How to connect Nilan CTS602 modbus interface
This is a full setup and how to connecting a Nilan ventilation or heatpump using the Nilan CTS602 modbus interface to openhab 2.4 using a RS485 USB dongle.
This example applies to Nilan Comfort 300LR (Ventilation) without pre- or after- heating, and no CO2 either. It´s a HVAC without heater or cooler. The three devices are optional addons for the Nilan Comfort 300LR. All data will be available through Modbus, if they´re applied. In this turtorial, they are not applied.
First you´ll need a RS485 USB device. The one I use is from In-Circuit and bought on Amazon.de.
In-Circuit USB RS485 Adapter: Amazon.de: Computer & Accessories
Its available with a housing as well.
Second you´ll need to know the modbus wiring for the Nilan CTS602 interface. On my Nilan Comfort 300LR, the modbus interface is located on the right side of the agregate.
My device is from before November 2017. Nilan has changed the modbus interface to a grey plug since then, but it´s still located on the right side of the agregate. The wiring is almost the same for both the green and the grey models, but to make sure, you should look into your setup manual.
The wiring in use for my specific device are:
A1 (yellow) B1 (brown) and GND (blue). (The other wires are used for the display which came with the Nilan Comfort 300LR).
At the other end (RS485 USB dongle), the same three wires will have to be connected like this:
In following order from left to right of the picture: Blue, Yellow and Brown.
The dip switches is set to, 1 = OFF, 2 = ON, 3 = ON and 4 = ON.
Setting up Openhab.
Go to PaperUI → Addons → Bindings and install the Modbus 2.4 (or later) binding.
Thats basicly it.
From here, all thats needed is a things, and items and sitemap. I have created a basic (full) setup ready to use, by just copying the files into their respective folders, covering the Nilan Comfort 300LR (without heater and CO2 addon If your agregate got heater and/or CO2, you should add the extra registers as well as the items).
.things:
Bridge modbus:serial:myNilan [ port="/dev/ttyUSB0", id=30, baud=19200, stopBits="1.0", parity="even", dataBits=8, encoding="rtu" ] {
  Bridge poller appRegisters [ start=000, length=4, refresh=6000, type="input" ] {
      Thing data inp000 [ readStart="000", readValueType="int16" ]
      Thing data inp001 [ readStart="001", readValueType="int16" ]
      Thing data inp002 [ readStart="002", readValueType="int16" ]
      Thing data inp003 [ readStart="003", readValueType="int16" ]
  Bridge poller 100Registers [ start=100, length=16, refresh=6000, type="input" ] {
      Thing data inp100 [ readStart="100", readValueType="int16" ]
      Thing data inp101 [ readStart="101", readValueType="int16" ]
      Thing data inp103 [ readStart="103", readValueType="int16" ]
      Thing data inp105 [ readStart="105", readValueType="int16" ]
      Thing data inp106 [ readStart="106", readValueType="int16" ]
      Thing data inp107 [ readStart="107", readValueType="int16" ]
      Thing data inp114 [ readStart="114", readValueType="int16" ]
      Thing data inp115 [ readStart="115", readValueType="int16" ]
  Bridge poller inputRegisters [ start=200, length=23, refresh=6000, type="input" ] {
      Thing data inp200 [ readStart="200", readValueType="int16", readTransform="JS(divide100.js)" ]
      Thing data inp202 [ readStart="202", readValueType="int16", readTransform="JS(divide100.js)" ]
      Thing data inp203 [ readStart="203", readValueType="int16", readTransform="JS(divide100.js)" ]
      Thing data inp204 [ readStart="204", readValueType="int16", readTransform="JS(divide100.js)" ]
      Thing data inp207 [ readStart="207", readValueType="int16", readTransform="JS(divide100.js)" ]
      Thing data inp208 [ readStart="208", readValueType="int16", readTransform="JS(divide100.js)" ]
      Thing data inp209 [ readStart="209", readValueType="int16", readTransform="JS(divide100.js)" ]
      Thing data inp210 [ readStart="210", readValueType="int16", readTransform="JS(divide100.js)" ]
      Thing data inp215 [ readStart="215", readValueType="int16", readTransform="JS(divide100.js)" ]
      Thing data inp221 [ readStart="221", readValueType="int16", readTransform="JS(divide100.js)" ]
  Bridge poller 400Registers [ start=400, length=10, refresh=6000, type="input" ] {
      Thing data inp400 [ readStart="400", readValueType="int16" ]
      Thing data inp401 [ readStart="401", readValueType="int16" ]
      Thing data inp402 [ readStart="402", readValueType="int16", readTransform="JS(nilan_alarmdate.js)" ]
      Thing data inp403 [ readStart="403", readValueType="int16", readTransform="JS(nilan_alarmdate.js)" ]
      Thing data inp404 [ readStart="404", readValueType="int16" ]
      Thing data inp405 [ readStart="405", readValueType="int16", readTransform="JS(nilan_alarmdate.js)" ]
      Thing data inp406 [ readStart="406", readValueType="int16", readTransform="JS(nilan_alarmdate.js)" ]
      Thing data inp407 [ readStart="407", readValueType="int16" ]
      Thing data inp408 [ readStart="408", readValueType="int16", readTransform="JS(nilan_alarmdate.js)" ]
      Thing data inp409 [ readStart="409", readValueType="int16", readTransform="JS(nilan_alarmdate.js)" ]
  Bridge poller statusRegisters [ start=1000, length=4, refresh=6000, type="input" ] {
      Thing data inp1000 [ readStart="1000", readValueType="int16" ]
      Thing data inp1001 [ readStart="1001", readValueType="int16" ]
      Thing data inp1002 [ readStart="1002", readValueType="int16" ]
      Thing data inp1003 [ readStart="1003", readValueType="int16" ]
  Bridge poller airflowRegisters [ start=1100, length=5, refresh=6000, type="input" ] {
      Thing data inp1100 [ readStart="1100", readValueType="int16" ]
      Thing data inp1101 [ readStart="1101", readValueType="int16" ]
      Thing data inp1102 [ readStart="1102", readValueType="int16" ]
      Thing data inp1103 [ readStart="1103", readValueType="int16" ]
      Thing data inp1104 [ readStart="1104", readValueType="int16" ]
  Bridge poller airRegisters [ start=1200, length=7, refresh=6000, type="input" ] {
      Thing data inp1200 [ readStart="1200", readValueType="int16" ]
      Thing data inp1201 [ readStart="1201", readValueType="int16", readTransform="JS(divide100.js)" ]
      Thing data inp1202 [ readStart="1202", readValueType="int16", readTransform="JS(divide100.js)" ]
      Thing data inp1203 [ readStart="1203", readValueType="int16", readTransform="JS(divide100.js)" ]
      Thing data inp1204 [ readStart="1204", readValueType="int16", readTransform="JS(divide100.js)" ]
      Thing data inp1205 [ readStart="1205", readValueType="int16", readTransform="JS(divide100.js)" ]
      Thing data inp1206 [ readStart="1206", readValueType="int16", readTransform="JS(divide100.js)" ]
  Bridge poller displayRegisters [ start=2000, length=12, refresh=6000, type="input" ] {
      Thing data inp2000 [ readStart="2000", readValueType="int16" ]
      Thing data inp2000 [ readStart="2002", readValueType="int16" ]
      Thing data inp2000 [ readStart="2003", readValueType="int16" ]
      Thing data inp2000 [ readStart="2004", readValueType="int16" ]
      Thing data inp2000 [ readStart="2005", readValueType="int16" ]
      Thing data inp2000 [ readStart="2006", readValueType="int16" ]
      Thing data inp2000 [ readStart="2007", readValueType="int16" ]
      Thing data inp2000 [ readStart="2008", readValueType="int16" ]
      Thing data inp2000 [ readStart="2009", readValueType="int16" ]
      Thing data inp2000 [ readStart="2010", readValueType="int16" ]
      Thing data inp2000 [ readStart="2011", readValueType="int16" ]
