40 04 00 ', cause2=null
15:19:14.224 [TRACE] [nternal.ModbusManagerImpl.PollMonitor] - <POLL MONITOR>
15:19:14.224 [INFO ] [smarthome.event.ThingStatusInfoEvent ] - 'modbus:poller:slave0x40:smokeDetector' updated: OFFLINE (COMMUNICATION_ERROR): Error with read: org.openhab.io.transport.modbus.internal.ModbusSlaveIOExceptionImpl: Modbus IO Error with cause=ModbusIOException, EOF=false, message='I/O exception: IOException CRC Error in received frame: 3 bytes: 40 04 00 ', cause2=null
15:19:14.224 [TRACE] [nternal.ModbusManagerImpl.PollMonitor] - POLL MONITOR: scheduled poll task. FC: READ_INPUT_REGISTERS, start 8, length 2, done: false, canceled: false, delay: -14933. Full task BasicPollTaskImpl@5d411317[request=ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@607b1c96[slaveId=32,functionCode=READ_INPUT_REGISTERS,start=8,length=2,maxTries=3],endpoint=ModbusSerialSlaveEndpoint@22a6ff3d[portName=/dev/ttyACM0],callback=org.openhab.binding.modbus.internal.handler.ModbusPollerThingHandlerImpl$ReadCallbackDelegator@329aa566]
15:19:14.226 [TRACE] [nternal.ModbusManagerImpl.PollMonitor] - POLL MONITOR: scheduled poll task. FC: READ_INPUT_REGISTERS, start 8, length 2, done: false, canceled: false, delay: 997. Full task BasicPollTaskImpl@6f9a43ba[request=ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@c19d0d4[slaveId=64,functionCode=READ_INPUT_REGISTERS,start=8,length=2,maxTries=3],endpoint=ModbusSerialSlaveEndpoint@17072183[portName=/dev/ttyACM0],callback=org.openhab.binding.modbus.internal.handler.ModbusPollerThingHandlerImpl$ReadCallbackDelegator@329aace8]
15:19:14.227 [TRACE] [nternal.ModbusManagerImpl.PollMonitor] - POLL MONITOR: scheduled poll task. FC: READ_MULTIPLE_REGISTERS, start 172, length 2, done: false, canceled: false, delay: -12388. Full task BasicPollTaskImpl@405e49bd[request=ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@65e2d032[slaveId=16,functionCode=READ_MULTIPLE_REGISTERS,start=172,length=2,maxTries=3],endpoint=ModbusSerialSlaveEndpoint@27d60e81[portName=/dev/ttyACM0],callback=org.openhab.binding.modbus.internal.handler.ModbusPollerThingHandlerImpl$ReadCallbackDelegator@49307ecd]
15:19:14.227 [TRACE] [nternal.ModbusManagerImpl.PollMonitor] - POLL MONITOR: scheduled poll task. FC: READ_INPUT_REGISTERS, start 8, length 2, done: false, canceled: false, delay: -16633. Full task BasicPollTaskImpl@3a515949[request=ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@3e6ecadb[slaveId=4,functionCode=READ_INPUT_REGISTERS,start=8,length=2,maxTries=3],endpoint=ModbusSerialSlaveEndpoint@7b6c5372[portName=/dev/ttyACM0],callback=org.openhab.binding.modbus.internal.handler.ModbusPollerThingHandlerImpl$ReadCallbackDelegator@818e012]
15:19:14.227 [TRACE] [nternal.ModbusManagerImpl.PollMonitor] - POLL MONITOR: scheduled poll task. FC: READ_INPUT_REGISTERS, start 8, length 2, done: false, canceled: false, delay: -12293. Full task BasicPollTaskImpl@3d3f7eaa[request=ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@69880c34[slaveId=128,functionCode=READ_INPUT_REGISTERS,start=8,length=2,maxTries=3],endpoint=ModbusSerialSlaveEndpoint@501d49b1[portName=/dev/ttyACM0],callback=org.openhab.binding.modbus.internal.handler.ModbusPollerThingHandlerImpl$ReadCallbackDelegator@329abbec]