  Bridge poller holdingRegisters [ start=100, length=28, refresh=6000, type="holding" ] {
      Thing data hold100 [ readStart="100", readValueType="int16" ]
      Thing data hold102 [ readStart="102", readValueType="int16" ]
      Thing data hold103 [ readStart="103", readValueType="int16" ]
      Thing data hold123 [ readStart="123", readValueType="int16", writeStart="123", writeValueType="int16", writeType="holding", writeMultipleEvenWithSingleRegisterOrCoil="true"  ]
      Thing data hold125 [ readStart="125", readValueType="int16", writeStart="125", writeValueType="int16", writeType="holding" ]
      Thing data hold126 [ readStart="126", readValueType="int16", writeStart="126", writeValueType="int16", writeType="holding" ]
  Bridge poller fanRegisters [ start=200, length=3, refresh=6000, type="holding" ] {
      Thing data hold200 [ readStart="200", readValueType="int16", readTransform="JS(divide100.js)" ]
      Thing data hold201 [ readStart="201", readValueType="int16", readTransform="JS(divide100.js)" ]
      Thing data hold202 [ readStart="202", readValueType="int16", readTransform="JS(divide100.js)" ]
  Bridge poller timeRegisters [ start=300, length=6, refresh=6000, type="holding" ] {
      Thing data hold300 [ readStart="300", readValueType="int16" ]
      Thing data hold301 [ readStart="301", readValueType="int16" ]
      Thing data hold302 [ readStart="302", readValueType="int16" ]
      Thing data hold303 [ readStart="303", readValueType="int16" ]
      Thing data hold304 [ readStart="304", readValueType="int16" ]
      Thing data hold305 [ readStart="305", readValueType="int16" ]
  Bridge poller ProgSelRegisters [ start=500, length=2, refresh=6000, type="holding" ] {
      Thing data hold500 [ readStart="500", readValueType="int16", writeStart="500", writeValueType="int16", writeType="holding", writeMultipleEvenWithSingleRegisterOrCoil="true" ]
  Bridge poller ProgUserFuncActRegisters [ start=600, length=7, refresh=6000, type="holding" ] {
      Thing data hold600 [ readStart="600", readValueType="int16", writeStart="600", writeValueType="int16", writeType="holding", writeMultipleEvenWithSingleRegisterOrCoil="true" ]
      Thing data hold601 [ readStart="601", readValueType="int16", writeStart="601", writeValueType="int16", writeType="holding", writeMultipleEvenWithSingleRegisterOrCoil="true" ]
      Thing data hold602 [ readStart="602", readValueType="int16", writeStart="602", writeValueType="int16", writeType="holding", writeMultipleEvenWithSingleRegisterOrCoil="true" ]
      Thing data hold603 [ readStart="603", readValueType="int16", writeStart="603", writeValueType="int16", writeType="holding", writeMultipleEvenWithSingleRegisterOrCoil="true" ]
      Thing data hold604 [ readStart="604", readValueType="int16", writeStart="604", writeValueType="int16", writeType="holding", writeMultipleEvenWithSingleRegisterOrCoil="true", readTransform="JS(divide100.js)", writeTransform="JS(multiply100.js)" ]
      Thing data hold605 [ readStart="605", readValueType="int16", writeStart="605", writeValueType="int16", writeType="holding", writeMultipleEvenWithSingleRegisterOrCoil="true", readTransform="JS(divide100.js)", writeTransform="JS(multiply100.js)" ]
  Bridge poller controlRegisters [ start=1001, length=7, refresh=6000, type="holding" ] {
      Thing data hold1001 [ readStart="1001", readValueType="int16", writeStart="1001", writeValueType="int16", writeType="holding", writeMultipleEvenWithSingleRegisterOrCoil="true" ]
      Thing data hold1002 [ readStart="1002", readValueType="int16", writeStart="1002", writeValueType="int16", writeType="holding", writeMultipleEvenWithSingleRegisterOrCoil="true"  ]
      Thing data hold1003 [ readStart="1003", readValueType="int16", writeStart="1003", writeValueType="int16", writeType="holding", writeMultipleEvenWithSingleRegisterOrCoil="true"  ]
      Thing data hold1004 [ readStart="1004", readValueType="int16", writeStart="1004", writeValueType="int16", writeType="holding", writeMultipleEvenWithSingleRegisterOrCoil="true", readTransform="JS(divide100.js)", writeTransform="JS(multiply100.js)"  ]
      Thing data hold1005 [ readStart="1005", readValueType="int16" ]
      Thing data hold1006 [ readStart="1006", readValueType="int16", readTransform="JS(divide100.js)" ]
      Thing data hold1007 [ readStart="1007", readValueType="int16" ]
  Bridge poller AirFlowExhMoRegisters [ start=1100, length=2, refresh=6000, type="holding" ] {
      Thing data hold1100 [ readStart="1100", readValueType="int16" ]
      Thing data hold1101 [ readStart="1101", readValueType="int16", writeStart="1101", writeValueType="int16", writeType="holding", writeMultipleEvenWithSingleRegisterOrCoil="true" ]
  Bridge poller AirTempRegisters [ start=1200, length=8, refresh=6000, type="holding" ] {
      Thing data hold1200 [ readStart="1200", readValueType="int16", writeStart="1200", writeValueType="int16", writeType="holding", writeMultipleEvenWithSingleRegisterOrCoil="true", readTransform="JS(divide100.js)", writeTransform="JS(multiply100.js)" ]
      Thing data hold1201 [ readStart="1201", readValueType="int16", writeStart="1201", writeValueType="int16", writeType="holding", writeMultipleEvenWithSingleRegisterOrCoil="true", readTransform="JS(divide100.js)", writeTransform="JS(multiply100.js)" ]
      Thing data hold1202 [ readStart="1202", readValueType="int16", writeStart="1202", writeValueType="int16", writeType="holding", writeMultipleEvenWithSingleRegisterOrCoil="true", readTransform="JS(divide100.js)", writeTransform="JS(multiply100.js)" ]
      Thing data hold1203 [ readStart="1203", readValueType="int16", writeStart="1203", writeValueType="int16", writeType="holding", writeMultipleEvenWithSingleRegisterOrCoil="true", readTransform="JS(divide100.js)", writeTransform="JS(multiply100.js)" ]
      Thing data hold1204 [ readStart="1204", readValueType="int16", writeStart="1204", writeValueType="int16", writeType="holding", writeMultipleEvenWithSingleRegisterOrCoil="true", readTransform="JS(divide100.js)", writeTransform="JS(multiply100.js)" ]
      Thing data hold1205 [ readStart="1205", readValueType="int16", writeStart="1205", writeValueType="int16", writeType="holding", writeMultipleEvenWithSingleRegisterOrCoil="true", readTransform="JS(divide100.js)", writeTransform="JS(multiply100.js)" ]
 Bridge poller AirQuaRhRegisters [ start=1910, length=4, refresh=6000, type="holding" ] {
      Thing data hold1910 [ readStart="1910", readValueType="int16", writeStart="1910", writeValueType="int16", writeType="holding", writeMultipleEvenWithSingleRegisterOrCoil="true" ]
      Thing data hold1911 [ readStart="1911", readValueType="int16", writeStart="1911", writeValueType="int16", writeType="holding", writeMultipleEvenWithSingleRegisterOrCoil="true" ]
      Thing data hold1912 [ readStart="1912", readValueType="int16", writeStart="1912", writeValueType="int16", writeType="holding", writeMultipleEvenWithSingleRegisterOrCoil="true", readTransform="JS(divide100.js)", writeTransform="JS(multiply100.js)" ]
      Thing data hold1913 [ readStart="1913", readValueType="int16", writeStart="1913", writeValueType="int16", writeType="holding", writeMultipleEvenWithSingleRegisterOrCoil="true" ]
items:
/* Nilan */
String nilan_generated_time         "Systemtime [%s]"    <time> (gNilan)
Number nilan_generated_chartperiod  "Chart period [%d]"  <line>  (gNilan)
Group gNilan            "All Modbus attributes (input + holding)"
Group gNilanProgram     "User program settings"
Group gAirSensor        "Air temperature and quality sensors"
Number nilan_BusVersion		          "Bus version [%s]"        {channel="modbus:data:myNilan:appRegisters:inp000:number"}
String nilan_AppVersionMajor	      "App Version Major [%s]"        {channel="modbus:data:myNilan:appRegisters:inp001:string"}
String nilan_AppversionMinor	      "App Version Minor [%s]"        {channel="modbus:data:myNilan:appRegisters:inp002:string"}
String nilan_AppVersionRelease	      "App Version Release [%s]"        {channel="modbus:data:myNilan:appRegisters:inp003:string"}
Switch  nilan_Input_UserFunc          "User function [%s]"                         	                           <boy_2>         (gNilan) 		                         {channel="modbus:data:myNilan:100Registers:inp100:switch"}
Switch  nilan_Input_AirFilter         "Air filter alarm [%s]"                      	                           <siren>         (gNilan)		                             {channel="modbus:data:myNilan:100Registers:inp101:switch"}
Switch  nilan_Input_Smoke             "Fire/Smoke alarm [%s]"                      	                           <smoke>         (gNilan) 		                         {channel="modbus:data:myNilan:100Registers:inp103:switch"}
Switch  nilan_Input_Frost_Overht      "Heating surface frost / overheat [%s]"      	                           <climate>       (gNilan) 		                         {channel="modbus:data:myNilan:100Registers:inp105:switch"}
Switch  nilan_Input_AirFlow           "Airflow monitor (guard) [%s]"               	                           <flow>          (gNilan) 		                         {channel="modbus:data:myNilan:100Registers:inp106:switch"}
Switch  nilan_Input_P_HI              "High pressure switch [%s]"                  	                           <pressure>      (gNilan)			                         {channel="modbus:data:myNilan:100Registers:inp107:switch"}
Switch  nilan_Input_DamperClosed      "Air Damper Closed position [%s]"                                        <flow>          (gNilan) 		                         {channel="modbus:data:myNilan:100Registers:inp114:switch"}
Switch  nilan_Input_DamperOpen        "Air Damper Open position [%s]"                                          <flow>          (gNilan) 		                         {channel="modbus:data:myNilan:100Registers:inp115:switch"}
Number nilan_Input_T0_Controller      "T0 Controller Board Temperature [%.1f °C]"                              <temperature>   (gNilan,heat_nilan) 			             {channel="modbus:data:myNilan:inputRegisters:inp200:number"}
// Number nilan_Input_T2_Inlet        "Inlet Temperature (before heater) [%.1f °C]"                            <temperature>   (gNilan)		 		                     {channel="modbus:data:myNilan:inputRegisters:inp202:number"}
Number nilan_Input_T3_Exhaust         "T3 Room Exhaust Temperature [%.1f °C]"                                  <temperature>   (gNilan,gAirSensor,gChart,heat_nilan)	 {channel="modbus:data:myNilan:inputRegisters:inp203:number"}
Number nilan_Input_T4_Outlet          "T4 Outlet Temperature [%.1f °C]"                                        <temperature>   (gNilan,heat_nilan)			             {channel="modbus:data:myNilan:inputRegisters:inp204:number"}
Number nilan_Input_T7_Inlet           "T7 Inlet Temperature (after heater) [%.1f °C]"                          <temperature>   (gNilan,gAirSensor,gChart,heat_nilan)	 {channel="modbus:data:myNilan:inputRegisters:inp207:number"}
Number nilan_Input_T8_Outdoor         "T8 Outdoor temperatur [%.1f °C]"                                        <temperature>   (gNilan,gAirSensor,gChart,heat_nilan)	 {channel="modbus:data:myNilan:inputRegisters:inp208:number"}
Number nilan_Input_T9_Heater          "T9 Heating Surface Temperature T9 [%.1f °C]"                            <temperature>   (gNilan,heat_nilan)  			         {channel="modbus:data:myNilan:inputRegisters:inp209:number"}
Number nilan_Input_T10_Extem          "T10 External room temperature T10 [%.1f °C]"                            <temperature>   (gNilan,heat_nilan)  			         {channel="modbus:data:myNilan:inputRegisters:inp210:number"}
Number nilan_Input_T15_Room           "T15 Userpanel Room Temperatur [%.1f °C]"                                <temperature>   (gNilan,gAirSensor,heat_nilan)   	     {channel="modbus:data:myNilan:inputRegisters:inp215:number"}
Number nilan_Input_RH                 "Humidity [%.0f %%]"                                                     <humidity>      (gNilan,gAirSensor,Fugtighed)		     {channel="modbus:data:myNilan:inputRegisters:inp221:number"}
Number Nilan_Alarm_Status             "Alarm state bit mask [%d]"                                        	   <keyring>       (gNilanAlarm) 	                         {channel="modbus:data:myNilan:400Registers:inp400:number"}
Number Nilan_Alarm_List_1_ID          "Alarm 1 - Code [MAP(nilan_alarmcode_to_string.map):%s]"           	   <keyring>       (gNilanAlarm) 	                         {channel="modbus:data:myNilan:400Registers:inp401:number"}
String Nilan_Alarm_List_1_Date        "Alarm 1 - Date [%s]"                                              	   <calendar>      (gNilanAlarm) 	                         {channel="modbus:data:myNilan:400Registers:inp402:string"}
String Nilan_Alarm_List_1_Time        "Alarm 1 - Time [%s]"                                              	   <clock>         (gNilanAlarm) 	                         {channel="modbus:data:myNilan:400Registers:inp403:string"}
Number Nilan_Alarm_List_2_ID          "Alarm 2 - Code [%s]"                                              	   <keyring>       (gNilanAlarm) 	                         {channel="modbus:data:myNilan:400Registers:inp404:number"}
String Nilan_Alarm_List_2_Date        "Alarm 2 - Date [%s]"                                                    <calendar>      (gNilanAlarm) 	                         {channel="modbus:data:myNilan:400Registers:inp405:string"}
String Nilan_Alarm_List_2_Time        "Alarm 2 - Time [%s]"                                                    <clock>         (gNilanAlarm) 	                         {channel="modbus:data:myNilan:400Registers:inp406:string"}
Number Nilan_Alarm_List_3_ID          "Alarm 3 - Code [%s]"                                              	   <keyring>       (gNilanAlarm) 	                         {channel="modbus:data:myNilan:400Registers:inp407:number"}
String Nilan_Alarm_List_3_Date        "Alarm 3 - Date [%s]"                                              	   <calendar>      (gNilanAlarm) 	                         {channel="modbus:data:myNilan:400Registers:inp408:string"}
String Nilan_Alarm_List_3_Time        "Alarm 3 - Time [%s]"                                              	   <clock>         (gNilanAlarm) 	                         {channel="modbus:data:myNilan:400Registers:inp409:string"}
Switch nilan_Control_RunAct           "Actual on/off state [%s]" <switch>    (gNilan)							                                                     {channel="modbus:data:myNilan:statusRegisters:inp1000:switch"}
Number nilan_Control_ModeAct          "Actual operation mode [MAP(nilan_control_modeact.map):%s]" 		       <settings>       (gNilan)	                         {channel="modbus:data:myNilan:statusRegisters:inp1001:number"}
Number nilan_Control_State	          "Actual control state [MAP(nilan_control_state.map):%s]"    		       <settings>                                            {channel="modbus:data:myNilan:statusRegisters:inp1002:number"}
Number nilan_Control_SeclnState	      "Actual time in state [%d s]"				    		                   <time>			                                     {channel="modbus:data:myNilan:statusRegisters:inp1003:number"}