15:19:14.228 [TRACE] [nternal.ModbusManagerImpl.PollMonitor] - POLL MONITOR: scheduled poll task. FC: READ_INPUT_REGISTERS, start 8, length 2, done: false, canceled: false, delay: -11315. Full task BasicPollTaskImpl@7b24be69[request=ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@399ec2a9[slaveId=1,functionCode=READ_INPUT_REGISTERS,start=8,length=2,maxTries=3],endpoint=ModbusSerialSlaveEndpoint@38c4b77[portName=/dev/ttyACM0],callback=org.openhab.binding.modbus.internal.handler.ModbusPollerThingHandlerImpl$ReadCallbackDelegator@329a9e03]
15:19:14.228 [TRACE] [nternal.ModbusManagerImpl.PollMonitor] - POLL MONITOR: scheduledThreadPoolExecutor queue size: 2, remaining space 2147483647. Active threads 5
15:19:14.228 [TRACE] [nternal.ModbusManagerImpl.PollMonitor] - </POLL MONITOR>
15:19:14.228 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - Starting new operation with task BasicPollTaskImpl@7b24be69[request=ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@399ec2a9[slaveId=1,functionCode=READ_INPUT_REGISTERS,start=8,length=2,maxTries=3],endpoint=ModbusSerialSlaveEndpoint@38c4b77[portName=/dev/ttyACM0],callback=org.openhab.binding.modbus.internal.handler.ModbusPollerThingHandlerImpl$ReadCallbackDelegator@329a9e03]. Trying to get connection [operation ID 91d4a4d1-395c-4fdf-a562-0dda8554227c]
15:19:14.228 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - Executing task BasicPollTaskImpl@7b24be69[request=ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@399ec2a9[slaveId=1,functionCode=READ_INPUT_REGISTERS,start=8,length=2,maxTries=3],endpoint=ModbusSerialSlaveEndpoint@38c4b77[portName=/dev/ttyACM0],callback=org.openhab.binding.modbus.internal.handler.ModbusPollerThingHandlerImpl$ReadCallbackDelegator@329a9e03] (oneOff=false)! Waiting for connection. Idle connections for this endpoint: 0, and active 1 [operation ID 91d4a4d1-395c-4fdf-a562-0dda8554227c]
15:19:15.146 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - Waited 925ms (interConnectDelayMillis 1000ms, interTransactionDelayMillis 35ms) before connecting disconnected connection SerialConnection@18e7b414[portName=/dev/ttyACM0,port=<null>] for endpoint ModbusSerialSlaveEndpoint@7b6c5372[portName=/dev/ttyACM0], to allow delay between connections re-connects
15:19:15.147 [TRACE] [net.wimpi.modbus.net.SerialConnection] - Got Port Identifier
15:19:15.155 [TRACE] [net.wimpi.modbus.net.SerialConnection] - Got Serial Port
15:19:15.156 [TRACE] [net.wimpi.modbus.net.SerialConnection] - i/o Streams prepared
15:19:15.156 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - Waited 0ms (interTransactionDelayMillis 35ms) before giving returning connection SerialConnection@18e7b414[portName=/dev/ttyACM0,port=/dev/ttyACM0] for endpoint ModbusSerialSlaveEndpoint@7b6c5372[portName=/dev/ttyACM0], to ensure delay between transactions.