Number nilan_AirFlow_VentSet	      "Actual ventilation step set point [MAP(nilan_ventset.map):%s]"          <fan> 			                                     {channel="modbus:data:myNilan:airflowRegisters:inp1100:number"}
Number nilan_AirFlow_InletAct	      "Actual Inlet step set point [MAP(nilan_ventset.map):%s]" 		       <fan> 			                                     {channel="modbus:data:myNilan:airflowRegisters:inp1101:number"}
Number nilan_AirFlow_ExhaustAct	      "Actual Exhaust step set point [MAP(nilan_ventset.map):%s]" 	           <fan> 			                                     {channel="modbus:data:myNilan:airflowRegisters:inp1102:number"}
Number nilan_AirFlow_SinceFiltDay     "Days since last airfilter change alarm [%s]" 				           <calendar> 		                                     {channel="modbus:data:myNilan:airflowRegisters:inp1103:number"}
Number nilan_AirFlow_ToFiltDay        "Days to next airfilter change alarm [%s]" 				               <calendar> 		                                     {channel="modbus:data:myNilan:airflowRegisters:inp1104:number"}
Number Nilan_AirTemp_IsSummer         "Summer state [MAP(nilan_summer_on_off.map):%s]"                         <sun>            (gNilan)	                         {channel="modbus:data:myNilan:airRegisters:inp1200:number"}
Number Nilan_AirTemp_TempinletSet     "Inlet temperature request (T7 setpoint) [%.1f °C]" 		               <temperature>  	(gNilan)	                         {channel="modbus:data:myNilan:airRegisters:inp1201:number"}
Number Nilan_AirTemp_TempControl      "Actual value for controlled temperature [%.1f °C]" 		               <temperature>    (gNilan)	                         {channel="modbus:data:myNilan:airRegisters:inp1202:number"}
Number Nilan_AirTemp_TempRoom         "Actual room temperature (T15 or T10) [%.1f °C]"    		               <temperature>    (gNilan)	                         {channel="modbus:data:myNilan:airRegisters:inp1203:number"}
Number Nilan_AirTemp_EffPct           "Passive Heat exchanger efficiency [%.1f %%]"       			           <line>           (gNilan)	                         {channel="modbus:data:myNilan:airRegisters:inp1204:number"}
Number Nilan_AirTemp_CapSet           "Requested capacity [%.1f %%]"        {channel="modbus:data:myNilan:airRegisters:inp1205:number"}
Number Nilan_AirTemp_CapAct           "Actual capacity [%.1f %%]"        {channel="modbus:data:myNilan:airRegisters:inp1206:number"}
Number Nilan_Display_LED_1		      "LED 1 [MAP(nilan_on_off.map):%s]"    				                   <cu_light> 	    (gNilan) 	                         {channel="modbus:data:myNilan:displayRegisters:inp2000:number"}
String Nilan_Display_Text_1_2         "Text line 1 character 1-2 [%s]"           					                            (gNilan) 	                         {channel="modbus:data:myNilan:displayRegisters:inp2002:string"}
String Nilan_Display_Text_3_4         "Text line 1 character 3-4 [%s]"            					                            (gNilan) 	                         {channel="modbus:data:myNilan:displayRegisters:inp2003:string"}
String Nilan_Display_Text_5_6         "Text line 1 character 5-6 [%s]"            					                            (gNilan)	                         {channel="modbus:data:myNilan:displayRegisters:inp2004:string"}
String Nilan_Display_Text_7_8         "Text line 1 character 7-8 [%s]"            					                            (gNilan) 	                         {channel="modbus:data:myNilan:displayRegisters:inp2005:string"}
Number Nilan_Display_Attr_1_8         "Text line 1 flags [%d]"                   					                            (gNilan) 	                         {channel="modbus:data:myNilan:displayRegisters:inp2006:number"}
String Nilan_Display_Text_9_10        "Text line 2 character 9-10 [%s]"           					                            (gNilan) 	                         {channel="modbus:data:myNilan:displayRegisters:inp2007:string"}
String Nilan_Display_Text_11_12       "Text line 2 character 11-12 [%s]"          					                            (gNilan) 	                         {channel="modbus:data:myNilan:displayRegisters:inp2008:string"}
String Nilan_Display_Text_13_14       "Text line 2 character 13-14 [%s]"          					                            (gNilan) 	                         {channel="modbus:data:myNilan:displayRegisters:inp2009:string"}
String Nilan_Display_Text_15_16       "Text line 2 character 15-16 [%s]"          					                            (gNilan) 	                         {channel="modbus:data:myNilan:displayRegisters:inp2010:string"}
Number Nilan_Display_Attr_9_16        "Text line 2 flags [%d]"                    					                            (gNilan) 	                         {channel="modbus:data:myNilan:displayRegisters:inp2011:number"}
Contact nilan_Output_AirFlap          "Air flap [%s]"                  					                       <contact>	    (gNilan)	                         {channel="modbus:data:myNilan:holdingRegisters:hold100:contact"}
Contact nilan_Output_BypassOpen       "Bypass flap open [%s]"           				                       <contact>	    (gNilan)	                         {channel="modbus:data:myNilan:holdingRegisters:hold102:contact"}
Contact nilan_Output_BypassClose      "Bypass flap close [%s]"          				                       <contact>	    (gNilan)	                         {channel="modbus:data:myNilan:holdingRegisters:hold103:contact"}
Switch  nilan_Output_UserFunc         "User function active [%s]"            				                   <boy_2>      	(gNilan)                             {channel="modbus:data:myNilan:holdingRegisters:hold123:switch"}
Switch  nilan_Output_Defrosting       "Defrost function active [%s]"         		                           <climate>    	(gNilan)                             {channel="modbus:data:myNilan:holdingRegisters:hold125:switch"}
Switch  nilan_AlarmRelayState	      "Alarm Relay state [%s]"						                           <switch>	        (gNilan)                             {channel="modbus:data:myNilan:holdingRegisters:hold126:switch"}
Number nilan_Output_ExhaustSpeed      "Exhaust fan speed [%.0f %%]"               			                   <fan>            (gNilan)	                         {channel="modbus:data:myNilan:fanRegisters:hold200:number"}
Number nilan_Output_InletSpeed        "Inlet fan speed [%.0f %%]"                			                   <fan>     	    (gNilan)	                         {channel="modbus:data:myNilan:fanRegisters:hold201:number"}
Number nilan_Output_AirHeatCap        "Air heater capacity [%.1f %%]"             			                   <line>			                                     {channel="modbus:data:myNilan:fanRegisters:hold202:number"}
Number	Nilan_Time_Second	          "Second [%d]" 							                               <time>		    (gNilan) 	                         {channel="modbus:data:myNilan:timeRegisters:hold300:number"}
Number	Nilan_Time_Minute	          "Minute [%d]" 							                               <time>		    (gNilan) 	                         {channel="modbus:data:myNilan:timeRegisters:hold301:number"}
Number	Nilan_Time_Hour		          "Hour [%d]" 							                                   <time>		    (gNilan) 	                         {channel="modbus:data:myNilan:timeRegisters:hold302:number"}
Number	Nilan_Time_Day		          "Day [%d]" 							                                   <calendar> 	    (gNilan) 	                         {channel="modbus:data:myNilan:timeRegisters:hold303:number"}
Number	Nilan_Time_Month	          "Month [%d]" 							                                   <calendar> 	    (gNilan) 	                         {channel="modbus:data:myNilan:timeRegisters:hold304:number"}
Number	Nilan_Time_Year		          "Year [%d]" 							                                   <calendar> 	    (gNilan) 	                         {channel="modbus:data:myNilan:timeRegisters:hold305:number"}
Number Nilan_Program_Select           "Week program nb. select [MAP(nilan_program_select.map):%s]"     	       <calendar>       (gNilan,gNilanProgram) 	             {channel="modbus:data:myNilan:ProgSelRegisters:hold500:number"}
Switch Nilan_Program_UserFuncAct      "User function active [%s]"                                              <boy_2>          (gNilan,gNilanProgram) 	             {channel="modbus:data:myNilan:ProgUserFuncActRegisters:hold600:switch"}
Number Nilan_Program_UserFuncSet      "User function select [MAP(nilan_program_userfuncset.map):%s]"           <settings>       (gNilan,gNilanProgram) 	             {channel="modbus:data:myNilan:ProgUserFuncActRegisters:hold601:number"}
Number Nilan_Program_UserTimeSet      "Min User function period [%d min.]"                                     <clock>          (gNilan,gNilanProgram)               {channel="modbus:data:myNilan:ProgUserFuncActRegisters:hold602:number"}
Number Nilan_Program_UserVentSet      "Step User function ventilation [MAP(nilan_ventset.map):%s]"             <fan_ceiling>    (gNilan,gNilanProgram) 	             {channel="modbus:data:myNilan:ProgUserFuncActRegisters:hold603:number"}
Number Nilan_Program_UserTempSet      "User function temperature (Extend function only) [%.1f °C]"             <temperature>    (gNilan,gNilanProgram) 	             {channel="modbus:data:myNilan:ProgUserFuncActRegisters:hold604:number"}
Number Nilan_Program_UserOffsSet      "User function temperature(Offset function only) [%.1f °C]"              <temperature>    (gNilan,gNilanProgram) 	             {channel="modbus:data:myNilan:ProgUserFuncActRegisters:hold605:number"}
Switch Nilan_Control_RunSet          "User on / off select"                                           	       <switch>         (gNilan) 	                         {channel="modbus:data:myNilan:controlRegisters:hold1001:switch"}
Number Nilan_Control_ModeSet         "User operation mode select [MAP(nilan_control_modeact.map):%s]" 	       <settings>       (gNilan) 	                         {channel="modbus:data:myNilan:controlRegisters:hold1002:number"}
Number Nilan_Control_VentSet         "User ventilation step select [MAP(nilan_ventset.map):%s]"       	       <fan_ceiling>    (gNilan) 	                         {channel="modbus:data:myNilan:controlRegisters:hold1003:number", autoupdate="false"}
Number Nilan_Control_TempSet         "User temperature setpoint [%.1f °C]"                            	       <temperature>    (gNilan) 	                         {channel="modbus:data:myNilan:controlRegisters:hold1004:number"}
Number Nilan_Control_ServiceMode     "Service mode select [MAP(nilan_control_servicemode.map):%s]"    	       <lock>           (gNilan) 	                         {channel="modbus:data:myNilan:controlRegisters:hold1005:number"}
Number Nilan_Control_ServicePct      "Service mode capacity [%.1f %%]"                                                	        (gNilan) 	                         {channel="modbus:data:myNilan:controlRegisters:hold1006:number"}
Number Nilan_Control_Preset          "Request preset to factory [%d]"                                                 	        (gNilan) 	                         {channel="modbus:data:myNilan:controlRegisters:hold1007:number"}
Number Nilan_AirFlow_AirExchMode     "Air exchange mode [MAP(nilan_airflow_airexchmode.map):%s]"      	       <flow>           (gNilan) 	                         {channel="modbus:data:myNilan:AirFlowExhMoRegisters:hold1100:number"}
Number Nilan_AirFlow_CoolVent        "Cooling high ventilation step [MAP(nilan_ventset.map):%s]"      	       <fan_ceiling>    (gNilan) 	                         {channel="modbus:data:myNilan:AirFlowExhMoRegisters:hold1101:number"}
Number Nilan_AirTemp_CoolSet         "Cooling temperature setpoint select [%d]"  			                   <temperature> 	(gNilan) 	                         {channel="modbus:data:myNilan:AirTempRegisters:hold1200:number"}
Number Nilan_AirTemp_TempMinSum      "Inlet temp. min. summer [%.1f °C]"         			                   <temperature> 	(gNilan) 	                         {channel="modbus:data:myNilan:AirTempRegisters:hold1201:number"}
Number Nilan_AirTemp_TempMinWin      "Inlet temp. min. winter [%.1f °C]"         			                   <temperature> 	(gNilan) 	                         {channel="modbus:data:myNilan:AirTempRegisters:hold1202:number"}
Number Nilan_AirTemp_TempMax         "Inlet temp. max. summer [%.1f °C]"         			                   <temperature> 	(gNilan) 	                         {channel="modbus:data:myNilan:AirTempRegisters:hold1203:number"}
Number Nilan_AirTemp_TempMaxWin      "Inlet temp. max. winter [%.1f °C]"         			                   <temperature> 	(gNilan) 	                         {channel="modbus:data:myNilan:AirTempRegisters:hold1204:number"}
Number Nilan_AirTemp_TempSummer      "Summer/winter limit [%.1f °C]"             			                   <temperature> 	(gNilan) 	                         {channel="modbus:data:myNilan:AirTempRegisters:hold1205:number"}
Number Nilan_AirQual_RH_VentLo       "Humidity low winter step select [MAP(nilan_ventset.map):%s]" 	           <fan_ceiling> 	(gNilan) 	                         {channel="modbus:data:myNilan:AirQuaRhRegisters:hold1910:number"}
Number Nilan_AirQual_RH_VentHi       "Humidity high step select [MAP(nilan_ventset.map):%s]"       	           <fan_ceiling> 	(gNilan) 	                         {channel="modbus:data:myNilan:AirQuaRhRegisters:hold1911:number"}
Number Nilan_AirQual_RH_LimLo        "Humidity limit for low ventilation [%.0f %%]"                	           <humidity>    	(gNilan) 	                         {channel="modbus:data:myNilan:AirQuaRhRegisters:hold1912:number"}
Number Nilan_AirQual_RH_TimeOut      "Humidity max. time on high ventilation [%d min.]"            	           <clock>       	(gNilan) 	                         {channel="modbus:data:myNilan:AirQuaRhRegisters:hold1913:number"}
sitemap:
sitemap nilan label="Nilan"  {
	Frame label="Inputs100" {
		Text item=nilan_Input_UserFunc
		Text item=nilan_Input_AirFilter
		Text item=nilan_Input_Smoke
		Text item=nilan_Input_Frost_Overht
		Text item=nilan_Input_AirFlow
		Text item=nilan_Input_P_HI
		Text item=nilan_Input_DamperClosed
		Text item=nilan_Input_DamperOpen
	Frame label="Inputs200" {
		Text item=nilan_Input_T0_Controller
//		Text item=nilan_Input_T2_Inlet // If No heating feature, inlet temperature reports from T7
		Text item=nilan_Input_T3_Exhaust
		Text item=nilan_Input_T4_Outlet
		Text item=nilan_Input_T7_Inlet
		Text item=nilan_Input_T8_Outdoor
//		Text item=nilan_Input_T9_Heater  // Requires a heater
//		Text item=nilan_Input_T10_Extem  // Requires external room thermostat
		Text item=nilan_Input_T15_Room
		Text item=nilan_Input_RH
	Frame label="Inputs400 Alarm" {
		Text item=Nilan_Alarm_Status
		Text item=Nilan_Alarm_List_1_ID
		Text item=Nilan_Alarm_List_1_Date
		Text item=Nilan_Alarm_List_1_Time
		Text item=Nilan_Alarm_List_2_ID
		Text item=Nilan_Alarm_List_2_Date
		Text item=Nilan_Alarm_List_2_Time
		Text item=Nilan_Alarm_List_3_ID
		Text item=Nilan_Alarm_List_3_Date
		Text item=Nilan_Alarm_List_3_Time
	Frame label="Inputs1000" {
		Text item=nilan_Control_RunAct
		Text item=nilan_Control_ModeAct
		Text item=nilan_Control_State
		Text item=nilan_Control_SeclnState
	Frame label="Inputs1100" {
		Text item=nilan_AirFlow_VentSet
		Text item=nilan_AirFlow_InletAct
		Text item=nilan_AirFlow_ExhaustAct