15:19:15.157 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - borrowing connection (got Optional[SerialConnection@18e7b414[portName=/dev/ttyACM0,port=/dev/ttyACM0]]) for endpoint ModbusSerialSlaveEndpoint@7b6c5372[portName=/dev/ttyACM0] took 5595 ms
15:19:15.157 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - Executing task BasicPollTaskImpl@3a515949[request=ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@3e6ecadb[slaveId=4,functionCode=READ_INPUT_REGISTERS,start=8,length=2,maxTries=3],endpoint=ModbusSerialSlaveEndpoint@7b6c5372[portName=/dev/ttyACM0],callback=org.openhab.binding.modbus.internal.handler.ModbusPollerThingHandlerImpl$ReadCallbackDelegator@818e012] (oneOff=false)! Connection received in 5595 ms [operation ID 71bd894e-f23c-47c1-a2ea-da1dcfb9ca5b]
15:19:15.158 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - Try 3 out of 3 [operation ID 71bd894e-f23c-47c1-a2ea-da1dcfb9ca5b]
15:19:15.158 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - Ensuring that enough time passes before retrying again. Sleeping if necessary [operation ID 71bd894e-f23c-47c1-a2ea-da1dcfb9ca5b]
15:19:15.159 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - Sleep ended, slept 0 [operation ID 71bd894e-f23c-47c1-a2ea-da1dcfb9ca5b]
15:19:15.161 [TRACE] [ort.modbus.internal.ModbusManagerImpl] - Going execute transaction with request request (FC=READ_INPUT_REGISTERS): 00 00 00 00 00 06 04 04 00 08 00 02 [operation ID 71bd894e-f23c-47c1-a2ea-da1dcfb9ca5b]
15:19:15.162 [DEBUG] [et.wimpi.modbus.io.ModbusRTUTransport] - Sent: 04 04 00 08 00 02 f0 5c
15:19:15.173 [TRACE] [et.wimpi.modbus.io.ModbusRTUTransport] - Managed to read at least one byte
15:19:15.177 [DEBUG] [et.wimpi.modbus.io.ModbusRTUTransport] - Response: 04 04 00 01 00
15:19:15.178 [ERROR] [et.wimpi.modbus.io.ModbusRTUTransport] - Last request: 04 04 00 08 00 02 f0 5c
15:19:15.178 [ERROR] [et.wimpi.modbus.io.ModbusRTUTransport] - failed to read: CRC Error in received frame: 3 bytes: 04 04 00
15:19:15.179 [ERROR] [mpi.modbus.io.ModbusSerialTransaction] - execute try 1/1 error: I/O exception: IOException CRC Error in received frame: 3 bytes: 04 04 00 . Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@2164008b (unit id 4 & transaction 7401). Serial parameters: SerialParameters@29f6f91c[portName=/dev/ttyACM0,baudRate=9600,flowControlIn=none,flowControlOut=none,databits=8,stopbits=1,parity=none,encoding=rtu,echo=false,receiveTimeoutMillis=1500]
15:19:15.179 [ERROR] [mpi.modbus.io.ModbusSerialTransaction] - execute reached max tries 1, throwing last error: I/O exception: IOException CRC Error in received frame: 3 bytes: 04 04 00 . Request: net.wimpi.modbus.msg.ReadInputRegistersRequest@2164008b (unit id 4 & transaction 7401). Serial parameters: SerialParameters@29f6f91c[portName=/dev/ttyACM0,baudRate=9600,flowControlIn=none,flowControlOut=none,databits=8,stopbits=1,parity=none,encoding=rtu,echo=false,receiveTimeoutMillis=1500]
15:19:15.180 [ERROR] [ort.modbus.internal.ModbusManagerImpl] - Last try 3 failed when executing request (ModbusPollerThingHandlerImpl.ModbusPollerReadRequest@3e6ecadb[slaveId=4,functionCode=READ_INPUT_REGISTERS,start=8,length=2,maxTries=3]). Aborting. Error was I/O error, so reseting the connection. Error details: net.wimpi.modbus.ModbusIOException I/O exception: IOException CRC Error in received frame: 3 bytes: 04 04 00 [operation ID 71bd894e-f23c-47c1-a2ea-da1dcfb9ca5b]
15:19:15.180 [TRACE] [ling.ModbusSlaveConnectionFactoryImpl] - destroyObject for connection SerialConnection@18e7b414[portName=/dev/ttyACM0,port=/dev/ttyACM0] and endpoint ModbusSerialSlaveEndpoint@7b6c5372[portName=/dev/ttyACM0] -> closing the connection
Please help me to solve the issue..