		Text item=nilan_AirFlow_SinceFiltDay
	Frame label="Inputs1200" {
		Text item=Nilan_AirTemp_IsSummer
		Text item=Nilan_AirTemp_TempinletSet
		Text item=Nilan_AirTemp_TempControl
		Text item=Nilan_AirTemp_TempRoom
		Text item=Nilan_AirTemp_EffPct
		Text item=Nilan_AirTemp_CapSet
		Text item=Nilan_AirTemp_CapAct
	Frame label="Inputs2000 Panel Display " {
		Text item=Nilan_Display_LED_1
		Text item=Nilan_Display_Text_1_2
		Text item=Nilan_Display_Text_3_4
		Text item=Nilan_Display_Text_5_6
		Text item=Nilan_Display_Text_7_8
		Text item=Nilan_Display_Attr_1_8
		Text item=Nilan_Display_Text_9_10
		Text item=Nilan_Display_Text_11_12
		Text item=Nilan_Display_Text_13_14
		Text item=Nilan_Display_Text_15_16
		Text item=Nilan_Display_Attr_9_16
	Frame label="Holding 100" {
		Text item=nilan_Output_AirFlap
		Text item=nilan_Output_BypassOpen
		Text item=nilan_Output_BypassClose
		Text item=nilan_Output_UserFunc
		Text item=nilan_Output_Defrosting
		Text item=nilan_AlarmRelayState
	Frame label="Holding 200" {
		Text item=nilan_Output_ExhaustSpeed
		Text item=nilan_Output_InletSpeed
		Text item=nilan_Output_AirHeatCap
    Frame label="Holding 300" {
		Text item=Nilan_Time_Second
		Text item=Nilan_Time_Minute
		Text item=Nilan_Time_Hour
		Text item=Nilan_Time_Day
		Text item=Nilan_Time_Month
		Text item=Nilan_Time_Year
    Frame label="Holding 500" {
		Selection   item=Nilan_Program_Select       label="Weekprogram" mappings=[0="None", 1="Program 1", 2="Program 2", 3="Program 3", 4="Erase"]
	Frame label="Holding 600" {
		Selection 	item=Nilan_Program_UserFuncAct 	label="Activate User Function" mappings=[OFF="ikke aktiv", ON="aktiv"] icon="fire"
		Selection 	item=Nilan_Program_UserFuncSet 	label="User Function" mappings=[0="None", 1="Extend", 2="Inlet", 3="Exhaust", 4="External heater offset", 5="Ventilate"]
		Setpoint 	item=Nilan_Program_UserTimeSet 	label="Ventilation time [%d min.]" minValue=0 maxValue=65000 step=1
		Selection 	item=Nilan_Program_UserVentSet 	label="Ventilation speed" mappings=[0="Off", 1="1", 2="2", 3="3", 4="4"]
		Setpoint 	item=Nilan_Program_UserTempSet 	label="Set temperatur" minValue=0 maxValue=65 step=1 visibility=[Nilan_Program_UserFuncSet==1]
		Setpoint 	item=Nilan_Program_UserOffsSet	label="Temperatur-Offset" minValue=0 maxValue=65000 step=1 visibility=[Nilan_Program_UserFuncSet==4]
    Frame label="Holding 1000" {
		Switch    item=Nilan_Control_RunSet
		Selection item=Nilan_Control_ModeSet mappings=[0="Off", 1="Heat", 2="Cool", 3="AUTO", 4="Service"]
		Switch    item=Nilan_Control_VentSet mappings=[0="0", 1="1", 2="2", 3="3", 4="4"]
		Setpoint  item=Nilan_Control_TempSet minValue=0 maxValue=65 step=1
		Text      item=Nilan_Control_ServiceMode
		Text      item=Nilan_Control_ServicePct
		Text      item=Nilan_Control_Preset
		Text      item=nilan_generated_time
    Frame label="Holding 1100" {
		Selection item=Nilan_AirFlow_AirExchMode label="Air Echange Mode (mode)" mappings=[0="Energy", 1="Comfort", 2="ComfortWater"] //only suitable when having a heater.
		Selection item=Nilan_AirFlow_CoolVent    label="Ventilation speed for cooling" mappings=[0="Off", 1="1", 2="2", 3="3", 4="4"]
	Frame label="AirTemp 1200 Holding" {
		Selection item=Nilan_AirTemp_CoolSet    label="Cooling set temperature" mappings=[0="Off (No cooling allowed)", 1="Set + 0 °C (User setpoint plus 0 degrees)", 2="Set + 1 °C", 3="Set + 2 °C", 4="Set + 3 °C", 5="Set + 4 °C", 6="Set + 5 °C", 7="Set + 7 °C", 8="Set + 10 °C"]
		Setpoint  item=Nilan_AirTemp_TempMinSum label="Temperaturminimum (Summer)" minValue=0 maxValue=65 step=1
		Setpoint  item=Nilan_AirTemp_TempMinWin label="Temperaturminimum (Winter)" minValue=0 maxValue=65 step=1
		Setpoint  item=Nilan_AirTemp_TempMax	label="Temperaturmaximum (Summer)" minValue=0 maxValue=65 step=1
		Setpoint  item=Nilan_AirTemp_TempMaxWin label="Temperaturmaximum (Winter)" minValue=0 maxValue=65 step=1
		Setpoint  item=Nilan_AirTemp_TempSummer label="Limit Summer / Winter" minValue=0 maxValue=65 step=1
	Frame label="AirQualRH 1910 Holding" {
		Selection item=Nilan_AirQual_RH_VentLo  label="Ventilation speed, if humidity is too low (Winter)" mappings=[0="Off", 1="1", 2="2", 3="3", 4="4"]
		Selection item=Nilan_AirQual_RH_VentHi  label="Ventilation speed, if humidity is too high" mappings=[0="Off", 1="1", 2="2", 3="3", 4="4"]
		Setpoint  item=Nilan_AirQual_RH_LimLo   label="Low humidity limit " minValue=0 maxValue=100 step=5
		Setpoint  item=Nilan_AirQual_RH_TimeOut label="Ventilation time, when humidity is too high [%d min.]"  minValue=0 maxValue=65000 step=1
	Frame label="app" {
		Text item=nilan_BusVersion
		Text item=nilan_AppVersionMajor
		Text item=nilan_AppversionMinor
		Text item=nilan_AppVersionRelease
Thats it. Please notice, the modbus ID in the things file is set for 30. This is the default modbus ID. If you for some reason have changed it, then you´ll have to change the things file as well.
Issues:
There are a few issues in the above setup.
Alarm dates are not transformed correctly or there is an issue with the modbus readings. I havn´t yet figure how to deal with this. The value returns date 0.0.1980, which is wrong. But I believe its possible to get the correct readings somehow. The problem with testing the alarm values, is to create an alarm issue. Filter exchanged is reported fine though.
The Display Text (LCD) values as well as the app registers needs to be translated in some way. I believe they uses the same scheme, but I havn´t yet understood fully. @nickma82 probably knows how to.
Whats missing is the transformations. There are quite a few in use, so I have compressed them into an RAR archive file for you to download insted. They are mostly self-explained I would say.
transform.rar.txt (3.0 KB)
Hopefully I covered all or most of it.
If anyone can apply with the rest of the registers for heating, CO2 as well as other missing informations about the alarm dates LCD Text and App data, feel free to contribute to this thread.
Hi Kim,
Nice work, the info here saved me a lot of time :slight_smile:
I will post if I make any addition to you work.
/Jon
Thank you for your post!
The post says that
Could somebody who knows more than I elaborate. My EC9 only has covered plugs (like the one on the right side of the modbus interface picture in this post). I have not wanted to start opening them in random before I know which/if any of them is the one that I want. The best would be if somebody could send me a couple of pictures.
Maybe a link to the docs of EC9 could help?
You can find something here.. I guess you´ll have to open it.
Hej Kim
i can’t make your setup work. install Bindings and the Modbus 2.4 an RS485 USB dongle),is unsure how things should be made,must install something on raspberry for USB dongle works
Is the USB dongle Oline?
-------- Oprindelig besked --------
I can not see it communicating..how can I see if it’s online?
In PaperUI.
Hej kim.
Kan se at modbus serial slave er online. Hvis det er den du mener USB dongle online? Er også i tvivl hvordan denne things fil skal laves
Mvh Michael
Hi Michael..
Remember to write in english..
If your dongle is online, you´ll just have to make the connection to a thing, either from PaperUI or by manual files, like my example above.
The thing files is placed in the folder /things/
Hi Kim..
i need a little more help: .. where in paperUI do you have to manually connect items? maybe you have some pictures of your setup … if i copy your things example files and put them in the things folder shouldn’t a file be created where they are put?
Manual created items are NOT in PaperUI. They´re in text based files, in the items folder.
If you copy the things files and place it into the things folder, you should be getting quite alot of modbus and poller Things visible in PaperUI. If not, then look into the log file, there should be tons of errors in there, probably cause by your connection isn´t established correctly.
Before this gets too complicated, take one step at a time.
Remember, my example above (original thread) is based on manual created text configuration files, and not through PaperUI.
Hi .. can it be appropriate to install modbus tcp and modbus serial? have been getting some data into basic UI but it doesn’t look right..thinks this file in things directory is not really
2019-09-28 22:43:07.951 [WARN ] [ui.internal.items.ItemUIRegistryImpl] - couldn’t transform value in label because transformationService of type ‘MAP’ is unavailable
2019-09-28 22:43:07.957 [WARN ] [ui.internal.items.ItemUIRegistryImpl] - couldn’t transform value in label because transformationService of type ‘MAP’ is unavailable
2019-09-28 22:43:07.968 [WARN ] [ui.internal.items.ItemUIRegistryImpl] - couldn’t transform value in label because transformationService of type ‘MAP’ is unavailable
2019-09-28 22:43:08.003 [WARN ] [ui.internal.items.ItemUIRegistryImpl] - couldn’t transform value in label because transformationService of type ‘MAP’ is unavailable
2019-09-28 22:43:08.010 [WARN ] [ui.internal.items.ItemUIRegistryImpl] - couldn’t transform value in label because transformationService of type ‘MAP’ is unavailable
2019-09-28 22:43:08.016 [WARN ] [ui.internal.items.ItemUIRegistryImpl] - couldn’t transform value in label because transformationService of type ‘MAP’ is unavailable
2019-09-28 22:43:08.025 [WARN ] [ui.internal.items.ItemUIRegistryImpl] - couldn’t transform value in label because transformationService of type ‘MAP’ is unavailable
2019-09-28 22:43:08.029 [WARN ] [ui.internal.items.ItemUIRegistryImpl] - couldn’t transform value in label because transformationService of type ‘MAP’ is unavailable
2019-09-28 22:43:08.041 [WARN ] [ui.internal.items.ItemUIRegistryImpl] - couldn’t transform value in label because transformationService of type ‘MAP’ is unavailable
2019-09-28 22:43:08.050 [WARN ] [ui.internal.items.ItemUIRegistryImpl] - couldn’t transform value in label because transformationService of type ‘MAP’ is unavailable
2019-09-28 22:43:08.055 [WARN ] [ui.internal.items.ItemUIRegistryImpl] - couldn’t transform value in label because transformationService of type ‘MAP’ is unavailable
2019-09-28 22:43:08.068 [WARN ] [ui.internal.items.ItemUIRegistryImpl] - couldn’t transform value in label because transformationService of type ‘MAP’ is unavailable
2019-09-28 22:43:08.072 [WARN ] [ui.internal.items.ItemUIRegistryImpl] - couldn’t transform value in label because transformationService of type ‘MAP’ is unavailable
MAP is an installable service. Use PaperUI>Add-ons>Transformations
Sure.
Why? I´m not sure I understand, it´s two different interfaces.
Hi
right now my problem is that i can’t get communication to usb dongle .. seems i read that one should install modbus TCP as master and modbus serial as slave ??? is there anything else i have overlooked that one needs to install to make usb dongle work
2019-09-29 20:22:07.627 [ERROR] [ui.internal.items.ItemUIRegistryImpl] - transformation throws exception [transformation=org.eclipse.smarthome.transform.map.internal.MapTransformationService@d8a23a, value=4]
org.eclipse.smarthome.core.transform.TransformationException: An error occurred while opening file.
at org.eclipse.smarthome.transform.map.internal.MapTransformationService.internalLoadTransform(MapTransformationService.java:66) ~[?:?]
at org.eclipse.smarthome.transform.map.internal.MapTransformationService.internalLoadTransform(MapTransformationService.java:1) ~[?:?]
at org.eclipse.smarthome.core.transform.AbstractFileTransformationService.transform(AbstractFileTransformationService.java:134) ~[111:org.eclipse.smarthome.core.transform:0.10.0.oh240]
at org.eclipse.smarthome.ui.internal.items.ItemUIRegistryImpl.transform(ItemUIRegistryImpl.java:513) [149:org.eclipse.smarthome.ui:0.10.0.oh240]
at org.eclipse.smarthome.ui.internal.items.ItemUIRegistryImpl.getLabel(ItemUIRegistryImpl.java:426) [149:org.eclipse.smarthome.ui:0.10.0.oh240]
at org.eclipse.smarthome.ui.basic.internal.render.AbstractWidgetRenderer.preprocessSnippet(AbstractWidgetRenderer.java:121) [199:org.eclipse.smarthome.ui.basic:0.10.0.oh240]
at org.eclipse.smarthome.ui.basic.internal.render.TextRenderer.renderWidget(TextRenderer.java:61) [199:org.eclipse.smarthome.ui.basic:0.10.0.oh240]
at org.eclipse.smarthome.ui.basic.internal.render.PageRenderer.renderWidget(PageRenderer.java:194) [199:org.eclipse.smarthome.ui.basic:0.10.0.oh240]
at org.eclipse.smarthome.ui.basic.internal.render.PageRenderer.processChildren(PageRenderer.java:160) [199:org.eclipse.smarthome.ui.basic:0.10.0.oh240]
at org.eclipse.smarthome.ui.basic.internal.render.PageRenderer.processPage(PageRenderer.java:124) [199:org.eclipse.smarthome.ui.basic:0.10.0.oh240]
at org.eclipse.smarthome.ui.basic.internal.servlet.WebAppServlet.service(WebAppServlet.java:209) [199:org.eclipse.smarthome.ui.basic:0.10.0.oh240]
at javax.servlet.http.HttpServlet.service(HttpServlet.java:790) [29:javax.servlet-api:3.1.0]
at org.eclipse.jetty.servlet.ServletHolder.handle(ServletHolder.java:865) [85:org.eclipse.jetty.servlet:9.4.11.v20180605]
at org.eclipse.jetty.servlet.ServletHandler.doHandle(ServletHandler.java:535) [85:org.eclipse.jetty.servlet:9.4.11.v20180605]
at org.ops4j.pax.web.service.jetty.internal.HttpServiceServletHandler.doHandle(HttpServiceServletHandler.java:71) [186:org.ops4j.pax.web.pax-web-jetty:7.2.3]
at org.eclipse.jetty.server.handler.ScopedHandler.handle(ScopedHandler.java:146) [84:org.eclipse.jetty.server:9.4.11.v20180605]
at org.eclipse.jetty.security.SecurityHandler.handle(SecurityHandler.java:548) [82:org.eclipse.jetty.security:9.4.11.v20180605]
at org.eclipse.jetty.server.handler.HandlerWrapper.handle(HandlerWrapper.java:132) [84:org.eclipse.jetty.server:9.4.11.v20180605]
at org.eclipse.jetty.server.handler.ScopedHandler.nextHandle(ScopedHandler.java:257) [84:org.eclipse.jetty.server:9.4.11.v20180605]
at org.eclipse.jetty.server.session.SessionHandler.doHandle(SessionHandler.java:1595) [84:org.eclipse.jetty.server:9.4.11.v20180605]
at org.eclipse.jetty.server.handler.ScopedHandler.nextHandle(ScopedHandler.java:255) [84:org.eclipse.jetty.server:9.4.11.v20180605]
at org.eclipse.jetty.server.handler.ContextHandler.doHandle(ContextHandler.java:1317) [84:org.eclipse.jetty.server:9.4.11.v20180605]
at org.ops4j.pax.web.service.jetty.internal.HttpServiceContext.doHandle(HttpServiceContext.java:293) [186:org.ops4j.pax.web.pax-web-jetty:7.2.3]
at org.eclipse.jetty.server.handler.ScopedHandler.nextScope(ScopedHandler.java:203) [84:org.eclipse.jetty.server:9.4.11.v20180605]
at org.eclipse.jetty.servlet.ServletHandler.doScope(ServletHandler.java:473) [85:org.eclipse.jetty.servlet:9.4.11.v20180605]
at org.eclipse.jetty.server.session.SessionHandler.doScope(SessionHandler.java:1564) [84:org.eclipse.jetty.server:9.4.11.v20180605]
at org.eclipse.jetty.server.handler.ScopedHandler.nextScope(ScopedHandler.java:201) [84:org.eclipse.jetty.server:9.4.11.v20180605]
at org.eclipse.jetty.server.handler.ContextHandler.doScope(ContextHandler.java:1219) [84:org.eclipse.jetty.server:9.4.11.v20180605]
at org.eclipse.jetty.server.handler.ScopedHandler.handle(ScopedHandler.java:144) [84:org.eclipse.jetty.server:9.4.11.v20180605]
at org.ops4j.pax.web.service.jetty.internal.JettyServerHandlerCollection.handle(JettyServerHandlerCollection.java:80) [186:org.ops4j.pax.web.pax-web-jetty:7.2.3]
at org.eclipse.jetty.server.Server.handle(Server.java:531) [84:org.eclipse.jetty.server:9.4.11.v20180605]
at org.eclipse.jetty.server.HttpChannel.handle(HttpChannel.java:352) [84:org.eclipse.jetty.server:9.4.11.v20180605]
at org.eclipse.jetty.server.HttpConnection.onFillable(HttpConnection.java:260) [84:org.eclipse.jetty.server:9.4.11.v20180605]
at org.eclipse.jetty.io.AbstractConnection$ReadCallback.succeeded(AbstractConnection.java:281) [75:org.eclipse.jetty.io:9.4.11.v20180605]
at org.eclipse.jetty.io.FillInterest.fillable(FillInterest.java:102) [75:org.eclipse.jetty.io:9.4.11.v20180605]
at org.eclipse.jetty.io.ChannelEndPoint$2.run(ChannelEndPoint.java:118) [75:org.eclipse.jetty.io:9.4.11.v20180605]
at org.eclipse.jetty.util.thread.strategy.EatWhatYouKill.runTask(EatWhatYouKill.java:333) [87:org.eclipse.jetty.util:9.4.11.v20180605]
at org.eclipse.jetty.util.thread.strategy.EatWhatYouKill.doProduce(EatWhatYouKill.java:310) [87:org.eclipse.jetty.util:9.4.11.v20180605]
at org.eclipse.jetty.util.thread.strategy.EatWhatYouKill.tryProduce(EatWhatYouKill.java:168) [87:org.eclipse.jetty.util:9.4.11.v20180605]
at org.eclipse.jetty.util.thread.strategy.EatWhatYouKill.run(EatWhatYouKill.java:126) [87:org.eclipse.jetty.util:9.4.11.v20180605]
at org.eclipse.jetty.util.thread.ReservedThreadExecutor$ReservedThread.run(ReservedThreadExecutor.java:366) [87:org.eclipse.jetty.util:9.4.11.v20180605]
at org.eclipse.jetty.util.thread.QueuedThreadPool.runJob(QueuedThreadPool.java:762) [87:org.eclipse.jetty.util:9.4.11.v20180605]
at org.eclipse.jetty.util.thread.QueuedThreadPool$2.run(QueuedThreadPool.java:680) [87:org.eclipse.jetty.util:9.4.11.v20180605]
Caused by: java.io.FileNotFoundException: /etc/openhab2/transform/nilan_ventset.map (No such file or directory)
at java.io.FileInputStream.open0(Native Method) ~[?:?]
at java.io.FileInputStream.open(FileInputStream.java:195) ~[?:?]
at java.io.FileInputStream.<init>(FileInputStream.java:138) ~[?:?]
at java.io.FileInputStream.<init>(FileInputStream.java:93) ~[?:?]
at java.io.FileReader.<init>(FileReader.java:58) ~[?:?]
at org.eclipse.smarthome.transform.map.internal.MapTransformationService.internalLoadTransform(MapTransformationService.java:62) ~[?:?]
... 44 more
You’d better be clear about what sort of dongle, there is some confusion here.
Makes no sense in openHAB context, openHAB binding is always the Modbus master whether you choose TCP or serial transport.
You do realise Modbus-TCP is Modbus over ethernet (which can be WiFi), Modbus-RTU is Modbus over serial line (usually RS-485) The binding supports both, at the same time if you wish. But your target slave device wil probably dictate which you actually want.
This is pretty clear (and nothing to do with Modbus)
In some Item or Thing you have specified a transform using a file called nilan_ventset.map, and you either haven’t got such a fie or you haven’t put it in the /transforms/ folder
Hi
it seems complicated trying to follow Kim’s example .. some ideas which file to use in transform ??? more mistakes
2019-09-29 21:44:51.154 [WARN ] [rest.core.item.EnrichedItemDTOMapper] - Failed transforming the state ‘NULL’ on item ‘nilan_AirFlow_InletAct’ with pattern ‘MAP(nilan_ventset.map):%s’: An error occurred while opening file.
2019-09-29 21:44:51.163 [WARN ] [rest.core.item.EnrichedItemDTOMapper] - Failed transforming the state ‘2’ on item ‘Nilan_AirQual_RH_VentLo’ with pattern ‘MAP(nilan_ventset.map):%s’: An error occurred while opening file.
2019-09-29 21:44:51.187 [WARN ] [rest.core.item.EnrichedItemDTOMapper] - Failed transforming the state ‘NULL’ on item ‘nilan_AirFlow_ExhaustAct’ with pattern ‘MAP(nilan_ventset.map):%s’: An error occurred while opening file.
2019-09-29 21:44:51.236 [WARN ] [rest.core.item.EnrichedItemDTOMapper] - Failed transforming the state ‘1’ on item ‘Nilan_AirTemp_IsSummer’ with pattern ‘MAP(nilan_summer_on_off.map):%s’: An error occurred while opening file.
2019-09-29 21:44:51.314 [WARN ] [rest.core.item.EnrichedItemDTOMapper] - Failed transforming the state ‘3’ on item ‘nilan_Control_ModeAct’ with pattern ‘MAP(nilan_control_modeact.map):%s’: An error occurred while opening file.
2019-09-29 21:44:51.321 [WARN ] [rest.core.item.EnrichedItemDTOMapper] - Failed transforming the state ‘0’ on item ‘Nilan_AirFlow_CoolVent’ with pattern ‘MAP(nilan_ventset.map):%s’: An error occurred while opening file.
2019-09-29 21:44:51.336 [WARN ] [rest.core.item.EnrichedItemDTOMapper] - Failed transforming the state ‘1’ on item ‘Nilan_Program_UserFuncSet’ with pattern ‘MAP(nilan_program_userfuncset.map):%s’: An error occurred while opening file.
2019-09-29 21:44:51.344 [WARN ] [rest.core.item.EnrichedItemDTOMapper] - Failed transforming the state ‘2’ on item ‘Nilan_Control_VentSet’ with pattern ‘MAP(nilan_ventset.map):%s’: An error occurred while opening file.
2019-09-29 21:44:51.354 [WARN ] [rest.core.item.EnrichedItemDTOMapper] - Failed transforming the state ‘0’ on item ‘Nilan_Alarm_List_1_ID’ with pattern ‘MAP(nilan_alarmcode_to_string.map):%s’: An error occurred while opening file.
Michael. Forget the transforms error for now.
Concentrate on getting your device online (your dongle). Things are getting out of hand, when you try to fix a later part in the process, but misses the first part.
You simply wont get anyhere untill you have your dongle online and working, even if you do manage to fix the transformation.
In order to provide the help correctly, lets take one step at a time.
First - You said earlier, that you´re using a USB RS485 dongle. Is it online? It has to be online for anything to work. It will look like this in PaperUI, (notice the RED circle).
Is your Modbus Serial Slave Online ?
If not, then this is where we need to focus first before going any futher.
As for the missing transformation file. Its inside the archive I have uploaded it to the bottom of the first post in this thread. But please concentrate on the serial slave first. Then we´ll deal with whatever transformation error you might get later.. Mind you, the modbus will work just fine, even though you get transformation error.
Hi
yes modbus serial slave is online has taken a picture of it and how i have configured it ..